8340-F410-P1M4-N2H143-16A
    E-T-A
8340-F410-P1M4-N2H143-16A 数据手册
Magnetic and Hydraulic-Magnetic Circuit Breaker 8340-F... Description Single and multipole magnetic circuit breakers with trip-free mechanism and toggle actuation. A choice of fast magnetic only or hydraulically delayed switching characteristics (S-type MO or HM CBE to EN 60934) ensures suitability for a wide range of applications. Industry standard dimensions and panel mounting. Options include auxiliary changeover contacts. Low temperature sensitivity at rated load. Approved to CBE standard EN 60934 (IEC 60934). Typical application Control equipment, communications systems, transportation, power supplies. Standard current ratings and typical internal resistance values Current rating (A) Internal resistance values (Ω) per pole 0,02 1 493 0,05 276 0,1 F1 F2 K1, M1, T1 K2, M2, T2 953 2 669 2 457 152 452 376 58 37 100 94 0,25 8,2 6,0 15,5 14,7 0,5 2,3 1,47 3,9 3,2 0,75 0,98 0,63 1,65 1,56 1 0,58 0,35 0,95 0,90 2 0,145 0,096 0,26 0,20 2,5 0,096 0,061 0,15 0,15 3 0,065 0,048 0,10 0,10 5 0,025 < 0,02 0,042 0,040 6 < 0,02 < 0,02 0,029 0,028 8 < 0,02 < 0,02 < 0,02 < 0,02 10 < 0,02 < 0,02 < 0,02 < 0,02 12 < 0,02 < 0,02 < 0,02 < 0,02 15 < 0,02 < 0,02 < 0,02 < 0,02 16 < 0,02 < 0,02 < 0,02 < 0,02 20 < 0,02 < 0,02 < 0,02 < 0,02 25 < 0,02 < 0,02 < 0,02 < 0,02 30 < 0,02 < 0,02 < 0,02 < 0,02 40 < 0,01 - < 0,01 - 50 < 0,01 - < 0,01 - 8340-F... 1-pole 1 2-pole Technical data For further details please see: http://www.e-t-a.de/ti_e Voltage rating 3 AC 415 V; AC 240 V, 50/60 Hz; DC 80 V (higher DC ratings to special order) Current ratings 0.02...50 A DC 0.02...30 A AC Auxiliary circuit 6 A, AC 240 V; 3 A, DC 28 V 1 A, DC 65 V; 0.5 A, DC 80 V Typical life 3 AC 415 V, AC 240 V: 0.02...30 A 6,000 operations at 1 x IN, inductive 10,000 operations at 1 x IN, resistive DC 80 V: 0.02...25 A 6,000 operations at 1 x IN, inductive 0.02...30 A 10,000 operations at 1 x IN, resistive 40 + 50 A 6,000 operations at 1 x IN, resistive Ambient temperature -40...+85 °C (-40...+185 °F) Insulation co-ordination rated impulse pollution (IEC 60664 and 60664A) withstand voltage degree 2.5 kV 2 reinforced insulation in operating area Dielectric strength (IEC 60664 and 60664A) operating area test voltage AC 3,000 V Line to Load test voltage AC 1,500 V pole to pole (2- and 3-pole) test voltage AC 1,500 V main to auxiliary circuit test voltage AC 3,000 V switching to trip circuit test voltage AC 1,500 V (version -X) Insulation resistance > 100 MΩ (DC 500 V) Interrupting capacity 6 x IN at AC; IEC 60934 - test sequence E 4 x IN at DC Interrupting capacity (UL 1077) AC: DC: IN 0.02...20 A 25...30 A 1-pole AC 250 V/3,500A AC 250 V/3,500A 2-pole AC 250 V/3,500A AC 250 V/5,000A 3-pole 3AC 250V/3,500A 3AC250V/5,000A 1-pole 0.02...50 A 2-pole 0.02...30 A DC 80 V/3,500 A DC 80 V/3500 A Degree of protection operating area IP40 (IEC 60529/DIN 40050) terminal area IP00 Vibration with toggle down: 10 g (57-2000Hz) ± 0.76 mm (10-57 Hz) at 0.9 x IN directions 1, 2, 3, 4, 5: 10 g (57-2000 Hz) at 1 x IN. Shock 100 g (11 ms) at 1 x IN, directions 1,2,3,4,5 Corrosion Humidity Mass 2137 www.e-t-a.de 100 g (11 ms) at 0.8 x IN, direction 6. 96 hours at 5 % salt mist, to IEC 60068-2-11, test Ka 240 hours at 95 % RH to IEC 60068-2-78, test Cab approx. 65 g per pole 1 Magnetic and Hydraulic-Magnetic Circuit Breaker 8340-F... Approvals Ordering information 1 Type No. 8340 magnetic circuit breaker with toggle actuator Mounting F flange mounting Configuration 1 with mounting nuts 6-32 UNC 4 with mounting nuts M3 9 snap-in frame Number of poles 1 single pole protected magnetic and 2 two pole protected hydraulic magnetic delayed 3 three pole protected Panel hardware 0 without panel hardware Terminal design (main contact) K4 screw terminals M5 recommended for IN > 20 A P1 blade terminals A6.3-0.8 mm (QC.250) (≤ 35 A) Characteristic curve *) Characteristic curve, instantaneous: F1 DC F2 AC 50/60 Hz Short delay: K1 DC K2 AC 50/60 Hz Medium delay: M1 DC M2 AC 50/60 Hz Long delay: T1 DC T2 AC 50/60 Hz Actuator colour/design A black, long toggle K black, short toggle Z black, without toggle, with slot (only 1-pole) other colours to special order Marking on actuator 0 without marking L I-O; ON-OFF N I-O; ON-OFF (IN on housing top) Auxiliary contacts H0 without auxiliary contacts H1 with auxiliary contacts, gold-flushed H2 auxiliary contacts, gold-flushed on one pole only (multipole) Auxiliary contact function 4 1 change over contact Auxiliary contact terminal design 2 blade terminal 2.8-0.5 mm Current ratings 0.02...50 A } Authority Standard Rated voltage Current ratings VDE IEC / EN 60934 UL UL 1077 AC 240/415 V AC 240 V DC 80 V AC 250 V DC 80 V DC 80 V CSA C22.2 No 235 AC 250 V DC 80 V 0.02 A…30 A 0.02 A…30 A 0.02 A…50 A 0.02 A…30 A 0.02 A…50 A 100 A (2 poles in parallel) 0.02 A…30 A 0.02 A…40 A CQC GB 17701 QPL Sweden Defence Material Admin. MIL-C-55629 AC 240/415 V AC 240 V DC 80 V AC 240 V DC 50 V AC 240 V AC 240 / 415 V 0.02 A…30 A 0.02 A…30 A 0.02 A…50 A 1 A…30 A (8340-F410) 1 A…30 A (8340-410) 1 A…30 A (8340-F420) 1 A…30 A (8340-F430) Internal connection diagrams 1-pole protected magnetic line 1 multipole line 1 11(C) 11(C) unit 1 12(NC) 14(NO) I> 12(NC) 14(NO) 2 I> unit 2 1-pole protected hydraulic-magnetic line 1 11(C) 1 2 load 12(NC) 14(NO) 11(C) I> 2 load unit 3 12(NC) 14(NO) I> 2 load 8340 - F 1 1 0 - P1 M1 - A L H1 4 2 - 30A ordering example  characteristic curves upon request (e.g. pulse delayed, for high *) Other inrush currents or capacitive loads) Please be informed that we have minimum ordering quantities to be observed. Preferred types Preferred types Standard current ratings (A) 1 2 3 5 8 10 12 16 20 8340-F410-P1K1-KNH0- x x x x x x x x x 25 30 40 50 8340-F410-P1K1-KNH142- x x x x x x x x x 8340-F410-P1M1-KNH0- x x x x x x x x x 8340-F410-P1M1-KNH142- x x x x x x x x 8340-F410-K4K1-KNH0- x x x x x 8340-F410-K4K1-KNH142- x x x x 8340-F410-K4M1-KNH0- x x x x 8340-F410-K4M1-KNH142- x x x x 2 www.e-t-a.de 2137 Magnetic and Hydraulic-Magnetic Circuit Breaker 8340-F... Dimensions Flange mounting Configuration: F4 Configuration: F9 Actuator: long toggle 3.3 .130 17.5 .689 OFF 30° 30° ON OFF 41.2 1.62 41.2 1.62 ON 5.5 .217 3 .118 30° 30° 14.4 .567 Actuator: long toggle 1 4 1 4 19 .748 2 Ø15 .591 19 .748 27.4 1.08 Actuator: short toggle ON 3 50.8 2.00 66 2.60 4.3 .169 26.7 1.05 42.2 1.66 30° 8.6 .339 30° 1 2 3 50.8 2.00 OFF Actuator: short toggle 5.5 .217 30° 30° OFF 5.6 .220 3.3 .130 ON 1 4 2 3 Actuator: without toggle, with slot 30° 30° ON Actuator: without toggle, with slot 30° 30° OFF OFF 3.3 .130 ON 4 2 3 5.3 .208 1 number of poles: 1-3 Pole Applicable for nominal dimensions without direct tolerance indication: DIN ISO 286 ± IT13 1 2 3 number of poles: 1-3 pole: 1 2 3 Cut-out dimensions max. panel thickness: 2 ± 0.1 mm or 4 ± 0.15 mm (snap-fit) 19 .748 Cut-out dimensions max. panel thickness: 3 mm mounting thread M3 or 6-32 UNC-2B mounting depth max. 4.5 mm/.177 in. tightening torque max. 0.33 Nm 19.2±0.2 .756±.008 3.5±0.1 (M3) +0.1 4 -0.15 (6-32UNC) 55.4±0.2 2.18±.008 1.66±.004 42.2±0.1 26.7±0.1 1.05±.004 Ø16±0.12 .630±.004 .138±.004 (M3) +.004 .157-.006 (6-32UNC) 57.6±0.2 2.27±.008 38.4±0.2 1.51±.008 Applicable for nominal dimensions without direct tolerance indication: DIN ISO 286 ± IT13 19.05±0.12 .750±.005 38.1±0.12 1.50±.005 This is a metric design and millimeter dimensions take precedence ( mm ) inch 2137 www.e-t-a.de 3 Magnetic and Hydraulic-Magnetic Circuit Breaker 8340-F... Actuator configuration Terminal design / Dimensions Actuator design number of poles: 1 - 3 Configuration: F4 K4 screw terminals M5 tightening torque max. 1.2 Nm Actuator long 1 1 1 OFF 0 OFF 0 16 A OFF 0 2 OFF 0 16 A 6 .236 Actuator short 9.4 .370 38.8 1.53 P1 blade terminals OFF 0 OFF 0 3 9.7 .382 OFF 0 OFF 0 16 A 4 16 A 16 A 1 Actuator long 16 A 3 6 .236 OFF 0 OFF 0 16 A 16 A OFF 0 OFF 0 OFF 0 16 A 16 A 16 A 38.8 1.53 blade terminals DIN 46244-A6.3-0.8 Auxiliary contacts number of poles: 1 Configuration: F4 / F9 1 2 11 5 .197 Actuator: Z (black, without toggle, with slot) OFF 2 OFF 17.9 .705 10.2 .401 14 12 14.5 .571 OFF 0 4 9.6 .378 number of poles: 1 - 3 Configuration: F9 5.1 .200 blade terminals DIN 46244-A2.8-0.5 16 A 16 A Shock directions / Mounting attitudes Installation drawing 12 Terminal design P mounting area 4 .157 2 .079 5 6 terminal area 8 .315 42 1.65 29 1.14 30 1.18 7 .276 1 .039 2 .079 7 .276 30 1.18 operating area (reinforced insulation) 1 .039 blow out outlet CBE 1 .039 Terminal design K 34 8 .315 42 1.65 29 1.14 blow out area (minuaturable on request) Trip time values indicated for front mounting on a vertical even surface This is a metric design and millimeter dimensions take precedence ( mm ) inch 4 www.e-t-a.de 2137 Magnetic and Hydraulic-Magnetic Circuit Breaker 8340-F... Typical time/current characteristics at 23 °C / +73.4 °F Curve F2 (instantaneous) for AC Curve F1 (instantaneous) for DC 1000 1000 100 100 Trip time in seconds 10000 Trip time in seconds 10000 10 1 0,1 10 1 0,01 0,01 0,001 0,001 0 1 2 3 4 5 6 7 8 … times rated current 9 10 11 0 12 Curve K1 (short delay) for DC 1000 100 100 Trip time in seconds 1000 Trip time in seconds 10000 10 1 0,1 0,01 4 5 6 7 … times rated current 8 9 10 11 12 Curve M1 (medium delay) for DC 0 9 10 11 12 1 2 3 4 6 5 7 … times rated current 8 9 10 11 12 8 9 10 11 12 8 9 10 11 12 Curve M2 (medium delay) for AC 50/60 Hz 10000 1000 1000 100 100 Trip time in seconds 10000 Trip time in seconds 5 7 8 4 6 … times rated current 0,1 0,001 3 3 1 0,001 2 2 10 0,01 1 1 Curve K2 (short delay) for AC 50/60 Hz 10000 0 10 1 0,1 0,01 10 1 0,1 0,01 0,001 0,001 0 1 2 3 4 5 6 7 8 … times rated current 9 10 11 12 Curve T1 (long delay) for DC 0 1 2 3 4 6 7 5 … times rated current Curve T2 (long delay) for AC 50/60 Hz 10000 1000 1000 100 100 Trip time in seconds 10000 Trip time in seconds 1 0,1 10 1 0,1 0,01 10 1 0,1 0,01 0,001 0 1 2 3 5 6 7 4 … times rated current 8 9 10 11 12 0,001 0 1 2 3 4 5 6 7 … times rated current N.B. All curves will only be maintained if the escutcheon is mounted on a vertical surface. Ambient temperature or mounting side-by-side does not influence the trip curve, derating is not required. The breakers may trip in the event of current peaks < 0.003 sec. For these applications we offer a mechanical pulse delay – please enquire. Other characteristic curves upon request (e.g. pulse delayed, for high inrush currents or capacitive loads). 2137 www.e-t-a.de 5 Magnetic and Hydraulic-Magnetic Circuit Breaker 8340-F... Accessories Splash cover with mounting plate and screws for 8340-F1.. and 8340-F4 1 pole Y 303 565 01 16.7 .657 mounting holes 18 .708 1 .039 Ø 2 pole for 8340-F4 X 211 118 01 [.1 38 40 1.57 ]- mounting holes 40.15±0.15 1.58±.006 M 3 19.2±0.1 .756±.004 6 2.2 .087 3 pole for 8340-F4 X 211 119 01 mounting holes 59.15±0.15 2.33±.006 37.9 1.49 2 .079 15.7 .618 19 .748 15.7 Ø2 5 Ø.9 .15 ±0.15 .618 90 ±.0 0 37.9 1.49 42.4±0.15 1.670±.006 2 .079 3.5 15 0. 8] - [.13 57 2.24 .5 2.2 .087 Ø3 19 .748 5± .1 .006 25 0± Ø .99 Ø 37.8±0.15 1.49±.006 42.4±0.15 1.670±.006 1 Ø1 7. Ø3 1 [.6 73 Ø4 .5 ] [.1 [.13 57 8] ]- -M 632 3 UN C 15.7 .618 30.7 1.20 42.4±0.15 1.670±.006 2 .079 M3 21 3.3 40 1.57 1.6 x 45° .063x45° Toggle guard for 8340-F1.. and 8340-F4 Y 307 250 01 17.7 .697 Ø 3.5 Ø .138 50.5 1.99 This is a metric design and millimeter dimensions take precedence ( mm ) inch All dimensions without tolerances are for reference only. In the interest of improved design, performance and cost effectiveness the right to make changes in these specifications without notice is reserved.Product markings may not be exactly as the ordering codes. Errors and omissions excepted. 6 www.e-t-a.de 2137
物料型号:8340-F
器件简介:该文档描述了一种单极和多极磁力断路器,具有无行程机构和切换操作。提供了快速磁力或液压延迟切换特性的选择,确保适用于广泛的应用场景。
引脚分配:文档中未明确提供引脚分配图,但提供了内部连接图和端子设计。
参数特性:包括额定电压、电流额定值、辅助电路、典型寿命、环境温度、绝缘协调、耐压强度、绝缘电阻、断路容量等。
功能详解:提供了详细的技术数据和特性曲线,例如瞬时动作的F1和F2曲线,短延时的K1和K2曲线,中延时的M1和M2曲线,长延时的T1和T2曲线。
应用信息:适用于控制设备、通信系统、运输、电源等。
封装信息:提供了详细的安装尺寸、操作区域尺寸、端子设计尺寸等。
8340-F410-P1M4-N2H143-16A 价格&库存
很抱歉,暂时无法提供与“8340-F410-P1M4-N2H143-16A”相匹配的价格&库存,您可以联系我们找货
