Relay with 2 changeover contact
and status indication
(Relay height: 15 mm)
Nominal input voltage VN
AC 24 V, 115 V, 230 V
Voltage (V)
Relay with 1 changeover contact
24 V, 115 V, 230 V AC
300
2-pole
resistive load
200
2 contacts in serie
100
1 contact
50
40
30
0.1 0.2
0.5
1
2
5
10 20
Current (A)
Load limit curve for 788-311 to 788-315, 788-512, 788515 and 788-516
Notes:
• Safe isolation between coil and contacts per DIN EN 50178
• A separator plate (e.g., 209-191) must be used for voltages
greater than 250 V between adjacent relay modules and for safe
isolation.
• Inductive loads have to be attenuated by an appropriate
protective circuit in order to protect relay coils and contacts.
Description
VN
IN
Item No.
Pack.
Unit
VN
IN
Item No.
Pack.
Unit
Relay socket with miniature switching relay,
for DIN 35 rail
24 V AC
115 V AC
230 V AC
34 mA
8 mA
3.5 mA
788-506
788-507
788-508
1
1
1
24 V AC
115 V AC
230 V AC
34 mA
8 mA
3.5 mA
788-512
788-515
788-516
1
1
1
Technical Data
Coil:
Input voltage range
Contacts:
Contact material
Max. continuous current
Max. make current
Max. switching voltage
Max. switching power (resistive)
Recommended minimum load
Pull-in/drop-out/bounce time typ.
Mechanical life
General specifications:
Nominal voltage to EN 60664-1
Dielectric strength, contact-coil (AC, 1 min)
Dielectric strength open contact (AC, 1 min)
Dielectric strength contact-contact (AC, 1 min)
Ambient operating temperature at VN
Storage temperature
Dimensions (mm) W x H x L
Wire connection
Cross sections
Strip length
Standards/specifications
WAGO Kontakttechnik GmbH & Co. KG
Subject to design changes
20.04.2015
Accessories see pages 50 … 55
VN ± 10 %
VN ± 10 %
AgNi 90/10
16 A
4 s 30 A (AC)
250 V AC
4 kVA AC, DC see load limit curve
12 VDC / 10 mA
8ms / 6ms / 6 ms
10 x 106 switching operations
AgNi 90/10
2x8A
4 s 15 A (AC)
250 V AC
2 x 2 kVA AC, DC see load limit curve
12 VDC / 10 mA
8ms / 6ms / 10 ms
5 x 106 switching operations
250 V / 4 kV / 3
5 kVrms
1 kVrms
-25 °C ... +50 °C
-40 °C ... +70 °C
15 x 54 x 86
Height from upper-edge of DIN 35 rail
Push-in CAGE CLAMP®
0.34 mm² … 2.5 mm² / AWG 22 … 12
9 … 10 mm / 0.35 … 0.39 in
EN 61140; EN 50178; g;
UL 508 (788-507, 788-508: UL 508, max. 40 °C/10 A)
250 V / 4 kV / 3
5 kVrms
1 kVrms
2.5 kVrms
-25 °C ... +50 °C
-40 °C ... +70 °C
15 x 54 x 86
Push-in CAGE CLAMP®
EN 61140; EN 50178; UL 508; g
Postfach 2880 - D-32385 Minden
Hansastr. 27 - D-32423 Minden
Tel.: +49(0)571/887-0
E-Mail: info@wago.com
Fax: +49(0)571/887-169
www.wago.com
很抱歉,暂时无法提供与“788-507”相匹配的价格&库存,您可以联系我们找货