1000 Eaton Boulevard
Cleveland, OH 44122
United States
SmartPro 230V 3kVA 2.25kW Line-Interactive
UPS, Tower, Extended Run, Network Card
Options, USB, DB9 Serial
Highlights
3kVA/3000VA/2250W line
interactive tower UPS system
230V nominal output during
brownouts to 151V and
overvoltages to 282V
Extended runtime options, Front
panel status LEDs
USB, RS232, EPO and slot for
Network Management Card
options; 3 switched load banks
C20 inlet; 8 C13 & 1 C19
outlets; 3 C13 to C14 cables
included
Add optional WEBCARDLX with
latest version of PADM20 for IPbased Auto Probe feature
MODEL NUMBER: SMARTINT3000VS
Package Includes
Description
Tripp Lite's SMARTINT3000VS intelligent, line-interactive tower uninterruptible power supply (UPS)
prevents data loss, downtime and equipment damage due to power outages, voltage fluctuations and
transient surges. Large internal batteries offer 14 minutes half load runtime and 4 minutes at full load.
Runtime is expandable with optional external battery packs. Maintains regulated 230V nominal output
without using battery power during brownouts and overvoltages from 151 to 282V. 3000VA power
handling capability offers compatibility with a variety of networking, telecom and other sensitive electronic
applications. Includes a total of 9 outlets with 3 load banks that are individually switchable via software
interface to reboot select equipment on demand or shed less significant loads to extend battery runtime
for more critical equipment. Supports simultaneous remote monitoring of UPS and site power conditions
via built-in USB and DB9 monitoring ports. PowerAlert UPS monitoring software is available via free
download. Built-in accessory slot supports Network Management Card option. Emergency Power Off
(EPO) interface offers option for instantaneous power-off of UPS and connected equipment in the case of
fire or emergency. Multi-function audible alarms and set of 5 front panel LEDs offer at-a-glance notification
of UPS and line power status. Network-grade AC surge suppression protects equipment from damage
and performance problems resulting from transient surges and line noise. Attractive gray color scheme.
Features
SMARTINT3000VS line-interactive UPS offers protection from blackouts, brownouts, overvoltages and
surges
3000VA/2250W capacity
Internal batteries support a half load of 1500VA for 14 minutes and a full load of 3000VA for 4 minutes
Runtime is further expandable with the addition of BP48V60RT-3U and BP48V27-2US external battery
packs
Intelligent battery management system extends battery life
Maintains regulated 230V nominal output during brownouts and overvoltages from 151 to 282V
Includes 9 UPS supported outlets with 3 individually controllable load banks (2 outlets per bank) that
can be powered off and back on again via software interface
IEC320-C20 input connection accepts a variety of detachable cord sets to match country or site-specific
wall receptacles
Optional WEBCARDLX (sold separately) with the latest version of PowerAlert Device Manager firmware
1/6
SMARTINT3000VS UPS
System
USB and DB9 cables
Cable for Emergency Power Off
interface
Instruction manual with warranty
information
C13 to C14 power cables (3)
Cleveland, OH 44122
United States
(PADM20) provides enhanced remote management capabilities
PADM20 and PowerAlert Element Manager (PAEM) form a powerful tool for expanding maintenance
functions in large installations, including firmware update checks and backup and restoration of device
configurations
IP-based Auto Probe detects lost connectivity and restores service autonomously
Offers simultaneous monitoring by up to 4 directly-connected devices through included USB and DB9
interface ports
Emergency Power Off (EPO) interface with cable
Supports timed inverter shutoff after unattended shutdown, activate self-test and UPS output power
control for delayed or immediate reboot of connected devices
Optional PDUBHV20 bypass PDU enables hot-swappable UPS replacement with no disruption to
connected equipment
Supports Tripp Lite's WatchDog software application (requires optional WATCHDOGSW)
Slot for Network Management Card options; Compatible with Tripp Lite UPS management card options
TLNETCARD, WEBCARDLX and SNMPWEBCARD
Specifications
OVERVIEW
UPC Code
037332120311
UPS Type
Line-Interactive
INPUT
Input Phase
Single-Phase
Rated input current (Maximum Load)
15.4A
Nominal Input Voltage(s) Supported
230V AC
UPS Input Connection Type
C20 inlet
UPS Input Connection Description
User supplies input cabling with C19 output connection
OUTPUT
Output Capacity (VA)
3000
Output Capacity (kVA)
3
Output Capacity (Watts)
2250
Output Capacity (kW)
2.25
Output Capacity Details
Output is reduced to 1500W maximum with 2 or more external battery packs
Power Factor
0.75
Nominal Voltage Details
230v nominal inverter output voltage
2/6
Cleveland, OH 44122
United States
Frequency Compatibility
50 / 60 Hz
Frequency Compatibility Details
Automatic frequency selection
Output Voltage Regulation (Line
Mode)
-19% +8%
Output Voltage Regulation (Battery
Mode)
+/- 5%
Included Output Power Cables
Includes 3 C13 to C14 output power cables
Load Management Receptacles
Three switchable two-outlet C13 load banks
Output Circuit Breakers
10A (x2) - each breaker protects 4 C13 outlets each, C19 is unbreakered
Output AC Waveform (AC Mode)
Sine wave
Output AC Waveform (Battery
Mode)
PWM sine wave
Nominal Output Voltage(s)
Supported
220V; 230V; 240V
Output Receptacles
(8) C13; (1) C19
Individually Controllable Load Banks
Yes
BATTERY
Battery Type
Valve Regulated Lead Acid (VRLA)
Runtime Full Load (min.)
4 min. (2250W)
Runtime Half Load (min.)
14 min. (1125W)
Expandable Runtime
Yes
External Battery Pack Compatibility
BP48V27-2US (multi-pack compatible); BP48V60RT-3U (multi-pack compatible)
DC System Voltage (VDC)
48
Battery Recharge Rate (Included
Batteries)
Less than 4 hours from 10% to 90% (typical, full load discharge)
Battery Access
Battery access door
Internal UPS Replacement Battery
Cartridge
RBC54
Battery Replacement Description
Hot-swappable, user replaceable batteries
VOLTAGE REGULATION
Voltage Regulation Description
Automatic voltage regulation (AVR) maintains line power operation with an input voltage range of 151V to 282V
Overvoltage Correction
Input voltages between 245 and 282 are reduced by 12%
Undervoltage Correction
Input voltages between 177 and 199 are boosted by 14%
Severe Undervoltage Correction
Input voltages between 151 and 176 are boosted by 30%
USER INTERFACE, ALERTS & CONTROLS
3/6
Cleveland, OH 44122
United States
Switches
2 Switches control off/on power status and alarm-cancel/self-test operation
Alarm Cancel Operation
Power-fail alarm can be silenced using alarm-cancel switch; once silenced, alarm will re-sound to indicate lowbattery status
Audible Alarm
Audible alarm indicates power-failure, overload and low-battery conditions
LED Indicators
5 LEDs indicate line power, battery power, overload, voltage regulation and battery low/replace status
SURGE / NOISE SUPPRESSION
UPS AC Suppression Joule Rating
480
UPS AC Suppression Response
Time
Instantaneous
EMI / RFI AC Noise Suppression
Yes
PHYSICAL
Primary Form Factor
Tower
Cooling Method
Fan
Installation Form Factors Supported
with Included Accessories
Tower
Primary UPS Depth (mm)
305
Primary UPS Height (mm)
361
Primary UPS Width (mm)
234
Shipping Dimensions (hwd / in.)
19.90 x 15.10 x 16.10
Shipping Dimensions (hwd / cm)
50.55 x 38.35 x 40.89
Shipping Weight (lbs.)
67.80
Shipping Weight (kg)
30.75
UPS Housing Material
Polycarbonate
UPS Power Module Dimensions
(hwd, cm)
36.07 x 23.37 x 30.48
(hwd, in.)
14.2 x 9.2 x 12
UPS Power Module Weight (kg)
27.67
UPS Power Module Weight (lbs.)
61
Unit Weight (lbs.)
53.4000
Unit Weight (kg)
24.22
ENVIRONMENTAL
Operating Temperature Range
32° to 104°F (0° to 40°C)
Storage Temperature Range
5° to 122°F (-15° to 50°C)
Relative Humidity
0 to 95%, non-condensing
4/6
Cleveland, OH 44122
United States
AC Mode Efficiency Rating (100%
Load)
94%
Audible Noise
Audible Noise < 47dBA At Front Side 1 Meter
COMMUNICATIONS
Network Management Cards
SNMPWEBCARD; TLNETCARD ; WEBCARDLX
Network Monitoring Port Description
Supports detailed monitoring of UPS and site power conditions
PowerAlert Software
For local monitoring via the UPS’s built-in communication ports, download PowerAlert software at
https://tripplite.eaton.com/products/power-alert
Communications Cable
2 USB and 2 DB9 cables included
WatchDog Compatibility
Supports Watchdog application, OS and hard-reboot restart options for remote applications
Description
Network management card optional
Communications Interface
DB9 Serial; EPO (emergency power off); Slot for SNMP/Web interface; USB
LINE / BATTERY TRANSFER
Transfer Time
2-4 milliseconds
Low Voltage Transfer to Battery
Power (Setpoint)
151
High Voltage Transfer to Battery
Power (Setpoint)
282
FEATURES & SPECIFICATIONS
Cold Start (Startup in Battery Mode
During a Power Failure)
Cold-start operation supported
High Availability UPS Features
Auto Probe Monitoring and Reboot (requires WEBCARDLX); Automatic Voltage Regulation (AVR); Hot swappable
batteries; Remote management; Surge/noise protection
STANDARDS & COMPLIANCE
Product Compliance
RoHS; CE (Europe)
WARRANTY & SUPPORT
Product Warranty Period
(International)
2-year limited warranty
Product Warranty Period (Mexico)
Product Warranty Period (Puerto
Rico)
5/6
Cleveland, OH 44122
United States
© 2023 Eaton. All Rights Reserved.
Eaton is a registered trademark. All other trademarks
are the property of their respective owners.
6/6
很抱歉,暂时无法提供与“SMARTINT3000VS”相匹配的价格&库存,您可以联系我们找货