SU750RTXL2U
SU750RTXL2U
    TRIPPLITE
    UPS 750VA 600W 6OUT RACK MOUNT
SU750RTXL2U 数据手册
1000 Eaton Boulevard Cleveland, OH 44122 United States SmartOnline 120V 750VA 600W DoubleConversion UPS, 2U Rack/Tower, Extended Run, Network Card Options, USB, DB9 Serial Highlights ● 750VA / .75kVA / 600 watt online double-conversion 2U rack/tower UPS ● 120V +/-2% output at 50/60Hz, high efficiency economy mode option ● Expandable runtime, Hot-swap batteries; 13.5 in / 34.3cm installed depth ● USB, RS232 & EPO ports; support for network management card options ● Front panel status LEDs with detailed load and battery metering ● 2 independently switchable output load banks ● NEMA 5-15P input; 5-15R outlets ● To use the Auto Probe feature, this product requires a WEBCARDLX network interface (sold separately) running LX firmware update 15.5.2 or later MODEL NUMBER: SU750RTXL2U Description 750VA online, double-conversion UPS system for critical server, network and telecommunications equipment. 2U rackmount form factor with an installed depth of only 13.5 inches. Extended runtime available with optional BP24V15RT2U (limit 1), BP24V28-2U (limit 1), BP24V70-3U (multi-pack compatible) and BP24V36-2US (multi-pack compatible) external battery packs. Full-time sine wave 120V output with +/-2% voltage regulation. Online, double-conversion Uninterruptible Power Supply (UPS) actively converts raw incoming AC power to DC, then re-converts output back to completely regulated, filtered AC output. Operates continuously without using battery power during brownouts to 65V and overvoltages to 150. NEMA 5-15P input plug; NEMA 5-15R output receptacles. Network-grade AC surge and noise suppression. Zero transfer time between AC and battery operation. Network management interfaces support simultaneous communications via USB port, DB9 serial port and slot for network management card options. Built-in DB9 port offers both enhanced RS-232 enabled monitoring data, plus contact closure monitoring ability. HID-compliant USB interface enables integration with built-in power management and auto shutdown features of Windows and Mac OS X. Supports simultaneous detailed monitoring of equipment load levels, self-test data and utility power conditions via all 3 network interfaces. PowerAlert monitoring software is available via free download. Emergency Power Off (EPO) interface. Integrated two-bank PDU switching supports load shedding and remote reboot of connected equipment. 3-stage metered current monitoring and battery charge status LEDs. LED display panel easily rotates for viewing in rackmount or tower configurations. Dataline surge suppression for dialup, DSL or network Ethernet connection. Utility power and voltage regulation LEDs. Audible alarm. Self-test. Fault-tolerant auto-bypass mode. 4-post rackmount accessories included; 2-9USTAND tower kit and 2POSTRMKITWM 2-post rack & wallmount accessories available. Field-replaceable, hot-swappable internal batteries and external battery packs. Attractive all-black color scheme. $250,000 Ultimate Lifetime Insurance (U.S., Canada, and Puerto Rico only). Features ● SmartOnline high-performance UPS system is ideal for critical voice, data, medical and industrial network applications ● True online, double-conversion UPS provides perfectly regulated sine wave output within 2% of 120V under all usage conditions ● Maintains continuous operation through blackouts, voltage fluctuations and surges with zero transfer time ● Removes harmonic distortion, fast electrical impulses, frequency variations and other hard-to-solve power problems not addressed by other UPS types 1/7 Package Includes ● SU750RTXL2U Online DoubleConversion UPS System ● USB, DB9 and EPO cables ● Mounting hardware for 4-post rack enclosures ● Instruction manual 1000 Eaton Boulevard Cleveland, OH 44122 United States ● Corrects line voltage conditions as low as 65V and as high as 150V back to 120V (+/-2%) values ● Standard internal battery set offers 11 min. runtime at half load (300W) and 6 min. at full load (600W) ● Extended runtime available with optional BP24V15RT2U (limit 1), BP24V28-2U (limit 1), BP24V70-3U (multi-pack compatible) and BP24V36-2US (multi-pack compatible) external battery packs ● Intelligent battery management system extends battery life ● Some external battery configurations require the use of Tripp Lite's External Battery Configuration Software (see manual) ● Compact rackmount form factor installs using only 2 rack spaces (2U) with a maximum installed depth of only 13.5 inches ● Ships with all mounting accessories for 4-post rackmount installation ● Optional 2POSTRMKITWM enables 2-post rackmount or wallmount installation ● Optional 2-9USTAND accessory enables small-footprint upright tower placement ● Fault tolerant electronic bypass maintains utility output during a variety of UPS fault conditions ● Network interfaces support simultaneous communications via built-in USB, DB9 serial / contact-closure and slot for network management card options ● Compatible with Tripp Lite UPS management card options TLNETCARD, WEBCARDLX, SNMPWEBCARD, MODBUSCARD and RELAYIOCARD ● HID-compliant USB interface enables integration with built-in power management and auto shutdown features of Windows and Mac OS X ● USB & Serial ports enable data-saving unattended shutdown when used with Tripp Lite's PowerAlert software, available via FREE download from tripplite.eaton.com/products/power-alert ● Built-in Emergency Power Off (EPO) interface with cable ● NEMA 5-15P input plug/NEMA 5-15R output receptacles ● Integrated 2-bank switched PDU enables remote outlet management for load shedding or remote reboot of individual devices (each load bank consists of a single outlet) ● Front panel LEDs offer current monitoring and battery charge level information ● UPS ships fully assembled in full compliance with DOT regulations; no time-consuming connection of internal batteries by user required ● Single-line tel/DSL or network Ethernet line surge suppression ● $250,000 Ultimate Lifetime Insurance (U.S., Canada, and Puerto Rico only) Specifications OVERVIEW UPC Code 037332126443 UPS Type On-Line INPUT Input Phase Single-Phase Rated input current (Maximum Load) 8.6A Nominal Input Voltage(s) Supported 120V AC UPS Input Connection Type 5-15P Input Circuit Breakers 15A UPS Input Cord Length (ft.) 6 2/7 1000 Eaton Boulevard Cleveland, OH 44122 United States UPS Input Cord Length (m) 1.8 Recommended Electrical Service 15A 120V OUTPUT Output Capacity (VA) 750 Output Capacity (kVA) 0.75 Output Capacity (Watts) 600 Output Capacity (kW) 0.6 Output Capacity Details OVERLOAD CAPACITY: Supports inverter operation up to 105% load continuously, 125% load for 3 minutes; 150% load for 30 seconds and >150% load for 0.5 seconds before switching to BYPASS (when bypass input voltage and frequency are WITHIN bypass limits) or SHUTDOWN (when bypass input voltage or frequency are OUTSIDE bypass limits) Power Factor 0.8 Crest Factor 3:1 Frequency Compatibility 50 / 60 Hz Frequency Compatibility Details Output frequency matches input nominal on startup, defaults to 60 Hz on cold-start Output Voltage Regulation (Line Mode) +/- 2% Output Voltage Regulation (Battery Mode) +/- 2% Load Management Receptacles Two switchable single-outlet 5-15R load banks Output AC Waveform (AC Mode) Sine wave Output AC Waveform (Battery Mode) Pure Sine wave Nominal Output Voltage(s) Supported 120V Output Receptacles (6) 5-15R Individually Controllable Load Banks Yes BATTERY Battery Type Valve Regulated Lead Acid (VRLA) Runtime Full Load (min.) 4 min. (600W) Runtime Half Load (min.) 11 min. (300W) Expandable Runtime Yes External Battery Pack Compatibility  BP24V15RT2U  (limit 1);  BP24V28-2U  (limit 1);  BP24V70-3U  (multi-pack compatible);  BP24V362US  (multi-pack compatible) DC System Voltage (VDC) 24 3/7 1000 Eaton Boulevard Cleveland, OH 44122 United States Battery Recharge Rate (Included Batteries) Less than 6 hours from 10% to 80% (typical, full load discharge) Battery Access Front panel battery access door Internal UPS Replacement Battery Cartridge  RBC92-2U  Battery Replacement Description Hot-swappable, user replaceable batteries VOLTAGE REGULATION Voltage Regulation Description Online, double-conversion power conditioning Overvoltage Correction 2% output voltage regulation during overvoltages to 150 Undervoltage Correction 2% output voltage regulation during undervoltages to 80 Severe Undervoltage Correction 2% output voltage regulation during undervoltages to 65 (under 70% load only) USER INTERFACE, ALERTS & CONTROLS Switches 2 Switches control off/on power status and alarm-cancel/self-test operation Alarm Cancel Operation Power-fail alarm can be silenced using alarm-cancel switch Audible Alarm Audible alarm indicates UPS startup, power-failure, low-battery, overload, UPS fault and remote shutdown conditions LED Indicators 14 LEDs indicate line power, online mode, bypass mode, on-battery, overload, battery low, replace battery and fault status information; 4-LED meter displays load and battery charge levels; LED panel rotates for viewing in rack/tower formats SURGE / NOISE SUPPRESSION UPS AC Suppression Joule Rating 480 UPS AC Suppression Response Time Instantaneous UPS Dataline Suppression 1 line TEL/DSL (1 in / 1 out); 10/100Base T Ethernet EMI / RFI AC Noise Suppression Yes PHYSICAL Primary Form Factor Rackmount Rack Height 2U Cooling Method Fan Included Mounting Accessory Description Included 4POSTRAILKIT mounting bracket enables installation in 4 post racks from 20.5 to 36 inches (521 to 914mm) Installation Form Factors Supported with Included Accessories 4 post 19 inch rackmount 4/7 1000 Eaton Boulevard Cleveland, OH 44122 United States Installation Form Factors Supported with Optional Accessories 2 post rackmount ( 2POSTRMKITWM ); 2-4 post front rail rackmount ( UPSHDEARKIT ); 4 post rackmount short-depth ( 4POSTRAILKITWM ); Tower ( 29USTAND ); Wallmount ( 2POSTRMKITWM ) Minimum Required Rack Depth (cm) 43.18 Minimum Required Rack Depth (inches) 17 Optional Mounting Accessory Notes Optional  2-9USTAND  enables upright tower UPS placement;  2POSTRMKITWM  enables wall-mount and 2-post rackmount installation;  4POSTRAILKITWM  enables installation in 4-post short-depth racks from 14.5 to 23.5 inches (368 to 597mm);  UPSHDEARKIT  enables installation in 2 or 4-post racks using front vertical rails only, without rear support Primary UPS Depth (mm) 343 Primary UPS Height (mm) 89 Primary UPS Width (mm) 445 Shipping Dimensions (hwd / in.) 9.10 x 23.30 x 19.60 Shipping Dimensions (hwd / cm) 23.11 x 59.18 x 49.78 Shipping Weight (lbs.) 41.00 Shipping Weight (kg) 18.60 UPS Housing Material Steel UPS Power Module Dimensions (hwd, cm) 8.89 x 44.45 x 34.29 UPS Power Module Dimensions (hwd, in.) 3.5 x 17.5 x 13.5 UPS Power Module Weight (kg) 13.15 UPS Power Module Weight (lbs.) 29 Unit Weight (lbs.) 29.0000 Unit Weight (kg) 13.15 ENVIRONMENTAL Operating Temperature Range 32° to 104°F (0° to 40°C) Storage Temperature Range 5° to 122°F (-15° to 50°C) Relative Humidity 0 to 95%, non-condensing AC Mode BTU / Hr. (Full Load) 279 Battery Mode BTU / Hr. (Full Load) 333 AC Mode Efficiency Rating (100% Load) 87% 5/7 1000 Eaton Boulevard Cleveland, OH 44122 United States AC Economy Mode Efficiency Rating (100% Load) 97% COMMUNICATIONS Network Management Cards SNMPWEBCARD;  TLNETCARD ;  WEBCARDLX ;  MODBUSCARD ;  RELAYIOCARD  Network Monitoring Port Description Supports detailed monitoring of UPS and site power conditions; DB9 port supports RS232 and contact closure communications; Economy-mode setting option is available using PowerAlert software and DB9 Serial cable connection OR via select Network Management Card options PowerAlert Software For local monitoring via the UPS’s built-in communication ports, download PowerAlert software at https://tripplite.eaton.com/products/power-alert Communications Cable USB and DB9 cabling included WatchDog Compatibility Supports Watchdog application, OS and hard-reboot restart options for remote applications Network Management Card Description Network management card optional Communications Interface Contact closure; DB9 Serial; EPO (emergency power off); Slot for SNMP/Web interface; USB (HID enabled) LINE / BATTERY TRANSFER Transfer Time No transfer time (0 ms.) in online, double-conversion mode Low Voltage Transfer to Battery Power (Setpoint) 80V (100% load), 65V (
SU750RTXL2U
物料型号:SU750RTXL2U 器件简介:SmartOnline 120V 750VA 600W 双转换 UPS,2U 机架/塔式,扩展运行时间,网络卡选项,USB,DB9 串行接口。
引脚分配:NEMA 5-15P 输入插头;NEMA 5-15R 输出插座。
参数特性:750VA 在线,双转换 UPS 系统,适用于关键服务器、网络和电信设备。
2U 机架安装尺寸,安装深度仅为 13.5 英寸。
扩展运行时间可通过选购外部电池包实现。
全时正弦波 120V 输出,电压调节在 +1-2% 之间。
功能详解:在线双转换不间断电源 (UPS) 在输入时将原始交流电源转换为直流,然后重新转换为完全调节、过滤后的交流输出。
在电压骤降至 65V 至过电压至 150V 期间,无需使用电池即可持续运行。
网络级交流浪涌和噪音抑制。
在交流和电池操作之间零转换时间。
网络管理接口支持通过 USB 端口、DB9 串行端口和网络管理卡选项插槽进行同时通信。
内置 DB9 端口提供增强的 RS-232 启用监控数据以及接触闭合监控功能。
符合 HID 标准的 USB 接口,可与 Windows 和 Mac OS X 的内置电源管理和自动关机功能集成。
支持通过所有 3 个网络接口同时详细监控设备负载水平、自检数据和公用电源条件。
可通过免费下载的 PowerAlert 监控软件进行监控。
紧急电源关闭 (EPO) 接口。
集成的两组 PDU 开关支持负载卸载和远程重启连接的设备。
3 阶段计量电流监控和电池充电状态 LED。
LED 显示面板易于旋转,以便在机架安装或塔式配置中查看。
拨号线浪涌抑制适用于拨号、DSL 或网络以太网连接。
公用电源和电压调节 LED。
声音报警。
自检。
容错自动旁路模式。
包括 4 柱机架配件;2-9USTAND 塔式套件和 2POSTRMKITWM 2 柱机架 & 壁挂配件可用。
现场可更换的热插拔内部电池和外部电池包。
全黑色方案。
250,000 美元终极终身保险(仅限美国、加拿大和波多黎各)。
应用信息:SmartOnline 高性能 UPS 系统非常适合关键语音、数据、医疗和工业网络应用。
封装信息:2U 机架安装尺寸,安装深度仅为 13.5 英寸。
包括所有 4 柱机架安装的安装配件。
可选的 2POSTRMKITWM 可实现 2 柱机架安装或壁挂安装。
可选的 2-9USTAND 配件可实现小型占地面积的直立塔式放置。
容错电子旁路在各种 UPS 故障条件下保持公用事业输出。
网络接口支持通过内置 USB、DB9 串行/接触闭合和网络管理卡选项插槽进行同时通信。
兼容 UPS 管理卡选项 TLNETCARD、WEBCARDLX、SNMPWEBCARD、MODBUSCARD 和 RELAYIOCARD。
符合 HID 标准的 USB 接口,可与 Windows 和 macOS 的内置电源管理和自动关机功能集成。
USB 和串行端口可在使用 PowerAlert 软件时实现数据保存的无人值守关机,PowerAlert 软件可从 tripplite.eaton.com/products/power-alert 免费下载。
内置紧急电源关闭 (EPO) 接口。
NEMA 5-15P 输入插头/NEMA 5-15R 输出插座。
集成的 2 组开关式 PDU 可实现远程插座管理,用于负载卸载或远程重启单个设备(每个负载组由一个单独的插座组成)。
前面板 LED 提供电流监控和电池充电水平信息。
用户需要更换的内部电池 UPS 完全组装,完全符合 DOT 规定;无需耗时连接。
单线电话/DSL 或网络以太网线浪涌抑制。
SU750RTXL2U 价格&库存
很抱歉,暂时无法提供与“SU750RTXL2U”相匹配的价格&库存,您可以联系我们找货