››em4
em4 alert
em4 alert 2G
››Connect your equipment to the GPRS 2G
network and get alerted
››Get alerted, receive data logs or control your
application by SMS or email
››Save time in designing your application and
remote functions using the most intuitive graphical function block language of the market
››Measure accurately your high end industrial
sensors with the embedded configurable
analog inputs (including 4-20mA)
››Integrate easily one of our three high tech
designs in your machine
››Adapt your application along the way of its
lifecycle thanks to the enhanced controlling
performances
em4 alert - Robust
em4 alert - Glossy black
em4 alert - Glossy white
Specific characteristics
Part number
88 981 112
88 981 113
88 981 114
Type
B26-2GS
Inputs
16 digital inputs (including 4 High Speed, 8 analog 0-10 V / potentiometers
and 4 analog 0-10 V / 4-20 mA)
Outputs
10 digital outputs (including 2 solid states 0.5 A PWM, 2 relays 6 A and 6 relays 8 A)
Supply
Finish
On front panel color
24 VDC
Robust
Glossy black
Black RAL 9011
On terminal block color
Glossy white
White RAL 9003
Blue RAL 5017
Protection rating
(in accordance with IEC/EN 60529)
IP 50 on front panel
IP 20 on terminal block
IP 40 on front panel
Weight
Without packing: 350 g
With packing: 400 g
Without packing: 345 g
With packing: 395 g
Dimensions
Without packing:
124.6 x 90 x 62.6 mm /
4.91 x 3.54 x 2.46 inch
With packing:
148 x 103 x 65 mm /
5.83 x 4.06 x 2.56 inch
Without packing:
124.6 x 90 x 60.4 mm / 4.91 x 3.54 x 2.38 inch
With packing:
148 x 103 x 65 mm / 5.83 x 4.06 x 2.56 inch
R&TTE Directive
Standards of North American type approval
1999/5/EC
US-Federal Communications Commission (FCC)
Frequency range GSM 900
880 - 960 MHz
Frequency range GSM 1800
1710 - 1880 MHz
Frequency range GSM 850
824 - 894 MHz
Frequency range GSM 1900
1850 - 1990 MHz
Antenna: impedance
50 Ω
Antenna: input power
>2W
Antenna: V.S.W.R
< 2:1 recommended
< 3:1 acceptable
Antenna: return loss
S11 < - 10 dB recommended
S11 < - 6 dB acceptable
Antenna: connector
RP SMA : SMA Female Reverse Polarity
I em4
I 02
I www.em4-remote-plc.com
General characteristics
Products certification (in accordance with IEC/EN 60529)
CE, cULus Listed
Conformity with the low voltage directive
(in accordance with BT 2006/95/EC)
IEC/EN 61131-2 (Open equipment)
Conformity with the EMC directive
(in accordance with 2004/108/EC)
IEC/EN 61000-6-1 (Residential, commercial and light-industrial environments)
IEC/EN 61000-6-2 (Industrial)
IEC/EN 61000-6-3 (Residential, commercial and light-industrial environments)
IEC/EN 61000-6-4 (Industrial)
Earthing
None
Overvoltage category
3 in accordance with IEC/EN 60664-1
Pollution
Degree: 2 in accordance with IEC/EN 61131-2
Maximum utilization altitude
Operation: 2000 m
Transport: 3000 m
Mechanical resistance
Immunity to vibrations IEC/EN 60068-2-6, Fc test
Immunity to shock IEC/EN 60068-2-27, Ea test
Resistance to electrostatic discharge
Immunity to ESD IEC/EN 61000-4-2, level 3
Resistance to HF interference
(Immunity)
Immunity to radiated electrostatic fields IEC/EN 61000-4-3, level 3
Immunity to fast transients (burst immunity) IEC/EN 61000-4-4, level 3
Immunity to shock waves IEC/EN 61000-4-5
Radio frequency in common mode IEC/EN 61000-4-6, level 3
Conducted and radiated emissions
(in accordance with EN 55022/11 group 1)
Class B
Operation temperature
-20°C (-4°F) +60°C (140°F) (+40°C (104°F) in a non-ventilated enclosure)
Storage temperature
-40°C (-40°F) +80°C (176°F)
Relative humidity
95% max. (no condensation or dripping water)
Screw terminals connection capacity
Flexible wire with ferrule: 1 conductor: 0.2 to 2.5 mm² (AWG 24-14)
Flexible wire with ferrule: 2 conductors: 0.2 to 0.75 mm² (AWG 24-18)
Rigid wire: 1 conductor: 0.2 to 2.5 mm² (AWG 24-14)
Rigid wire: 2 conductors: 0.2 to 0.75 mm² (AWG 24-18)
Tightening torque: 0.5 N.m (4.5 lb-in) (tighten using screwdriver diam. 3.5 mm)
Stripping length: 6 mm
Processing characteristics
LCD display
Display with 4 lines of 18 characters
Programming method
FBD (Function Block Diagram), including SFC (Sequential Function Chart, Grafcet)
Program size
Function blocks: typically 1000 blocks
Macro blocks: 64 max. (256 blocks per macro)
Program memory
Flash
Removable memory
N.A
Data memory
2 k octets
Backup time
(in the event of power failure)
Program and settings in the controller: 10 years
Data memory: 10 years
Data backup
Data backup in the flash memory is guaranteed if the product is powered on more
than 10 seconds
Cycle time
From 2 ms to 90 ms, default value: 10 ms
Clock data retention
10 years (lithium battery) at 25°C (77°F)
Clock drift
Drift < 12 min/year (at 25°C (77°F))
6 s / month (at 25°C (77°F) with user-definable correction of drift).
Synchronizable by network
Timer block accuracy
0.5 % +/- 2 cycle time
Start up time on power up
< 3 s base alone, < 1.5 s base + 2 expansions + accessory interface
(USB or Modbus RS485)
Self test
Test firmware integrity (checksum memory)
Stability of the internal power supply
Check the conformity of the em4 device configuration with the configuration
in the application program.
I em4
I 03
Supply
Nominal voltage
24 VDC (-15% / +20%)
Operating limits
20.4 - 28.8 VDC
Immunity from micro power cuts
y 1 ms (repetition 20 times)
Max. absorbed power
5.3 W
Protection against polarity inversions
Yes
Inputs
Digital and high speed digital inputs 24 VDC - 4 inputs from I1 to I4
Input used as digital input
Input voltage
Input current
1.8 mA @ 20.4 V
2.1 mA @ 24 V
2.5 mA @ 28.8 V
Input impedance
11.6 kΩ
Logic 1 voltage threshold
u 15 VDC
Making current at logic state 1
u 1.3 mA
Logic 0 voltage threshold
y 10 VDC
Release current at logic state 1
y 0.8 mA
Response time
1 to 2 cycle times
Sensor type
Contact or 3-wire PNP
Conforming to IEC/EN 61131-2
Type 1
Input type
Resistive
Isolation between power supply and inputs
None
Isolation between inputs
None
Yes
Status indicator
On LCD screen
Cable length
y 100 m
Input used as high speed digital input
Maximum counting frequency
3 channels encoder (I1, I2, I3): 20 kHz*
2 independent counters (I1, I2) (I3, I4) (Cumul, IND, DIR): 2 channels: 40 kHz*,
4 channels: 20 kHz*,
2 independent counters (I1, I2) (I3, I4) (PH, PH2): 2/4 channels: 20 kHz*
4 independent counters (I1, I2, I3, I4) (Up/Down) : 1 channel: 60 kHz*, 2 channels:
40 kHz*, > 2 channels: 20 kHz*
* with a time cycle
20,4V
Other functions
4 chronometers (I1, I2, I3, I4 )
4 tachometers (I1, I2, I3, I4 )
Cable length
y 3 m with shielded twisted cable
Digital 24 VDC and analog inputs 12 bits / 28.8 V - potentiometer - 8 inputs from I5 to IC
Input voltage
Input current
1.8 mA @ 20.4 V
2.1 mA @ 24 V
2.5 mA @ 28.8 V
Input impedance
11.6 kΩ
u 11 VDC
u 1 mA
y 9 VDC
y 0.7 mA
Response time
1 to 2 cycle times
Sensor type
Type 1
Input type
Resistive
None
None
Yes
Status indicator
On LCD screen
Cable length
y 100 m
I em4
I 04
Input used as analog input
Measuring range
0 10 V or 0 V power supply
Input impedance
11.6 kΩ
Maximum value without destruction
28.8 VDC max
Input type
Common mode
Resolution
12 bit at maximum input voltage (10.5 bit at 10V)
Value of LSB
7.03 mV
Conversion time
Controller cycle time
Maximum error in 0-10V mode
+/- 1.1 % of full scale at 25°C (77°F)
+/- 1.6 % of full scale at 55°C (131°F)
Maximum error in 0-V power supply mode
+/- 2 % of full scale at 25°C (77°F)
+/- 3 % of full scale at 55°C (131°F)
Repeat accuracy at 55°C (131°F)
+/- 0.5 %
Isolation between analog channel and power supply
None
Yes
Potentiometer control
2.2 kΩ / 0.5 W (recommended), 10 KΩ max.
Cable length
y 10 m with shielded twisted cable (sensor not isolated)
Digital 24 VDC and analog inputs 12 bits / 10 V & 11 bits / 0-20 mA- potentiometer - 4 inputs from ID to IG
Input used as digital input (power off state)
Input voltage
Input current
1.5 mA @ 20.4 V
1.7 mA @ 24 V
2.1 mA @ 28.8 V
Input impedance
13.9 kΩ
u 11 VDC
u 0.8 mA
y 8 VDC
y 0.5 mA
Response time
1 to 2 cycle times
Sensor type
Type 1
Input type
Resistive
None
None
Yes
Status indicator
On LCD screen
Cable length
y 100 m
Input used as 0-10 V analog input
Measuring range
0 10 V
Input impedance
13.9 kΩ
28.8 VDC max
Input type
Common mode
Resolution
12 bit / 10V
Value of LSB
2.45 mV
Conversion time
Maximum error at 25°C (77°F)
+/- 0.8 % of full scale
Maximum error at 55°C (131°F)
+/- 1.2 % of full scale
+/- 0.5 %
None
Yes for voltage y 10 V
Cable length
I em4
I 05
Input used as 0-20 mA analog input
Measuring range
0 20 mA (4 20 mA by the application)
Input impedance
245 Ω
30 mA max
Input type
Common mode
Resolution
11 bit (normalized at 0 - 2000) / 20 mA
Value of LSB
10 µA
Conversion time
+/- 1.7 % of full scale
+/- 0.5 %
None
Yes
Overvoltage protection
Yes If the input voltage is > 7 V, this one is automatically switched on 0-10V configuration.
Cable length
y 30 m with shielded twisted cable (sensor not isolated)
Outputs
Digital / PWM solid state output - 2 solid state outputs from O1 to O2
Output used as digital output
Breaking voltage
10 28.8 VDC
Nominal voltage
12 / 24 VDC
Nominal current
0.5 A on resistive load @ 25°C (77°F)
Max. breaking current
0.625 A
Non repetitive overload current
1A
Maximum breaking voltage in the common
1A
Voltage drop
< 1 V for I = 0.5 A
Response time
Make = 1 cycle time + 30 µs typical
Release = 1 cycle time + 40 µs typical
Built-in protections
Against overloads and short-circuits: Yes
Against over voltages (*): Yes
Against inversions of power supply: Yes
Min. load
1 mA
Galvanic isolation
No (*) In the absence of a potential free contact between the output of the
programmable logic controller and the load
Cable length
Truth table of the default
y 10 m
Command Output
Fault
Normal condition
No
1
1
No
Overheating
No
1
Yes
Underpowered
X
1
X
Short circuit (current limit)
0 0 No
1
Yes
Output used as PWM output
PWM frequency
14.11 Hz ; 56.45 Hz ; 112.90 Hz ; 225.80 Hz ; 451.59 Hz ; 1758.24 Hz
PWM cyclic ratio
0 100 % 100 steps
PWM Max. error
y 2 % (from 10 % 90 %)
Status indicator
On LCD screen
Cable length
Distance between the power source and the static outputs
y 30 m
I em4
I 06
6 A relay output - 2 outputs from O3 to O4
Breaking voltage
250 VAC max
Breaking current
6A
Maximum breaking current in the common
IEC @ 25°C (77°F): 12 A
IEC @ 60°C (140°F) or UL: 10 A
Mechanical life
5 000 000 operations (cycles)
Electrical durability for 50 000 operating cycles
24 VDC tau = 0 ms: 6 A, tau = 7 ms: 3 A, tau = 15 ms: 1.8 A
Usage category DC-12: 24 V, 6 A
Usage category DC-14: 24 V, 1.8 A
250 VAC cos phi = 1: 6 A, cos phi = 0.7: 5 A, cos phi = 0.4: 2.5 A
Usage category AC-12: 250 V, 6 A
Usage category AC-13: 250 V, 5 A
Usage category AC-15: 250 V, 2 A
Minimum switching capacity
100 mA (at minimum voltage of 12V)
Maximum operating rate
Off load: 10 Hz
At operating current: 0.1 Hz
Voltage for withstanding shocks
In accordance with IEC/EN 60947-1 and IEC/EN 60664-1: 4 kV
Response time
Make = 8 ms max
Release = 4 ms max
Against short-circuits: None
Against over voltages and overload: None
Status indicator
On LCD screen
Cable length
y 30 m
8 A relay output - 6 outputs from O5 to OA
Breaking voltage
250 VAC max
Breaking current
8 A, u 55°C: 6 A
IEC @ 25°C (77°F): C3, C6: 8 A ; C4, C5: 16 A
IEC @ 60°C (140°F) or UL: C3, C6: 8 A ; C4, C5: 10 A
Mechanical life
20 000 000 operations (cycles)
24 VDC tau = 0 ms: 8 A, tau = 7 ms: 3 A, tau = 15 ms: 1.5 A
Usage category DC-12: 24 V, 8 A
Usage category DC-14: 24 V, 1.5 A
250 VAC cos phi = 1: 8 A, cos phi = 0.7: 4.75 A, cos phi = 0.4: 3 A
Usage category AC-12: 250 V, 8 A
Usage category AC-13: 250 V, 4.3 A
Usage category AC-15: 250 V, 1.5 A
Off load: 10 Hz
Response time
Make = 8 ms max
Release = 4 ms max
Status indicator
On LCD screen
Cable length
y 30 m
I em4
I 07
Schemes
Dimensions
B26 2GS Robust
90 / 3.54
108.1 / 4.25
90 / 3.54
108.1 / 4.25
48.7 / 1.91
62.6 / 2.46
80 / 3.15
99.4
3.91
45 / 1.77
124.6 / 4.90
87.6 / 3.45
43.2 / 1.70
mm
inch
64.8 / 2.55
B26 2GS Glossy
45 / 1.77
99.4
3.91
80 / 3.15
124.6 / 4.90
87.6 / 3.45
43.2 / 1.70
48.7 / 1.91
60.4 / 2.38
mm
inch
64.8 / 2.55
Connections
Inputs
I1 ... IG 0/1
+ 24 VDC
PNP
BL
I1 ... IG
(2)
24V
PNP
+ (1)
B26
BN
BK
I1 I2 I3 I4 I5 I6 I7 I8
I9 IA IB IC ID IE IF IG
100 m Max
3937 inches Max
30 V, NTC, LDR, R
I5 ... IC U
+ 24 VDC
LDR
NTC
2K2
0 - 30V
0 - 10V
0.5 W
10k max
24V
12 bits / 28,8V
(2)
I5 ... IC
B26
+ (1)
10 m Max
393.7 inches Max
I em4
I 08
ID ... IG U / I
20 mA, 10 V, R
+ 24 VDC
3K3
2K2
0.5 W
10k max
11 bits
0 - 20 mA
(2)
ID ... IG
24V
+ (1)
12 bits / 10V
0 - 10V
B26
20 mA
30 m Max
1181 inches Max
10 V, R
10 m Max
393.7 inches Max
3 m Max
118.1 inches Max
3 m Max
118.1 inches Max
3 m Max
118.1 inches Max
I1 ... I4
Hz
2604
+ 24 VDC
A
B
Z
A
I1
I2
I3
CNT 1
(2)
24V
+ (1)
B
I4
90°
Z
PNP
B26
I1 ... I4
Hz
2604
+ 24 VDC
I1
I2
A
B
CNT 1
24V
I3
I4
A
B
(2)
+ (1)
CNT 2
B26
I1 ... I4
2604
Hz, s, Rpm
+ 24 VDC
BL
BN
BK
(2)
I1 ... I4
24V
PNP
B26
+ (1)
(1) 1 A (UL248) quick-blowing fuse, circuit-breaker or circuit
protector (US)
(2) Isolating source
I em4
I 09
Outputs
0.5 A
O1 & O2
12 ...24V
30 m Max
1181 inches Max
(1)
C1 O1 O2
C2 O3 O4
C3 O5
C4 O6 O7
C5 O8 O9
C6 OAOA/
10 m Max
393.7 inches Max
C1
On
B26
(3)
12…24 V
U
(1)
C1 = 1 A max
12 ...24V
6 A, 8 A
O3 ... OA
12…240V 50/60Hz
12 ...24V
L
Cn
C1 O1 O2
6A
8A
8A
8A
C2 O3 O4
C3 O5
C4 O6 O7
C5 O8 O9
On
B26
(3)
(3)
12…240 V
50 / 60 Hz
or 12…24 V
U
U
N
Protection / Protection / Schutzschaltung / Protección / Protezione
L/+
N/–
L/+
N/–
C2 = 12 A max
C4, C5 = 16 A max
C3 ... C6 : Same polarity
(3) Inductive load
I/O installations
C1 O1 O2
C2 O3 O4
C3 O5
C4 O6 O7
C5 O8 O9
C6 OAOA/
C3 = 8 A max
C6 = 8 A max
8A
C6 OAOA/
30 m Max
1181 inches Max
Mouser Electronics
Authorized Distributor
Click to View Pricing, Inventory, Delivery & Lifecycle Information:
Crouzet:
88981114 88981117 88981113 88981116