PML-24V150W1AG

PML-24V150W1AG

  • 厂商:

    DELTA(台达)

  • 封装:

    -

  • 描述:

    AC/DC CONVERTER 24V 150W

  • 详情介绍
  • 数据手册
  • 价格&库存
PML-24V150W1AG 数据手册
TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ PMT Highlights & Features • • • • • AC input voltage range selectable by switch (90-132 Vac, 180-264 Vac) Conforms to harmonic current IEC/EN 61000-3-2, Class A High MTBF > 700,000 hrs as per Telcordia SR-332 Versatile configuration options (Enclosed, L Frame) Versatile connector options (Terminal Block, Front Face, Harness) Safety Standards CB Certified for worldwide use Model Number: PMT-24V150W1A☐ Unit Weight: 0.48 kg (1.06 lb) Dimensions (L x W x H): 178 x 97 x 38 mm (7.01 x 3.82 x 1.50 inch) General Description The new PMT series of panel mount power supplies is the latest offering from one of the world’s largest power supply manufacturers and solution providers - Delta. The product offers a wide operating temperature range from -10°C to +70°C and can withstand shock and vibration requirements (in accordance to IEC 60068-2-27 and IEC 60068-2-6 respectively). In addition to features like overvoltage and overload protections, Delta’s PMT series of panel mount power supplies is unlike many other brands in the same price level. The PMT series is designed for cost competitive markets without compromising the quality of the components and product specifications. The series of products has an expected life time of 10 years. This versatile series has three different connector options (Terminal Block, Front Face and Harness) and can also be converted into L Frame (PML) type of power supplies to satisfy different application needs. Model Information PMT Panel Mount Power Supply Model Number Input Voltage Range Rated Output Voltage Rated Output Current PMT-24V150W1A☐☐ 90-132 Vac, 180-264 Vac (Selectable by Switch) 24 Vdc 6.50 A Model Numbering CC Code** PM □– 24V Panel Mount Product Type T – Enclosed L – L Frame* Output Voltage Output Power Single Phase 150W 1 A □ No PFC Connector Type A – Terminal Block G – Front Face* H – Harness* *Options **For Enclosed type with Terminal Block A 1 G H All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) □ Blank – Without connector cover A – With connector cover B – With conformal coating TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Specifications Input Ratings / Characteristics Nominal Input Voltage 100-120 Vac, 200-240 Vac (Selectable by Switch) Input Voltage Range 90-132 Vac, 180-264 Vac (Selectable by Switch) Nominal Input Frequency 50-60 Hz Input Frequency Range 47-63 Hz Input Current < 3.00 A @ 115 Vac, < 2.00 A @ 230 Vac Efficiency at 100% Load Max Power Dissipation 89.0% typ. @ 230 Vac 0% load 0.45 W typ. @ 230 Vac 100% load 18.6 W typ. @ 230 Vac Max Inrush Current (Cold Start) < 45 A @ 230 Vac Leakage Current < 0.5 mA @ 240 Vac Output Ratings / Characteristics* Nominal Output Voltage 24 Vdc Factory Set Point Tolerance 24 Vdc ± 1% Output Voltage Adjustment Range 22.8-27.6 Vdc Output Current 6.50 A (156 W max.) Output Power 156 W Line Regulation ± 0.5% typ. (@ 100-132 Vac & 200-264 Vac) Load Regulation ± 0.5% typ. (@ 100-132 Vac & 200-264 Vac ) PARD** (20MHz) < 120 mVpp Rise Time < 30 ms @ 115 Vac, < 20 ms @ 230 Vac (100% load) Start-up Time < 1200 ms @ 115 Vac, < 800 ms @ 230 Vac (100% load) Hold-up Time > 20 ms @ 115 Vac, > 24 ms @ 230 Vac (100% load) Dynamic Response (Overshoot & Undershoot O/P Voltage) ± 5% @ 0-100% load (Slew Rate: 0.1 A/μS, 50% duty cycle @ 10 KHz) Start-up with Capacitive Loads 8,000 µF Max *For power de-rating from 50°C to 70°C, see power de-rating on page 3. **PARD is measured with an AC coupling mode, 5cm wires, and in parallel with 0.1µF ceramic capacitor & 47µF electrolytic capacitor. 2 All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Mechanical Case Chassis / Cover Aluminium / SGCC Dimensions (L x W x H) 178 x 97 x 38 mm (7.01 x 3.82 x 1.50 inch) Unit Weight 0.48 kg (1.06 lb) Indicator Green LED (DC OK) Cooling System Convection Terminal Wire PM☐-24V150W1AA☐ M3.5 x 7 Pins (Rated 300 V/15 A) PM☐-24V150W1AG M3.5 x 7 Pins (Rated 300 V/20 A) PM☐-24V150W1AH I/P (JWT): A3963WV2-5P-A O/P (JWT): A3963WV2-7P-U PM☐-24V150W1AA☐ AWG 22-12 PM☐-24V150W1AG PM☐-24V150W1AH Noise (1 Meter from power supply) AWG 22-18 (For the recommended Mating Connector and Terminal, please refer to the Table on Page 8) Sound Pressure Level (SPL) < 25 dBA Environment Surrounding Air Temperature Operating -10°C to +70°C Storage -25°C to +85°C Power De-rating Operating Humidity > 50°C de-rate power by 2.5% / °C < 100 Vac de-rate power by 3% / 1V 5 to 95% RH (Non-Condensing) Operating Altitude 0 to 5,000 Meters (16,400 ft.) Shock Test Non-Operating IEC 60068-2-27, Half Sine: 50G for a duration of 11ms, 3 times per direction, 18 times in total Vibration Non-Operating IEC 60068-2-6, Random: 5Hz to 500Hz @ 2.09Grms, 20 min per axis for all X, Y, Z direction Over Voltage Category II Pollution Degree 2 Protections Overvoltage 115-135%, Hiccup Mode, Non-Latching (Auto-Recovery) Overload / Overcurrent 110-150%, Hiccup Mode, Non-Latching (Auto-Recovery) Over Temperature Hiccup Mode, Non-Latching (Auto-Recovery when the fault is removed) Short Circuit Hiccup Mode, Non-Latching (Auto-Recovery when the fault is removed) Internal Fuse at L pin T5AH Degree of Protection IPX0 Protection Against Shock Class I with PE* connection *PE: Primary Earth 3 All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Reliability Data MTBF > 700,000 hrs as per Telcordia SR-332 I/P: 100 Vac, O/P: 100% load, Ta: 35°C Expected Cap Life Time 10 years (115 Vac, 50% load @ 40°C) Safety Standards / Directives Safety Entry Low Voltage Electrical Safety SELV TUV Bauart UL/cUL recognized CB scheme BIS CE UKCA EN 60950-1, EN 62368-1 UL 60950-1 and CSA C22.2 No. 60950-1 (File No. E131881) UL 62368-1 and CSA C22.2 No. 62368-1 (File No. E131881) IEC 60950-1, IEC 62368-1 IS 13152-1 In conformance with EMC Directive 2014/30/EU and Low Voltage Directive 2014/35/EU In conformance with Electromagnetic Compatibility Regulations 2016 and Electrical Equipment (Safety) Regulations 2016 Galvanic Isolation Input to Output 3.0 KVac Input to Ground 1.5 KVac Output to Ground 0.5 KVac EMC Emissions (CE & RE) CISPR 32, EN/BS EN 55032, FCC Title 47: Class B Immunity EN/BS EN 55024 Electrostatic Discharge IEC 61000-4-2 Radiated Field IEC 61000-4-3 Electrical Fast Transient / Burst IEC 61000-4-4 Level 2 Criteria A1) 2 kV Surge IEC 61000-4-5 Conducted IEC 61000-4-6 Level 3 Criteria A1) Common Mode2): 2 kV Differential Mode3): 1 kV Level 2 Criteria A1) 150 kHz-80 MHz, 3 Vrms Power Frequency Magnetic Fields IEC 61000-4-8 Voltage Dips and Interruptions IEC 61000-4-11 Level 4 Criteria A1) Air Discharge: 15 kV Contact Discharge: 8 kV Level 2 Criteria A1) 80 MHz-1 GHz, 3 V/M with 1 kHz tone / 80% modulation Criteria A1) 1 A/Meter 100% dip; 1 cycle (20 ms); Self Recoverable Harmonic Current Emission IEC/EN/BS EN 61000-3-2, Class A Voltage Fluctuation and Flicker IEC/EN/BS EN 61000-3-3 1) Criteria A: Normal performance within the specification limits 2) Asymmetrical: Common mode (Line to earth) 3) Symmetrical: Differential mode (Line to line) 4 All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Block Diagram Device Description PMT-24V150W1AA☐: Terminal Block PMT-24V150W1AG: Front Face PMT-24V150W1AH: Harness 1) 2) 3) 4) 5 Input & Output terminal block connector DC voltage adjustment potentiometer DC OK control LED (Green) AC selectable switch All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Dimensions L x W x H: 178 x 97 x 38 mm (7.01 x 3.82 x 1.50 inch) 6 All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Engineering Data Output Load De-rating VS Surrounding Air Temperature Note 1. 2. 3. Fig. 1 De-rating for Vertical and Horizontal Mounting Orientation > 50°C de-rate power by 2.5% / °C 4. 5. Power supply components may degrade, or be damaged, when the power supply is continuously used outside the shaded region, refer to the graph shown in Fig. 1. If the output capacity is not reduced when the surrounding air temperature exceeds its specification as defined on Page 3 under “Environment”, the device will run into Over Temperature Protection. When activated, the output voltage will go into bouncing mode and will recover when the surrounding air temperature is lowered or the load is reduced as far as necessary to keep the device in working condition. In order for the device to function in the manner intended, it is also necessary to keep a safety distance of 20 mm (0.79 inch) with adjacent units while the device is in operation. Depending on the surrounding air temperature and output load delivered by the power supply, the device can be very hot! If the device has to be mounted in any other orientation, please contact info@deltapsu.com for more details. Output Load De-rating VS Input Voltage  No output power de-rating for the input voltage from 100Vac to 132Vac & 200Vac to 264Vac ■ L Frame / Enclosed 7 All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Assembly & Installation Mounting holes for power supply assembly onto the mounting surface. Ⓐ The power supply shall be mounted on minimum 2 mounting holes using M3 screw minimum 5mm (0.20 inch) length. Ⓑ This surface belongs to customer’s end system or panel where the power supply is mounted. Ⓒ Connector Side Mounting (Vertical) Base Mounting (Vertical) Fig. 2 • • Side Mounting (Horizontal) Recommended Mounting Orientations PM☐-24V150W1AA☐ / PM☐-24V150W1AG: Use flexible cable (stranded or solid) of AWG No. 22-12. The torque at the connector shall not exceed 13Kgf.cm (11.23 lbf.in). The insulation stripping length should not exceed 0.275” or 7mm. PM☐-24V150W1AH: Please refer the table below for the recommended mating connector, terminal and AWG wire size. Header (Board Mounting) Mating Connector Input (JWT) A3963WV2-5P-A A3963H02-5P Output (JWT) A3963WV2-7P-U A3963H02-7P Terminal AWG A3963T0P-2 22-18 Installation of Mounting Accessories Fig. 3 Mounting Hole Locations With reference to Fig. 3, the device should be mounted on a sturdy heat conducting surface with minimum of 4 mounting holes for base mounting or 3 mounting holes for side mounting. Use M3 screws only. 8 All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□   Fig. 4 Only use M3 screw ≤ 4.0 mm (0.16 inch) through the base and side mounting holes. This is to keep a safe distance between the screw and internal components. Recommended mounting tightening torque: 4~7 Kgf.cm (3.47~6.08 lbf.in). Mounting Screw Safety Instructions • • • • • • • • • 9 Must select correct AC input voltage before turning on (Refer to the “Device Description” on Page 5). If user’s mounting orientation is not according to the recommended mounting orientations, please consult Delta for further information. To ensure sufficient convection cooling, always maintain a safety distance of ≥ 20 mm (0.79 inch) from all ventilated surfaces while the device is in operation. The device is not recommended to be placed on low thermal conductive surfaces, for example, plastics. The enclosure of the device can become very hot depending on the ambient temperature and load of the power supply. Do not touch the device while it is in operation or immediately after power is turned OFF. Risk of burning! Do not touch the terminals while power is being supplied. Risk of electric shock. Prevent any foreign metal, particles or conductors from entering the device through the openings during installation. It may cause electric shock, safety hazard, fire and/or product failure. The power supply must be mounted by metal screws onto a grounded metal surface. It is also highly recommended that the Earth terminal on the connector be connected to the grounded metal surface. Warning (For Standard Terminal Block and Front Face Terminal Block products): When connecting the device, secure Earth connection before connecting L and N. When disconnecting the device, remove L and N connections before removing the Earth connection. All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Functions Start-up Time The time required for the output voltage to reach 90% of its final steady state set value, after the input voltage is applied. Rise Time The time required for the output voltage to change from 10% to 90% of its final steady state set value. Hold-up Time Time between the collapse of the AC input voltage, and the output falling to 95% of its steady state set value. ■ Graph illustrating the Start-up Time, Rise Time, and Hold-up Time Inrush Current Dynamic Response Inrush current is the peak, instantaneous, input current measured and, occurs when the input voltage is first applied. For AC input voltages, the maximum peak value of inrush current will occur during the first half cycle of the applied AC voltage. This peak value decreases exponentially during subsequent cycles of AC voltage. The power supply output voltage will remains within ±5% of its steady state value, when subjected to a dynamic load from 0 to 100% of its rated current. 10 ■ 50% duty cycle / 5Hz to 10KHz All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Overload & Overcurrent Protections (Auto-Recovery) Overvoltage Protection (Auto-Recovery) The power supply’s Overload (OLP) and Overcurrent (OCP) Protections will be activated when output current exceeds 110150% of IO (Max load). In such occurrence, the VO will start to droop and once the power supply has reached its maximum power limit, the protection is activated and the power supply will go into “Hiccup mode” (Auto-Recovery). The power supply will recover once the fault condition of the OLP and OCP is removed and IO is back within the specifications. The power supply’s overvoltage circuit will be activated when its internal feedback circuit fails. The output voltage shall not exceed its specifications defined on Page 3 under “Protections”. Over Temperature Protection (Auto-Recovery) It is not recommended to prolong the duration of IO when it is 100%, since it may cause damage to the PSU. As described in load de-rating section, the power supply also has Over Temperature Protection (OTP). In the event of a higher operating temperature at 100% load, the power supply will run into OTP when the operating temperature is beyond what is recommended in the de-rating graph. When activated, the output voltage will go into bouncing mode until the temperature drops to its normal operating temperature as recommended in the de-rating graph. Short Circuit Protection (Auto-Recovery) The power supply’s output OLP/OCP function also provides protection against short circuits. When a short circuit is applied, the output current will operate in “Hiccup mode”, as shown in the illustration in the OLP/OCP section on this page. The power supply will return to normal operation after the short circuit is removed. 11 All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Operating Mode  Redundant Operation In order to ensure proper redundant operation for the power supply units (PSUs), the output voltage difference between the two units must be kept at 0.45~0.50V for these 24V supplies. Follow simple steps given below to set them up for the redundant operation: Step 1. Measure output voltage of PSU 1 and PSU 2. If PSU 1 is the master unit, then VO of PSU 1 must be higher than PSU 2. In order to set the output voltage, individually connect each power supply to 50% of rated load at any line voltage from 85-264Vac, and set the PSU 1 and PSU 2 output voltage. Step 2. Connect the power supply units PSU 1 and PSU 2 to Vin 1 & Vin 2, respectively, of the DRR-20N (or 20A) module shown on the right of above diagram. PSU 1 PSU 2 DRR-20N or DRR-20A LOAD Terminal Com KEY + Output – Common Signal DC OK Signal Terminal N L (L1) N (L2) PE Fig. 5 Redundancy Operation Connection Diagram Step 3. Connect the system load from Vout. Please note that output voltage Vout from DRR module will be = VO (output voltage of power supply) – Vdrop* (in DRR module). *Vdrop will vary from 0.60V to 0.90V (Typical 0.65V) depending on the load current and surrounding air temperature.  Parallel Operation The power supply units (PSUs) can also be used for parallel operation in order to increase the output power. The difference in output voltage between the two units must be kept to within 25mV of each other. This difference must be verified with the same output load connected independently to each unit. Parameters such as EMI, inrush current, leakage current, PARD, start up time will be different from those on the datasheet, when two units are connected in parallel. The user will need to verify that any differences will still allow the two power supplies connected in parallel will work properly in their product/application. Fig. 6 12 Parallel Operation Connection Diagram All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08) TECHNICAL DATASHEET PMT Panel Mount Power Supply 24 V 150 W 1 Phase / PMT-24V150W1A□□ Others PFC – Norm EN 61000-3-2 Line Current Harmonic content Typically, the input current waveform is not sinusoidal due to the periodical peak charging of the input capacitor. In industrial environment, complying with EN 61000-3-2 is only necessary under special conditions. Complying to this standard can have some technical drawbacks, such as lower efficiency as well as some commercial aspects such as higher purchasing costs. Frequently, the user does not profit from fulfilling this standard, therefore, it is important to know whether it is mandatory to meet this standard for a specific application. Attention Delta provides all information in the datasheets on an “AS IS” basis and does not offer any kind of warranty through the information for using the product. In the event of any discrepancy between the information in the catalog and datasheets, the datasheets shall prevail (please refer to www.DeltaPSU.com for the latest datasheets information). Delta shall have no liability of indemnification for any claim or action arising from any error for the provided information in the datasheets. Customer shall take its responsibility for evaluation of using the product before placing an order with Delta. Delta reserves the right to make changes to the information described in the datasheets without notice. Manufacturer and Authorized Representatives Information Manufacturer Thailand Delta Electronics (Thailand) PCL. 909 Pattana 1 Rd., Muang, Samutprakarn, 10280 Thailand Taiwan Delta Electronics, Inc. 3 Tungyuan Road, Chungli Industrial Zone, Taoyuan County 32063, Taiwan Authorized Representatives The Netherlands Delta Greentech (Netherlands) B.V. Zandsteen 15, 2132 MZ Hoofddorp, The Netherlands 13 United Kingdom Delta Electronics Europe Limited 1 Redwood Court, Peel Park Campus, East Kilbride, Glasgow, G74 5PF, United Kingdom All parameters are specified at 25°C ambient and AC input unless otherwise indicated. www.DeltaPSU.com (February 2022, Rev. 08)
PML-24V150W1AG
物料型号:PMT-24V150W1A□□

器件简介:PMT系列电源供应器由Delta生产,提供宽广的工作温度范围(-10°C至+70°C),并可承受震动和冲击要求。具有过电压和过载保护功能,设计寿命为10年。

引脚分配:根据不同型号,提供3种不同的连接器选项:端子块(Terminal Block)、前面板(Front Face)和束线(Harness)。

参数特性: - 输入电压范围:90-132Vac或180-264Vac,可通过开关选择。 - 额定输出电压:24Vdc。 - 额定输出电流:6.50A。 - 效率:在230Vac时典型值为89.0%。 - 最大功耗:在0%负载时为0.45W,在100%负载时为18.6W。 - 启动时间:在115Vac时小于1200ms,在230Vac时小于800ms。

功能详解: - 电源供应器具有多种保护功能,包括过电压、过载/过电流、过温度、短路保护,并且具有自动恢复功能。 - 提供冗余操作和并联操作模式,以增加输出功率或确保电源供应的可靠性。

应用信息:适用于需要高可靠性和灵活性的工业和商业应用。

封装信息:尺寸为178 x 97 x 38 mm(7.01 x 3.82 x 1.50 inch),重量为0.48 kg(1.06 lb)。
PML-24V150W1AG 价格&库存

很抱歉,暂时无法提供与“PML-24V150W1AG”相匹配的价格&库存,您可以联系我们找货

免费人工找货