D-Series Hydraulic-Magnetic Circuit Breaker P ROD UC T W E BP A GE request sample, configure part, watch video DIN Rail Mounted Circuit Breaker The D-Series hydraulic-magnetic circuit breakers feature simple snap on back panel DIN rail mounting for easy assembly and removal. Added safety features round out this thoughtful breaker design with recessed wire ready terminals that are both touch proof and shock resistant. D-Series breakers are available as a one to four pole breaker, rated up to 50 amps, 480Y/277VAC or 80VD and with a max IC of 5,000 amps. 1-4 0.02-50 80 Poles Amps Typical Applications ∙ Industrial Controls www.carlingtech.com ∙ Renewable Energy 860.793.9281 sales@carlingtech.com VDC Max 480Y VAC Max Tech Specs Mechanical Electrical Endurance 10,000 ON-OFF operations @ 6 per minute; with rated current & voltage. Trip Free All D-Series circuit breakers will trip on overload, even when actuator is forcibly held in the ON position. Trip Indication The operating actuator moves positively to the OFF position when an overload causes the breaker to trip. Maximum Voltage AC, 480Y VAC (See Table A), 50/60 Hz, 80VDC Standard Current Coils 0.100, 0.250, 0.500, 0.750, 1.00, 2.50, 5.00, 7.50, 10.0, 15.0, 20.0, 25.0, 30.0, 35.0, 40.0 & 50.0. Other ratings available - consult factory. Standard Voltage Coils DC - 6V, 12V; AC - 120V, other ratings available, see ordering scheme. Insulation Resistance Minimum of 100 Megohms at 500 VDC. Dielectric Strength UL, CSA: 1960 V 50/60 Hz for one minute between all electrically isolated terminals. D-Series circuit breakers comply with the 8mm spacing and 3750V 50/60 Hz dielectric requirements from hazardous voltage to operator accessible surfaces and between adjacent poles per Publications EN 60950 and VDE 0805. Physical Values from Line to Load Terminal based on Series Trip Circuit Breaker Resistance, Impedance Number of Poles Rocker Type: 1-3; Handle Type: 1-4 Internal Circuit Config. Switch Only and Series Trip with current or voltage trip coils. Weight Approximately 128 grams/pole (Approximately 4.57 ounces/pole) Standard Colors Housing - Black; Actuator - See Ordering Scheme. Mounting Mounts on a standard 35mm Symmetrical DIN Rail (35 x 7.5 or 35 x 15mm per DIN EN5002). RESISTANCE, IMPEDANCE VALUES RESISTANCE PER POLE VALUES from Line toto Load Terminals from Line Load Terminals (Values (ValuesBased Basedon onSeries SeriesTrip TripCircuit CircuitBreaker Breaker) 1000 TOLERANCE 0.10 - 5.0 15 (AMPS) 100 10 O H M S CURRENT 1 Environmental (%) 5.1 - 20.0 25 20.1 - 50.0 35 Designed and tested in accordance with requirements of specification MIL-PRF-55629 & MIL-STD-202 as follows: 0.001 0.01 0.1 1 10 AMPERE RATING 60 Hz 1/2 Cycle Inrush Pulse Tolerance Time Delay Curves 42, 44 & 46 (50 Amps Max.) 25x Ir 50 Hz 1/2 Cycle Inrush Pulse Tolerance Time Delay Curves 42, 44 & 46 (50 Amps Max.) 22x Time Delay Curves 22, 24, 26 (70 Amps Max.) 12x Multiple of Rated Current Multiple of Rated Current Vibration Withstands 0.060” excursion from 10-55 Hz, and 10 Gs 55-500 Hz, at rated current per Method 204C, Test Condition A. Instantaneous and ultra-short curves tested at 90% of rated current. Moisture Resistance Method 106D, i.e., ten 24-hour cycles @ + 25°C to +65°C, 80- 98% RH. Salt Spray Method 101, Condition A (90-95% RH @ 5% NaCl Solution, 96 hrs). Thermal Shock Method 107D, Condition A (Five cycles @ -55°C to +25°C to +85°C to +25°C). Operating Temperature -40° C to +85° C 100 Pulse Tolerance Curves Time Delay Curves 22, 24 (100 Amps Max.) 26 (70 Amps Max.) 10x t t 4.165 8.33 16.67 Time in Milliseconds 2. Withstands 100 Gs, 6ms, sawtooth while carrying rated current per Method 213, Test Condition “I”. Instantaneous and ultra-short curves tested @ 90% of rated current. 0.1 0.01 Ir Shock 5.0 10.0 20.0 Time in Milliseconds *Manufacturer reserves the right to change product specification without prior notice. Tech Specs Tables Table A: Lists UL Recognized, CSA Accepted and VDE Certified configurations and performance capabilities as a Component Supplementary Protector. Component Supplementary Protectors Voltage Circuit Configuration Max Rating DC 80 125 / 250 250 277 50 / 60 1&3 --0.02 - 50 5,000 2 1 1&3 65 DC 250 277 --1 480 Y 3 Switch Only UL/CSA Application Codes VDE Frequency Phase 1 Full Load with without (Inc) with (Icn) without Amps Backup Fuse Backup Fuse Backup Fuse Backup Fuse 65 Series Short Circuit Capacity (Amps) Current Rating 480 Y 3 5,000 1,500 3,000 --- --- --- --- --- CSA TC1, 2, OL1, U1 TC1, 2, OL1, U1 TC1, 2, OL1, C1 TC1, 2, OL1, C1 --3 50 / 60 5,000 UL 0.02 - 50 1 1&3 0.02 - 30 Notes: 1 DC and 1 Phase 277 V ratings are 1 or 2 poles breaking. Three phase ratings are 3 poles breaking. 2 Requires branch circuit backup with a UL LISTED Type K5 or RK5 fuse rated 15A minimum and no more than 4 times full load amps not to exceed 150 A for 250V rating and 125 A for 277 and 480 V ratings. 3 UL recognition and CSA Acceptance at 480 volts refers to 3 and 4 pole versions, used only in a 3 phase WYE connected circuit or 2 pole versions connected with 2 poles breaking 1 phase and backed up with series fusing per note 2 Agency Approvals UL 1077 Component Recognition Program as Protectors, Supplementary (Guide QVNU2, File E75596) UL 508 Switches, Industrial Control (Guide NRNT2, File E148683) CSA Accepted Component Supplementary Protector under Class 3215 30, File 047848 0 000 CSA Standard C22.2 No. 235 VDE Certified EN60934, VDE 0642 under File No. 10537 Time Delay Specs To view all hydraulic-magnetic circuit breaker time delay values, please visit www.carlingtech.com/sites/default/files/documents/Carling-HM-CB-Time-Delays.pdf 3. Ordering Scheme D Sample Part Number A 3 - B0 - 10 -450 - 1 2 1 - C 1 Selection 2 3 4 5 1. SERIES D CODE AMPERES 1 Handle 2 A Handle, one per pole B Handle, one per multipole unit Visi-Rocker 3 C Indicate ON, vertical legend D Indicate ON, horizontal legend E Indicate ON, no legend (VDE approval not available with no legend) F Indicate OFF, vertical legend G Indicate OFF, horizontal legend H Indicate OFF, no legend (VDE approval not available with no legend) Single Color Rocker 3 J Vertical legend K Horizontal legend L No legend (VDE approval not available with no legend) ROCKER STYLE DESCRIPTIONS INDICATE “OFF” VERTICAL STYLE INDICATE “ON” CODE “C” LINE INDICATE COLOR LOCATION LINE LINE HORIZONTAL STYLE CODE “D” LINE CODE “J”, ”R” CODE “F”, ”N” CODE “K”, ”U” CODE “G”, ”O” LINE LINE 2 1 One 2 Two 3 Three 4 Four 4. CIRCUIT A0 Switch Only (No Coil) 4 B0 Series Trip (Current) C0 Series Trip (Voltage) 5. FREQUENCY & DELAY 03 DC 50/60Hz, Switch Only 10 5 DC Instantaneous 11 DC Ultra Short 12 DC Short 14 DC Medium 16 DC Long 20 5 50/60Hz Instantaneous 21 50/60Hz Ultra Short 22 50/60Hz Short 24 50/60Hz Medium 7 8 9 275 0.750 280 0.800 285 0.850 410 1.000 512 1.250 413 1.300 414 1.400 415 1.500 517 1.750 420 2.000 522 2.250 425 2.500 527 2.750 430 3.000 532 3.250 435 3.500 436 3.600 440 4.000 445 4.500 547 4.750 10 9 450 5.000 455 5.500 460 6.000 465 6.500 470 7.000 572 7.250 475 7.500 480 8.000 485 8.500 490 9.000 495 9.500 610 10.000 710 10.500 611 11.000 711 11.500 612 12.000 712 12.500 613 13.000 614 14.000 615 15.000 616 16.000 617 17.000 618 18.000 619 19.000 620 20.000 621 21.000 622 22.000 623 23.000 624 24.000 625 25.000 626 26.000 627 27.000 628 28.000 629 29.000 630 30.000 632 32.000 635 35.000 640 40.000 645 45.000 650 50.000 OR VOLTAGE COIL (NORMAL RATED VOLTAGE) A06 A12 A18 A24 A32 6 DC, 5 DC 12 DC, 10 DC 18 DC, 15 DC 24 DC, 20 DC 32 DC, 25 DC A48 48 DC, 40 DC A65 65 DC, 55 DC J06 6 AC, 5 AC J12 12 AC, 10 AC J18 18 AC, 15 AC J24 J48 K20 L40 26 50/60Hz Long 32 DC, 50/60Hz Short 34 DC, 50/60Hz Medium 36 DC, 50/60Hz Long 42 6 50/60Hz Short, High-inrush 44 6 50/60Hz Medium, High-inrush 46 6 50/60Hz Long, High-inrush 52 6 DC, Short, High-inrush 54 6 DC, Medium, High-inrush 56 6 DC, Long, High-inrush Configure Complete Part Number > Browse Standard Parts > 24 AC, 20 AC 48 AC, 40 AC 120 AC, 65 AC 240 AC, 130 AC 7. TERMINAL 1 2 #10 Screw & Pressure Plate for Direct Wire Connection #10 Screw without Pressure Plate 8. ACTUATOR COLOR & LEGEND Actuator or Visi-Color Marking: Color: I-O ON-OFF Dual/None White A B 1 Black C D 2 Red F G 3 Green H J 4 Blue K L 5 Yellow M N 6 Gray P Q 7 Orange R S 8 Marking Color: Single Color Rocker/Handle Visi-Rocker 7 Black White White n/a White Red White Green White Blue Black Yellow Black Gray Black Orange 9. MOUNTING / VOLTAGE Notes: 1 Handle breakers available up to four poles. Rocker breakers available up to three poles. 2 Actuator Code: A: Multi-pole units factory assembled with common handle tie. B: Handle location as viewed from front of breaker: 2 pole - left pole 3 pole - center pole 4 pole - two handles at center poles 3 Multipole rocker breakers have one rocker per breaker, as viewed from the front of the panel. Two pole - left pole. Three pole - center pole 4 ≤ 30A, select Current Rating code 630. 31-50A, select Current Rating code 650. 5 Voltage coil only available with delay codes 10 & 20. 6 Available to 50A max with circuit code BO only. 7 Color shown is visi and legend with remainder of rocker black. 8 ≥ 300V: Three pole breaker 3Ø or 2 pole breaker 1Ø, UL/CSA limited to 30 FLA max. 9 VDE Approval requires Dual (I-O, ON-OFF) or I-O markings 4. 020 0.020 025 0.025 030 0.030 050 0.050 075 0.075 080 0.080 085 0.085 210 0.100 215 0.150 220 0.200 225 0.250 230 0.300 235 0.350 240 0.400 245 0.450 250 0.500 255 0.550 260 0.600 265 0.650 270 0.700 CODE AMPERES SINGLE COLOR FIG.B 3. POLES 6 6. CURRENT RATING (AMPERES) D-Series 2. ACTUATOR Handle & Rocker 1 C 8 2 D 8 MOUNTING STYLE Threaded Insert 6-32 x 0.195 inches 6-32 X 0.195 inches ISO M3 x 5mm ISO M3 x 5mm VOLTAGE < 300 ≥ 300 < 300 ≥ 300 10. AGENCY APPROVAL C D 9 UL Recognized & CSA Accepted VDE Certified, UL Recognized & CSA Accepted Circuit & Terminal Diagram inches [millimeters] HANDLE ACTUATOR ROCKER ACTUATOR INDICATE “ON” SERIES TRIP (2 TERM’S.) SWITCH ONLY (2 TERM’S.) LINE LINE MULTI-POLE INDENTIFICATION SCHEME POLE 1 POLE 2 POLE 3 LINE LOAD LOAD LOAD ROCKER ACTUATOR INDICATE “OFF” & SINGLE COLOR SERIES TRIP (2 TERM’S.) LOAD SWITCH ONLY (2 TERM’S.) LOAD MULTI-POLE INDENTIFICATION SCHEME POLE 1 POLE 2 POLE 3 LOAD LINE LINE LINE (HANDLE ACTUATOR SHOWN) .346 [8.79] TYP LINE TABLE A ON TIGHTENING TORQUE SPEIFICATIONS 2.920 [74.17]TYP 3.612 [91.75]TYP F OF 1.240 [31.49]TYP TERMINAL ARE SUPPLIED WITH #10-32 SCREW AND PRESSURE PLATE PER TERMINAL 5. #6-32[M3] HARDWARE #6-32 THD TERMINAL SCREW LOAD Notes: 1 Tolerance ±.020 [.51] unless otherwise specified. THREAD SIZE TORQUE 7-9 IN-LBS [0.8-1.0 NM] 15-20 IN-LBS [1.7-2.3 NM] Dimensional Specs Rocker inches [millimeters] INDICATE”ON” .346 [8.79] .775 [19.68] INDICATE”OFF” & SINGLE COLOR #10-32 x .375 LONG SCREW (2 REQ’D.)/ POLE #6-32[M3] THREAD x .195[4.95] DEEP (2 PLC’S.)/POLE 2.062 [52.37] TYP LINE 2.920 [74.17] TYP 1.438 [36.53] TYP .755 [19.18] MAX LOAD 2.165 [54.99]TYP 1.929 [49.00] .962 [24.43] (INDICATE “OFF” SHOWN) LOAD LINE 1.681 [42.69] 1-POLE (DF1) .430 [10.92] TYP .590 [14.98] 1.240 [31.49] LOAD 3.612 [91.75] TYP 1.410 [35.81] .705 [17.90] LINE 1.681 [42.69] REF 2-POLE (DF2) 2-POLE (DC2) .750 [19.05] 1.515 [38.48] MAX 3-POLE (DF3) 3-POLE (DC3) LINE P(3) P(2) P(1) .750 [19.05] TYP 2.265 [57.53] P(3) P(2) P(1) MAX (SEE NOTE 4) (SEE NOTE 4) STANDARD 35mm SYMMETRICAL DIN RAIL (35 X 7.5 OR 35 x 15mm DIN EN50022) SCREW DRIVER ASSEMBLY 6. Notes: 1 Tolerance ±.020 [.51] unless otherwise specified. 2 Dimensions apply to all variations shown. Notice that circuit breaker line and load terminal orientation on indicate OFF is opposite of indicate ON. 3 For pole orientation with horizontal legend, rotate front view clockwise 90°. REMOVAL Dimensional Specs Handle inches [millimeters] #10-32 x.375 LONG SCREW (2 REQ’D) / POLE #6-32 [M3] THREADED x .195[4.95]DEEP (2 PLC’S.)/POLE .962 [24.43] LINE 1 POLE (DA1) 2.165 [54.99]TYP .705 [17.91] 1.410 [35.81] 1.438 [36.53]TYP 2.062 [52.37]TYP 2.920 [74.17] TYP .755 [19.18] MAX TYPICAL-OPTIONAL “I-O” OR “ON-OFF” LEGEND LOAD 2 POLE (DA2) 3.612 [91.75] TYP .150 [3.81]TYP .540 [13.72] MULTI-POLE UNITS ARE ASSEMBLED AT FACTORY WITH COMMON HANDLE TIE. 1.240 [31.49]TYP 2 POLE (DB2) .750 [19.05] 1.515 [38.48] 3 POLE (DA3) 1.515 [38.48] 1.520 [38.61] .760 [19.30] TYP. PER POLE 3 POLE (DB3) 2.265 [57.53] MAX 2.062 [52.37] .750 [19.05] MAX 4 POLE (DA4) 2.265 [57.53] MAX .750 [19.05] TYP Notes: 1 Tolerance ±.010 [.25] unless otherwise specified. .156DIA[ 3.96] 2 PLC’S TYP. 3.040 PER POLE [77.22] 2.280 [57.91] 1.448 [36.78] .432 [10.97] DA1 DB2 DB3 DA2 DB4 DA3 .750 [19.05] TYP DA4 PANEL CUTOUT DETAIL 4 POLE (DB4) 3.015 [76.58] MAX 7. 1.929 [49.00] 1.681 [42.69] TOLERANCES +.005[.12] 3.015 [76.58] MAX STANDARD 35mm SYMMETRICAL DIN RAIL (35 X 7.5 OR 35 x 15mm DIN EN50022) SCREW DRIVER ASSEMBLY REMOVAL Authorized Sales Representatives and Distributors Click on a region of the map below to find your local representatives and distributors or visit www.carlingtech.com/findarep. CANADA EUROPE USA MIDDLE EAST MEXICO AFRICA ASIA-PACIFIC OCEANIA SOUTH AMERICA About Carling Founded in 1920, Carling Technologies is a leading manufacturer of electrical and electronic switches and assemblies, circuit breakers, electronic controls, power distribution units, and multiplexed power distribution systems. With six ISO9001 and IATF16949 registered manufacturing facilities and technical sales offices worldwide, Carling Technologies Sales, Service and Engineering teams do much more than manufacture electrical components, they engineer powerful solutions! To learn more about Carling please visit www.carlingtech.com/company-profile. To view all of Carling’s environmental, quality, health & safety certifications please visit www.carlingtech.com/environmental-certifications. 8. © Carling Technologies, Inc. Carling, Visi-Rocker are registered trademarks of Carling Technologies, Inc. in the U.S. and other countries. Mouser Electronics Authorized Distributor Click to View Pricing, Inventory, Delivery & Lifecycle Information: Carling Technologies: DA2-B0-34-450-121-C DA1-B0-34-650-121-C DA1-B0-34-620-121-D DA1-B0-10-610-121-D DA2-B0-46-615-121-D DA3-B0-42-615-121-C DA1-B0-14-615-121-C DG1-B0-34-650-131-C DB4B020650122D DB4B024620122D DC1B024210141D DC1B034450141D DC2B024615131C DC3B024615131C DD3B024650131D DF2A003630131C DF2B044410132C DF2B046450131D DF2B046615131D DF3B026475131D DF3B034630131D DF3B034650131D DG1B014450131C DG1B014620131C DG1B024610131C DG1B024615131C DG1B034450131C DG1B034610131C DG1B034620131C DG2B034650131C DG2B046620131C DG3B024620131C DG3B034630131C DG3B046650131C DJ1B010250121D DJ1B010410121D DJ1B010450121D DJ1B010610121D DJ1B034450121C DJ1B034615121D DJ1B034620121D DJ2B024640121D DJ3B024650121D DJ3B026620122D DK1B014450131C DK1B014610131C DK1B014620131C DK1B014650131C DA2B034650121D DC1A003650141C DC1B024410141D DC1B024450141D DC1B034610131C DC2B024620131C DC2B026650141C DC2B044630141D DC3B024650131C DC3B026630141C DD1B034450131C DD1B034610131C DD1B034630131C DD1B034650131C DD2B024650131D DD2B044620111D DF1B012410141C DF1B014450131C DF1B024615131C DF1B034610131C DF1B034650131C DF1B046450131D DF1B046625131D DF1B056650131C DG2B034615131C DK3B042615121C DC1B0104501G1C DC1B0546101G1C DA1A003630112C DA1A003630122C DA1A0036301D1C DA1B010420122D DF2B0246152F1C DF2B0246201F1C DF2B0246202F1C DF2B0466151GCC DF2B0466211G1C DD2B024615162C DD2B024625162C DD3B0246101G2C DD3B0246301G2C DF1A0036301A1C DF2B0246151F1C DC1B034450241C DC1B034460241C DC2B0246501B1C DC2B0446251B1C DD1B0342501G2C DD2B024450162C DC1B0246101B1C DC1B034410141C DC1B034410241C
DA1-B0-52-615-121-C
物料型号:D-Series液压-磁路断路器
器件简介:D-Series液压-磁路断路器是Carling Technologies品牌下的产品,具有简单的卡扣式后面板DIN导轨安装,便于组装和拆卸。断路器设计考虑了附加的安全特性,例如内陷的电线就绪端子,这些端子既防触电又抗冲击。D-Series断路器提供一至四极断路器,额定电流高达50安培,适用于480Y/277VAC或80VDC,最大断路电流(IC)为5,000安培。
引脚分配:文档中未明确列出具体的引脚分配图,但提到了断路器的极数和安装方式,包括一至四极断路器。
参数特性: - 最大电压:AC 480Y VAC (见表A),50/60 Hz,80VDC - 标准电流线圈:0.100, 0.250, 0.500, 0.750, 1.00, 2.50, 5.00, 7.50, 10.0, 15.0, 20.0, 25.0, 30.0, 35.0, 40.0 & 50.0。其他额定值可咨询工厂。 - 标准电压线圈:DC-6V, 12V; AC-120V,其他额定值见订购方案。 - 绝缘电阻:最小100兆欧姆,在500VDC下。 - 抗电强度:符合UL和CSA标准,1960V 50/60 Hz,持续一分钟,所有电气隔离端子之间。
功能详解: - 断路器能够在过载时即使在强制保持在ON位置时也能跳闸。 - 操作执行器在过载导致断路器跳闸时会明确移动到OFF位置。
应用信息:适用于工业控制和可再生能源领域。
封装信息:D-Series断路器设计用于标准35mm对称DIN导轨(35 x 7.5或35 x 15mm每DIN EN50022)安装。
环境测试:根据MIL-PRF-55629和MIL-STD-202规范进行设计和测试,包括冲击、振动、耐湿性、盐雾、热冲击和工作温度范围(-40°C至+85°C)。