02/11/2015
www.crouzet.com
Smart "Compact" range with display CD12 Smart Part number 88974041
Highly visible blue LCD with 4 lines of 18 characters and configurable backlighting
Allow the use of the entire library of specific functions blocs of the software workshop
Extended temperature range (-20 °C →+70 °C)
Analogue inputs 0-10 VDC, Potentiometer, NTC, LDR (0-20 mA/Pt100 with converters)
Selective parameter setting : you can choose the parameters that can be adjusted on the front panel
Part numbers
88974041
Type
Inputs
Outputs
Supply
CD12 Smart
8 digital (including 4 analogue)
4 relays 8 A
24 V DC
Specifications
General environment characteristics for CB, CD, XD, XB, XR and XE product types
Certifications
Conformity to standards (with the low voltage directive
and EMC directive)
Earthing
Protection rating
Overvoltage category
Pollution
Max operating Altitude
Mechanical resistance
Resistance to electrostatic discharge
Resistance to HF interference
Conducted and radiated emissions
Operating temperature
Storage temperature
Relative humidity
Mounting
Screw terminals connection capacity
CE, UL, CSA, GL
IEC/EN 61131-2 (Open equipment)
IEC/EN 61131-2 (Zone B)
IEC/EN 61000-6-2,
IEC/EN 61000-6-3 (*)
IEC/EN 61000-6-4
(*) Except configuration (88 970 1.1 or 88 970 1.2) + (88 970 250 or 88 970 270) + 88 970 241 class A (class B in a metal enclosure)
Not included
In accordance with IEC/EN 60529 :
IP40 on front panel
IP20 on terminal block
3 in accordance with IEC/EN 60664-1
Degree : 2 in accordance with IEC/EN 61131-2
Operation : 2000 m
Transport : 3048 m
Immunity to vibrations IEC/EN 60068-2-6, test Fc
Immunity to shock IEC/EN 60068-2-27, test Ea
Immunity to ESD
IEC/EN 61000-4-2, level 3
Immunity to radiated electrostatic fields
IEC/EN 61000-4-3
Immunity to fast transients (burst immunity)
IEC/EN 61000-4-4, level 3
Immunity to shock waves
IEC/EN 61000-4-5
Radio frequency in common mode
IEC/EN 61000-4-6, level 3
Voltage dips and breaks (AC)
IEC/EN 61000-4-11
Immunity to damped oscillatory waves
IEC/EN 61000-4-12
Class B (*) in accordance with EN 55022, EN 55011 (CISPR22, CISPR11) group 1
-20 →+70 °C
except CB and XB versions in VDC : -30 →+70 °C (+40 °C in a non-ventilated enclosure)
in accordance with IEC/EN 60068-2-1 and IEC/EN 60068-22
-40 →+80 °C in accordance with IEC/EN 60068-2-1 and
IEC/EN 60068-2-2
95 % max. (no condensation or dripping water) in accordance with
IEC/EN 60068-2-30
On symmetrical DIN rail, 35 x 7.5 mm and 35 x 15 mm, or on panel (2 x Ø 4 mm)
Flexible wire with ferrule =
1 conductor : 0.25 to 2.5 mm2 (AWG 24...AWG 14)
2 conductors 0.25 to 0.75 mm2 (AWG 24...AWG 18)
Semi-rigid wire =
1 conductor : 0.2 to 2.5 mm2 (AWG 25...AWG 14)
Rigid wire =
2 conductors 0.2 to 1.5 mm2 (AWG 25...AWG 16)
Tightening torque =
0.5 N.m (4.5 lb-in) (tighten using screwdriver diam. 3.5 mm)
Also valid for spring cage connectors (ref 88 970 313 and 88 970 317 for the RBT range)
General characteristics
Unless otherwise specified, the characteristics given are applicable to all or part of the product range selected
02/11/2015
Operating factor
Storage temperature
LCD display
www.crouzet.com
-20 →+70 °C
100 % (6 A relays)
66 % (8 A relays)
-40 →+80 °C
Display with 4 lines of 18 characters, white characters on a blue background
Processing characteristics of CB, CD, XD & XB product types
LCD display
Programming method
Program size
Program memory
Removable memory
Data memory
Back-up time in the event of power failure
Cycle time
Response time
Clock data retention
Clock drift
Timer block accuracy
Start up time on power up
CD, XD : Display with 4 lines of 18 characters
Function blocks / SCF (Grafcet) or Ladder
8 Kb : 350 typical blocks, 64 macros maximum, 256 blocks maximum per macro
or
120 lines in Ladder
Flash EEPROM
EEPROM
368 bit/200 words
Program and settings in the controller : 10 years
Program and settings in the plug-in memory : 10 years
Data memory : 10 years
FBD : 6 →90 ms (typically 20 ms)
Ladder : typically 20 ms
Input acquisition time : 1 to 2 cycle times
10 years (lithium battery) at 25 °C
Drift < 12 min/year (at 25 °C)
6 s/month (at 25 °C with user-definable correction of drift)
1 % ± 2 cycle times
< 1,2 s
Characteristics of products with AC power supplied
Supply
Nominal voltage
Operating limits
Supply frequency range
Immunity from micro power cuts
Max. absorbed power
Isolation voltage
24 V AC
-15 % / +20 %
or 20.4 V AC→28.8 V AC
50/60 Hz (+4 % / -6 %)
or 47 →53 Hz/57 →63 Hz
10 ms (repetition 20 times)
CB12-CD12-XD10-XB10 : 4 VA
CB20-CD20 : 6 VA
XD10-XB10 with extension : 7.5 VA
XD26-XB26 : 7.5 VA
XD26-XB26 with extension : 10 VA
1780 V AC
100 →240 V AC
-15 % / +10 %
or 85 V AC→264 V AC
50/60 Hz (+ 4 % / - 6 %) or 47 →53 Hz/57 →63 Hz
CB12-CD12-XD10-XB10 : 7 VA
CB20-CD20 : 11 VA
XD10-XB10 with extension : 12 VA
XD26-XB26 : 12 VA
XD26-XB26 with extension : 17 VA
1780 V AC
Inputs
Input voltage
Input current
Input impedance
Logic 1 voltage threshold
Making current at logic state 1
Logic 0 voltage threshold
Release current at logic state 0
Response time with LADDER programming
Response time with function blocks programming
Maximum counting frequency
Sensor type
Input type
Isolation between power supply and inputs
Isolation between inputs
Protection against polarity inversions
Status indicator
24 V AC (-15 % / +20 %)
4.4 mA @ 20.4 V AC
5.2 mA @ 24.0 V AC
6.3 mA @ 28.8 V AC
4.6 kΩ
≥ 14 V AC
> 2 mA
≤ 5 V AC
< 0.5 mA
50 ms
State 0 →1 (50/60 Hz)
Configurable in increments of 10 ms
50 ms min. up to 255 ms
In accordance with cycle time (Tc) and input response time (Tr) :
1/ ( (2 x Tc) + Tr)
Contact or 3-wire PNP
Resistive
None
None
Yes
On LCD screen for CD and XD
100 →240 V AC (-15 % / +10 %)
0.24 mA @ 85 V AC
0.75 mA @ 264 V AC
350 kΩ
≥ 79 V AC
> 0.17 mA
≤ 20 V AC (≤ 28 V AC : XE10, XR06, XR10, XR14)
< 0.5 mA
50 ms
1/ ( (2 x Tc) + Tr)
Resistive
None
None
Yes
Characteristics of relay outputs common to the entire range
Max. breaking voltage
Breaking current
Electrical durability for 500 000 operating cycles
Max. Output Common Current
Minimum switching capacity
Minimum load
Maximum rate
Mechanical life
5 →30 V DC
24 →250 V AC
CB-CD-XD10-XB10-XR06-XR10 : 8 A
XD26-XB26 : 8 x 8 A relays, 2 x 5 A relays
XE10 : 4 x 5 A relays
XR14 : 4 x 8 A relays, 2 x 5 A relays
RBT (Removable Terminal Blocks) versions : verify the maximum current according to the type of connection used
Utilization category DC-12 : 24 V, 1.5 A
Utilization category DC-13 : 24 V (L/R = 10 ms), 0.6 A
Utilization category AC-12 : 230 V, 1.5 A
Utilization category AC-15 : 230 V, 0.9 A
12 A for O8, O9, OA
10 mA (at minimum voltage of 12 V)
12 V, 10 mA
Off load : 10 Hz
At operating current : 0.1 Hz
10,000,000 (operations)
02/11/2015
Voltage for withstanding shocks
Off-cycle response time
Built-in protections
Status indicator
www.crouzet.com
In accordance with IEC/EN 60947-1 and IEC/EN 60664-1 : 4 kV
Make 10 ms
Release 5 ms
Against short-circuits : None
Against overvoltages and overloads : None
Characteristics of product with DC power supplied
Supply
Nominal voltage
Operating limits
Max. absorbed power
12 V DC
-13 % / +20 %
or 10.4 V DC→14.4 V DC (including ripple)
≤ 1 ms (repetition 20 times)
CB12 with solid state outputs : 1.5 W
CD12 : 1.5 W
CD20 : 2.5 W
XD26-XB26 : 3 W
XD26-XB26 with extension : 5 W
XD26 with solid state outputs : 2.5 W
Yes
24 V DC
-20 % / +25 %
or 19.2 V DC→30 V DC (including ripple)
CB12-CD12-CD20 with solid state outputs - XD10-XB10 with solid state outputs : 3 W
XD10-XB10 with relay outputs : 4 W
XD26-XB26 with solid state outputs : 5 W
CB20-CD20 with relay outputs : 6 W
XD26 with relay outputs : 6 W
XD10-XB10 with extension : 8 W
XD26-XB26 with extension : 10 W
Yes
Digital inputs (I1 to IA and IH to IY)
Input voltage
Input current
Input impedance
Response time
Sensor type
Conforming to IEC/EN 61131-2
Input type
Status indicator
12 V DC (-13 % / +20 %)
3.9 mA @ 10.44 V DC
4.4 mA @ 12.0 V DC
5.3 mA @ 14.4 VDC
2.7 kΩ
≥ 7 V DC
≥ 2 mA
≤ 3 V DC
< 0.9 mA
1 →2 cycle times + 6 ms
Inputs I1 & I2 : FBD (up to 6 k Hz) & Ladder (1 k Hz)
Inputs I3 to IA & IH to IY : In accordance with cycle time (Tc) and
input response time (Tr) : 1/ ( (2 x Tc) + Tr)
Type 1
Resistive
None
None
Yes
24 V DC (-20 % / +25 %)
2.6 mA @ 19.2 V DC
3.2 mA @ 24 V DC
4.0 mA @ 30.0 VDC
7.4 kΩ
≥ 15 V DC
≥ 2.2 mA
≤ 5 V DC
< 0.75 mA
Type 1
Resistive
None
None
Yes
4 inputs IB →IE
6 inputs IB →IG
4 inputs IB →IE
6 inputs IB →IG
(0 →10 V) or (0 →V power supply)
14 kΩ
14.4 V DC max.
14 mV
Common mode
10 bit at max. input voltage
Controller cycle time
±5%
± 6.2 %
±2%
None
10 m maximum, with shielded cable (sensor not isolated)
Yes
2.2 kΩ/0.5 W (recommended)
10 kΩ max.
12 kΩ
30 V DC max.
29 mV
Common mode
±5%
± 6.2 %
±2%
None
Yes
10 kΩ max.
0.7 mA @ 10.44 VDC
0.9 mA @ 12.0 VDC
1.0 mA @ 14.4VDC
14 kΩ
≥ 7 V DC
≥ 0.5 mA
≤ 3 V DC
≤ 0.2 mA
1 →2 cycle times
1/ ( (2 x Tc) + Tr)
Type 1
Resistive
None
None
Yes
1.6 mA @ 19.2 VDC
2.0 mA @ 24.0 V DC
2.5 mA @ 30.0 VDC
12 kΩ
≥ 15 VDC
≥ 1.2 mA
≤ 5 V DC
≤ 0.5 mA
1 →2 cycle times
1/ ( (2 x Tc) + Tr)
Type 1
Resistive
None
None
Yes
Analogue or digital inputs (IB to IG)
CB12-CD12-XD10-XB10
CB20-CD20-XB26-XD26
Inputs used as analogue inputsonly in FBD
Measurement range
Input impedance
Input voltage
Value of LSB
Input type
Resolution
Conversion time
Accuracy at 25 °C
Accuracy at 55 °C
Repeat accuracy at 55 °C
Isolation between analogue channel and power supply
Cable length
Potentiometer control
Inputs used as digital inputs
Input voltage
Input current
Input impedance
Response time
Maximum counting frequency in FBD
Sensor type
Input type
02/11/2015
www.crouzet.com
Status indicator
Breaking current
Minimum load
Maximum rate
Mechanical life
Status indicator
5 →30 V DC
24 →250 V AC
12A (10A UL) for O8, O9, OA
12 V, 10 mA
Off load : 10 Hz
Make 10 ms
Release 5 ms
Digital / PWM solid state output
PWM solid state output*
* Only available with "FBD" programming language
Breaking voltage
Nominal voltage
Nominal current
Max. breaking current
Voltage drop
Response time
Operating frequency
Min. load
Maximum incandescent load
Galvanic isolation
PWM frequency
PWM cyclic ratio
Max. Breaking current PWM
Max. cable length PWM
PWM accuracy at 120 Hz
PWM accuracy at 500 Hz
Status indicator
CB12 : O4
XD26 : O4 →O7
10.4 →30 V DC
12-24 VDC
0.5 A
0,625 A
≤ 2 V for I = 0.5 A (at state 1)
Make ≤ 1 ms
Release ≤ 1 ms
1 Maximum on inductive load
Against overloads and short-circuits : Yes
Against overvoltages (*) : Yes
Against inversions of power supply : Yes
(*) In the absence of a volt-free contact between the logic
controller output and the load
1 mA
0,2 A / 12 V DC
0,1 A / 24 V DC
No
14.11 Hz
56.45 Hz
112.90 Hz
225.80 Hz
451.59 Hz
1806.37 Hz
0 →100 % (256 steps for CD, XD and 1024 steps for XA)
50 mA
20 m