PDU3VSR3G30
PDU3VSR3G30
    TRIPPLITE
    PDU3-PHASESWITCHED208V8.6KW
PDU3VSR3G30 数据手册
1000 Eaton Boulevard Cleveland, OH 44122 United States 8.6kW 3-Phase Switched PDU, 208V Outlets (21 C13 & 3 C19), IEC-309 30A Blue, 3ft Cord, 0U Vertical Highlights ● Switched 8.6kW 3 Phase 208V PDU; 70 in. / 178cm 0U vertical rackmount ● Reports voltage, frequency & load per-outlet or phase via ethernet interface ● Visual current meter; Toolless button-mount installation ● IEC-309 Blue 30A (3P+E) 208V 3 phase input; 3 ft. / 1m line cord ● 21 C13 & 3 C19 single phase switched outlets with cord retention brackets ● Temperature, humidity and contact closure monitoring options MODEL NUMBER: PDU3VSR3G30 Package Includes ● Switched rackmount PDU with pre-installed mounting buttons ● Cord retention brackets ● Spare installation buttons (2 9mm / 4 6mm) ● Rack mounting brackets ● Owner's manual Description Tripp Lite 3 phase Switched PDU / Power Distribution Unit offers advanced network control and monitoring with the ability to turn on, turn off, recycle or lock-out power to each individual receptacle, monitor site electrical conditions and remotely monitor output power consumption per-phase or perreceptacle. PowerAlert interface supports remote control and custom notification of user-specified conditions via email, secure web, SNMP, Telnet or SSH interface. Individually switched outlets can be controlled in real-time to remotely reboot unresponsive network hardware, or be custom programmed for user-defined power-up and power-down sequences to ensure proper startup of interdependent IT systems and prevent inrush-related overloads as network equipment is first energized. Unused PDU outlets can be electronically locked off to prevent the connection of unauthorized hardware. PDU output current consumption in amps per-phase or per-receptacle can be displayed locally via visual meter or remotely via web/network interface to warn of potential overloads before critical IT mains or branch breakers trip. Features ● 8.6kW 3 phase 208V Switched Power Distribution Unit / PDU with built-in web/network interface ● Attached IEC-309 Blue 30A (3P+E) 208V 3 phase input; 3 ft. / 1m cord ● 0U, 70 inch / 178cm vertical form factor ● 24 switched 208V outlets (21 C13, 3 C19) in 3 single phase load banks ● Supports power-on, power-off or reboot of each outlet on a real-time or programmable basis ● Enables reboot of locked equipment, custom power-on/power-off sequences, load-shedding of optional loads and disabling unused outlets ● Network interface provides PDU control and data regarding input voltage, per-outlet and per-phase load levels ● Digital display with scroll-buttons supports per-outlet or per-phase load levels, IP-address selfidentification and 180 degree display rotation ● Supports user-specified alarm notification thresholds 1/4 1000 Eaton Boulevard Cleveland, OH 44122 United States ● In-rack environmental reporting with optional ENVIROSENSE temperature / humidity sensor and rack access notification with up to 4 optional SRSWITCH door sensors ● DHCP/Manual configuration support ● 10/100 Mbps auto-sensing ● Real-time clock backup maintains the time of day and date even if the PDU is unpowered ● Tiered access privileges allow an administrator and a guest to login via web browser ● Alert notifications via email or SNMP traps offer immediate event notification ● Firmware upgrade ability supports future product enhancements ● Supports HTTP, HTTPS, PowerAlert Network Management System, SMTP, SNMPv1, SNMPv2, SNMPv3, Telnet, SSH, FTP, DHCP, BOOTP, NTP protocols ● Fully compatible with FREE PowerAlert Network Management System / NMS Software ● Included cord retention brackets ● Toolless mounting supported in button-mount compatible racks, plus nut-and-bolt mounting brackets for other mounting applications (set of 2 9mm buttons pre-installed, 2 9mm and 4 6mm spare buttons included) ● Nut-and-bolt mounting support for other racks ● TAA Compliant Version Available - Order Tripp Lite PDU3VSR3G30TAA Specifications OVERVIEW UPC Code 037332158000 PDU Type Switched INPUT Recommended Electrical Service 30A 208V with IEC309 30A Blue (3P+E) outlet Maximum Input Amps 24 Maximum Input Amps Details Agency de-rated to 24A continuous PDU Plug Type IEC-309 30A BLUE (3P+E) Input Phase 3-Phase Input Cord Details Cord length specifications are nominal and subject to manufacturing variance Input Cord Length (ft.) 3 Input Cord Length (m) 0.91 OUTPUT Output Capacity Details 8.6kW (208V) total capacity; 13.9A max per output phase (L1-L2, L2-L3, L3-L1), 12A max per C13 outlet Frequency Compatibility 50 / 60 Hz Output Receptacles (21) C13; (3) C19 Output Nominal Voltage 208 Overload Protection 3 20A circuit breakers, one per output load bank 2/4 1000 Eaton Boulevard Cleveland, OH 44122 United States Customized Load Management Receptacles Each outlet is individually controllable via remote interface USER INTERFACE, ALERTS & CONTROLS Reported Load Segments Supports local monitoring of current for each output phase (13.9A max per L1-L2, L2-L3 & L3-L1, balanced) and for each output receptacle; BANK "L1" is powered by L1-L2 (outlets 1-8); BANK "L2" is powered by L2-L3 (outlets 9-16); BANK "L3" is powered by L3-L1 (outlets 17-24) Front Panel LCD Display SELECT switch advances the digital display and LED to report power consumption for load segments L1, L2, L3 and for each individual output receptacle (short press); SELECT switch also rotates the local display 90 degrees for overhead power input (long press); SCROLL IP button scrolls the configured IP address (long press) Front Panel LEDs Set of 3 LEDs (L1, L2, L3) indicate the output load segment the digital current display is reporting; LEDs for L1, L2, L3 will also flash to indicate that the display is reporting current level for one of the outlets in that load bank; One additional LED per output receptacle indicates power ON/OFF status for that outlet Switches Pushbutton scroll switch enables local power consumption display of each phase or outlet separately, display rotate and display IP address functions. Current Measurement Accuracy (Amps) +/-1% Voltage Measurement Accuracy (Volts) +/-1% Power Measurement Accuracy (Watts) +/-1% SURGE / NOISE SUPPRESSION Automatic Shut-Off No PHYSICAL Material of Construction Metal Form Factors Supported Vertical rackmount installation supported with included mounting brackets; supports toolless mounting in buttonmount compatible racks PDU Form Factor Vertical (0U) Shipping Dimensions (hwd / in.) 7.20 x 9.65 x 75.86 Shipping Dimensions (hwd / cm) 18.29 x 24.51 x 192.68 Shipping Weight (lbs.) 19.57 Shipping Weight (kg) 8.88 Unit Dimensions (hwd / in.) 70.000 x 2.200 x 3.580 Unit Dimensions (hwd / cm) 177.8 x 5.6 x 8.3 Unit Weight (lbs.) 12.4 Unit Weight (kg) 5.62 ENVIRONMENTAL Storage Temperature Range 5 to 122F (-15 to 50C) Relative Humidity 5-95% non condensing Operating Elevation (ft.) 0-10,000 3/4 1000 Eaton Boulevard Cleveland, OH 44122 United States Operating Elevation (m) 0-3000 COMMUNICATIONS PowerAlert Software SNMPWEBCARD Interface: PowerAlert 12 Communications Cable RJ45-to-DB9 configuration/console Access cable SNMP Compatibility Yes, pre-installed SNMPWEBCARD provides remote monitoring via web, telnet, SSH and SNMP management systems Network Compatibility 10 Mbps; 100 Mbps (Fast Ethernet) STANDARDS & COMPLIANCE TAA Compliant Option TAA Compliant Version Available - Order Tripp Lite PDU3VSR3G30TAA WARRANTY & SUPPORT Product Warranty Period (Worldwide) 2-year limited warranty © 2022 Eaton. All Rights Reserved. Eaton is a registered trademark. All other trademarks are the property of their respective owners. 4/4
PDU3VSR3G30
### 物料型号 - 型号:PDU3VSR3G30
### 器件简介 - Tripp Lite的3相开关式PDU(电源分配单元)提供高级网络控制和监控功能,能够对每个单独的插座进行开启、关闭、重启或锁定电源,监控现场电气条件,并远程监控每个相位或每个插座的输出功率消耗。
### 引脚分配 - 输入:3相输入,推荐电气服务为30A 208V,带有IEC309 30A蓝色(3P+E)插座。 - 输出:24个208V插座(21个C13和3个C19),分为3个单相负载组。
### 参数特性 - 功率:8.6kW,最大输入电流24A(连续)。 - 频率兼容性:50/60Hz。 - 过载保护:每个输出负载组有1个20A的断路器。 - 电流测量精度:±1%。 - 电压测量精度:±1%。 - 功率测量精度:±1%。
### 功能详解 - 支持远程控制和自定义通知,通过电子邮件、安全网页、SNMP、Telnet或SSH接口实现。 - 可以实时控制每个插座,远程重启无响应的网络硬件,或自定义编程用户定义的上电和断电序列。 - 网络接口提供PDU控制和输入电压、每个插座和每个相位的负载水平数据。 - 数字显示支持每个插座或每个相位的负载水平,IP地址自我识别和180度显示旋转。 - 支持用户指定的报警通知阈值。 - 可选的ENVIROSENSE温湿度传感器和多达4个可选的SRSWITCH门传感器,用于机架访问通知。
### 应用信息 - 适用于需要远程控制和监控电源分配的数据中心和网络环境。
### 封装信息 - 物理结构:金属材质,支持垂直机架安装。 - 尺寸:70英寸(178cm)高,2.2英寸(5.6cm)宽,3.58英寸(8.3cm)深。 - 重量:12.4磅(5.62公斤)。 - 存储温度范围:5到122°F(-15到50°C)。 - 相对湿度:5-95%非凝结。 - 操作海拔:0-10,000英尺。
PDU3VSR3G30 价格&库存
很抱歉,暂时无法提供与“PDU3VSR3G30”相匹配的价格&库存,您可以联系我们找货