IAR1-1-52-32.0-AC-00 数据手册
Introduction
49
Poles & Terminals
50
Configurations
53
Delay Curves & Specs
54
Operating Characteristics
55
Hardware
56
Decision Tables
57
IAR/IUR/IER/CUR/CER [1RU]
IAR/IUR/IER/CUR/CER Series
“1RU” Magnetic Circuit Protectors
“1RU” Hydraulic Magnetic Circuit Protectors
FEATURES
• UL1077, TÜV, UL489A approved
• Designed to fit in a “1RU” application
• 5,000 AIC interrupt capacity (65/80VDC, 120/240VAC)
• Series or mid-trip with auxiliary switch alarm options
• Various delays including motor start
• 1 to 2 poles, multiple termination options
INTRODUCTION
The Airpax™ IAR/IUR/IER/CUR/CER series is a snap-acting hydraulic-magnetic circuit breaker / protector that combines power
switching and accurate, reliable circuit protection in one aesthetically pleasing, “1U” or “1RU” sized package.
Designed for rack mount applications, the IAR/IUR/IER/CUR/CER series allows efficient use of rack space without sacrificing
performance via proven hydraulic-magnetic technology that provides consistent operation from -40°C to 85°C, with a circuit interrupt
capacity up to 5,000 AIC at 65/80 VDC and120/240 VAC. Available in series trip and mid-trip configurations, with auxiliary alarm switch
options to provide monitoring of critical circuits.
The CER series circuit breaker provides the necessary ratings for wireless and wired applications while meeting UL489A and TÜV
requirements for approval.
APPROVALS
49
Ratings
Voltage
A.I.C.
Agency Approvals
Poles
2 to 50 amps
65 VDC
5,000
UL489A & C-UL
1
2 to 50 amps
80 VDC
5,000
TÜV to EN60934
1
2 to 50 amps
250 VAC
2,000
UL1077 & TÜV to EN60934
1
2 to 50 amps
80 VDC
5,000
UL489A & TÜV to EN60934
2
2 to 30 amps
120 / 240 VAC
5,000
UL1077, C-UL, TÜV to EN60934
2
IAR/IUR/IER/CUR/CER Series - Introduction
http://airpax.sensata.com/
TOGGLE ACTUATION MAGNETIC CIRCUIT PROTECTORS
Panel Mounting Detail, Single Pole
0.755
[19.18]
POLES & TERMINALS
The Airpax™ IAR/IUR/IER/CUR/CER series is available with one or two poles with
various bullet, stud and screw terminals. Engineered for safe, sure operation, the
toggle handles may be specified in blue, white, red, orange, green, yellow or black.
Single Pole
Two Pole
(with or without two handles)
2x 6-32 THREAD
0.140 [3.56] DEEP
M3 ISO THREAD OPTIONAL
0.311
[7.90]
0.154
[3.91]
0.832
[21.13]
1.146
[29.11]
0.154
[3.91]
0.832
[21.13]
0.325
[8.26]
0.152
[3.86]
0.755
[19.18]
4X
0.156
Ø
[3.96]
1.146 0.842
[29.11] [21.39]
0.152
[3.86]
1.146
[29.11]
0.750
[19.05]
Panel Mounting Detail, Two Pole, Two Handles
0.325
[8.26]
0.250
[6.35]
1.530
[38.86]
0.400
[10.16]
Auxiliary switch wires not shown for clarity
0.156
Ø
[3.96]
1.515
MAX
[38.48]
0.750
MAX
[19.05]
0.400
[10.16]
0.842
[21.39]
Panel Mounting Detail, Two Pole, One Handle
2x 6-32 THREAD
0.140 [3.56] DEEP
0.311
[7.90]
2X
1.146
[29.11]
1.146
[29.11]
4X
0.156
Ø
[3.96]
0.842
[21.39]
0.152
[3.86]
0.750
[19.05]
IAR/IUR/IER/CUR/CER Series - Poles & Terminals
50
Single Pole
AUXILIARY SWITCH
OUTPUT LEADS
Two Pole (with or without 2nd handle)
AUXILIARY SWITCH
OUTPUT LEADS
0.297
[7.55]
1.90
[0.075]
SEE TERMINAL OPTIONS
32°
1.458
MAX
[37.03]
32°
0.250
RAD. x2
[6.35]
0.860
[21.83]
SEE TABLE
DIM. “A”
4.678
[118.81]
0.605
[15.37]
SEE TABLE
DIM. “B”
DIMENSIONS
51
Bullet Type
Dim. “A”
Dim. “B”
Dim. “C”
1/4” Bullet
4.778
[121.35]
5.019
[127.48]
Ø 0.251 ± 0.001
Ø [6.38 ± 0.03]
5/16” Bullet
4.851
[123.22]
5.092
[129.35]
Ø 0.312 ± 0.001
Ø [7.92 ± 0.03]
Stud Type
Dim. “E”
Dim. “F”
10-32
0.545
[13.84]
0.622
[15.81]
M5
0.510
[12.95]
0.588
[14.92]
1/4” Bullet Terminals
0.265
[6.73]
BULLET RECEIVING
HOLE DIMENSIONS
x2 DIM. “C” WITH
0.050 [1.27] x 45°
CHAMFER ON ENTRY EDGE
FINISH INSIDE
SURFACE OF HOLES
0.860 ± 0.13
[21.84 ± 0.005]
Two Pole Bullet Terminal
Mounting Detail
0.860 ± 0.13
[21.84 ± 0.005]
Single Pole Bullet Terminal
Mounting Detail
0.275
[6.98]
0.205
[5.21]
5/16” Bullet Terminals
0.265
[6.73]
BULLET RECEIVING
HOLE DIMENSIONS
x4 DIM. “C” WITH
0.050 [1.27] x 45°
FINISH INSIDE
SURFACE OF HOLES
0.275
[6.98]
0.205
[5.21]
0.750 ± 0.13
[19.05 ± 0.005]
10-32 or M5 Screw Terminals
0.265
[6.73]
0.275
[6.98]
0.205
[5.21]
10-32 or M5 Stud Terminals
0.297
[7.54]
DIM. “E”
0.860
[21.84]
DIM. “F”
52
10000
DELAY 51
1000
TIME IN SECONDS
TIME IN SECONDS
CONFIGURATIONS
MAY TRIP
100
10000
10
1000
1
100
MAY TRIP
Series Trip
The most popular configuration for magnetic protectors is the
series trip where the sensing coil and the contacts are in
series with the load being protected. In addition to providing
conventional overcurrent protection, it is simultaneously used
as an on-off switch.
.1
10
.01
1
.001
.1
125
300
100 150 200
125
300
.01
Single Pole, Series Trip
Two Pole, Series Trip
LOAD
DELAY 51
.001
LOAD
400
500
600
700
800
900
1000
800
900
1000
900
1000
900
1000
800
900
1000
800
900
1000
900
1000
PERCENT OF RATED CURRENT
400
500
600
700
10000
TIME IN SECONDS
TIME IN SECONDS
100
10000
Mid-Trip
This is furnished
as an integral part
of a series pole in single
LOAD
LOAD
or, multi-pole
IsolatedLINE
electrically from the
LINE assemblies. Mid-Trip
protectors circuit, the switch works in unison with the power
contacts and
location of the
LOADprovides indication at a remote
LOAD
10000
protector’s ON-OFF status.
LOAD
10
1000
.01
1
MAY TRIP
.1
10
LOAD
LINE
LINE
LOAD
MAY TRIP
Auxiliary Switch
LINE
LINE
This is .001
furnished
as200an300
integral
part
of
single
400
500
600 a series
700
800pole
900in 1000
C
125
Breaker shown
in ON position or
Breaker
shown in mid-trip
position
PERCENT
OF RATED
CURRENT
or, multi-pole
assemblies.
Isolated
electrically
from
the
Auxiliary
Switch
NO
manually turned OFF position
(electrically tripped)
protectors circuit, theNCswitch works in unison with the power
10000
LOAD
contacts
and provides indication
at a remote location of the
protector’s
ON-OFF
status.
LINE
1000
DELAY 52
TIME IN SECONDSTIME IN SECONDS
100
10000
C
Breaker
shown in OFF position
NO
Auxiliary Switch
NC
LOAD
MAY TRIP
10
1000
1
100
LINE
100 150 200
125
300
100 150 200
125
300
600
700
800
400
500
600
700
53
800
DELAY 53
.1
10
.001
.1 0
400
500
600
700
.01
.001
500
600
700
10000
1000
DELAY 59
DELAY 59
1
100
.1
10
NC
.01
1
LINE
.001
.1 0 detail
mounting
tolerance
0.005 [0.13]
100
150 200of ± 300
400
500
600
700
unless otherwise125
noted BreakerPERCENT
OF RATED CURRENT
800
900
1000
.01
.001
300
500
1
100
10
1000
DELAY 52
.01
1
53
100 150 200
125
400
DELAY
100
10000
mounting detail tolerance
ofC ± 0.005
[0.13]in OFF position
Breaker
shown
unless otherwise noted NO
.1
10
100 150 200
125
.01
1
Breaker
shown in ON position or
Breaker
shown in mid-trip position
C
C
.001
manually
(electrically
tripped)
100 OFF
150 position
200
300
400 Switch
500
700
800
900
1000
NO .1 0 turned
NO 600
Auxiliary
125
NC
NC CURRENT
PERCENT OF RATED
.01
1000
C
Breaker
NO
NC
LOAD
10000
.001
.1
100
10000
.001
DELAY 51
LINE
C
1
Breaker
NO100 shown in ON position or
manually turned OFF position Mid-Trip
NC
.01
1
1000
.01
LOAD
LINE
.1
10
10000
MAY TRIP
Mid-Trip
NO LINE
NC
100
DELAY 51
C
NO
LINE
NC
1
100
1000
C
DELAY 52
MAY TRIP
10
1000
MAY TRIP
LINE
MAY TRIP
LINE
DELAY 52
MAY TRIP
MAY
LOAD
MAY TRIP
1000
LOAD
MAY TRIP
MAY
.001
.1 0
100 150 200
125
300
100 150 200
125
300
400
500
600
700
800
.01
125
IAR/IUR/IER/CUR/CER
Series
PERCENT OF RATED
CURRENT - Configurations
300
400
mounting detail tolerance of ± 0.005 [0.13]
500
600
700
800
900
1000
.001
600
700
800
900
1000
500
10000
TIME IN SECONDS
10
1
.1
.01
MAY TRIP
1000
100 150 200
125
TIME IN SECONDS
TIME IN SECONDS
TIME IN SECONDS
100
10000
400
500
600
.1
10
1000
800
900
1000
DELAY 61
Trip Indication
1
10000
The operating handle moves forcibly and positively to the OFF
.1
position on
1000overload.
DELAY 69
DELAY 63
.01
1001
.01
300
400
500
600
700
800
900
1000
.01
1
1000
MAY TRIP
TIME IN SECONDSTIME IN SECONDSTIME IN SECONDS
100
10000
.001
100 150 200
125
MAY TRIP
1000
.01
100 150 200
125
300
400
500
600
700
800
DELAY
300
400
500
600
700
900
1000
62
800
900
1000
DELAY 63
.001
.1 0
100 150 200
125
300
100 150 200
125
300
MAY TRIP
.01
1
300
400
500
600
700
800
900
1000
800
900
1000
800
900
1000
400
500
600
700
.01
10000
.001
400
500
600
700
DELAY
69
TIME IN SECONDS
100
MAY TRIP
10
1
.01
125
DELAY 69
3,750 VAC
600 VAC
3,750 between main circuit
breaker terminal and auxiliary
switch terminal
.1
Shock
.01
Shall not trip
when tested per MIL-STD-202, method 213, test
condition .001
1 with 100% rated current applied to delayed units, except
100 150 200
300
400
500
600
700
800
900
1000
90% current 0in plane
4, (i.e.
handle
down). Instantaneous
units shall
125
have 80% rated current applied in all planes.
Vibration
Shall not trip when vibrated per MIL-STD-202, method 204, test
condition A with 100% rated current applied to delayed units and 80%
rated current to instantaneous units.
Endurance
In many applications contact wear due to the electrical load
determines unit life. At maximum electrical ratings, the IAR/IUR/IER/
CUR/CER can perform 10,000 operations at rated current and voltage
at a maximum rate of 6 operations per minute.
.1
.001
Dielectric.01Strength
10000
Shall withstand
AC voltage 60 Hz, for 60 seconds between all
.001
300
400
500
600
700
800
900
1000
electrically isolated
125 terminals as described below.
TIME IN SECONDS
DELAY 69
100 150 200
125
1
Insulation Resistance
Not less than
100 megaohms at 500Vdc.
.1
Series, switch
only
100
Auxiliary switches
10
Series w/ auxiliary
switch :
1
.01
1
100
.001
.1
10 0
125
1000
1
100
10000
.1
10
1000
MAY TRIP
100 150 200
125
100
Ambient Operation
Operates .001
normally
in200
temperatures
+85°C.
10 0
100 150
300
400
500between
600
700–40°
800 C and
900
1000
MAY TRIP
.001
.1 0
10
10000
.001
.1
10000
.001
Trip Free 0 100125150 200 300 400 500 600 700 800 900 1000
1000
DELAY 62
Will trip open on overload, even when forcibly held on. This prevents
operator from
damaging the circuit by holding handle in the ON
100
position.
10
DELAY 62
MAY TRIP
1
100
10000
700
MAY TRIP
10
1000
300
MAY TRIP
TIME IN SECONDS
10000
.001
MAY TRIP
100
DELAY 62
DC, 50/60Hz Delay Curves (typ)
A choice of10 delays is offered for DC and 50/60Hz applications. Delays
59 and 69 provide
fast-acting, instantaneous trip and are often used
1
to protect sensitive electronic equipment (not recommended where
known inrush
exists). Delays 51 and 61 have a short delay for general
.1
purpose applications. Delays 52 and 62 are long enough to start
.01
certain types
of motors and most transformer and capacitor loads.
TIME IN SECONDS
TIME IN SECONDS
100
DELAY CURVES
& SPECIFICATIONS
1000
DELAY 61
MAY TRIP
1000
10000
300
400
500
600
700
800
900
1000
IAR/IUR/IER/CUR/CER Series - Delay Curves & Specifications
54
OPERATING CHARACTERISTICS
MAXIMUM DCR AND IMPEDANCE (APPROXIMATE VALUES)
Inrush Pulse Tolerance
Many circuit protector applications involve a
transformer turn-on, an incandescent lamp load,
or a capacitor charge from a DC source. Each of
these applications has one common factor: a
steep transient of very high current amplitude and
short duration. This takes the form of a spike or a
single pulse and is the cause of most nuisance
tripping associated with magnetic circuit
breakers.
The IAR/IUR/IER/CUR/CER series will withstand,
without tripping, a single pulse of 8 milliseconds
duration (half sine wave configuration) and peak
amplitude of 10 times its rating.
Current Ratings
(Amps)
DC Resistance
(Ohms)
51, 52, 53, 59
50/60Hz Impedance
(Ohms)
61, 62, 63, 69
2.0
0.027
0.038
3.0
0.074
0.098
6.0
0.037
0.048
7.5
0.025
0.029
15.0
0.010
0.011
32.0
0.003
0.003
40.0
0.003
0.003
50.0
0.0024
0.0025
Tolerance: 2 to 2.5 amps ±20%; 2.6 to 20 amps ± 25%; 21 to 50 amps ±50%
*Consult factory for special values and for coil impedance of delays
not shown
AUXILIARY SWITCH RATING
APPROXIMATE WEIGHT PER POLE
10.0 amps
250 VAC, 60 Hz
3.0 amps
50 VDC
1.0 amps
80 VDC
PULSE TOLERANCE
1 pole
134 grams
Delay
Pulse Tolerance
2 pole
263 grams
61, 62, 63
10 Times Rated Current
PERCENTAGE OF RATED CURRENT VS TRIP TIME IN SECONDS AT +25°C (APPROXIMATE VALUES)
55
Delay
100%
125%
150%
200%
400%
600%
800%
1000%
51
No Trip
0.5 to 6.5
0.3 to 3
0.1 to 1.2
0.031 to 0.5
0.011 to 0.25
0.004 to 0.1
0.004 to 0.08
52
No Trip
2 to 60
1.8 to 30
1 to 10
0.15 to 2
0.015 to 1
0.008 to 0.5
0.006 to 0.1
53
No Trip
80 to 700
40 to 400
15 to 150
2 to 20
0.015 to 9
0.015 to 0.55
0.012 to 0.2
59
No Trip
0.120 max
0.1 max
0.05 max
0.022 max
0.017 max
0.017 max
0.017 max
61
No Trip
0.7 to 12
0.35 to 7
0.13 to 3
0.03 to 1
0.015 to 0.3
0.01 to 0.15
0.008 to 0.1
62
No Trip
10 to 120
6 to 60
2 to 20
0.2 to 3
0.015 to 2
0.015 to 0.8
0.01 to 0.25
63
No Trip
50 to 700
30 to 400
10 to 150
1.5 to 20
0.015 to 10
0.013 to 0.85
0.013 to 0.5
69
No Trip
0.12 max
0.1 max
0.05 max
0.022 max
0.017 max
0.017 max
0.017 max
IAR/IUR/IER/CUR/CER Series - Operating Characteristics
Single Pole:
RED = 762-600-7651
BLACK = 762-600-7650
Handle lock installed
in factory will be
mounted from the
case side with logo
on single pole
Barrier (-B)
HARDWARE
Handle Lock
1.460
[37.08]
Retainer
(required f
single pole
386-000-09
Handle Lock
Single Pole:
A handle lock option
is available to prevent accidental
RED = 762-600-7651
actuation of the handle.
handle lock may be used in the
BLACK = The
762-600-7650
ON or OFF position. Use of the handle lock on breakers with
Handle
lock installed
alarm style auxiliary
switches
may defeat the alarm feature
in factory will be
on electrical trip. This
option
is available separately or
mounted
from the
side with
pre-assembled (oncase
single
polelogo
constructions only).
1.715
[43.56]
Handle Lock
Retainer
(required for
single pole only)
386-000-0930
on single pole
Bullets
Barrier (-B)
Socket 1/4-20 UNC-2A
Order # 641-480-5032
(silver plated copper)
Barrier (-B)
0.725
[18.42]
1.460
[37.08]
0.510
[12.95]
0.251 ± 0.001
Ø
[6.38 ± 0.03]
0.375
[9.53]
1.715
[43.56]
Retainer
(required for
single pole only)
386-000-0930
Handle Lock
Single Pole:
RED = 762-600-7651
1.460
[37.08]
in factory will be
mounted from the
case side with logo
on single pole
Ø
ON on
siti
Po
0.510
[12.95]
0.251 ± 0.001
1.715
[6.38 ± 0.03]
[43.56]
0.375
0.438
[11.13]
Order # 641-480-5030
The handle position
indicates the status of the circuit
Socket 1/4-20 UNC-2A (silver plated copper)
breaker. In addition
to #full
ON and full OFF positions, there
Order
641-480-5032
(silver
plated copper)
a middle “MID-TRIP”
position
indicating that the breaker
0.510
[12.95
Order # 641-480-5022
0.510
[12.95]
ON
0.438
[11.13]
Ø
0.156
[3.96]
N n
O0.725
o
siti
0.510
[12.95
Po
[18.42]
0.725
0.510
0.312 ± 0.001
Mid-Trip
[18.42] Ø [7.92 ± 0.03]Position[12.95]
0.375
0.251 ± 0.001
[6.38 ± 0.03]
Ø [9.52]OF
Po F
Nut 1/4-20 sUNC-2B
itio
n
Order # 388-899-5010
0.438
[11.13]
0.156
[3.96]
is
[9.53]
n
0.312
itio± 0.001
Ø Pos
[7.92 ± 0.03]
Mid-Trip
Position
Nut 1/4-20 UNC-2B
O
Po FF
siti
on
Bullets
0.725
O
Po FF
siti
on
0.725
[18.42]
0.438
[11.13]
Mid-Trip
has electrically tripped from an overload. It is available in
[18.42]
0.725 per pole only) series
0.510
single pole and multi-pole (handle
[12.95] in
constructions. Switch only[18.42]
configuration is not available
0.375
mid-trip build. An auxiliary switch
be furnished as an
0.251can
± 0.001
Ø
Ø [9.52]
0.251
± 0.001breaker.
integral part ofØthe
mid-trip
The switch provides an
[6.38 ± 0.03]
[6.38 ±location
0.03]
when the circuit breaker has
0.375
electrically tripped and handle is in the mid-trip position.
[9.52]
0.510
[12.95
[9.53]
Mid-Trip0.375
Ø
Position
0.251 ± 0.001
[6.38 ± 0.03]
0.725
[18.42]
Ø
0.725
[18.42]
Bullets
0.725
0.510
IAR/IUR/IER/CUR/CER
Series - Hardware
[18.42]
[12.95]
56
HOW TO ORDER
The ordering code for these circuit
breakers / protectors may be determined
by following the steps in the decision
tables shown here.
The example shown is the code for a
UL1077 & TÜV approved circuit protector
with series trip, one handle per unit,
single pole circuit protector with 10-32
terminal screws standard and a
mechanical auxiliary switch. This unit is
designed with a slow DC time delay and
a rating of 20 amperes with optional
metric threads and optional 80VDC
capability. Handle color is black with
white markings, and is has been met all
the selection criteria to obtain the TÜV
approval.
1
First Decision
First Choice: Type
IAR
Magnetic circuit protector, one handle per unit
IARH
Magnetic circuit protector, one handle per pole
K
10-32 stud terminal
IER
UL1077 & TÜV, series trip, one handle per unit
B
0.250” bullet terminal
IERH
UL1077 & TÜV, series trip, one handle per pole
IUR
UL1077, series trip, one handle per unit
IURH
UL1077, series trip, one handle per pole
IMR
UL1077 & TÜV, mid trip, one handle per unit
IMRH
UL1077 & TÜV, mid trip, one handle per pole
CER
UL489A & TÜV, series trip, one handle per unit
CERH
UL489A & TÜV, series trip, one handle per pole
CUR
UL489A, series trip, one handle per unit
CURH
UL489A, series trip, one handle per pole
CMR
UL489A & TÜV, mid trip, one handle per unit
CMRH
UL489A & TÜV, mid trip, one handle per pole
To determine the ordering code for your
particular unit, simply follow the steps
shown, then fill in the letters and/or
numbers in the boxes. Space is available
on the circuit breaker label for your part
number (up to 12 digits). You may then
use your own part number to place an
order or as a reference for further
questions you may have. This option
does require a factory assigned part
number for traceability to your drawing
or internal part number.
57
Second Choice: Terminal
IAR/IUR/IER/CUR/CER Series - Decision Tables
10-32 screw terminal, standard (no entry)
The shaded areas denote TÜV approval
options. This approval requires the
addition of a “T” at the end of the part
number (8th decision).
The “T” will automatically be added to
any part number formed entirely from
these shaded decisions. If non-shaded
areas are selected, the unit will not be
TÜV approved, but other approvals (if
applicable) will still apply.
IER 1 - 1REC4C - 52 - 20.0 - AD - 01 - T
1 2
2
Second Decision
3
4
5
6
7
8
TÜV Approval
Per first decision’s description: The shaded areas denote
TÜV approval options. This approval requires the addition
of a “T” at the end of the part number (8th decision).
271
Number of Poles
1
11
231
Seventh Decision
Handle Color & Markings
Single pole
-00
Black
-01
Black w/ white markings (standard)
Two pole
-10
Yellow
-11
Yellow w/ black markings
-20
Red
-21
Red w/ white markings
-30
Blue
-31
Blue w/ white markings
-40
Green
-41
Green w / white markings
-60
Orange
-61
Orange w/ black markings
-90
White
-91
White w/ black markings
Third Decision
Internal Configuration
-1
Series trip
-1REC4C
Mechanical trip auxiliary switch*
-1RS4C
Electrical trip auxiliary switch*
-1RLS4C
(mid-trip only)
-1REG4C
Series trip with auxiliary switch*
0.110 quick-connects (gold contacts)
-1REC40
Mechanical trip auxiliary switch**
-1RS40
-1RLS40
(mid-trip only)
-1REG40
* Alarms when circuit breaker closes
** Alarms when circuit breaker opens
Only one auxiliary switch is normally supplied on two pole units.
Switch is located in the right hand pole (viewed from terminal end)
unless otherwise specified.
241
Eighth Decision
Fourth Decision
Frequency & Delay
-51
DC short delay
-52
DC long delay
-53
DC motor start / extra long delay
-59
DC 125% instant trip
-61
50 - 60 Hz short delay
-62
50 - 60 Hz Long Delay
-63
50 - 60 Hz motor start / extra long delay (30A max)
-69
50 - 60 Hz 125% instant trip
8
261
Sixth Decision
Optional
-A
Metric thread mounting (M3) & terminals (M5)
-B
Barrier (AC only)
-C
65 VDC
-D
80VDC
-E
0.312” diameter bullet
(standard is 0.250” when prefix with “B” is chosen
in first decision)
-F
250VAC
-L
Handle Lock
Notes:
1. One or more descriptions may be used as required
(for example, to get a barrier, 250VAC and handle lock, put -BFL)
2. When the sixth decision is not required, the seventh decision
may be substituted and U.S. thread will be supplied
5
Fifth Decision
Rated Current
Use three numbers to print required current value between
2.00 amps minimum and 50.0 amps maximum.
58