SmartOnline Expandable Rack/Tower UPS System - On-line, double-conversion protection for mission-critical applications MODEL NUMBER: SU7500RT3U Highlights ● 7500VA on-line 6U rack/tower UPS with expandable runtime (3U power module + 3U battery pack) ● Detachable PDU with manual bypass switch enables hot-swap UPS replacement without powering off connected loads ● 200/208/230/240V selectable input/output voltage ● 2% output voltage regulation over an input voltage range of 156V to 276V ● Enhanced serial communications ports, SNMP/Web Card Slot and EPO interfaces ● $250,000 Ultimate LIfetime Insurance (USA & Canada only). Description 7,500 VA (7.5kVA) on-line, double-conversion UPS system for critical server, network and telecommunications equipment. Installs in only 6 rack spaces (3U power module and 3U battery pack). Maximum installed rack depth of 32.5 in. Expandable battery runtime with optional BP240V10RT3U and BP240V32 external battery packs. Full-time sine wave 200, 208, 220, 230, or 240V +/-2% output. Actively converts raw incoming AC power to DC, then re-converts output back to completely regulated, filtered AC output. Operates continuously without using battery power during brownouts to 156V and overvoltages to 276V. Standard 3-wire 208V hardwire input connection; NEMA L6-30R and L6-20R output receptacles. Detachable input-output PDU module with manual bypass switch enables hot-swap UPS replacement without disrupting power to connected equipment. Network-grade AC surge and noise suppression. Zero transfer time between AC and battery operation. Network management interfaces support communications via RS-232, contact-closure port and optional SNMPWEBCARD slot. Supports detailed monitoring of equipment load levels, self-test data and utility power conditions via network interfaces. Includes PowerAlert monitoring software and complete cabling. Emergency Power Off (EPO) interface. Front panel LEDs offer at-a-glance confirmation of line power status, battery power status, AC-to-DC conversion, DC-to-AC conversion, bypass mode and output power status. LCD panel with scroll buttons offers detailed diagnostic test information at startup and during self tests, plus real-time data on input and output voltage, frequency (Hz), load percentage and battery charge level. LED/LCD display panel easily rotates for viewing in rackmount or tower configurations. Audible alarm. Self-test. Fault-tolerant autobypass mode. 4-post rackmount accessories and 2-9USTAND tower kit included; 2POSTRMKITWM 2post rackmount hardware accessories available. Field replaceable, hot-swappable power module and external battery packs. Attractive all-black color scheme. 2-year warranty and $250,000 connected equipment insur; extended warranty and service contracts available. Package Includes ● 3U power module with detachable hot-swap PDU input/output panel and bypass switch ● 3U external battery pack ● Two sets of 4 post rackmount rails (one for each of the 3U components) ● One set of tower stands for upright tower configuration ● PowerAlert software, complete data cabling, user manual with warranty information Features ● 7,500 VA (7.5kVA) on-line, double-conversion UPS system (High voltage input/High voltage output) ● Detachable input-output PDU module with manual bypass switch enables hot-swap UPS replacement without powering off connected equipment ● Installs in only 6 rack spaces (3U power module/3U battery pack) with a maximum installed depth of 32.5 inches ● Offers 9 min. runtime at full load (7500VA/6000W) and 20 min. at half load (3750VA/3000W). Runtime is expandable with any number of optional BP240V10RT3U external battery packs ● Full-time sine wave 200, 208, 220, 230, or 240V +/-2% output (user selectable) ● Actively converts raw incoming AC power to DC, then re-converts output back to completely regulated, filtered AC output ● Operates continuously without using battery power during brownouts to 156V and overvoltages to 276V ● Standard 3-wire 208V hardwire input connection ● 2 x NEMA L6-30R and 4 x L6-20R output receptacles ● Detailed LCD panel with scroll buttons offers detailed diagnostic test information on startup and during self tests, plus real-time data on input and output voltage, frequency (Hz), load percentage, battery charge level and more ● Network-grade AC surge and noise suppression ● Zero transfer time between AC and battery operation ● Network management interfaces support communications via RS-232, contact-closure port and optional SNMPWEBCARD slot ● Supports detailed monitoring of equipment load levels, self-test data and mains power conditions via network interfaces. Includes PowerAlert monitoring software and complete cabling ● Emergency Power Off (EPO) interface 1/4 ● Front panel LEDs offer at-a-glance confirmation of line power status, battery power status, AC-to-DC & DC-to-AC conversion, bypass mode and output power status. ● Fault-tolerant auto-bypass mode prevents loss of output during UPS fault conditions or excessive UPS loading ● 4-post rackmount and upright tower installation accessories included. 2POSTRMKITWM two post rackmount hardware accessories available ● Field replaceable, hot swappable power module and external battery packs ● Attractive all-black color scheme ● 2-year warranty; $250,000 connected equipment insur ● Extended warranty and service contracts available Specifications OVERVIEW UPC Code 037332127396 INPUT Maximum Input Amps 200 Input Connection Type Hardwire Voltage Compatibility (VAC) 200; 208; 220; 230; 240 OUTPUT Frequency Compatibility 50 / 60 Hz Output (VA) 7500 Output (Watts) 6000 Output Nominal Voltage 208V AC (200/208/220/230/240V) Output Voltage Regulation Maintains pure sine wave output at all times, regulated within 2% of selected nominal output voltage, less than 3% total harmonic distortion when used with computer loads Output Frequency Regulation Regulates line frequency to 50/60Hz +/- 0.05Hz BATTERY Full Load Runtime (min.) 9 min. (7500VA/6000W) Half Load Runtime (min.) 20 min. (3750VA/3000W) Expandable Battery Runtime Runtime is expandable with optional  BP240V10RT3U  and BP240V32 external battery packs DC System Voltage (VDC) 240 Battery Access User replaceable, hot swappable external battery pack Battery Pack Accessory (Optional)  BP240V10RT3U , BP240V32 UPS Connection Included 3-wire DC cable 2/4 Typical Battery Lifespan 4-6 years Battery Charge Less than 8 hours to 90% (included battery set only) VOLTAGE REGULATION Voltage Regulation Description On-line, double-conversion process give this UPS the ability to maintain output voltage within +/-2% of selected nominal voltage at all times Overvoltage Correction Maintains continuous operation without using battery power during overvoltages to 276V AC, regulating output within 2% of selected nominal Brownout Correction Maintains continuous operation without using battery power during brownout / undervoltage conditions to 156V AC, regulating output within 2% of selected nominal USER INTERFACE, ALERTS & CONTROLS Front Panel LEDs 6 LED DISPLAY: line power, bypass, inverter, charger, output AC and battery operation. LED/LCD display panel easily rotates for viewing in rackmount or tower configurations. Switches Includes main power off/on switch, plus 2 switches to set and execute scrollable LCD functions Audible Alarm Multi-function audible alarm offers notification of UPS start, backup operation, low battery, overload, UPS fault, inverter fault, DC bus fault, overtemperature, remote shutdown, shutdown imminent and shutdown complete SURGE / NOISE SUPPRESSION EMI / RFI AC Noise Suppression Yes AC Suppression Response Time Instantaneous PHYSICAL Material of Construction Steel Cooling Method Fan Form Factors Supported Rack (6U) Shipping Dimensions (hwd / cm) 100.96 x 58.42 x 80.01 Shipping Dimensions (hwd / in.) 39.75 x 23.00 x 31.50 Shipping Weight (kg) 149.94 Shipping Weight (lbs.) 330.56 Unit Dimensions (hwd / in.) Power Module 5.14 x 17.5 x 25, Battery Pack 5.16 x 17.5 x 25 (Installed depth of power module extends to 32.5 inches once detachable PDU backplate is installed) Unit Dimensions (hwd / cm) Power Module 13.3 x 44.4 x 63.5, Battery Pack 13.4 x 40.6 x 63.5 (Installed depth of power module extends to 82.6 cm once detachable PDU backplate is installed) Unit Weight (lbs.) 191.5 Unit Weight (kg) 86.86 ENVIRONMENTAL Relative Humidity 0 to 95%, non-condensing Line Mode BTU / Hr. (max.) 2025 btu/hr. (91% efficiency line mode) 3/4 COMMUNICATIONS WatchDog Compatibility Yes, compatible with Tripp Lite's Watchdog system service to restore operation to locked equipment through soft reboot of application / OS or hard power off/on reboot of connected equipment—ideal for unattended kiosk applications Network Monitoring Port Includes 2 built-in DB9 monitoring ports (1-RS232 / 1-contact closure) EPO Port Includes dedicated EPO (emergency power off) interface and cabling SNMP Compatibility Built-in accessory slot accommodates internal SNMP / Web card and other network accessories LINE / BATTERY TRANSFER Transfer Time (Line Power to Battery Mode) Zero, online UPS continuously converts incoming AC to DC, then back to AC. When line power is interrupted, UPS maintains continuous output from battery reserves with absolutely no disruption in output AC power. Low Voltage Transfer to Battery Power Maintains continuous operation during undervoltages as low as 156VAC. Below this point, output is maintained utilizing battery reserves. High Voltage Transfer to Battery Power Maintains continuous operation during overvoltages to 276V AC. Above this point, output is maintained utilizing battery reserves. FEATURES & SPECIFICATIONS Cold Start Yes, inverter can be "cold started" to enable temporary AC output during a power failure WARRANTY Product Warranty Period (Worldwide) 2-year limited warranty Optional Coverage 3 year, 5 year, next day and on-site warranty coverage available for select opportunities - contact Tripp Lite Connected Equipment Insurance (U.S., Canada & Puerto Rico) $250,000 Ultimate Lifetime Insurance  © 2022 Tripp Lite. All rights reserved. All product and company names are trademarks or registered trademarks of their respective holders. Use of them does not imply any affiliation with or endorsement by them. Tripp Lite has a policy of continuous improvement. Specifications are subject to change without notice. Tripp Lite uses primary and third-party agencies to test its products for compliance with standards. See a list of Tripp Lite's testing agencies: https://www.tripplite.com/products/product-certification-agencies 4/4
SU7500RT3U
物料型号:SU7500RT3U 器件简介:7500VA(7.5kVA)在线式双变换UPS系统,适用于关键服务器、网络和电信设备。
安装仅占用6U机架空间(3U功率模块和3U电池包),最大安装机架深度为32.5英寸。
支持通过可选的BP240V10RT3U和BP240V32外部电池包扩展电池运行时间。
引脚分配:标准3线208V硬线输入连接;2个NEMA L6-30R和4个L6-20R输出插座。
参数特性:全时正弦波200,208,220,230,或240V±1-2%输出。
在电压跌落至156V和过电压至276V时,可不使用电池电源持续运行。
支持通过RS-232、接触闭合端口和可选的SNMPWEBCARD插槽进行网络管理接口通信。
功能详解:提供网络级AC浪涌和噪声抑制,AC和电池操作之间的零转换时间。
支持通过网络接口详细监控设备负载水平、自测数据和公用电源条件。
包括PowerAlert监控软件和完整的布线。
应用信息:适用于需要在线双变换保护的关键任务应用。
封装信息:4柱机架安装配件和2-9USTAND塔式套件包括在内;2POSTRMKITWM两柱机架硬件配件可用。
现场可更换、热插拔功率模块和外部电池包。
提供2年保修和$250,000连接设备保险;可延长保修和服务合同。