CFP-AO-200 数据手册
Analog Output Modules for Compact FieldPoint NI cFP-AO-200, NI cFP-AO-210 • 8 voltage or current outputs • 0 to 10 V • 0 to 20, 4 to 20 mA • 12-bit resolution • Output ranges software-configurable per channel • 2,300 Vrms bank isolation for transient overvoltage protection • Hot-swappable with autoconfiguration • -40 to 70 °C operating range Module cFP-AO-200 cFP-AO-210 1The Input Channels 8 8 Resolution 12 bits 12 bits Output Types Current Voltage Output Ranges (Software Configurable per Channel) 0 to 20 mA, 4 to 20 mA 0 to 10 V (up to 10 mA/ch) All Channel Update Rate1 200 Hz 200 Hz all-channel update rate refers to the time the module takes to sample all channels. The overall system update rate is affected by other factors, such as the aggregate module update rate and software loop rate. To calculate the system update rate, visit ni.com/info and enter “systemrate.” Overview National Instruments cFP-AO-2xx devices are versatile analog output modules for Compact FieldPoint that you can use to control valves, gauges, and other industrial actuators. All modules include overranging and onboard diagnostics to ensure trouble-free installation and maintenance. The NI cFP-AO-2xx modules come with NIST-traceable calibration certificates, ensuring accurate and reliable analog control. The cFP-AO-210 includes eight 0 to 10 V output channels, generated with a 12-bit DAC. Each channel provides a voltage source capable of supplying up to 1 mA. You can obtain up to 10 mA by powering the cFP-AO-210 with an optional external power supply of 15 to 30 VDC. Isolation The cFP-AO-2xx modules feature optical bank isolation with 2,300 Vrms of breakdown isolation. They do not have channel-to-channel isolation. Smart I/O Modules With cFP-AO-2xx modules, you can directly connect to your industrial actuators or units under test and get high-accuracy control. The I/O modules calibrate and scale engineering units to sensor signals, as well as perform self-diagnostics to detect problems with the module or with the wiring such as open current loops. With cFP-AO-2xx modules, your software application writes an engineering value to the I/O module, eliminating the error-prone step of converting voltage or current to binary values. The cFP-AO-2xx modules have an update rate of 200 Hz. Overall data throughput to the controller or PC depends on the software loop speeds and the network speeds. The cFP-AO-200 includes eight 0 to 20 mA or 4 to 20 mA analog output channels, generated with a 12-bit DAC. Each output channel features a monitoring circuit and LED indicator for open current loop detection. The cFP-AO-200 requires an external power supply that provides 5 to 24 VDC. Field I/O Connections Compact FieldPoint modules include a built-in power distribution bus that provides multiple power connections on the module. A field-wired power supply connected to the voltage (V) and common (C) terminals is internally connected to a power distribution bus that offers additional breakout terminals for voltage supply (VSUP) and common (COM). These terminals deliver a convenient way to distribute power to field devices that require external power. The cFP-AO-200 has: • 8 current output terminals (IOUT) • 16 common terminals (COM) • 8 power connections for field devices or current loops (VSUP) The cFP-AO-210 has: • 8 voltage output terminals (VOUT) • 16 common terminals (COM) • 8 power connections for field devices or current loops (VSUP) Analog Output Modules for Compact FieldPoint + External 15 to 30 VDC Supply + – C V VSUP Current Limit VOUT COM VSUP VSUP + – cFP-AO-210 Figure 1. Wiring Schematic for the cFP-AO-210 Module V C – Loop Supply VSUP + – V+ Vin 3-wire device requiring COM power IOUT Load COM Current Limit VOUT COM Load requiring up to 10 mA current IOUT 3-wire device requiring power COM cFP-AO-200 Figure 2. Wiring Schematic for the cFP-AO-200 Module Ordering Information NI cFP-AO-200 ....................................................................777318-200 NI cFP-AO-210 ....................................................................777318-210 Recommended Compact FieldPoint System Products NI cFP-2120 ......................................................................777317-2120 NI cFP-BP-4 ............................................................................778617-04 NI cFP-CB-1............................................................................778618-01 NI PS-5 power supply............................................................778805-90 NI Developer Suite Professional Control Edition ....................777906-03 BUY NOW! For complete product specifications, pricing, and accessory information, call 800 813 3693 (U.S.) or go to ni.com/compactfieldpoint. BUY ONLINE a t ni.com o r CALL 800 813 3693 (U.S.) 2 Analog Output Modules for Compact FieldPoint Physical Characteristics LED indicators POWER (green) ............................... Power on and self-test passed READY (green) ................................ Module configured and ready Fault status (red)............................. Open circuit (cFP-AO-200) or current limit (cFP-AO-210) on channel Dimensions.......................................... 127.0 by 65.9 by 23.9 cm (5.00 by 2060 by 0.94 in.) Weight cFP-AO-200 ..................................... 113 g (4.0 oz) cFP-AO-210 ..................................... 115 g (4.1 oz) Specifications Typical for -40 to 70 °C unless otherwise noted. Output Characteristics Number of channels............................ 8 single-ended DAC resolution.................................... 12 bits, 1 in 4,096 Current Output (cFP-AO-200) Output range ....................................... 0 to 20 or 4 to 20 mA, programmable (0 to 21 or 3.5 to 21 mA with overranging) Output type ......................................... Current source (external loop power required) External loop power............................ 5 to 24 VDC Internal voltage drop........................... 3 V Resistive load .......................................... Up to 1 kΩ with 24 VDC supply, up to 100 Ω with 5 V supply Protection and error detection............ Short-circuit and open-circuit Default power-up state....................... 0 mA Resolution ........................................... 6 µA Power Requirement Power from network module cFP-AO-200 ..................................... 350 mW Environment Operating temperature ....................... -40 to 70 °C Storage temperature........................... -55 to 85 °C Relative humidity ................................ 10 to 90%, noncondensing Voltage Output (cFP-AO-210) Output range ....................................... 0 to 10 V (0 to 10.2 V with overranging) Output type ......................................... Voltage source (external power optional) External power supply ........................ 15 to 30 VDC Internal voltage drop........................... 3 V Current drive ....................................... 1 mA sourcing or sinking, 10 mA sourcing with external power supply Overvoltage protection ....................... -10 to 20 V Default power-up state....................... 0 V Resolution ........................................... 2.5 mA Shock and Vibration Operating vibration, random (IEC 60068-2-64) ............................. 10 to 500 Hz, 5 grms Operating vibration, sinusoidal (IEC 60068-2-6) ............................... 10 to 500 Hz, 5 g Operating shock (IEC 60068-2-27) ............................. 50 g, 3 ms half sine, 18 shocks at 6 orientations; 30 g, 11 ms half sine, 18 shocks at 6 orientations Isolation Voltage Maximum isolation voltage ................ 250 Vrms, Installation Category II Channel-to-channel isolation.............. No isolation between channels Transient overvoltage.......................... 2,300 Vrms Accuracy Absolute accuracy (cFP-AO-200)......... Gain error (cFP-AO-210) ...................... Offset error (cFP-AO-210).................... Monotonicity ....................................... Offset temperature coefficient cFP-AO-200 ..................................... cFP-AO-210 ..................................... Gain temperature coefficient cFP-AO-200 ..................................... cFP-AO-210 ..................................... 0.1% typ, 0.3% max 0.2% typ, 0.4% max 4 mV typ, 14 mV max Guaranteed over temperature range 50 nA/°C 70 µV/°C 40 ppm/°C 20 ppm/°C Dynamic Characteristics Maximum update rate ........................ 200 updates/s Slew rate cFP-AO-200 ..................................... 0.4 mA/µs cFP-AO-210 ..................................... 0.5 V/µs BUY ONLINE a t ni.com o r CALL 800 813 3693 (U.S.) 3 Analog Output Modules for Compact FieldPoint Safety and Compliance Safety This product is designed to meet the requirements of the following standards of safety for electrical equipment for measurement, control, and laboratory use: • IEC 61010-1, EN 61010-1 • UL 61010-1, CSA 61010-1 Note: For UL and other safety certifications, refer to the product label or visit ni.com/certification, search by model number or product line, and click the appropriate link in the Certification column. Electromagnetic Compatibility This product is designed to meet the requirements of the following standards of EMC for electrical equipment for measurement, control, and laboratory use: • EN 61326 EMC requirements; Minimum Immunity • EN 55011 Emissions; Group 1, Class A • CE, C-Tick, ICES, and FCC Part 15 Emissions; Class A Note: For EMC compliance, operate this device according to product documentation. CE Compliance This product meets the essential requirements of applicable European Directives, as amended for CE marking, as follows: • 2006/95/EC; Low-Voltage Directive (safety) • 2004/108/EC; Electromagnetic Compatibility Directive (EMC) Note: Refer to the Declaration of Conformity (DoC) for this product for any additional regulatory compliance information. To obtain the DoC for this product, visit ni.com/certification, search by model number or product line, and click the appropriate link in the Certification column. Waste Electrical and Electronic Equipment (WEEE) EU Customers: At the end of their life cycle, all products must be sent to a WEEE recycling center. For more information about WEEE recycling centers and National Instruments WEEE initiatives, visit ni.com/environment/weee.htm. BUY ONLINE a t ni.com o r CALL 800 813 3693 (U.S.) 4 NI Services and Support IN TA PL SERVICE NEEDS LO Y V DE NI has the services and support to meet your needs around the globe and through the application life cycle – from planning and development through deployment and ongoing maintenance. We offer services and service levels to meet customer requirements in research, design, validation, and manufacturing. Visit ni.com/services. Local Sales and Technical Support In offices worldwide, our staff is local to the country, giving you access to engineers who speak your language. NI delivers industry-leading technical support through online knowledge bases, our applications engineers, and access to 14,000 measurement and automation professionals within NI Developer Exchange forums. Find immediate answers to your questions at ni.com/support. We also offer service programs that provide automatic upgrades to your application development environment and higher levels of technical support. Visit ni.com/ssp. MA IN Training and Certification NI training is the fastest, most certain route to productivity with our products. NI training can shorten your learning curve, save development time, and reduce maintenance costs over the application life cycle. We schedule instructor-led courses in cities worldwide, or we can hold a course at your facility. We also offer a professional certification program that identifies individuals who have high levels of skill and knowledge on using NI products. Visit ni.com/training. EL OP AN Professional Services Our NI Professional Services team is composed of NI applications and systems engineers and a worldwide National Instruments Alliance Partner program of more than 600 independent consultants and integrators. Services range from start-up assistance to turnkey system integration. Visit ni.com/alliance. OEM Support We offer design-in consulting and product integration assistance if you want to use our products for OEM applications. For information about special pricing and services for OEM customers, visit ni.com/oem. P DE Hardware Services NI Factory Installation Services NI Factory Installation Services (FIS) is the fastest and easiest way to use your PXI or PXI/SCXI combination systems right out of the box. Trained NI technicians install the software and hardware and configure the system to your specifications. NI extends the standard warranty by one year on hardware components (controllers, chassis, modules) purchased with FIS. To use FIS, simply configure your system online with ni.com/pxiadvisor. Calibration Services NI recognizes the need to maintain properly calibrated devices for high-accuracy measurements. We provide manual calibration procedures, services to recalibrate your products, and automated calibration software specifically designed for use by metrology laboratories. Visit ni.com/calibration. Repair and Extended Warranty NI provides complete repair services for our products. Express repair and advance replacement services are also available. We offer extended warranties to help you meet project life-cycle requirements. Visit ni.com/services. ni.com • 800 813 3693 National Instruments • info@ni.com *351577A-01* 351577A-01 2007-9290-161-101-D ©2008 National Instruments Corporation. All rights reserved. FieldPoint, National Instruments, National Instruments Alliance Partner, NI, ni.com, NI Developer Suite, and SCXI are trademarks of National Instruments. Other product and company names listed are trademarks or trade names of their respective companies. A National Instruments Alliance Partner is a business entity independent from NI and has no agency, partnership, or joint-venture relationship with NI.
CFP-AO-200
1. 物料型号: - NI cFP-AO-200 - NI cFP-AO-210

2. 器件简介: - NI cFP-AO-2xx系列是用于Compact FieldPoint的模拟输出模块,可用于控制阀门、仪表和其他工业执行器。所有模块均包含超量程和板载诊断功能,确保安装和维护无忧。这些模块附带NIST可追溯的校准证书,确保模拟控制的准确性和可靠性。

3. 引脚分配: - cFP-AO-200: - 8个电流输出端子(IOUT) - 16个共用端子(COM) - 8个现场设备或电流环路的电源连接(V_SUP) - cFP-AO-210: - 8个电压输出端子(VOUT) - 16个共用端子(COM) - 8个现场设备或电流环路的电源连接(V_SUP)

4. 参数特性: - 8路电压或电流输出 - 0至10V和0至20mA、4至20mA的输出范围 - 12位分辨率 - 每个通道的输出范围软件可配置 - 2300V/ms的银行隔离,用于瞬态过电压保护 - 支持热插拔和自动配置 - 工作温度范围-40至70°C

5. 功能详解: - cFP-AO-2xx模块可以直接连接到工业执行器或被测单元,并实现高精度控制。I/O模块将工程单位校准和缩放到传感器信号,并执行自诊断以检测模块或接线问题,如开路电流环路。cFP-AO-2xx模块的更新率为200Hz,整体数据吞吐量取决于软件循环速度和网络速度。

6. 应用信息: - 用于控制阀门、仪表和其他工业执行器。

7. 封装信息: - 尺寸:127.0 mm x 65.9 mm x 23.9 cm(5.00 in x 2060 in x 0.94 in) - 重量:cFP-AO-200为113g(4.0 oz),cFP-AO-210为115g(4.1 oz)
CFP-AO-200 价格&库存

很抱歉,暂时无法提供与“CFP-AO-200”相匹配的价格&库存,您可以联系我们找货

免费人工找货
CFP2-1FC4-AW
  •  国内价格
  • 1+14.448

库存:0

CFP2-1FC6-AW
  •  国内价格
  • 1+17.888
  • 10+16.512
  • 30+16.2368
  • 100+15.4112

库存:0

LL60PW
  •  国内价格
  • 50+0.07194
  • 600+0.05603
  • 1200+0.05519
  • 3000+0.0472

库存:2950

T-1N4148W
  •  国内价格
  • 50+0.0644
  • 600+0.05051
  • 1200+0.04975
  • 3000+0.04278

库存:2655

MM1Z39BW
    •  国内价格
    • 50+0.09982
    • 600+0.07599
    • 1200+0.07485
    • 3000+0.06274

    库存:6000

    BZT52C2V0W
      •  国内价格
      • 50+0.092
      • 600+0.07112
      • 1200+0.07005
      • 3000+0.05952

      库存:5800

      BZT52C4V7W
      •  国内价格
      • 50+0.09007
      • 600+0.06918
      • 1200+0.06814
      • 3000+0.05759

      库存:6000

      BZT52C8V2W
      •  国内价格
      • 50+0.045
      • 500+0.0405
      • 5000+0.0375
      • 10000+0.036
      • 30000+0.0345
      • 50000+0.0336

      库存:1600

      BZT52C18W
      •  国内价格
      • 50+0.07903
      • 600+0.06017
      • 1200+0.05927
      • 3000+0.04968

      库存:2750

      BZT52C3V6W
      •  国内价格
      • 50+0.08807
      • 600+0.0691
      • 1200+0.06841
      • 3000+0.0585

      库存:4900