Magnetic Overcurrent Circuit Breaker 808-...
Description
Single pole miniaturised magnetic circuit breakers with unique
high-speed operating mechanism and push/pull on/off manual
actuation. Fitted with electrically separate excitation and switching
circuits, and one pair of auxiliary contacts which close when the
main circuit is open. Also suitable for impulse operation. Designed for
printed circuit board mounting. Low temperature sensitivity.
Typical applications
Printed circuit boards and components, safety and control systems.
808
Ordering information
Type No.
808
fast-acting
Manual release
01 press-to-reset button, blue
B
manual release facility, blue (Standard)
Current ratings
0.01...5 A
808 - B - 5 A
Technical data
Voltage rating
Current ratings
ordering example
Standard current ratings and typical internal resistance values
Current
rating (A)
0.01
0.02
0.03
0.04
0.05
0.08
0.1
0.2
0.3
0.4
0.5
0.6
0.7
Internal
resistance (Ω)
625
170
77
47
29.2
10.3
5.6
1.65
0.89
0.39
0.28
0.198
0.143
Current
rating (A)
0.8
0.9
1
1.2
1.5
2
2.5
3
3.25
4
4.5
5
Internal
resistance (Ω)
0.096
0.085
0.073
0.050
0.031
≤ 0.02
≤ 0.02
≤ 0.02
≤ 0.02
≤ 0.02
≤ 0.02
≤ 0.02
Ambient temperature
Insulation co-ordination
(IEC 60664-1)
Dielectric strength
(UL 1077)
operating area
excitation to
switching circuit
excitation to
auxiliary circuit
Insulation resistance
Interrupting capacity
(o-o-o)
(UL 1077)
Degree of protection
(IEC 60529/DIN 40050)
Vibration
Approvals
Authority
CSA
UL
Max. continuous load
excitation circuit (2-3)
switching circuit 6-7
auxiliary circuit 4-5
Typical life
Voltage ratings
AC 120 V; DC 60 V
DC 60 V
AC 120 V
Current ratings
0.01...5 A
0.01...5 A
0.01...5 A
Shock
Corrosion
Humidity
Mass
Issue C
www.e-t-a.com
DC 24 V (higher voltages to special order)
UL: AC 120 V; DC 60 V
0.01...5 A
(higher current ratings to special order)
2.65 x IN
5A
6,000 operations
at 5 A for switching circuit
-30...+70 °C (-22...+158 °F)
rated impulse
pollution
withstand voltage
degree
1.5 kV
2
test voltage
AC 1,240 V
AC 1,240 V
AC 1,240 V
> 100 MΩ (DC 500 V)
100 A
2,000 A AC 120 V
1,000 A DC 60 V
operating area IP30
terminal area IP00
3 g (57-500 Hz), ± 0.23 mm (10-57 Hz),
to IEC 60068-2-6, test Fc
10 frequency cycles/axis
25 g (11 ms)
to IEC 60068-2-27, test Ea
48 hours at 5 % salt mist,
to IEC 60068-2-11, test Ka
240 hours at 95 % RH
to IEC 60068-2-78, test Cab
approx. 10 g
3-5
3
Dimensions
ø9.3
.366
ø4
.157
4
5
6
7
2-3: excitation circuit
6-7: switching circuit
4-5: auxiliary circuit
5
.197
5
.197
0 ON
5 OFF
.197
808-01
Internal connection diagram
30
1.18
2
3
14
.551
15
.591
0.5
.020
10
.394
15.5
.610
0.6
.024
Typical time/current characteristics at +23 °C/+73.4 °F
10000
3
Trip time in milliseconds
1000
ø9.3
.366
ø4
.157
100
10
5
.197
5
.197
2.5 ON
.098
7.5 OFF
.295
808-B
14
.551
30
1.18
1
15
.591
0.6
.024
0.1
1
2
4
6 8 10
... times rated current
0.5
.020
10
.394
15.5
.610
This is a metric design and millimeter dimensions take precedence ( mm )
inch
All dimensions without tolerances are for reference only. In the interest of improved design,
performance and cost effectiveness the right to make changes in these specifications
without notice is reserved.Product markings may not be exactly as the ordering codes.
Errors and omissions excepted.
3-6
www.e-t-a.com
Issue C
很抱歉,暂时无法提供与“808-B-1A”相匹配的价格&库存,您可以联系我们找货