2210-T210-K0M1-H121-5A 数据手册
Thermal-Magnetic Circuit Breaker 2210-T2..
Description
One, two and three pole thermal-magnetic circuit breakers with trip-free
mechanism and toggle actuation (S-type TM CBE to EN 60934/IEC 934).
Featuring a combi-foot design for both symmetric and asymmetric rail
mounting. Available with auxiliary contact (1 x N/O or 1 x N/C) for status
signalling. Two and three pole models are internally linked to ensure that
both/all poles trip in the event of an overload on one pole, even if the
actuator is held in the ON position. This CBE can be supplied in current
ratings up to 32 A with a choice of characteristic curves. All screw
terminals are recessed for safety. Approved to CBE standard EN 60934
(IEC 60934).
Typical applications
1
2210-T2..
2-pole
Process control equipment, robotics, machine tool control,
communications systems, instrumentation.
Features
Your benefits
l
l
l
Comprehensive approvals allow global use
Current rating range from 0.1 A to 32 A
l Very small width of only 12.5 mm including auxiliary contacts
l High vibration resistance to DNV GL Class B for mounting with
combustion engines, pumps, compressors
l Compliant with the relevant requirements of the railway
standards DIN EN 50155, DIN EN 61373 and EN 45545
(detailed information upon request)
Space and weight savings of at least 50 % compared to
conventional MCBs
l Reduced assembly times thanks to integral auxiliary contacts
l Optimum equipment protection through fine grading of
current ratings
Preferred types – for more details on all configurations please see order numbering code
Preferred types are E-T-A products most frequently used by E-T-A
customers. We manufacture E-T-A preferred types in particularly high
Preferred types
1-pole
2210-T210-K0M1-H1212-pole
2210-T220-K0M1-H221-
Approvals
volumes. Our preferred types are supplied at shorter lead times than
non-standard versions.
Standard current ratings (A)
0.5
1
2
3
4
5
6
8
10
16
x
x
x
x
x
x
x
x
x
x
x
0.5
1
2
3
4
5
6
8
10
16
x
x
x
x
x
x
Data sheet
For access to the latest documents please follow:www.e-t-a.de/en053
Compliances
2011
www.e-t-a.de
1
Technical data
1
Standard current ratings and typical internal resistance values
For further details please see: www.e-t-a.de/ti_e
Voltage rating
AC 250 V; 3 AC 433 V (50/60 Hz); DC 65 V
(UL: AC 277/480 V; DC 65 V)
0.1...32 A for curves M1, T1
0.1...16 A for curves F1, F2
Auxiliary circuit
1 A, AC 240 V / DC 65 V, resistive
(min. 10 V / 10 mA)
Typical life
3 AC 433 V; AC 250 V: 0.1...25 A
10,000 operations at 1 x IN, inductive
DC 65 V:
0.1...32 A
3 AC 433 V; AC 250 V: 32 A
6,000 operations at 1 x IN, resistive
Ambient temperature
-30...+60 °C (-22...+140 °F) T 60
Insulation co-ordination
rated impulse
pollution
(IEC 60664 and 60664 A) withstand voltage degree
2.5 kV
2
reinforced insulation in operating area
Dielectric strength
(IEC 60664 and 60664A)
test voltage
operating area
AC 3,000 V
main/aux. circuit
AC 3,000 V
pole/pole
AC 1,500 V
Insulation resistance
> 100 MΩ (DC 500 V)
Interrupting capacity Icn 0.1...5 A 400 A
6...32 A 800 A
curves F1, F2, M1, T1: 0.1...16 A 2,500 A (at DC 32 V)
Interrupting capacity (UL 1077)
Current rating (A)
Internal resistance (Ω)
F1
F2
M1
T1
fast acting
for DC only
fast acting
delay for
AC + DC
standard for
AC+DC
delayed low
resistance
for AC only
0.1
162
162
92
81
0.2
39.3
39.3
26.1
24.2
0.3
17.5
17.5
11.6
10.4
0.4
9.2
9.2
6.6
6.0
0.5
6.8
6.8
4.1
3.9
0.6
4.2
4.2
3
2.7
0.8
2.8
2.8
1.65
1.53
1
1.6
1.6
1.10
0.98
1.5
0.78
0,78
0.47
0.42
2
0.42
0,42
0.28
0.24
2.5
0.26
0.26
0.183
0.17
3
0.18
0.18
0.124
0.12
4
0.12
0.12
0.077
0.073
5
0.092
0.092
0.063
0.055
6
0.054
0.054
0.045
0.039
8
0.025
0.025
≤ 0.02
≤ 0.02
10
0.022
0.02
≤ 0.02
≤ 0.02
IN
0.1...16 A
20...32 A
12
≤ 0.02
≤ 0.02
≤ 0.02
≤ 0.02
AC 277 V 1-pole
AC 277/480 V 2-/3-pole
DC 65 V
5,000 A
5,000 A
2,000 A
2,000 A
2,000 A
2,000 A
16
≤ 0.02
≤ 0.02
≤ 0.02
≤ 0.02
Degree of protection
operating area IP30
(IEC 60529/DIN 40050)
terminal area IP20
Vibration curves F1, F2: 3 g (57-500 Hz), ± 0.23 mm (10-57 Hz)
curves M1, T1: 5 g (57-500 Hz), ± 0.38 mm (10-57 Hz)
to IEC 60068-2-6, test Fc
10 frequency cycles/axis
Shock
curves F1, F2: 25 g (11 ms), directions 1, 2, 3, 4, 5
10 g (11 ms), direction 6
curves M1, T1: 25 g (11 ms), directions 1, 2, 3, 4, 5
20 g (11 ms), direction 6
to IEC 60068-2-27, test Ea
Corrosion
96 hours at 5 % salt mist
to IEC 60068-2-11, test Ka
Humidity
240 hours at 95 % RH
to IEC 60068-2-78, test Cab
Mass
approx. 60 g per pole
2
≤ 0.02
≤ 0.02
25
≤ 0.02
≤ 0.02
32
≤ 0.02
≤ 0.02
Approvals
Authority
Standard
Rated voltage
Current ratings
VDE
IEC/EN
60934
3 AC 433 V
AC 250 V
DC 65 V
0.1 A…32 A
0.1 A…32 A
0.1 A…32 A
UL
UL 1077
AC 277/480 V
AC 277 V
DC 65 V
0.1 A…32 A
0.1 A…32 A
0.1 A…32 A
CSA
C22.2 No
235
AC 277/480 V
AC 277 V
DC 65 V
0.1 A…32 A
0.1 A…32 A
0.1 A…32 A
CQC
GB 17701
AC 250/433 V
AC 250 V
DC 65 V
0.1 A…32 A
0.1 A…32 A
0.1 A…32 A
DNV GL
IEC 60934,
DNVGLCG 0339
3 AC 433 V
AC 250 V
DC 65 V
0.1 A…32 A
0.1 A…32 A
0.1 A…32 A
KTL
KC60934
AC 250 V, 1-pole
AC 433 V, 2-pole
0.1 A...16 A
0.1 A...16 A
www.e-t-a.de
2011
Preferred types
Preferred types
1-pole
0.5
1
2
3
4
5
6
8
10
16
x
x
x
x
x
x
x
x
x
x
x
0.5
1
2
3
4
5
6
8
10
16
x
x
x
x
x
x
Ordering information
Type No.
2210 single and multipole thermal-magnetic circuit breaker
Mounting
T
rail mounting
Actuator design
2 toggle
Number of poles
1 single pole protected
2 2-pole protected
3 3-pole protected
Accessories
0 without accessories
Terminal design (main contacts)
K0 screw terminals
Characteristic curve
F1 fast acting: therm.1.01-1.4xIN;
magn.2-4xIN DC (DC only)
F2 fast acting: therm.1.01-1.4xIN;
magn.3,5-6,5xIN AC/4,5-8,5xIN DC
M1 standard delay: therm. 1.01-1.4xIN;
magn. 6-12xIN AC, 7.8-15.6xIN DC
T1 delayed: therm. 1.01-1.4xIN; magn. 10-20xIN AC
Auxiliary contact design
H without intermediate position
Auxiliary contacts
1 with auxiliary contacts
2 auxiliary contacts on pole 1 only
(multipole devices)
Auxiliary contact function (see diagrams)
2 1 N/O contact
3 1 N/C contact
Auxiliary contact - terminal design
1 screw terminals
Current ratings
0.1...32 A
2210 - T 2 1 0 - K0 M1- H 1 2 1 - 10 A ordering example
Please be informed that we have minimum ordering quantities to be
observed.
Custom designed versions
Looking for a version you cannot find in our ordering number code?
Please get in touch. We will be pleased to find a solution for you.
2011
www.e-t-a.de
3
Dimensions
Internal connection diagrams
37.5
1.48
toggles linked
for multipole
devices
11.5
.453
1
slot fitting labels from
Phoenix
Weidmüller
Wieland
45
1.77
OFF
...-H131-...
30.5
1.20
25
.984
18
.709
OFF position
line (Si)
I
1
11
.453
78.5
3.09
88.5
3.48
...-H121-...
12-14
Si
2
.472-.551
I>
I>
2
2
line
1
(Si)
13
N/O contact
I
line
1
14
(Si)
15
.591
12
.472
42.5
1.67
G-profile
EN 50035-G32
12.5 12.5
.492 .492
7.5
.295
5.5
.217
I
12
(Si)
40
1.57
symmetric rail
EN 50022-35x7.5
EN 50022-35x15/1.5
main contact terminal
max. 6 mm2 (AWG 10)
(rigid conductor)
tightening torque 0.5 Nm
unit I
rigid
flexible
I>
2
2
5
6
12.5
.492
1
2
3
4
Cable cross section
Conductor
I>
5.5
.217
12A 12A 12A
M1 M1 M1
unit II
14
(Si)
Shock directions
Si-terminal M3
max. 1.5 mm2 (AWG 16) (rigid conductor)
unit III
(Si)
13
44
1.73
Si
1
ON position
line (Si)
I
1
11
(Si)
ON
9-12
.354-.472
N/C contact
Main contacts 1 & 2 Aux. contact IN
0.2 mm²
min. 0.2 mm²
max. 6 mm²
1.5 mm²
0.2 mm²
min. 0.2 mm²
max. 4 mm²
1.0 mm²
flexible with wire end ferrule min. 0.25 mm²
without plastic sleeve
max. 4 mm²
with plastic sleeve
max. 2.5 mm²
0.25 mm²
1.0 mm²
0.25 mm²
0.75 mm²
Installation drawing
operating area
(reinforced insulation)
Si
1
Si
2
mounting area
4
This is a metric design and millimeter dimensions take precedence ( mm )
inch
www.e-t-a.de
2011
Typical time/current characteristics
-F1 0.1…16 A
DC only
10000
Trip time in seconds
1000
100
10
1
1
0.1
0.01
0.001
1
2
4 6 8 10 20 406080100
… times rated current
-F2 0.1…7.5 A
AC/ DC1)
10000
1000
100
10
1
0.1
0.01
0.001
1
2
-F2 8…16 A
AC/ DC1)
10000
1000
100
10
1
0.1
0.01
0.001
1
+60 °C
+140 °F
1)
2
4 6 8 10 20 40 6080100
+23 °C
+73.4 °F
-30 °C
-22 °F
Magnetic tripping currents are increased by 30% on DC supplies.
2011
www.e-t-a.de
5
1
AC/DC 1)
10000
1000
1000
100
10
1
10
1
0.1
0.01
0.01
1
0.001
2
-T1 0.1…6 A
AC only
1000
1000
10000
100
10
1
2
10
1
0.1
0.01
0.01
0.001
2
AC only
100
0.1
1
1
-T1 8…32 A
10000
0.001
AC/DC 1)
100
0.1
0.001
-M1 8…32 A
10000
-M1 0.1…6 A
60 °C
23 °C
-30 °C
1
2
The time/current characteristic curve depends on the ambient temperature
prevailing. In order to eliminate nuisance tripping, please multiply the circuit
breaker current ratings by the derating factor shown below. See also section
Technical information.
Ambient °F
temp.
°C
-22
-30
-4
-20
+14
-10
+32 +73.4 +86
+104 +122 +140
+40 +50 +60
Derating factor
0.76 0.79
0.83
0.88
1.11
6
1
1.04
1.19
Multi pole devices: all poles symmetrically loaded. With single pole overload,
thermal tripping will be at max. 1.7 x IN with curves F1, F2 and M1.
1)
Magnetic tripping currents are increased by 30 % on DC supplies
(curves F2, M1).
1.29
www.e-t-a.de
2011
Accessories
Plug-on cap, busbar 2/3-pole
Y 308 506 01
Connector bus links -K10
X210 589 01/ 2.5 mm2, (AWG 14) (black) up to 20 A max. load
X210 589 02/ 1.5 mm2, (AWG 16) (brown) up to 13 A max. load
ø2.5
.099
50 pin lugs to
DIN 46230
tinned copper
L 3
L 1
L 2
L 3
L 1
L 2
L 3
L 1
L 2
L 3
L 1
L 2
L 3
16
L 3
16-1
6.30-.394
L 2
4.6
1.81
20-1
7.87-394
L 2
L2
L2
L1
L1
L3
L3
L2
L2
L1
X22254011
16 mm2
L1
L3
79 x 12.7 = 1003.3
31.1 x 5 = 3950
G E R M A N Y
D-90518 Altdorf
Made in Germany
G E R M A N Y
D-90518 Altdorf
Made in Germany
L3
3±0.2
1.81±.079
1.5
.590
12.7
5
L2
G E R M A N Y
D-90518 Altdorf
Made in Germany
X22254011
16 mm2
L1
L2
3±0.2
1.81±.079
Y30850001
2
16 mm
L1
5.79
1030+2
405+.787
Y30850001
16 mm2
Busbar 1-pole, 90° X 222 540 11
The one metre long busbars can be cut to suitable lengths.
Plug-on caps can be fitted on the ends to provide brush
contact protection. cross section: 16 mm²
14.7
12.7
5
1
15.8
6.22
17.3
6.81
33.3±0.4
13.1±.157
~70
~2.76
Busbar 3-pole
Y 308 500 01
1.5
.591
80 x 12.7 = 1016
31.5 x 5 = 400
Y 308 506 01
G E R M A N Y
D-90518 Altdorf
Made in Germany
+2
1016
400+.787
1016+2
400+.787
1.5
.591
16
6.30
12.7
5
79 x 12.7 = 1003.3
31.1 x 5 = 3950
3
.118
33.7
1.327
3±0.2
1.81±.079
G E R M A N Y
D-90518 Altdorf
Made in Germany
14.7
5.79
Y30849801
16 mm2
G E R M A N Y
D-90518 Altdorf
Made in Germany
30,7±0,4
12.1±.157
Y30849801
16 mm2
4.6
1.81
Supply terminal
Y 308 503 01
Imax 63 A with 1-pole busbar,
50 A with multipole busbar
Max. tightening torque of terminal screw 2 Nm
Max. cable cross section: 25 mm2 / single strand
16 mm2 / multistrand
Busbar for 1-pole devices
Firmly mounted supply terminals, placed at fixed distances
(1 supply terminal every 7 modules)
For cable feed from the side
Ideal for applications with high vibration requirements
Y31270901 cross section: 16 mm²
1.5
.059
16.2
.638
Busbar 1-pole Y 308 498 01
13
.512
18.4
.724
1012.8+2
399+.787
Y31270901
16 mm2
Y31270901
16 mm2
G E R M A N Y
D-90518 Altdorf
Made in Germany
79x12.7=1003,3
31.1 x 5 = 3950
3
1.18
1.5
.591
35
13.8
12.7
5
G E R M A N Y
D-90518 Altdorf
Made in Germany
76.2
30
23.5
9.25
12x76.2=914.4
4.72x30=360
Plug-on cap, 1-pole
Y 307 851 01
Caution:
When using multipole busbars please leave at least one pole’s
width between two adjacent line entry terminals.
Busbar 2-pole
Y 308 499 01 cross section: 16 mm²
1016+2
400+.787
L 2
L 1
L 2
L 1
L 2
L 1
L 2
L 1
L 2
16
6.30
L2
79x12.7 = 1003.3
4.72x30=360
17.3
6.81
L 1
L1
L2
L2
L1
L1
L2
L2
L 1
L 2
L 1
L 2
3±0.2
1.81±.079
L1
L1
L2
33.3±0.4
13.1±.157
G E R M A N Y
D-90518 Altdorf
Made in Germany
L 1
L 2
2011
L1
L2
12.7
5
G E R M A N Y
D-90518 Altdorf
Made in Germany
L2
L1
L1
Y30849901
16 mm2
Y30849901
16 mm2
15.8
6.22
1.5
.591
inch
All dimensions without tolerances are for reference only. In the interest of improved design,
performance and cost effectiveness the right to make changes in these specifications
without notice is reserved.Product markings may not be exactly as the ordering codes.
Errors and omissions excepted.
www.e-t-a.de