2CLE-15E
2CLE-15E
    EATON(伊顿)
    Cartridge,Non-Standard
    FUSE CARTRIDGE 15A 2.75KVAC
2CLE-15E 数据手册
Technical Data 10350 Effective October 2019 Supersedes April 2015 BUSSMANN SERIES 2.75kV E-Rated medium voltage fuses for feeder circuit, switchgear and transformer protection Features and benefits • Current-limiting E-Rated medium voltage fuses are defined by their melting time-current characteristic that permit their electrical interchangeability with other fuses of the same E Rating. • E-Rated fuses must have a defined current response time specified by ANSI C37.46. E-Rated fuse of 100 amps and below must melt in 300 seconds at an RMS current within the range of 200% to 240% of the fuse’s nameplate current rating. E-Rated fuses greater than 100 amps must melt in 600 seconds at an RMS current within the range of 220% to 264% of the fuse’s nameplate current rating. • E-Rated fuses are physically dimensioned for easy installation in existing hardware. • Current-limiting fuses provide positive interruption even on low fault currents. The fuse limits the magnitude of electromechanical stresses in the protected apparatus. • Open fuse indicator speeds troubleshooting by providing a positive visual indication of fuse operation. • 50/60Hz operating frequency for worldwide application. • Mountings are available in disconnect and nondisconnect versions with porcelain or glass polyester insulators. • Live parts and end fittings available. Description: • E-Rated, current-limiting, medium voltage fuses for feeder circuit, switchgear and transformer protection. Typical applications: • Medium voltage transformer primary protection • Medium voltage feeder circuit protection • Medium voltage switches • Medium voltage metal-enclosed switchgear Technical Data 10350 2.75kV E-Rated medium voltage fuses for feeder circuit, switchgear and transformer protection Effective October 2019 2.75kV E-Rated medium voltage ferrule fuses Dimensions (see catalog number tables for values) C Catalog symbols: • 2CLE-_E • JCX-_E B Ratings: • Volts — 2.75kV • Amps — 10 to 450A • Interrupting ratings • 50kA RMS Sym (2CLE-_E) • 3.31 (84.1) B 40kA RMS Sym (JCX-_E) Agency information: • A E-Rated fuses meet the performance characteristics of ANSI C37.46 Recommended fuse holders: CLE Catalog number Approximate dimensions - in (mm) Fuse mounting type* Amp rating Voltage BIL (kV) Diameter A Clip center B Length C Mounting (including live parts, end fittings)** Porcelain insulator Glass-polyester insulator Live parts (including end fittings) End fittings (disconnect only) 2CLE-PNM-C 2CLE-GNM-C CLE-NL-C — 2CLE-PDM-C 2CLE-GDM-C CLE-DL-C CLE-DF-C 2CLE-PNM-D 2CLE-GNM-D CLE-NL-D — 2CLE-PDM-D 2CLE-GDM-D CLE-DL-D CLE-DF-D 2CLE-PNM-E 2CLE-GNM-E CLE-NL-E — 2CLE-PDM-E 5CLE-GDM-E CLE-DL-E CLE-DF-E CLE 15E–25E Single barrel Non-disconnect 60 Disconnect† 60 10E–225E Single barrel Non-disconnect 60 Disconnect† 60 250E–300E 350X-450X Double barrel Non-disconnect 60 Disconnect† 60 2 (51) 8.1 (206) 9.5 (241) 3 (76) 7 (178) 10.9 (277) 3 (76) 7 (178) 10.9 (277) * See page 9 for illustrations and dimensions. ** End fittings supplied only when required. † Disconnect mountings provide a means for fuse extraction only. Do not use a disconnect mounting for load switching or fuse removal while energized. Recommended fuseclips: Clip dimensions - in (mm) Fuse diameter in (mm) 2 (51) 3 (76) 3 (76) 3 (76) Description Enclosed fuseclip Enclosed fuseclip Open fuseclip Spring loaded open fuseclip Figure 1 1 2 3 A 3.75 (95) 4.14 (105) B 1.98 (50) 2.45 (62) C D E F 2.01 (51) 1.19 (30) 4.54 (115) 1.51 (38) 3.01 (76) 1.19 (30) 5.64 (143) 1.51 (38) See dimensions drawing See dimensions drawing *For single barrel applications only. Not sold in pairs. Figure 1 Figure 2 C A D B G F E 2 Eaton.com/bussmannseries Figure 3 Catalog G number 0.4 (10) A3354710* 0.4 (10) A3354730* 1A0065 9078A67G04 2.75kV E-Rated medium voltage fuses for feeder circuit, switchgear and transformer protection Technical Data 10350 Effective October 2019 CLE and JCX Amp rating 1 Length A 9.2 (234) 2 3 5 7 10 10 15 20 25 30 40 50 65 80 100 125 150 200 225 250* 300* 350** 400** 450** 9.2 (234) 9.2 (234) 9.2 (234) 9.2 (234) 9.2 (234) 10.9 (277) 9.5 (241) 9.5 (241) 9.5 (241) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) 10.9 (277) Dimensions - in (mm) Diameter Clip centers B C 2 (51) 7 (178) 2 2 2 2 2 3 2 2 2 3 3 3 3 3 3 3 3 3 3 3 3 3 3 3 (51) (51) (51) (51) (51) (76) (51) (51) (51) (76) (76) (76) (76) (76) (76) (76) (76) (76) (76) (76) (76) (76) (76) (76) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 8.1 (206) 8.1 (206) 8.1 (206) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) 7 (178) Interrupting rating kA (RMS Sym.) 40 Number of barrels 1 Installation location Indoor/outdoor Catalog number JCX-1E 40 40 40 40 40 50 50 50 50 50 50 50 50 50 50 50 50 50 50 50 50 50 50 50 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 1 2 2 2 2 2 Indoor/outdoor Indoor/outdoor Indoor/outdoor Indoor/outdoor Indoor/outdoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor Indoor JCX-2E JCX-3E JCX-5E JCX-7E JCX-10E 2CLE-10E 2CLE-15E 2CLE-20E 2CLE-25E 2CLE-30E 2CLE-40E 2CLE-50E 2CLE-65E 2CLE-80E 2CLE-100E 2CLE-125E 2CLE-150E 2CLE-200E 2CLE-225E 2CLE-250E 2CLE-300E 2CLE-350X 2CLE-400X 2CLE-450X * 250A and 300A ratings may also be applied at 280 and 325 amps respectively, but fuses will no longer be complaint with ANSI E Rating criteria. ** Does not comply with ANSI C37.46 for “E” rating. Eaton.com/bussmannseries 3 Technical Data 10350 Effective October 2019 2.75kV Time-current curves — minimum melt for JCX-_E 4 Eaton.com/bussmannseries 2.75kV E-Rated medium voltage fuses for feeder circuit, switchgear and transformer protection 2.75kV E-Rated medium voltage fuses for feeder circuit, switchgear and transformer protection Technical Data 10350 Effective October 2019 2.75kV Time-current curves — total clear for JCX-_E Eaton.com/bussmannseries 5 Technical Data 10350 Effective October 2019 2.75kV E-Rated medium voltage fuses for feeder circuit, switchgear and transformer protection 2.75kV Time-current curves — minimum melt for 2CLE-_E and 2CLE-_X 2CLE-_ 6 Eaton.com/bussmannseries Curve 53653202 July 2001 Reference # 563532 Curve 53686104 July 2001 Reference # 536861 Curve 53690002 July 2001 Reference # 536900 2.75kV E-Rated medium voltage fuses for feeder circuit, switchgear and transformer protection Technical Data 10350 Effective October 2019 2.75kV Time-current curves — total clear for 2CLE-_E and 2CLE-_X 2CLE-_ Curve 56353302 July 2001 Reference # 563533 Curve 53690102 Curve 53686204 July 2001 July 2001 Reference # 536862 Reference # 536901 Eaton.com/bussmannseries 7 Technical Data 10350 Effective October 2019 2.75kV E-Rated medium voltage fuses for feeder circuit, switchgear and transformer protection 2.75kV Peak let-through for 2CLE-_E and 2CLE-_X 2CLE-_ 8 Eaton.com/bussmannseries Curve 63931702 July 2001 Reference # 639317 Curve 63931704 May 2002 Reference # 639317 Curve 63931802 July 2001 Reference # 639318 2.75kV E-Rated medium voltage fuses for feeder circuit, switchgear and transformer protection Technical Data 10350 Effective October 2019 CLE Type mountings - in (mm) Hole centers Catalog number A B 2CLE-GDM-C 2CLE-GDM-D 2CLE-PDM-C 2CLE-PDM-D 9.37 8.24 9.37 8.24 (238.0) (209.3) (238.0) (209.3) 6 6 6 6 2CLE-GDM-E 2CLE-PDM-E 8.24 (209.3) 8.24 (209.3) 6 (152.4) 6 (152.4) 2CLE-GNM-C 2CLE-PNM-C 2CLE-GNM-D 2CLE-PNM-D 9.37 9.37 8.24 8.24 6 6 6 6 2CLE-GNM-E 2CLE-PNM-E 8.24 (209.3) 8.24 (209.3) (238.0) (238.0) (209.3) (209.3) (152.4) (152.4) (152.4) (152.4) (152.4) (152.4) (152.4) (152.4) 6 (152.4) 6 (152.4) Overall length Hole Inset Hole centers C D E Disconnect single barrel† 22.13 (562.1) 0.75 (19.0) 1.75 (44.4) 18 (457.2) 0.62 (15.7) 1.75 (44.4) 22.13 (562.1) 0.75 (19.0) 1.75 (44.4) 18 (457.2) 0.62 (15.7) 1.75 (44.4) Disconnect double barrel† 18 (457.2) 0.62 (15.7) 1.75 (44.4) 18 (457.2) 0.62 (15.7) 1.75 (44.4) Non-disconnect single barrel 18.63 (473.2) 0.75 (19.0) 1.75 (44.4) 18.63 (473.2) 0.75 (19.0) 1.75 (44.4) 18 (457.2) 0.62 (15.7) 1.75 (44.4) 18 (457.2) 0.62 (15.7) 1.75 (44.4) Non-disconnect double barrel 18 (457.2) 18 (457.2) 0.62 (15.7) 0.62 (15.7) CLE Type disconnect mounting† 1.75 (44.4) 1.75 (44.4) Contact height F Overall height G BIL kV (114.3) (114.3) (114.3) (114.3) 9.75 (247.6) 11.72 (297.7) 9.75 (247.6) 11.72 (297.7) 60 60 60 60 4.5 (114.3) 4.5 (114.3) 15.28 (388.1) 15.28 (388.1) 60 60 4.5 4.5 4.5 4.5 7.25 (184.1) 7.25 (184.1) 8.79 (223.3) 8.79 (223.3) 60 60 60 60 12.48 (317.0) 12.48 (317.0) 60 60 4.5 4.5 4.5 4.5 (114.3) (114.3) (114.3) (114.3) 4.5 (114.3) 4.5 (114.3) CLE Type non-disconnect mounting G G F D F D E E C A A C E E D B D B † Disconnect mountings provide a means for fuse extraction only. Do not use a disconnect mounting for load switching or fuse removal while energized. Eaton.com/bussmannseries 9 Technical Data 10350 2.75kV E-Rated medium voltage fuses for feeder circuit, switchgear and transformer protection Effective October 2019 The only controlled copy of this Data Sheet is the electronic read-only version located on the Bussmann Network Drive. All other copies of this document are by definition uncontrolled. This bulletin is intended to clearly present comprehensive product data and provide technical information that will help the end user with design applications. Bussmann reserves the right, without notice, to change design or construction of any products and to discontinue or limit distribution of any products. Bussmann also reserves the right to change or update, without notice, any technical information contained in this bulletin. Once a product has been selected, it should be tested by the user in all possible applications. Eaton 1000 Eaton Boulevard Cleveland, OH 44122 Eaton.com Bussmann Division 114 Old State Road Ellisville, MO 63021 United States Eaton.com/bussmannseries © 2019 Eaton All Rights Reserved Printed in USA Publication No. 10350 October 2019 10 Eaton and Bussmann are valuable trademarks of Eaton in the U.S. and other countries. You are not permitted to use the Eaton trademarks without prior written consent of Eaton. ANSI is a registered trademark of the American National Standards Association IEEE is a registered trademark of the Institute of Electrical and Electronics Engineers NEMA is a registered trademark of the National Electrical Mfgrs. Association NFPA is a registered trademark of the National Fire Protection Association UL is a registered trademark of the Underwriters Laboratories, Inc.
2CLE-15E
物料型号:2.75kV E-Rated 中压保险丝,用于馈线电路、开关设备和变压器保护。
器件简介:E-Rated中压保险丝以其熔断时间-电流特性定义,允许与具有相同E等级的其他保险丝电气互换。这些保险丝具有限流特性,即使在低故障电流下也能提供确定的中断。
引脚分配:文档中未明确提及引脚分配,但提供了保险丝的安装尺寸和安装类型。
参数特性: - 额定电压:2.75kV - 额定电流:10到450安培 - 切断额定值:2CLE-_E型号为50kA RMS对称,JCX-_E型号为40kA RMS对称 - 操作频率:50/60Hz,适用于全球应用
功能详解: - 开启保险丝指示器通过提供保险丝操作的明确视觉指示,加快故障排查。 - 保险丝的物理尺寸设计便于在现有硬件中安装。 - 限流保险丝在保护设备中限制了电磁应力的大小。
应用信息: - 中压变压器初级保护 - 中压馈线电路保护 - 中压开关 - 中压金属封闭开关设备
封装信息:提供了多种安装类型和电压等级下的尺寸信息,包括带电部件和端接件的安装尺寸,以及瓷质或玻璃增强聚酯绝缘体的尺寸。
2CLE-15E 价格&库存
很抱歉,暂时无法提供与“2CLE-15E”相匹配的价格&库存,您可以联系我们找货
