TMC 7... and TMC 8... Thermal magnetic UL Listed and UL Recognized miniature circuit breakers Data sheet 3644_en_C 1 © PHOENIX CONTACT 2018-11-08 Description TMC 8... miniature circuit breakers (MCB) are UL 489 Listed to provide branch overload and short-circuit protection. An interrupt capacity of 10 kAIC at up to 277/480 V AC and 125 V DC makes the TMC 8... ideal for a wide range of applications that require a UL 489 Listed circuit breaker. TMC 7... miniature circuit breakers are UL 1077 Recognized and provide supplemental overload and shortcircuit protection. Short-circuit current ratings range from 5 kAIC to 7.5 kAIC, depending upon the supply voltage. The circuit breakers are available in 1-, 2-, and 3-pole configurations with B, C, and D trip curve options, making them ideal for a wide range of applications. They are 17.6 mm wide (per pole) and mount on 35 mm NS35 rail. Available accessories include an auxiliary contact, alarm contact, shunt trips, and busbars. The TMC 7... is UL Recognized for the U.S. and Canada. The TMC 8... is UL Listed for the U.S. and Canada. Both products lines carry the CE mark. 1.1 Typical applications TMC 7/8... circuit breakers are suitable for protection of – cables – motors – generators and transformers – thyristors – silicon rectifiers – computers and peripheral equipment – industrial process control systems – telecommunications equipment – power supplies 1.2 – – – – – – – – Features TMC 7... is UL 1077 Recognized TMC 8... is UL 489 Listed 1-, 2-, and 3-pole configurations Current ratings of 1 to 63 A Available with B, C, and D trip curves Visual status indication Trip-free, snap-action mechanism cannot be manually overridden in an overload situation Full range of bus bars and accessories This document is valid for all products listed in the “Ordering data” on page 3. TMC 7... and TMC 8... Table of contents 1 Description.................................................................................................................................. 1 1.1 1.2 Typical applications........................................................................................................................................ 1 Features ......................................................................................................................................................... 1 2 Ordering data.............................................................................................................................. 3 3 Technical data ...........................................................................................................................11 3.1 3.2 3.3 3.4 4 Trip curve .................................................................................................................................................... 12 Current rating and voltage drop @ 25°C ....................................................................................................... 12 Dimensions .................................................................................................................................................. 13 Environmental influences ............................................................................................................................. 14 Circuit breaker installation .........................................................................................................14 4.1 4.2 4.3 Mounting ...................................................................................................................................................... 14 Removal ....................................................................................................................................................... 14 DC connection diagram ............................................................................................................................... 14 5 Accessories ...............................................................................................................................15 6 Ordering data for accessories....................................................................................................16 7 Technical data for accessories ..................................................................................................17 7.1 7.2 8 Accessory descriptions..............................................................................................................19 8.1 8.2 8.3 9 Technical data for TMC 7/8 AUX and TMC 7/8 ALARM accessories .......................................................... 17 Technical data for busbars and termination pins ......................................................................................... 18 Auxiliary contact (TMC 7/8 AUX) .................................................................................................................. 19 Alarm contact (TMC 7/8 ALARM) ................................................................................................................. 19 Shunt trip (TMC 7/8...SHNT) ........................................................................................................................ 20 TMC 7/8 AUX / TMC 7/8 ALARM / TMC 7/8...SHNT installation ...............................................20 9.1 3644_en_C Busbars and related accessories ................................................................................................................. 21 PHOENIX CONTACT 2/24 TMC 7... and TMC 8... 2 Ordering data Order key TMC 81C 01A Current rating Trip curve (B, C, or D) Number of poles (1, 2, or 3) Design criteria (UL 489) Thermal magnetic circuit breaker family Products Description Type Order No. MCB, up to 60 V DC and 277 V AC, B curve 1-pole 1 A TMC 81B 01A 2907478 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 2 A TMC 81B 02A 2907479 1 Pcs./Pkt. MCB, up to 60 V DC and 277 V AC, B curve 1-pole 3 A TMC 81B 03A 2907480 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 4 A TMC 81B 04A 2907481 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 5 A TMC 81B 05A 2907482 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 6 A TMC 81B 06A 2907483 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 7 A TMC 81B 07A 2907484 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 8 A TMC 81B 08A 2907485 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 10 A TMC 81B 10A 2907487 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 12 A TMC 81B 12A 2907488 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 13 A TMC 81B 13A 2907489 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 15 A TMC 81B 15A 2907490 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 16 A TMC 81B 16A 2907491 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 20 A TMC 81B 20A 2907492 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 25 A TMC 81B 25A 2907493 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 30 A TMC 81B 30A 2907494 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 32 A TMC 81B 32A 2907495 1 MCB, up to 60 V DC and 120 V AC, B curve 1-pole 35 A TMC 81B 35A 2907496 1 MCB, up to 60 V DC and 120 V AC, B curve 1-pole 40 A TMC 81B 40A 2907497 1 MCB, up to 60 V DC and 120 V AC, B curve 1-pole 50 A TMC 81B 50A 2907498 1 MCB, up to 60 V DC and 120 V AC, B curve 1-pole 60 A TMC 81B 60A 2907500 1 MCB, up to 60 V DC and 120 V AC, B curve 1-pole 63 A TMC 81B 63A 2907501 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 1 A TMC 82B 01A 2907502 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 2 A TMC 82B 02A 2907503 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 3 A TMC 82B 03A 2907504 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 4 A TMC 82B 04A 2907505 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 5 A TMC 82B 05A 2907506 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 6 A TMC 82B 06A 2907507 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 7 A TMC 82B 07A 2907508 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 8 A TMC 82B 08A 2907510 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 10 A TMC 82B 10A 2907511 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 12 A TMC 82B 12A 2907512 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 13 A TMC 82B 13A 2907513 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 15 A TMC 82B 15A 2907514 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 16 A TMC 82B 16A 2907515 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 20 A TMC 82B 20A 2907516 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 25 A TMC 82B 25A 2907530 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 30 A TMC 82B 30A 2907531 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 32 A TMC 82B 32A 2907532 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), B curve 2-pole 35 A TMC 82B 35A 2907533 1 3644_en_C PHOENIX CONTACT 3/24 TMC 7... and TMC 8... Products Description Type Order No. MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), B curve 2-pole 40 A TMC 82B 40A 2907534 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), B curve 2-pole 50 A TMC 82B 50A 2907535 1 Pcs./Pkt. MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), B curve 2-pole 60 A TMC 82B 60A 2907536 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), B curve 2-pole 63 A TMC 82B 63A 2907537 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 1 A TMC 83B 01A 2907539 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 2 A TMC 83B 02A 2907540 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 3 A TMC 83B 03A 2907542 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 4 A TMC 83B 04A 2907543 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 5 A TMC 83B 05A 2907544 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 6 A TMC 83B 06A 2907545 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 7 A TMC 83B 07A 2907546 1 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 8 A TMC 83B 08A 2907547 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 10 A TMC 83B 10A 2907548 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 12 A TMC 83B 12A 2907549 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 13 A TMC 83B 13A 2907550 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 15 A TMC 83B 15A 2907551 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 16 A TMC 83B 16A 2907552 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 20 A TMC 83B 20A 2907553 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 25 A TMC 83B 25A 2907555 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 30 A TMC 83B 30A 2907556 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 32 A TMC 83B 32A 2907557 1 MCB, up to 240 V AC (240D), B curve 3-pole 35 A TMC 83B 35A 1010309 1 MCB, up to 240 V AC (240D), B curve 3-pole 40 A TMC 83B 40A 1010308 1 MCB, up to 240 V AC (240D), B curve 3-pole 50 A TMC 83B 50A 1010307 1 MCB, up to 240 V AC (240D), B curve 3-pole 60 A TMC 83B 60A 1010306 1 MCB, up to 240 V AC (240D), B curve 3-pole 63 A TMC 83B 63A 1010286 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 1 A TMC 81C 01A 2907558 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 2 A TMC 81C 02A 2907559 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 3 A TMC 81C 03A 2907560 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 4 A TMC 81C 04A 2907561 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 5 A TMC 81C 05A 2907562 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 6 A TMC 81C 06A 2907563 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 7 A TMC 81C 07A 2907564 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 8 A TMC 81C 08A 2907565 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 10 A TMC 81C 10A 2907566 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 12 A TMC 81C 12A 2907568 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 13 A TMC 81C 13A 2907569 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 15 A TMC 81C 15A 2907571 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 16 A TMC 81C 16A 2907572 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 20 A TMC 81C 20A 2907573 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 25 A TMC 81C 25A 2907574 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 30 A TMC 81C 30A 2907575 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 32 A TMC 81C 32A 2907576 1 MCB, up to 60 V DC and 120 V AC, C curve 1-pole 35 A TMC 81C 35A 2907577 1 MCB, up to 60 V DC and 120 V AC, C curve 1-pole 40 A TMC 81C 40A 2907578 1 MCB, up to 60 V DC and 120 V AC, C curve 1-pole 50 A TMC 81C 50A 2907579 1 MCB, up to 60 V DC and 120 V AC, C curve 1-pole 60 A TMC 81C 60A 2907580 1 MCB, up to 60 V DC and 120 V AC, C curve 1-pole 63 A TMC 81C 63A 2907581 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 1 A TMC 82C 01A 2907582 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 2 A TMC 82C 02A 2907584 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 3 A TMC 82C 03A 2907585 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 4 A TMC 82C 04A 2907586 1 3644_en_C PHOENIX CONTACT 4/24 TMC 7... and TMC 8... Products Description Type Order No. MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 5 A TMC 82C 05A 2907587 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 6 A TMC 82C 06A 2907588 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 7 A TMC 82C 07A 2907589 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 8 A TMC 82C 08A 2907590 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 10 A TMC 82C 10A 2907591 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 12 A TMC 82C 12A 2907592 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 13 A TMC 82C 13A 2907593 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 15 A TMC 82C 15A 2907594 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 16 A TMC 82C 16A 2907595 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 20 A TMC 82C 20A 2907597 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 25 A TMC 82C 25A 2907598 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 30 A TMC 82C 30A 2907599 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 32 A TMC 82C 32A 2907600 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), C curve 2-pole 35 A TMC 82C 35A 2907601 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), C curve 2-pole 40 A TMC 82C 40A 2907602 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), C curve 2-pole 50 A TMC 82C 50A 2907603 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), C curve 2-pole 60 A TMC 82C 60A 2907604 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), C curve 2-pole 63 A TMC 82C 63A 2907605 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 1 A TMC 83C 01A 2907607 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 2 A TMC 83C 02A 2907608 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 3 A TMC 83C 03A 2907609 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 4 A TMC 83C 04A 2907610 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 5 A TMC 83C 05A 2907611 1 Pcs./Pkt. MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 6 A TMC 83C 06A 2907612 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 7 A TMC 83C 07A 2907613 1 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 8 A TMC 83C 08A 2907614 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 10 A TMC 83C 10A 2907615 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 12 A TMC 83C 12A 2907616 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 13 A TMC 83C 13A 2907617 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 15 A TMC 83C 15A 2907618 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 16 A TMC 83C 16A 2907620 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 20 A TMC 83C 20A 2907621 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 25 A TMC 83C 25A 2907623 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 30 A TMC 83C 30A 2907624 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 32 A TMC 83C 32A 2907625 1 MCB, up to 240 V AC (240D), C curve 3-pole 35 A TMC 83C 35A 1010303 1 MCB, up to 240 V AC (240D), C curve 3-pole 40 A TMC 83C 40A 1010305 1 MCB, up to 240 V AC (240D), C curve 3-pole 50 A TMC 83C 50A 1010302 1 MCB, up to 240 V AC (240D), C curve 3-pole 60 A TMC 83C 60A 1010301 1 MCB, up to 240 V AC (240D), C curve 3-pole 63 A TMC 83C 63A 1010291 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 1 A TMC 81D 01A 2907626 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 2 A TMC 81D 02A 2907627 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 3 A TMC 81D 03A 2907628 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 4 A TMC 81D 04A 2907629 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 5 A TMC 81D 05A 2907630 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 6 A TMC 81D 06A 2907631 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 7 A TMC 81D 07A 2907632 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 8 A TMC 81D 08A 2907633 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 10 A TMC 81D 10A 2907634 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 12 A TMC 81D 12A 2907636 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 13 A TMC 81D 13A 2907637 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 15 A TMC 81D 15A 2907638 1 3644_en_C PHOENIX CONTACT 5/24 TMC 7... and TMC 8... Products Description Type Order No. MCB, up to 60 V DC and 277 V AC, D curve 1-pole 16 A TMC 81D 16A 2907639 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 20 A TMC 81D 20A 2907640 1 Pcs./Pkt. MCB, up to 60 V DC and 277 V AC, D curve 1-pole 25 A TMC 81D 25A 2907641 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 30 A TMC 81D 30A 2907642 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 32 A TMC 81D 32A 2907643 1 MCB, up to 60 V DC and 120 V AC, D curve 1-pole 35 A TMC 81D 35A 2907644 1 MCB, up to 60 V DC and 120 V AC, D curve 1-pole 40 A TMC 81D 40A 2907645 1 MCB, up to 60 V DC and 120 V AC, D curve 1-pole 50 A TMC 81D 50A 2907646 1 MCB, up to 60 V DC and 120 V AC, D curve 1-pole 60 A TMC 81D 60A 2907647 1 MCB, up to 60 V DC and 120 V AC, D curve 1-pole 63 A TMC 81D 63A 2907649 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 1 A TMC 82D 01A 2907650 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 2 A TMC 82D 02A 2907652 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 3 A TMC 82D 03A 2907653 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 4 A TMC 82D 04A 2907654 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 5 A TMC 82D 05A 2907655 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 6 A TMC 82D 06A 2907656 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 7 A TMC 82D 07A 2907657 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 8 A TMC 82D 08A 2907658 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 10 A TMC 82D 10A 2907659 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 12 A TMC 82D 12A 2907660 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 13 A TMC 82D 13A 2907661 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 15 A TMC 82D 15A 2907662 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 16 A TMC 82D 16A 2907663 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 20 A TMC 82D 20A 2907665 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 25 A TMC 82D 25A 2907666 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 30 A TMC 82D 30A 2907667 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 32 A TMC 82D 32A 2907668 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), D curve 2-pole 35 A TMC 82D 35A 2907669 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), D curve 2-pole 40 A TMC 82D 40A 2907670 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), D curve 2-pole 50 A TMC 82D 50A 2907671 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), D curve 2-pole 60 A TMC 82D 60A 2907672 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), D curve 2-pole 63 A TMC 82D 63A 2907673 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 1 A TMC 83D 01A 2907674 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 2 A TMC 83D 02A 2907675 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 3 A TMC 83D 03A 2907676 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 4 A TMC 83D 04A 2907678 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 5 A TMC 83D 05A 2907679 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 6 A TMC 83D 06A 2907681 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 7 A TMC 83D 07A 2907682 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 8 A TMC 83D 08A 2907683 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 10 A TMC 83D 10A 2907684 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 12 A TMC 83D 12A 2907685 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 13 A TMC 83D 13A 2907686 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 15 A TMC 83D 15A 2907687 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 16 A TMC 83D 16A 2907688 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 20 A TMC 83D 20A 2907689 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 25 A TMC 83D 25A 2907690 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 30 A TMC 83D 30A 2907691 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 32 A TMC 83D 32A 2907692 1 MCB, up to 240 V AC (240D), D curve 3-pole 35 A TMC 83D 35A 1010290 1 MCB, up to 240 V AC (240D), D curve 3-pole 40 A TMC 83D 40A 1010289 1 3644_en_C PHOENIX CONTACT 6/24 TMC 7... and TMC 8... Products Description Type Order No. Pcs./Pkt. MCB, up to 240 V AC (240D), D curve 3-pole 50 A TMC 83D 50A 1010284 1 MCB, up to 240 V AC (240D), D curve 3-pole 60 A TMC 83D 60A 1010288 1 MCB, up to 240 V AC (240D), D curve 3-pole 63 A TMC 83D 63A 1010287 1 Pcs./Pkt. TMC 71C 04A Current rating Trip curve (B, C, or D) Number of poles (1, 2, or 3) Design criteria (UL 1077) Thermal magnetic circuit breaker family Products Description Type Order No. MCB, up to 60 V DC and 277 V AC, B curve 1-pole 1 A TMC 71B 01A 1011962 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 2 A TMC 71B 02A 1019909 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 3 A TMC 71B 03A 1019910 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 4 A TMC 71B 04A 1019911 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 5 A TMC 71B 05A 1019912 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 6 A TMC 71B 06A 1019913 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 7 A TMC 71B 07A 1019914 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 8 A TMC 71B 08A 1019915 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 10 A TMC 71B 10A 1019916 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 12 A TMC 71B 12A 1019917 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 13 A TMC 71B 13A 1019918 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 15 A TMC 71B 15A 1019919 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 16 A TMC 71B 16A 1019920 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 20 A TMC 71B 20A 1019921 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 25 A TMC 71B 25A 1019922 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 30 A TMC 71B 30A 1019923 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 32 A TMC 71B 32A 1019924 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 40 A TMC 71B 40A 1019925 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 50 A TMC 71B 50A 1019926 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 60 A TMC 71B 60A 1019927 1 MCB, up to 60 V DC and 277 V AC, B curve 1-pole 63 A TMC 71B 63A 1019928 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 1 A TMC 72B 01A 1019930 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 2 A TMC 72B 02A 1019931 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 3 A TMC 72B 03A 1019932 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 4 A TMC 72B 04A 1019933 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 5 A TMC 72B 05A 1019934 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 6 A TMC 72B 06A 1019935 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 7 A TMC 72B 07A 1019936 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 8 A TMC 72B 08A 1019937 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 10 A TMC 72B 10A 1019938 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 12 A TMC 72B 12A 1019939 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 13 A TMC 72B 13A 1019940 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 15 A TMC 72B 15A 1019941 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 16 A TMC 72B 16A 1019942 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 20 A TMC 72B 20A 1019943 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 25 A TMC 72B 25A 1019944 1 3644_en_C PHOENIX CONTACT 7/24 TMC 7... and TMC 8... Products Description Type Order No. MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 30 A TMC 72B 30A 1019945 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), B curve 2-pole 32 A TMC 72B 32A 1019946 1 Pcs./Pkt. MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), B curve 2-pole 40 A TMC 72B 40A 1019947 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), B curve 2-pole 50 A TMC 72B 50A 1019948 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), B curve 2-pole 60 A TMC 72B 60A 1019949 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), B curve 2-pole 63 A TMC 72B 63A 1019950 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 1 A TMC 73B 01A 1019951 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 2 A TMC 73B 02A 1019952 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 3 A TMC 73B 03A 1019953 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 4 A TMC 73B 04A 1019954 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 5 A TMC 73B 05A 1019955 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 6 A TMC 73B 06A 1019956 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 7 A TMC 73B 07A 1019957 1 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 8 A TMC 73B 08A 1019958 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 10 A TMC 73B 10A 1019959 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 12 A TMC 73B 12A 1019960 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 13 A TMC 73B 13A 1019961 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 15 A TMC 73B 15A 1019962 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 16 A TMC 73B 16A 1019963 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 20 A TMC 73B 20A 1019964 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 25 A TMC 73B 25A 1019965 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 30 A TMC 73B 30A 1019966 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 32 A TMC 73B 32A 1019967 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 40 A TMC 73B 40A 1019968 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 50 A TMC 73B 50A 1019969 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 60 A TMC 73B 60A 1019970 1 MCB, 277 V AC (277/480Y, 240D), B curve 3-pole 63 A TMC 73B 63A 1019971 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 1 A TMC 71C 01A 1019972 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 2 A TMC 71C 02A 1019973 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 3 A TMC 71C 03A 1019974 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 4 A TMC 71C 04A 1019975 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 5 A TMC 71C 05A 1019976 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 6 A TMC 71C 06A 1019977 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 7 A TMC 71C 07A 1019978 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 8 A TMC 71C 08A 1019979 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 10 A TMC 71C 10A 1019980 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 12 A TMC 71C 12A 1019981 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 13 A TMC 71C 13A 1019982 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 15 A TMC 71C 15A 1019983 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 16 A TMC 71C 16A 1019984 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 20 A TMC 71C 20A 1019985 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 25 A TMC 71C 25A 1019986 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 30 A TMC 71C 30A 1019987 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 32 A TMC 71C 32A 1019988 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 40 A TMC 71C 40A 1019989 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 50 A TMC 71C 50A 1019990 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 60 A TMC 71C 60A 1019991 1 MCB, up to 60 V DC and 277 V AC, C curve 1-pole 63 A TMC 71C 63A 1019992 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 1 A TMC 72C 01A 1019994 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 2 A TMC 72C 02A 1019995 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 3 A TMC 72C 03A 1019996 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 4 A TMC 72C 04A 1019997 1 3644_en_C PHOENIX CONTACT 8/24 TMC 7... and TMC 8... Products Description Type Order No. MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 5 A TMC 72C 05A 1019998 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 6 A TMC 72C 06A 1019999 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 7 A TMC 72C 07A 1020000 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 8 A TMC 72C 08A 1020001 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 10 A TMC 72C 10A 1020002 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 12 A TMC 72C 12A 1020003 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 13 A TMC 72C 13A 1020004 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 15 A TMC 72C 15A 1020005 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 16 A TMC 72C 16A 1020006 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 20 A TMC 72C 20A 1020007 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 25 A TMC 72C 25A 1020008 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 30 A TMC 72C 30A 1020009 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), C curve 2-pole 32 A TMC 72C 32A 1020010 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), C curve 2-pole 40 A TMC 72C 40A 1020011 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), C curve 2-pole 50 A TMC 72C 50A 1020012 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), C curve 2-pole 60 A TMC 72C 60A 1020013 1 MCB, up to 125 V DC (two poles in series) and 240 V AC (120/240S, 240D), C curve 2-pole 63 A TMC 72C 63A 1020014 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 1 A TMC 73C 01A 1020015 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 2 A TMC 73C 02A 1020016 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 3 A TMC 73C 03A 1020017 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 4 A TMC 73C 04A 1020018 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 5 A TMC 73C 05A 1020019 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 6 A TMC 73C 06A 1020020 1 Pcs./Pkt. MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 7 A TMC 73C 07A 1020021 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 8 A TMC 73C 08A 1020022 1 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 10 A TMC 73C 10A 1020023 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 12 A TMC 73C 12A 1020024 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 13 A TMC 73C 13A 1020025 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 15 A TMC 73C 15A 1020026 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 16 A TMC 73C 16A 1020027 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 20 A TMC 73C 20A 1020028 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 25 A TMC 73C 25A 1020029 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 30 A TMC 73C 30A 1020030 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 32 A TMC 73C 32A 1020031 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 40 A TMC 73C 40A 1020032 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 50 A TMC 73C 50A 1020033 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 60 A TMC 73C 60A 1020035 1 MCB, 277 V AC (277/480Y, 240D), C curve 3-pole 63 A TMC 73C 63A 1020036 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 1 A TMC 71D 01A 1020037 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 2 A TMC 71D 02A 1020038 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 3 A TMC 71D 03A 1020039 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 4 A TMC 71D 04A 1020040 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 5 A TMC 71D 05A 1020041 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 6 A TMC 71D 06A 1020042 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 7 A TMC 71D 07A 1020043 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 8 A TMC 71D 08A 1020044 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 10 A TMC 71D 10A 1020045 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 12 A TMC 71D 12A 1020046 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 13 A TMC 71D 13A 1020048 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 15 A TMC 71D 15A 1020049 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 16 A TMC 71D 16A 1020051 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 20 A TMC 71D 20A 1020052 1 3644_en_C PHOENIX CONTACT 9/24 TMC 7... and TMC 8... Products Description Type Order No. MCB, up to 60 V DC and 277 V AC, D curve 1-pole 25 A TMC 71D 25A 1020053 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 30 A TMC 71D 30A 1020054 1 Pcs./Pkt. MCB, up to 60 V DC and 277 V AC, D curve 1-pole 32 A TMC 71D 32A 1020055 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 40 A TMC 71D 40A 1020056 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 50 A TMC 71D 50A 1020057 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 60 A TMC 71D 60A 1020058 1 MCB, up to 60 V DC and 277 V AC, D curve 1-pole 63 A TMC 71D 63A 1020059 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 1 A TMC 72D 01A 1020060 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 2 A TMC 72D 02A 1020061 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 3 A TMC 72D 03A 1020062 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 4 A TMC 72D 04A 1020064 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 5 A TMC 72D 05A 1020065 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 6 A TMC 72D 06A 1020066 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 7 A TMC 72D 07A 1020067 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 8 A TMC 72D 08A 1020068 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 10 A TMC 72D 10A 1020069 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 12 A TMC 72D 12A 1020070 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 13 A TMC 72D 13A 1020071 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 15 A TMC 72D 15A 1020072 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 16 A TMC 72D 16A 1020073 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 20 A TMC 72D 20A 1020074 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 25 A TMC 72D 25A 1020075 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 30 A TMC 72D 30A 1020076 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 32 A TMC 72D 32A 1020077 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 40 A TMC 72D 40A 1020078 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 50 A TMC 72D 50A 1020079 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 60 A TMC 72D 60A 1020080 1 MCB, up to 125 V DC (two poles in series) and 277 V AC (277/480Y, 240D), D curve 2-pole 63 A TMC 72D 63A 1020081 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 1 A TMC 73D 01A 1020082 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 2 A TMC 73D 02A 1020083 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 3 A TMC 73D 03A 1020084 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 4 A TMC 73D 04A 1020085 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 5 A TMC 73D 05A 1020086 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 6 A TMC 73D 06A 1020087 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 7 A TMC 73D 07A 1020088 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 8 A TMC 73D 08A 1020090 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 10 A TMC 73D 10A 1020091 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 12 A TMC 73D 12A 1020093 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 13 A TMC 73D 13A 1020094 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 15 A TMC 73D 15A 1020095 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 16 A TMC 73D 16A 1020096 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 20 A TMC 73D 20A 1020097 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 25 A TMC 73D 25A 1020098 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 30 A TMC 73D 30A 1020099 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 32 A TMC 73D 32A 1020100 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 40 A TMC 73D 40A 1020101 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 50 A TMC 73D 50A 1020103 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 60 A TMC 73D 60A 1020104 1 MCB, 277 V AC (277/480Y, 240D), D curve 3-pole 63 A TMC 73D 63A 1020105 1 3644_en_C PHOENIX CONTACT 10/24 TMC 7... and TMC 8... 3 Technical data General data Ambient temperature, operating -35°C … 70°C (-31°F … 158°F) Degree of protection IP20 Weight (approximate) TMC 8... 131 g per pole TMC 7... 116 g per pole Installation NS35 rail (EN 60715) Conductor cross section 1 ... 35 mm²/18 ... 2 AWG1 Connection type Screw-clamp terminals Conductor tightening torque, maximum 2 Nm (17.7 lbf-in.) 1 Use copper wire only. Electrical data Nominal voltage, UN See product description for specifics for each model Nominal current See product description for specifics for each model NOTE: Current ratings are 0.80 of nominal current when mounted side by side. Service life Mechanical 20,000 cycles Electrical 6,000 cycles Conformance IEC 60068-2-6 (Sinusoidal vibration) test Fc ±0.38 mm (10-57 Hz), 5g (57-500 Hz) 10 frequency cycles per axis IEC 60068-2-27 (Shock) Test Ea 30g, 11 ms IEC 60068-2-11 (Corrosion) Test Ka 96 h in 5% salt mist IEC 60068-2-78 (Humidity) Test Cab 48 h at 95% relative humidity, 40°C Approvals (UL 489/CSA-C22.2 No. 5) TMC 81... Nominal current range Rated voltage AC Rated voltage DC Interrupt capacity 1 ... 32 A 277 V AC 60 V DC 10 kA TMC 81... 35 ... 63A 120 V AC 60 V DC 10 kA TMC 82... 1 ... 32 A 277 V AC (277/480Y, 240D) 125 V DC (two poles in series) 10 kA TMC 82... 35 ... 63A 240 V AC (120/240S, 240D) 125 V DC (two poles in series) 10 kA TMC 83... 1 ... 32 A 277 V AC (277/480Y, 240D) 125 V DC (two poles in series) 10 kA TMC 83... 35 ... 63 A 240 V AC (120/240S, 240D) 10 kA Approvals (UL 1077/CSA-C22.2 No. 235) Nominal current range Rated voltage AC Rated voltage DC TMC 71... 1 ... 63 A 240 V AC 60 V DC TMC 71... 1 ... 63A 277 V AC TMC 72... 1 ... 63 A 277/480Y, 240D TMC 73… 1 ... 63 A 277/480Y, 240D 3644_en_C Short-circuit current rating (SCCR) 7.5 kA, U1 5 kA, U1 125 V DC (two poles in series) 7.5 kA, U1 7.5 kA, U1 PHOENIX CONTACT 11/24 TMC 7... and TMC 8... Approvals (IEC/EN 60947-2) TMC 71… Nominal current range Rated voltage AC Rated voltage DC – 240 V AC 80 V DC TMC 81... Rupture capacity 7.5 kA AC/10 kA DC (Ics) 10 kA (Icu) TMC 72… – 240/415 V AC 125 V DC (two poles in series) TMC 73… 7.5 kA AC/10 kA DC (Ics) 10 kA DC (Icu) TMC 82... TMC 83… 3.1 Trip curve 3.2 Current rating and voltage drop @ 25°C 10000 Ambient temperature +30°C No-trip current Trip current 1.05x In 1.30x In Curve B magnetic trip current 4x In (±20%) Curve C magnetic trip current 8x In (±20%) Curve D magnetic trip current 12x In (±20%) 1000 Trip time (s) 100 10 1 TMC … IN (A) Voltage drop (V) 1 1.50 2 0.80 3 0.60 4 0.60 5 0.20 6 0.20 7 0.20 8 0.15 10 0.15 12 0.15 13 0.10 15 0.10 16 0.10 20 0.08 25 0.08 30 0.07 32 0.07 35 0.07 40 0.07 50 0.06 60 0.06 63 0.06 0,1 B C D 0,01 0,8 1 2 4 6 8 10 20 40 Times rated current Figure 1 Trip curves The current rating is reduced to 80% when mounted side by side. Magnetic tripping currents are increased by 30% on DC supplies (ambient temperature 30°C). 3644_en_C PHOENIX CONTACT 12/24 TMC 7... and TMC 8... 3.3 Dimensions 116 ±0.4 17,6 ±0.2 35,3 ±0.4 52,9 ±0.6 5,5 ±0.3 60,1 60,2 ±0.3 45 ±0.3 Figure 2 TMC 8... dimensions (mm) 81,4 ±0.4 17,6 ±0.2 52,9 ±0.6 49,8 35,3 ±0.4 5,5 ±0.3 60,2 ±0.3 45 ±0.3 Figure 3 3644_en_C TMC 7... dimensions (mm) PHOENIX CONTACT 13/24 TMC 7... and TMC 8... 3.4 Environmental influences The following correction factors must be considered when selecting the appropriate nominal current rating for the circuit breaker. IN (A) Maximum operating currents (A) depending on ambient temperature (°C) -35 -30 -25 -20 -15 -10 -5 +5 +10 +15 +20 +25 +30 +35 +40 +45 +50 +55 +60 +65 +70 1 1.27 1.25 1.23 1.21 1.19 1.17 1.15 1.13 0 1.10 1.08 1.06 1.05 1.02 1.00 0.97 0.94 0.91 0.89 0.86 0.83 0.80 0.77 2 2.54 2.50 2.46 2.42 2.38 2.34 2.30 2.26 2.20 2.16 2.12 2.10 2.04 2.00 1.94 1.88 1.82 1.78 1.72 1.66 1.60 1.54 3 3.89 3.83 3.76 3.70 3.64 3.57 3.50 3.44 3.37 3.30 3.22 3.14 3.06 3.00 2.92 2.84 2.76 2.67 2.58 2.49 2.38 2.27 4 5.08 5.00 4.92 4.84 4.76 4.68 4.60 4.52 4.40 4.32 4.24 4.20 4.08 4.00 3.88 3.76 3.64 3.56 3.44 3.32 3.20 3.08 5 6.68 6.56 6.44 6.32 6.19 6.07 5.94 5.81 5.68 5.54 5.40 5.25 5.12 5.00 4.82 4.66 4.50 4.34 4.17 3.99 3.81 3.62 6 7.70 7.58 7.46 7.34 7.21 7.09 6.96 6.83 6.70 6.56 6.42 6.27 6.14 6.00 5.84 5.68 5.52 5.36 5.19 5.01 4.83 4.64 7 8.78 8.66 8.54 8.42 8.29 8.17 8.04 7.91 7.78 7.64 7.50 7.35 7.22 7.00 6.92 6.76 6.60 6.44 6.27 6.09 5.91 5.72 8 9.80 9.68 9.56 9.44 9.31 9.19 9.06 8.93 9.80 8.66 8.52 8.37 8.24 8.00 7.94 7.78 7.62 7.46 7.29 7.11 6.93 6.74 10 13.89 13.62 13.35 13.07 12.81 12.53 12.23 11.93 11.63 11.33 11.01 10.67 10.34 10.00 9.63 9.24 8.85 8.45 8.01 7.55 7.06 6.55 12 15.91 15.64 15.37 15.09 14.83 14.55 14.25 13.95 13.65 13.35 13.03 12.69 12.36 12.00 11.65 11.26 10.60 10.47 10.03 9.57 9.08 8.57 13 16.92 16.65 16.38 16.10 15.84 15.56 15.26 14.96 14.66 14.36 14.04 13.70 13.37 13.00 12.66 12.27 11.61 11.48 11.04 10.58 10.09 9.58 15 19.77 19.42 19.07 18.74 18.39 18.04 17.69 17.32 16.95 16.57 16.19 15.79 15.39 15.00 14.54 14.10 13.65 13.19 12.70 12.20 11.69 11.64 16 20.78 20.43 20.08 19.75 19.40 19.05 18.70 18.33 17.96 17.58 17.20 16.80 16.40 16.00 15.55 15.11 14.66 14.20 13.71 13.21 12.70 12.75 20 25.67 25.28 24.88 24.47 24.06 23.64 23.22 22.78 22.34 21.89 21.43 20.96 20.47 20.00 19.47 18.95 18.42 17.87 17.30 16.71 16.10 15.47 25 32.21 31.72 31.22 30.70 30.18 29.65 29.10 28.55 27.98 27.41 26.82 26.22 25.61 25.00 24.33 23.67 23.00 22.28 21.56 20.80 20.02 19.21 30 39.00 38.42 37.78 37.13 36.47 35.80 35.11 34.43 33.71 32.99 32.26 31.50 30.73 30.00 29.13 28.30 27.44 26.56 25.65 24.71 23.74 22.73 32 41.04 40.46 39.82 39.17 38.51 37.84 37.15 36.47 35.75 35.03 34.30 33.54 32.77 32.00 31.17 30.34 29.48 28.69 27.69 26.75 25.78 24.77 35 44.08 43.50 42.86 42.21 41.55 40.88 40.19 39.51 38.79 38.07 37.34 36.58 35.81 35.00 34.21 33.38 32.52 31.64 30.73 29.79 28.82 27.81 40 51.63 50.86 50.04 49.21 48.37 47.51 46.63 45.74 44.83 43.90 42.95 41.98 40.99 40.00 38.93 37.85 36.75 35.61 34.43 33.21 31.95 30.63 50 64.92 63.97 62.92 61.86 60.77 59.67 58.54 57.40 56.23 55.05 53.81 52.56 51.23 50.00 47.82 46.24 44.81 43.33 41.81 40.23 38.58 35.77 60 80.45 79.03 77.61 76.16 74.69 73.19 71.67 70.11 68.51 66.88 65.21 63.50 61.75 60.00 57.08 55.16 53.18 51.13 49.00 46.78 44.47 40.47 63 83.48 82.06 60.64 79.19 77.72 76.22 74.70 73.14 71.54 69.91 68.24 66.53 64.78 63.00 60.11 58.19 56.21 54.16 52.03 49.81 47.50 43.05 4 Circuit breaker installation WARNING: 4.3 DC connection diagram 60 V DC 125 V DC Always remove power before installing or performing maintenance. 4.1 1. 2. 3. 4.2 1. 2. 3. Mounting Hook the device over the top edge of the DIN rail and rotate it down until it snaps onto the bottom edge of the rail. Ensure that the orange DIN rail latch securely locks the device to the rail. Repeat for any additional devices. Slide the devices together into the desired configuration. TMC 81 C 20A 1 TMC 82 C 16A 1 2 2 I ON O OFF I cu=10KA I ON O OFF I cu=10KA TMC 82 C 16A 1 2 I ON O OFF I cu=10KA Removal Slide the device away to gain sufficient clearance from the next device. Use a screwdriver to raise the latch and release the unit from the bottom edge of the DIN rail. Rotate the device up and lift off of the top edge of the rail. 3644_en_C Figure 4 DC connection diagram PHOENIX CONTACT 14/24 TMC 7... and TMC 8... 5 Accessories Several accessories are available for use with the TMC 7/8... circuit breakers. The accessory modules are mounted on the left side (see Figure 10) of the circuit breaker. A variety of busbars are also available. NOTE: Accessory modules must be installed in the proper order: shunt trip, alarm contact, and then the auxiliary contact. Figure 5 3644_en_C Busbar and other accessories PHOENIX CONTACT 15/24 TMC 7... and TMC 8... 6 Ordering data for accessories Accessories Description Type Order No. Pcs./Pkt. Auxiliary contact, one NO and one NC switch TMC 7/8 AUX 2908219 1 Alarm contact, one NO and one NC TMC 7/8 ALARM 2908220 1 Shunt trip, 12 V DC, one NO and one NC TMC 7/8 12VDC SHNT 2908221 1 Shunt trip, 24 V DC, one NO and one NC TMC 7/8 24VDC SHNT 2908222 1 Shunt trip, 48 V DC, one NO and one NC TMC 7/8 48VDC SHNT 2908224 1 Shunt trip, 125 V DC, one NO and one NC TMC 7/8 125VDC SHNT 2908225 1 1 Shunt trip, 120 V AC, one NO and one NC TMC 7/8 120VAC SHNT 2908226 Shunt trip, 240 V AC, one NO and one NC TMC 7/8 240VAC SHNT 2908227 1 Shunt trip, 277 V AC, one NO and one NC TMC 7/8 277VAC SHNT 2908228 1 Busbar, cut to length, for TMC 7... 1-pole applications, up to 57 positions, UL Listed TMC 7 B1 80 57 C 1022238 1 Busbar, cut to length, for TMC 7... 1-pole plus auxiliary applications, up to 37 positions, UL Listed TMC 7 B1 80 37 CA 1022237 1 Busbar, cut to length, for TMC 7... 2-pole applications, up to 56 positions, UL Listed TMC 7 B2 80 56 C 1022236 1 Busbar, cut to length, for TMC 7... 2-pole plus auxiliary applications, up to 46 positions, UL Listed TMC 7 B2 80 46 CA 1022235 1 Busbar, cut to length, for TMC 7... 3-pole applications, up to 57 positions, UL Listed TMC 7 B3 80 57 C 1022234 1 Busbar, cut to length, for TMC 7... 3-pole plus auxiliary applications, up to 48 positions, UL Listed TMC 7 B3 80 48 CA 1025400 1 Busbar terminal, 1-pole incoming connections, for TMC 7... TMC 7 B1 TERM 1022233 1 Busbar terminal, 2- and 3-pole incoming connections, for TMC 7... TMC 7 B2/3 TERM 1022232 1 Busbar, end cap, 1-pole, protects open busbar positions, for TMC 7... TMC 7 B1 END CAP 1022231 1 Busbar, end cap, 2- and 3-pole, protects open busbar positions, for TMC 7... TMC 7 B2/3 END CAP 1022229 1 Busbar, bus cap, protects three open busbar positions, for TMC 7... TMC 7 B BUS CAP 1022224 1 Busbar, cut to length, for TMC 8... 1-pole applications, up to 57 positions, UL Listed TMC 8 B1 80 57 C 2907991 1 Busbar, cut to length, for TMC 8... 1-pole plus auxiliary applications, up to 37 positions, UL Listed TMC 8 B1 80 37 CA 2907992 1 Busbar, cut to length, for TMC 8... 2-pole applications, up to 56 positions, UL Listed TMC 8 B2 80 56 C 2907993 1 Busbar, cut to length, for TMC 8... 2-pole plus auxiliary applications, up to 46 positions, UL Listed TMC 8 B2 80 46 CA 2907995 1 Busbar, cut to length, for TMC 8... 3-pole applications, up to 57 positions, UL Listed TMC 8 B3 80 57 C 2907996 1 Busbar, cut to length, for TMC 8... 3-pole plus auxiliary applications, up to 48 positions, UL Listed TMC 8 B3 80 48 CA 2907997 1 Busbar terminal, incoming connections, TMC 8... TMC 8 B TERM PIN 2907998 1 Busbar, end cap, protects open busbar positions, TMC 8... TMC 8 B END CAP 2907999 1 Busbar, bus cap, protects three open busbar positions, TMC 8... TMC 8 B BUS CAP 2908000 1 3644_en_C PHOENIX CONTACT 16/24 TMC 7... and TMC 8... 7 Technical data for accessories 7.1 Technical data for TMC 7/8 AUX and TMC 7/8 ALARM accessories General data (TMC 7/8 AUX and TMC 7/8 ALARM) Ambient temperature, operating -35 … 70°C (-31 … 158°F) Degree of protection IP20 Weight 29 g (approximate) Width 9 mm Installation Left side of circuit breaker Conductor cross section 1 ... 35 mm²/18 ... 2 AWG Connection type Screw-clamp terminals Conductor tightening torque, maximum 1 Nm (8.9 lbf-in.) Service life, mechanical 20,000 cycles Electrical data (TMC 7/8 AUX and TMC 7/8 ALARM) Nominal voltage, UN (IEC/EN 60947-5-1) 12 V DC ... 220 V DC 12 V AC ... 277 V AC Rated current (IEC/EN 60947-5-1) 240 V AC 6A 24 V DC 6A 48 V DC 2A 130 V DC 1A Rated current (UL 489) 12 … 240 V AC 6A 277 V AC 3A 12 … 24 V DC 6A 48 V DC 3A 110 … 220 V DC 1.5 A General data (TMC 7/8…SHNT) Ambient temperature, operating -35 … 70°C (-31 … 158°F) Degree of protection IP20 Weight 60 g (approximate) Width 18 mm Installation Left side of circuit breaker Conductor cross section 1 ... 35 mm²/18 ... 2 AWG Connection type Screw-clamp terminals Conductor tightening torque, maximum 1 Nm (8.9 lbf-in.) Service life, mechanical 20,000 cycles 3644_en_C PHOENIX CONTACT 17/24 TMC 7... and TMC 8... Electrical data (TMC 7/8…SHNT) Nominal voltage, UN 12 V DC ... 125 V DC 120 V AC ... 277 V AC Trip voltage 277 V AC 160 V AC 240 V AC 160 V AC 120 V AC 80 V AC 125 V DC 125 V DC 48 V DC 24 V DC 24 V DC 16 V DC 12 V DC 8 V DC Power consumption/minimum response power 277 V AC 240 W/35 W 240 V AC 200 W/35 W 120 V AC 200 W/35 W 125 V DC 200 W/30 VA 48 V DC 200 W/30 VA 24 V DC 200 W/30 VA 12 V DC 200 W/30 VA Trip time 7.2
1020081
物料型号: - TMC 7... 和 TMC 8... 系列微型断路器(MCB)

器件简介: - TMC 8... 系列微型断路器是UL 489认证的,用于提供分支过载和短路保护。 - TMC 7... 系列微型断路器是UL 1077认证的,提供附加过载和短路保护。

引脚分配: - 断路器有1极、2极和3极配置,具有B、C和D型脱扣曲线选项。

参数特性: - 额定电压:交流277/480V,直流60V或125V(两极串联)。 - 额定电流范围:1到63安培。 - 断路器宽度:每极17.6毫米。 - 安装在35毫米NS35导轨上。

功能详解: - 提供过载和短路保护。 - 具有视觉状态指示和自复位、快动机构。 - 不能在过载情况下手动覆盖。

应用信息: - 适用于电缆、电动机、发电机、变压器、晶闸管、硅整流器、计算机及其外围设备、工业过程控制系统、电信设备和电源的保护。

封装信息: - 断路器安装在35毫米宽的NS35导轨上,可配辅助触点、报警触点、分流旅行和母线。
1020081 价格&库存

很抱歉,暂时无法提供与“1020081”相匹配的价格&库存,您可以联系我们找货

免费人工找货
1020081
  •  国内价格 香港价格
  • 1+326.660041+42.34136

库存:19