8345-C01A-R0K1-DB1B2B-20A
    E-T-A
8345-C01A-R0K1-DB1B2B-20A 数据手册
Magnetic and Hydraulic-Magnetic Circuit Breaker 8345-... Description Single or multipole hydraulic-magnetic circuit breakers with trip-free­­mechanism and toggle actuation. A choice of switching characteristics ensures suitability for a wide range of applications. Industry standard dimensions and panel mounting. Auxiliary contacts optional. Low temperature sensitivity at rated load. Approved to CBE standard EN 60934 (IEC 60934) S-type HM CBE. Typical applications In the business fields Communication and Transport: power supplies, switchgear, instrumentation and process control engineering. 1-pole 8345 1 2-pole Standard current ratings and typical internal resistance values Current rating (A) Technical data Trip curves and internal resistance (Ω) per pole F1 0,05 --- 0,1 F2 K1, M1, T1 K2, M2, T2 --- 531 542 --- --- 129 127 1 0,578 0,347 1,10 1,08 2 0,144 0,0959 0,295 0,291 3 0,0644 0,0477 0,121 0,118 5 0,0250 0,0192 0,0437 0,0449 10 0,00901 0,00714 0,0147 0,0133 15 0,00597 0,00483 0,00794 0,00794 20 0,00468 0,00410 0,00597 0,00597 25 0,00410 0,00385 0,00456 0,00456 30 0,00385 0,00371 0,00458 0,00458 40 0,00371 0,00371 0,00373 0,00373 50 0,00358 0,00358 0,00335 0,00335 60 --- --- 0,00333 0,00333 80 --- --- 0,00325 0,00325 100 --- --- 0,00316 0,00316 125 --- --- 0,00314 0,00314 Interrupting capacity to EN 60934, CCC, UL 489, UL 1077 IEC 60934 / CCC (3-pole) – test series E: voltage number of poles IN max. (A) Icn (A) DC 80 V 1+2 0.02...125 10 000 AC 240/415 V 1–4 0.016...80 6 x IN AC 240 V 1 0.016...20 5 000 voltage number of poles IN max. (A) Icn (A) DC 80 V 1+2 0.5...125 10 000 UL 489 – test sequence Z: AC 120 V 1 0.5...80 5 000 AC 120/240 V 1 (2) 0.5...80 5 000 AC 240 V 1 0.5...20 5 000 voltage number of poles IN max. (A) Icn (A) DC 80 V 1+2 0.02...125 10 000 AC 277/480 V 1–4 0.02...70 5 000 For further details please Voltage rating Current rating range Auxiliary circuit Typical life see: http://www.e-t-a.de/ti_e 3 AC 415 V; AC 277/480 V; AC 120/240 V; AC 240 V; DC 80 V (higher DC voltages to special order) 0.02...125 A single and multipole higher ratings upon request AC 240 V 6 A DC 28 V 3 A DC 65 V 1 A DC 80 V 0.5 A 10,000 operations at 1 x IN Ambient temperature -40...+85 °C (-40...+185 °F) Insulation co-ordination (IEC 60664) 2.5 kV/2 reinforced insulation in operating area Dielectric strength operating area test voltage AC 3,000 V Line to Load test voltage AC 1,500 V pole to pole (2- and 3-pole) test voltage AC 1,500 V main to auxiliary circuit test voltage AC 3,000 V switching to trip circuit test voltage AC 1,500 V (version -X) Insulation resistance > 100 MΩ (DC 500 V) Degree of protection operating area IP40 (IEC 60529) terminal area IP00 Vibration 10 g (57...2000 Hz) ± 0.76 mm (10...57 Hz) at IN 5 g mounting position toggle down at 0.9 IN 5 g mounting position toggle up at IN trip curve F1, F2, all mounting positions: 10 g at 0.8 x IN test to IEC 60068-2-6, test Fc, 10 frequency cycles/axis Shock directions 1, 2, 3, 4, 5: 100 g (11 ms) at 1 x IN, direction 6: 100 g (11 ms) at 0.8 x IN, with curves F1, F2: 100 g (11 ms) at 0.8 x IN to IEC 60068-2-27, test Ea Corrosion 96 hours at 5 % salt mist, to IEC 60068-2-11, test Ka Humidity 240 hours at 95 % RH, to IEC 60068-2-78, test Cab Mass approx. 90 - 120 g per pole depending on version UL 1077: 2009 www.e-t-a.de 1 Magnetic and Hydraulic-Magnetic Circuit Breaker 8345-... Ordering information for EN 60934 and UL 1077 1 Type No. 8345 Mounting B flange mounting, with rectangular aperture with mounting nut 6-32UNC C flange mounting, with rectangular aperture with mounting nut M3 F flange mounting, with round aperture with mounting nut M3 Configuration 0 without barrier 1 with small barrier 2 with large barrier (requested for multipole AC applications) Number of poles 1 single pole protected 2 two pole protected 3 three pole protected 4 four pole protected Actuator configuration A all poles with standard toggle B reduced number of standard toggles Z without actuator Terminal design P blade terminals ≤ 35 A R round connectors 6 mm U stud terminals M6 ≤ 125 A V stud terminals 1/4-20UNC-3A ≤ 125 A W laminated round terminals ≤ 125 A Terminal hardware 0 without 3 with washer and nut Characteristic curve *) Characteristic curve, instantaneous: F1 DC (limited to ratings of 1 A to 50 A) F2 AC 60/50 Hz (limited to ratings of 1 A to 50 A) Short delay: K1 DC K2 AC Medium delay: M1 DC M2 AC 60/50 Hz Long delay: T1 DC T2 AC 60/50 Hz Version D standard Colour configuration B1 black actuator Marking actuator base front plate B1 without ON-OFF B2 IN ON-OFF B3 IN, characteristic curves ON-OFF Rated voltage B AC or ≤ 80 V DC Current ratings Ordering information for auxiliary contact module Type number X8345 Module S auxiliary contact module Auxiliary contacts 01 in all poles 02 in pole 1 only Auxiliary contact version K auxiliary contacts (symmetrical terminals) Auxiliary contact function W1 1 changeover Terminal design 02 microswitch with blade terminals DIN 46244-A2.8-0.5 M mounted to base unit X8345 - S 01 K W1 02 M ordering example Approvals Authority Standard Rated voltage Current ratings VDE IEC / EN 60934 UL UL 1077 C22.2 No 235 AC 240/415 V AC 240 V DC 80 V AC 277/480 V AC 277 V DC 80 V 0.016 A…80 A 0.016 A…80 A 0.02 A…125 A 0.02 A…70 A 0.02 A…70 A 0.02 A…125 A UL UL 489 C22.2 No 5 CQC GB 17701 AC 120/240 V AC 240 V AC 120 V DC 80 V AC 240/415 V AC 240 V DC 80 V DC 110 V 0.05 A…80 A (2 pole) 0.05 A…20 A (1 pole) 0.05 A…80 A (1 pole) 0.05 A…125 A (1+2 pole) 0.02 A…80 A (3 pole) 0.02 A…80 A (1 + 2 pole) 0.02 A…125 A (1 + 2 pole) 0.05 A…125 A (1 + 2 pole) 0.02...125 A higher current ratings upon request 8345 - C 0 1 A - U 3 M1 - D B1 B1 B - 60 A ordering example Please be informed that we have minimum ordering quantities to be observed. Remote trip coil available to special order.  *) Other characteristic curves upon request (e.g. pulse delayed, for high inrush currents or capacitive loads) Note: Move actuator of multipole devices slowly and smoothly into ON position to ensure reliable latch-on behaviour of all poles. 2 www.e-t-a.de 2009 Magnetic and Hydraulic-Magnetic Circuit Breaker 8345-... Ordering information for UL 489 Type No. 8345 Mounting B flange mounting, with rectangular aperture with mounting nut 6-32UNC C flange mounting, with rectangular aperture with mounting nut M3 F flange mounting, with round aperture with mounting nut M3 Configuration 0 without barrier for DC 1 with small barrier for DC (optional) 2 with large barrier for AC Number of poles 1 single pole protected 2 two pole protected Actuator configuration A all poles with standard toggle B reduced number of standard toggles Z without actuator Terminal design P blade terminals ≤ 35 A R round connectors 6 mm U stud terminals M6 ≤ 125 A V stud terminals 1/4-20UNC-3A ≤ 125 A W laminated round terminals ≤ 125 A Terminal hardware 0 without 3 with washer and nut Characteristic curve *) Characteristic curve, instantaneous: F1 DC (limited to ratings of 1 A to 50 A) F2 AC 60/50 Hz (limited to ratings of 1 A to 50 A) Short delay: K1 DC K2 AC Medium delay: M1 DC M2 AC 60/50 Hz Long delay: T1 DC T2 AC 60/50 Hz Version D standard Colour configuration B1 black actuator Marking actuator base front plate B1 without ON-OFF B2 IN ON-OFF B3 IN, characteristic curves ON-OFF Rated voltage B AC or ≤ 80 V DC Current ratings 0.05...125 A for DC 0.05...20 A for AC higher current ratings upon request Approvals (optional) V UL 489 8345 - C 0 1 A - U 3 M1 - D B1 B1 B - 60 A - . Ordering information for auxiliary contact module Type number X8345 Module S auxiliary contact module Auxiliary contacts 01 in all poles 02 in pole 1 only Auxiliary contact version K auxiliary contacts (symmetrical terminals) Auxiliary contact function W1 1 changeover Terminal design 02 microswitch with blade terminals DIN 46244-A2.8-0.5 M mounted to base unit X8345 - S 01 K W1 02 M ordering example 1 ordering example Please be informed that we have minimum ordering quantities to be observed. Remote trip coil available to special order.  *) Other characteristic curves upon request (e.g. pulse delayed, for high inrush currents or capacitive loads) 2009 www.e-t-a.de 3 Magnetic and Hydraulic-Magnetic Circuit Breaker 8345-... Installation drawing Dimensions Mounting version B/C pole 1 2 3 blow out space (can be reduced on request) 4 LINE 45 1.77 19.1±0.1 .752±.004 63.5 2.50 1.13 ON 28.6 48 1.89 OFF OFF OFF 29 1.14 8 .315 number of poles 1 to 4 Flange mounting rectangular aperture OFF OFF 68 2.68 mounting thread M3 or 6-32 all dimensions referred to the top edge mounting depth 4.2 mm/.165 in. max. insertion depth 5.5 mm max. tightening torque 0.33 Nm operating area (reinforced insulation) 2 .079 2 .079 LOAD 1 mounting area terminal area Cut-out dimensions: multipole 76.5 3.01 66.9 2.63 47.8 1.88 11 .433 52.4 2.06 36.8 1.45 ø4 .157 19.2 .756 1 .039 1-pole 9.6 3.5±0.1 (M3) .378 +0.1 4 -0.15 (6-32UNC) .138±.004 (M3) +.004 .157-.006 (6-32UNC) n x 19.1 n x .752 19.1 .752 28.7 1.13 Mounting version F number of poles 1 to 4 Flange mounting round aperture pole 1 3 4 LINE OFF OFF OFF OFF 63.5 2.50 28.6 1.13 ON 2 19.1±0.1 .752±.004 48 1.89 LOAD OFF 68 2.68 Cut-out dimensions: mounting thread M3 or 6-32 all dimensions referred to the top edge mounting depth 4.2 mm/.165 in. max. insertion depth 5.5 mm max. tightening torque 0.33 Nm 1-pole max. panel thickness: 3 mm 4-pole ø15.4 .606 15.45 .608 44.75 1.76 ø15.4 .606 3.5±0.1 (M3) +0.1 4 -0.15 (6-32UNC) .138±.004 (M3) +.004 .157-.006 (6-32UNC) 19.1 .752 n x 19.1 n x .752 This is a metric design and millimeter dimensions take precedence ( mm ) inch 4 www.e-t-a.de 2009 Magnetic and Hydraulic-Magnetic Circuit Breaker 8345-... Internal connection diagrams Terminal design / Dimensions P - with blade terminals 1-pole protected magnetically 49.2 1.94 9.5 .374 line 1 11(C) unit 1 LINE R - round connectors D = 6 mm I > 12(NC) 14(NO) I > 12(NC) 14(NO) blade terminal A6.3-0.8 (QC .250) DIN 46244 2 (load) 1-pole protected hydraulic-magnetically line 1 line 1 2 (load) 11(C) 1 unit 2 11(C) I > 12(NC) 14(NO) unit 3 2 (load) ... LINE 19.2 .756 LOAD line 1 11(C) I > 12(NC) 14(NO) 49.2 1.94 2 (load) unit 4 ... LOAD multipole W - laminated round terminals LINE 5 .197 12.2 .480 27.6 1.09 LOAD ø6.3 ø.248 plug-in hole 6.3+0.1 .248+.004 49.2 1.94 cylindrical terminal area U/V stud terminals with auxiliary contacts LINE 17 .669 LOAD 17 NC NC NO NO C C 7.5 .295 17.5 .689 auxiliary contact module (change over) 7.5 .295 16.6 .653 tightening torque: 10-32 UNF. M5 max. 2 Nm 1/4-20 UNC. M6 max. 3 Nm This is a metric design and millimeter dimensions take precedence ( mm ) inch All dimensions without tolerances are for reference only. In the interest of improved design, performance and cost effectiveness the right to make changes in these specifications without notice is reserved. Product markings may not be exactly as the ordering codes. Errors and omissions excepted. 2009 www.e-t-a.de 5 Magnetic and Hydraulic-Magnetic Circuit Breaker 8345-... Typical time/current characteristics at +23 °C / +73.4 °F Curve F2 (instantaneous) for AC Curve F1 (instantaneous) for DC 1000 1000 100 100 1 Trip time in seconds 10000 Trip time in seconds 10000 10 1 0,1 10 1 0,1 0,01 0,01 0,001 0,001 0 1 2 3 4 5 6 7 8 … times rated current 9 10 11 0 12 Curve K1 (short delay) for DC 100 Trip time in seconds 1000 100 Trip time in seconds 10000 1000 10 1 0,1 3 5 7 8 4 6 … times rated current 9 10 11 12 10 1 0,1 0,01 0,001 0 1 2 3 4 5 6 7 … times rated current 8 9 10 11 0,001 12 Curve M1 (medium delay) for DC 0 1 2 3 4 6 5 7 … times rated current 8 9 10 11 12 8 9 10 11 12 8 9 10 11 12 Curve M2 (medium delay) for AC 50/60 Hz 10000 1000 1000 100 100 Trip time in seconds 10000 Trip time in seconds 2 Curve K2 (short delay) for AC 50/60 Hz 10000 0,01 10 1 0,1 0,01 10 1 0,1 0,01 0,001 0,001 0 1 2 3 4 5 6 7 8 … times rated current 9 10 11 12 Curve T1 (long delay) for DC 0 1 2 3 4 6 7 5 … times rated current Curve T2 (long delay) for AC 50/60 Hz 10000 1000 1000 100 100 Trip time in seconds 10000 Trip time in seconds 1 10 1 0,1 0,01 10 1 0,1 0,01 0,001 0 1 2 3 5 6 7 4 … times rated current 8 9 10 11 12 0,001 0 1 2 3 4 5 6 7 … times rated current N.B. All curves will only be maintained if the escutcheon is mounted on a vertical surface. Ambient temperature or mounting side-by-side does not influence the trip curve, derating is not required. The breakers may trip in the event of current peaks < 0.003 sec. For these applications we offer a mechanical pulse delay – please enquire. Other characteristic curves upon request (e.g. pulse delayed, for high inrush currents or capacitive loads). 6 www.e-t-a.de 2009 Magnetic and Hydraulic-Magnetic Circuit Breaker 8345-... Actuator configuration Accessories A 1 toggle per pole, mounting version B/C OFF OFF OFF OFF OFF OFF OFF OFF OFF OFF B reduced number of toggles per unit, mounting version B/C Splash cover (IP65) for 1-, 2-, 3-pole (only for mounting version B/C) number of mounting actuator poles version configuration X 222 444 01 1-pole B 1 X 222 444 02 1-pole C 1 X 222 444 11 2-pole B 2 X 222 444 12 2-pole C 2 X 222 444 21 3-pole B 3 X 222 444 22 3-pole C 3 panel thickness max. 2 mm 1 ON ON 66.7 2.63 OFF 67.5 2.66 52.4 2.05 OFF A 1 toggle per pole, mounting version F OFF OFF OFF OFF OFF OFF OFF OFF OFF 35 1.38 OFF 9,5 56.5 2.22 0.374 22.25 .876 ON OFF 67.5 2.66 B reduced number of toggles per unit, mounting version F OFF 74 2.91 Z without toggles version B/C OFF 64 2.52 OFF 2.8 .110 19.6 .772 OFF Toggle guard (only for mounting version B/C) Y 307 381 01 OFF OFF OFF ø4 .157 Interphase barriers / Dimensions 1 - Interphase barrier (small) 16.7 .657 37.3 1.47 19.2 .756 Z without toggles, mounting version F 52.4 2.06 Shock directions 2 - Interphase barrier (large) 2 4 3 1 LINE LOAD 70 2.75 76 2.99 LINE 5 31.5 1.24 LOAD 76 2.99 6 75 2.95 thickness 1mm / .039 in. LIN 100 3.94 E AD LO This is a metric design and millimeter dimensions take precedence ( mm ) inch 2009 www.e-t-a.de 7 Remote trip module X8345-F for Circuit Breaker 8345-... Description Dimensions A module which adds remote trip capability to all versions of type 8345. A voltage applied across the coil, by means of an external sensor for example, will cause disconnection of the main switch/circuit breaker mechanism. Additional remote trip module Typical applications LOAD LINE 1 19.0 .748 7.8 .307 Electrical monitoring of safety systems, remote trip. Ordering information 23.2 .913 Type No. X8345 Module for type 8345 Module F remote trip module Assembly version 01 only in pole 1 02 only in pole 2 Remote trip version X1 DC Voltage rating 12 12 V 24 24 V Terminal design 02 blade terminals DIN 4644-A2.8-0.5 M module mounted to circuit breaker X8345 - F 01 X1 12 02 M ordering example Internal connection diagram 1-pole protected hydraulic-magnetically with additional remote trip coil 1 line FA Preferred types + Preferred types remote trip module: X8345-F-01-X1-12-02-M X8345-F-01-X1-24-02-M Voltage rating Internal resistance (Ω) DC 12 V  3.2 DC 24 V 14.6 2 - Technical data Voltage ratings and typical internal resistance values This is a metric design and millimeter dimensions take precedence ( mm ) inch All dimensions without tolerances are for reference only. In the interest of improved design, performance and cost effectiveness the right to make changes in these specifications without notice is reserved. Product markings may not be exactly as the ordering codes. Errors and omissions excepted. 8 8.3 .327 16 .63 16.4 .645 Voltage ratings DC 12 V; DC 24 V Power consumption approx. 40 W Pulse operation 20 ms < tON < 100 ms/tOFF > 10 sec (Continuous duty possible for multipole devices upon request) Typical life 10,000 operations at UN Ambient temperature -40...+85 °C (-40...+185 °F) Insulation co-ordination (IEC 60664) 2.5 kV/2 (EN 60934) Dielectric strength test voltage between main circuit and trip coil circuit AC 3,000 V (EN 60934) Insulation resistance > 100 MΩ (DC 500 V) Vibration 6 g (57-2000 Hz) ± 0.46 mm (10-57 Hz) shock direction 1/2 4 g (57-2000 Hz) ± 0.30 mm (10-57 Hz) shock direction 3/4 3 g (57-2000 Hz) ± 0.23 mm (10-57 Hz) shock direction 5/6 to IEC 60068-2-6, test Fc 10 frequency cycles/axis Shock 100 g (11 ms) (not when mounted upside down) to IEC 60068-2-27, test Ea Corrosion 96 hours at 5 % salt mist, to IEC 60068-2-11, test Ka Humidity 240 hours at 95 % RH to IEC 60068-2-78, test Cab Mass approx. 8.5 g (without base unit) www.e-t-a.de 2009 Remote ON/OFF actuation X8345-R for Circuit Breaker 8345 Description The X8345-R is an additional module which provides remotely controlled ON and OFF functionality for the E-T-A series 8345 magnetic circuit breaker range. The module actuator, which is motor driven, is factory fitted adjacent to the circuit breaker(s) which it is controlling. The module can be operated by a suitable external changeover switch, momentary switches (one ON, one OFF). The status of the actuator will follow the position of the external switch, i.e. if the circuit breaker trips electrically or is operated manually, the actuator will not change. A single module will control a single pole breaker or multipole circuit breakers up to 3 poles. In the application it has to be ensured that the supply voltage is maintained at all times. When switching the circuit breaker OFF manually the module has also to be switched off by means of the changeover switch before switching the breaker on again. The same is true for normal switch-on of the breaker. 1 X8345-R US patent number: US 7,532,095 B2 Internal connection diagrams Ordering information single pole, hydraulic-magnetic protection, with remote ON/OFF actuation (operated by changeover switch) Type number X8345 Module for type 8345, 1, 2 pole and 3 pole Module R remote ON/OFF actuation Operating voltage 24 DC 24 V  Add-on version 01 mounted on right side Mounting method 00 front panel mounting (standard) 02 2-bracket: module and circuit breaker fitted Terminal design 01 spring loaded screwless terminal 5-pin Supply status M module mounted to the base unit X8345 - R 24 01 00 01 M changeover switch (not part of the product) OFF C X8345-R 1 11 8345 with Si 2 ordering example 12 14 single pole, hydraulic-magnetic protection, with remote ON/OFF actuation (actuated by two momentary switches) Voltage rating ON duty Trip time Blocking current Control current Typical life DC 24 V (16...32 V) 50 % / 60 sec < 2 sec < 1.5 A < 3 mA 10,000 operations (ON/OFF) Ambient temperature Insulation co-ordination (IEC 60664) Dielectric strength pole to module Insulation resistance Vibration Shock Corrosion Humidity -25...70 °C (-13...158 °F) 2009 + M Technical data Mass ON - momentary switch (not part of the product) OFF C ON - + X8345-R M 1 11 2 12 14 8345 with Si 2.5 kV/2 (EN 60934) test voltage AC 1,500 V (EN 60934) > 100 MΩ (DC 500 V) 10 g (57-2000 Hz), ± 0,76 mm (10-57 Hz) to IEC 60068-2-6, test Fc, 10 frequency cycles/axis 100 g (11 ms) to IEC 60068-2-27, test Ea 96 hours at 5 % salt mist, to IEC 60068-2-11, test Ka 240 hours at 95 % RH, to IEC 60068-2-78, test Cab approx. 65 g (without base unit) Typical applications Remote circuit breaker control (ON/OFF) for communication systems, marine installations, automation equipment and similar requirements. Caution: During actuation of the remote control, free travel of the toggle must be ensured. www.e-t-a.de 9 Remote ON/OFF actuation X8345-R for Circuit Breaker 8345 Dimensions X8345-R-24-01-02-01-M 63.5 2.5 42 1.65 1 19 38 .748 1.49 57 2.24 OFF C ON M6 63.5 2.5 spring loaded screwless terminal 5-pin 0,2 – 1,2 mm2 (AWG 24 – AWG16) - + 76 2.99 62 2.44 78 3.07 X8345-R-24-01-00-01-M OFF C ON 14.2 .559 14 .551 11 .433 48 1.89 19.7 .775 30° - + 23 .905 49.2 1.94 12 .472 16 .629 63.5 2.5 This is a metric design and millimeter dimensions take precedence ( mm ) inch 10 All dimensions without tolerances are for reference only. In the interest of improved design, performance and cost effectiveness the right to make changes in these specifications without notice is reserved. Product markings may not be exactly as the ordering codes. Errors and omissions excepted. www.e-t-a.de 2009
物料型号:8345
器件简介:8345系列是单极或多极液压-电磁式断路器,具有自由脱扣机制和切换操作。提供多种切换特性选择,适用于广泛的应用场景。符合行业标准尺寸和面板安装。可选配辅助触点。在额定负载下低温敏感性低。符合CBE标准EN 60934 (IEC 60934) S型HM CBE。
引脚分配:文档中未明确提供引脚分配的详细信息,但提到了辅助电路的电压和电流规格。
参数特性: - 额定电压:3 AC415V; AC 277/480V; AC 120/240 V; AC 240V; DC 80V(更高直流电压可特殊定制) - 额定电流范围:0.02...125 A单极和多极,更高额定电流可应要求提供 - 辅助电路:AC240V 6A,DC28V 3A,DC65V 1A,DC 80V 0.5 A - 典型寿命:在1xIN下10,000次操作 - 环境温度:-40...+85°C(-40...+185°F) - 绝缘协调(IEC60664):2.5kV/2,操作区域加强绝缘 - 绝缘电阻:>100M (DC500V) - 防护等级(IEC60529):操作区域IP40,端子区域P00
功能详解: - 提供远程脱扣能力,可通过外部传感器施加的电压来实现主开关/断路器机构的断开。 - 适用于安全系统的电气监控和远程脱扣。
应用信息:典型应用领域包括通信和运输业务领域的电源、开关设备、仪表和过程控制工程。
8345-C01A-R0K1-DB1B2B-20A 价格&库存
很抱歉,暂时无法提供与“8345-C01A-R0K1-DB1B2B-20A”相匹配的价格&库存,您可以联系我们找货