MicroSmart FC6A PLC
Digital I/O Specifications
KEY FEATURES
• 16 modules to choose from
• Screw or MIL type terminal block
• 8/16/32 points I/O module
SPECIFICATIONS
Input Module Specifications
Part Number
FC6A-N08B1
Input Points
8 (8/1 common)
Rated Input Voltage
Input Voltage Range
Rated Input Current
Input Impedance
OFF Voltage
ON Voltage
OFF Current
ON Current
Input Delay Time (24V DC)
FC6A-N16B1
FC6A-N16B3
16 (16/1 common)
32 (16/1 common)
8 (4/1 common)
24V DC sink/source input signal
0 to 28.8V DC
7 mA/point (24V DC)
5 mA/point (24V DC)
3.4 kΩ
4.4 kΩ
5V maximum
15V minimum
1.2 mA maximum
0.9 mA maximum
4.2 mA minimum (at 15V DC)
3.2 mA minimum (at 15V DC)
Turn ON: 4.1ms, Turn OFF: 4.1ms
Signal Determination Method
Effect of Improper Input
Connection
Cable Length
Turn ON: 25ms, Turn OFF: 30ms
Not needed
Static
Both sink and source input signals can be connected. If any input exceeding the rated value is
applied, permanent damage may be caused.
3m in compliance with electromagnetic immunity
Connector Insertion/
Removal Durability
Applicable Ferrule
100 to 120V AC
0 to 132V AC (50/60 Hz)
17 mA/point (120V AC, 60 Hz)
0.8 kΩ (60 Hz)
20V maximum
79V minimum
Between input terminals in the same common: Not isolated
Between input terminals in different commons: Isolated
Between input terminals and internal circuits: Photocoupler-isolated
External Load for
I/O Interconnection
If any input exceeding the rated value is applied, permanent damage
may be caused.
100 times minimum
1-wire: AI 0.5-8 WH (Phoenix Contact)
2-wire: AI-TWIN 2×0.5-10 (Phoenix Contact)
All Inputs ON
30mA (5V DC)
0mA (24V DC)
40mA (5V DC)
0mA (24V DC)
40mA (5V DC)
0mA (24V DC)
65mA (5V DC)
0mA (24V DC)
40mA (5V DC)
0mA (24V DC)
All Inputs OFF
17mA (5V DC)
0mA (24V DC)
17mA (5V DC)
0mA (24V DC)
17mA (5V DC)
0mA (24V DC)
17mA (5V DC)
0mA (24V DC)
17mA (5V DC)
0mA (24V DC)
Internal Power Consumption
(at 24V DC while all inputs ON)
Weight (approx.)
FC6A-N08A11
Between input terminals: Not isolated
Internal circuit: Photocoupler-isolated
Isolation
Internal
Current Draw
FC6A-N32B3
0.20W
0.27W
0.27W
0.44W
0.27W
110g
105g
75g
110g
110g
1
Relay Output Module Specifications
Part Number
Transistor Output Module Specifications
FC6A-R081
FC6A-R161
Output Points
8 (4/1 common)
16 (8/1 common)
Output Type
1NO
2A per point
7A per common
8A per common
Maximum Load
Current
Minimum Switching
Load
Initial Contact
Resistance
Electrical Life
Mechanical Life
Rated Load
Dielectric Strength
Removal Durability
Applicable
Ferrule
All
outputs
Internal ON
Current
All
Draw
outputs
OFF
Internal Power
Consumption
outputs ON)
Weight (approx.)
FC6A-T08K1
FC6A-T08P1
Part Number
Output Type
Rated Load Voltage
Operating Load Voltage Range
30 mΩ maximum
Maximum Load Current
100,000 operations minimum
(rated load 1,800 operations/hour)
20,000,000 operations minimum
(no load 18,000 operations/hour)
Resistive load: 240V AC 2A, 30V DC 2A
Inductive load: 240V AC 2A (cos ø = 0.4)
30V DC 2A (L/R =7 ms)
Between output and ground terminals: 1,500V AC,
1 minute
Between output terminal and internal circuit:
1,500V AC, 1 minute
Between output terminals (COMs): 1,500V AC, 1
minute
Voltage Drop (ON Voltage)
Inrush Current
Leakage Current
Clamping Voltage
Maximum Lamp Load
Inductive Load
External Current Draw
Overcurrent Protection
Isolation
100 times minimum
Connector Insertion/ Removal Durability
1-wire: AI 0.5-10 (Phoenix Contact)
35mA (5V DC)
50mA (24V DC)
50mA (5V DC)
100mA (24V DC)
17mA (5V DC)
0mA (24V DC)
17mA (5V DC)
0mA (24V DC)
1.44W
2.74W
130g
140g
Applicable Ferrule
All outputs ON
Internal
Current
Draw
FC6A-T16K3
FC6A-T16P3
FC6A-T32K3
FC6A-T32P3
8 (8/1 common)
Output Points
1 mA/ 5V DC (reference value)
FC6A-T16K1
FC6A-T16P1
All outputs OFF
(at 24V DC while all outputs ON)
Turn ON Time
Output
Delay
Turn OFF Time
Weight (approx)
16 (16/1 common)
32 (16/1 common)
FC6A-TK: Transistor sink output
FC6A-TP: Transistor source output
24V DC
19.2 to 28.8V DC
0.5A per point
0.1A per point
3A per common
1A per common
1V maximum (voltage between COM and output terminals when output is on)
1A maximum
0.1mA maximum
Approx. 50V
12W
2.4W
L/R = 10ms (28.8V DC 1Hz)
FC6A-TK: 100 mA maximum, 24V DC (power voltage at the +V terminal)
FC6A-TP: 100 mA maximum, 24V DC (power voltage at the -V terminal)
Transistor Sink Output: No
Transistor Source Output: Yes
Between output terminal and internal circuit: Photocoupler-isolated
Between output terminals: Not isolated
100 times minimum
1-wire: AI 0.5-10 (Phoenix Contact) 2-wire: AI-TWIN 2×0.5-10 (Phoenix Contact)
25mA (5V DC)
30mA (5V DC)
45mA (5V DC)
15mA (24V DC)
25mA (24V DC)
50mA (24V DC)
17mA (5V DC)
17mA (5V DC) 17mA (5V DC)
17mA (5V DC)
0mA (24V DC)
0mA (24V DC) 0mA (24V DC)
0mA (24V DC)
0.53W
0.80W
1.50W
110g
400 μs maximum
450 μs maximum
105g
75g
115g
Mixed I/O Module Specifications
Part Number
Input Points
FC6A-M08BR1
FC6A-M24BR1
4 (4/1 common)
16 (16/1 common)
Rated Input Voltage
Input Voltage Range
0 to 28.8V DC
Rated Input Current
7 mA/point (24V DC)
3.4 kΩ
Input Specification
Input Impedance
5V maximum
OFF Voltage
ON Voltage
15V minimum
OFF Current
1.2 mA maximum
ON Current
Turn ON Time: 4.1ms, Turn OFF Time: 4.1ms
Between input terminals: Not isolated Internal circuit: Photocoupler-isolated
Isolation
Not needed
External Load for I/O Interconnection
Static
Effect of Improper Input Connection
Both sinking and sourcing input signals can be connected. If any input exceeding the rated value is applied, permanent damage may be caused.
Cable Length
4 (4/1 common)
Output Points
8 (4/1 common)
1NO
2A per point
7A per common
Output Type
Minimum Switching Load
30 mΩ maximum
Output Specifications
Initial Contact Resistance
100,000 operations minimum (rated load 1,800 operations/hour)
Electrical Life
Mechanical Life
Rated Load
Dielectric Strength
Connector Insertion/Removal Durability
20,000,000 operations minimum (no load 18,000 operations/hour)
Inductive load: 240V AC 2A (cos ø = 0.4), 30V DC 2A (L/R =7 ms)
Between output and PE terminals: 1,500V AC, 1 minute
Between output terminal and internal circuit: 1,500V AC, 1 minute
Between output terminals (COMs): 1,500V AC, 1 minute
100 times minimum
1-wire: AI 0.5-10 (Phoenix Contact), 2-wire: AI-TWIN 2×0.5-10 (Phoenix Contact)
Applicable Ferrule
Internal Current Draw
All I/Os ON
30mA (5V DC), 25mA (24V DC)
55mA (5V DC), 25mA (24V DC)
All I/Os OFF
17mA (5V DC), 0mA (24V DC)
0.80W
0.97W
120g
165g
(at 24V DC while all I/Os are ON)
Weight (approx.)
2
Temperature derating curves: Input voltage vs. I/O Simultaneous ON Ratio (%)
FC6A-N08B1
FC6A-N16B1
Ambient Temp.
55 ºC
Input Voltage
28.8V
26.4V
24.0V
0V
0%
100%
I/O Simultaneous ON Ration (%)
FC6A-N08A11
Input Voltage
0V
28.8V
26.4V
24.0V
0%
100%
Input Voltage
0V
28.8V
26.4V
24.0V
0V
0%
FC6A-T08P1/FC6A-T16P1
FC6A-T16P3/FC6A-T32P3
V (+)
Internal
Circuit
Internal
Circuit
COM (+ )
Output
50% 70% 90% 100%
Logic
COM (− )
Input Voltage
Ambient Temp.
45 ºC
Ambient
Temp.
55 ºC
28.8V
26.4V
24.0V
0V
100%
0%
70% 100%
Input Internal Circuit
4.3KΩ
Input
COM
Input
3.3KΩ
FC6A-N08A11
COM
Input
2.21
kΩ
COM
Internal Circuit
COM
FC6A-M08BR1/FC6A-M24BR1
Internal Circuit
Internal Circuit
3.3KΩ
Input
FC6A-N16B3/FC6A-N32B3
Internal Circuit
FC6A-N08B1/FC6A-N16B1
DIMENSIONS (all dimensions are in mm)
FC6A-N16B1/FC6A-R161
FC6A-T16K1/FC6A-T16P1
FC6A-J4A1/FC6A-J8A1
FC6A-J4CN1/FC6A-J8CU1
FC6A-L06A1
FC6A-N08B1/FC6A-N08A11/FC6A-R081
FC6A-T08K1/FC6A-T08P1/FC6A-M08BR1
FC6A-J2C1/FC6A-K4A1/FC6A-L03CN1
3.8
23.6
3.8
FC6A-N16B3/FC6A-T16K3
FC6A-T16P3
3.8
23.6
90.0
73.0
5.0
11.7
10.1
73.0
FC6A-M24BR1/FC6A-F2M1
FC6A-F2MR1
30.2
3.8
39.2
4.0
10.1
73. 0
5.0
90.0
90.0
4.0
5.0
4.0
90.0
5.0
90.0
5.0
73.0
FC6A-N32B3/FC6A-T32K3
FC6A-T32P3
3.8
17.6
4.0
4.0
15.8
11.4
Output
V (− )
Overcurrent Protection Element
FC6A-M24BR1
Ambient Temp.
55 ºC
0%
Ambient Temp.
30 ºC
Ambient
Temp.
55 ºC
Input Voltage
0V
70% 100%
0%
28.8V
26.4V
24.0V
FC6A-T08K1/FC6A-T16K1
FC6A-T16K3/FC6A-T32K3
Ambient Temp.
45 ºC
Ambient
Temp.
55 ºC
FC6A-M08BR1
Ambient Temp.
55 ºC
132V
120V
102V
Input Voltage
Output Internal Circuit
73. 0
∗ 9.3 mm when the clamp is pulled out.
IDEC Corporation • 1175 Elko Drive • Sunnyvale, CA 94089 • 800-262-IDEC (4332) • Fax: 408-745-5258 • www.IDEC.com/usa
©2016 IDEC Corporation. All Rights Reserved. FC9Y-DS100-0b PDF only
1603091339