HS1T-VD44ZSM-G.
HS1T-VD44ZSM-G.
    IDEC
    IDEC - HS1T-VD44ZSM-G. - 5000N INTERLOCK SW 4CONTACTS SPRING LOCK 28AH8550
HS1T-VD44ZSM-G. 数据手册
Interlock Switches with Solenoid HS1T  2-Contact/4-Contact Supporting safety for advancing technology Slim interlock switches with 5000N locking force HS1T Interlock switches with 5000N locking force Locking force of more than 5000N (40mm-wide slim model) Smallest size in the industy (*1) Greatly downsized from IDEC’s HS1L interlock switches. *1) Based on IDEC research (as of March, 2019) Downsized 129 143 Volume 70% less Approx. 88 40 63 40 All dimensions in mm. Conventional (HS1L): Volume 715 cm3 Locking force 3000N HS1T: Volume 229 cm3 Locking force 5000N The head can be rotated to allow the actuator entry direction to be changed easily • Head rotating structure. Can be roated without removing the head. • Prevents invalid operation. (On usual interlock switches, the NC contact closes when the head is removed) HS1T 1 2 Change orientation of the head in 3 easy steps 3 Align ➀ Turn the flathead screwdriver in ➁ Rotate the head to the desired the direction shown above until the head stopper screw stops and is lifted up. ➂ Align the  marks indicated on position. the head and body and tighten the head stopper screw. Many screws ... Conventional IDEC interlock switches (HS5L) 1 1 2 2 3 4 4 3 ➀ Loosen the four screws using a cross point screwdriver. 2 ➁ Remove the head. ➂ Attach to the desired position. ➃ Tighten the four screws. Lock status can be identified from the front – Rear unlock mechanical indicator (First in the industry) (*1) Mechanical indicator function allows the lock status to be easily identified from the front while the rear unlock mechanical indicator is pressed. Note: Interlock switches with rear unlock mechanical indicator function only. *1) Based on IDEC research (as of March, 2019). Before unlock Conventional (HS5L) After unlock Rear unlocking button is pressed Button is pressed If HS1T is used Mechanical indicator In conventional models, because the lock status cannot be identified from the front, the system cannot be restarted when the safety circuit is on. Therefore, it is necessary to find out which safety circuit is on. The lock status can be easily identified from the front even when the lock is released. Energy efficient 200mA solenoid consumption Because the solenoid current for locking operation is 200mA, the solenoid can be activated without using a relay. Controller solenoid can be activated directly Rear unlocking button Door lock can be unlocked inside the barrier by a worker left inside a hazardous area. HS1T Rear unlocking button Spring clamp terminals Side-conduit model Spring clamp terminals offer excellent vibration resistance, preventing wires from loosening. No need for additional tightening. Cables can be connected to the right, left, or bottom (for straight cable orientation) of the terminal cover. Long marking tubes can be used on the wiring cables. Driver port Wiring port Left cable orientation Right cable orientation Driver port Wiring port Straight cable orientation 3 HS1T Interlock Switches with Solenoid Ideal for use on large doors and large equipment requiring strong locking force • Smallest in the industry with 5000N locking force. (*1) • Rear unlock mechanical indicator allows the lock status to be identified from the front and back. (First in the industry) (*1) • Head rotating function enables the actuator entry direction to be changed easily. • Side-conduit model available. • Two- and four-contact models available. • Spring clamp terminal prevents loosening of wires. • Energy efficient 200mA solenoid consumption. • Solenoid lock and spring lock models available. • Mechanical durability: 2,000,000 operations *1) Based on IDEC research (as of March, 2019) (pending) Specifications Operating Temperature –25 to + 55°C (no freezing) Relative Humidity 20 to 95% (no condensation) Applicable Standards Storage Temperature –40 to +80°C (no freezing) Pollution Degree Impulse Withstand Voltage Insulation Resistance (500V DC megger) Electric Shock Protection Degree of Protection 3 (contacts: 2) 2.5kV (between LED, solenoid and grounding: 0.5kV) Between live and dead metal parts: 100MΩ min. Between terminals of different poles: 100MΩ min. Class II (IEC61140) IP67 (IEC60529) Type 4X Indoor Use Only Operating extremes: 100m/s2 (10G), Shock Resistance Damage limits: 1000m/s2 (100G) Operating extremes: 10 to 55Hz, amplitude 0.35 min. Vibration Resistance Damage limits: 30Hz, amplitude 1.5mm min. Actuator Operating Speed 0.05 to 1.0m/s Direct Opening Travel 12mm min. Direct Opening Force 120N Actuator Retention Force Fzh = 5,000N min. (GS-ET-19) (*3) (*1) Operating Frequency 900 operations per hour Rear Unlock Button 3,000 times min. (HS1T-L) Mechanical Durability Mechanical Durability 2,000,000 times min. Electrical Durability 100,000 times min. (AC-15  0.75A/250V) 2,000,000 times min. (24V AC/DC, 100mA) (Operating Frequency: 900 operations per hour) Conditional Short-circuit Current 50A (250V) (*2) Cable Weight (approx.) 0.3mm2 min. and 1.5mm2 max. or AWG22 min. to AWG16 max. stranded wire or solid wire 450g *1) See page 17 regarding actuator retention force. *2) Use 250V/10A fast-blow fuse for short-circuit protection. *3) The actuator retention force of HS1T is 5000N at static load. Make sure that a force exceeding the above specification is not applied. In the event where the actuator retention force might exceed the expected load, add a system that can detect the opening of the door and stops the machine, such as adding another safety switch without lock (such as HS5D) or a sensor. 4 Additional Marking to indicate Lock Monitoring This new international marking for lock monitoring is described in clause 9.2.1 of ISO14119 and is used to satisfy the requirements shown below. 5.7.1 General requirements 5.7.2.2 Locking monitoring The lock monitor circuit (contacts) with this marking can monitor both the status of protective doors and locking function. (locking monitor contact [circuits] opens when the protective door is closed and locked) Both HS1T spring lock and solenoid lock models have marking for lock monitoring. Note that solenoid lock models can be used in applications where lock for safety purpose is found unnecessary after a risk assessment, e.g. locking is needed for purposes such as in production process. Ratings Contact Ratings Rated Insulation Voltage (Ui) 250V (between LED, solenoid and grounding: 30V) Rated Current (Ith) 2.5A Rated Voltage (Ue) 30V 125V 250V Resistive Load (AC-12) — 2.5A 1.5A AC Inductive Load (AC-15) — 1.5A 0.75A Resistive Load (DC-12) 2.0A 0.4A 0.2A DC Inductive Load (DC-13) 1.0A 0.22A 0.1A Rated Current (Ie)* Type and Coded level EN ISO / ISO14119, IEC60947-5-1 (pending), EN60947-5-1 (TÜV approval), GS-ET-19 (TÜV approval), UL508 (UL Listing approval), CSA C22.2 No.14 (c-UL Listing approval), GB/T 14048. 5 (CCC pending) IEC60204-1/EN60204-1 Type 2 low level coded interlocking device (ISO14119) • Minimum applicable load (reference): 3V AC/DC, 5mA (Applicable range may vary with operating conditions and load types.) * UL, c-UL rating: Pilot Duty AC 0.75A/250V, Pilot Duty DC 1.0A/30V TÜV rating: AC-15  0.75A/250V, DC-13  1.0A/30V CCC rating: AC-15  0.75A/250V, DC-13  1.0A/30V (pending) Solenoid Locking Mechanism Rated Voltage Rated Current Coil Resistance Pickup Voltage Dropout Voltage Maximum Continuous Applicable Voltage Maximum Continuous Applicable Time Insulation Class Spring Lock Solenoid Lock 100% duty cycle at 24V DC 200mA (initial value) 120Ω (at 20°C) Rated voltage × 85% max. (at 20°C) Rated voltage × 10% min. (at 20°C) Rated voltage × 110% Continuous Class F Indicator Rated Voltage Rated Current Light Source Illumination Color 24V DC 100% duty cycle 10mA LED G (Green) HS1T Interlock Switches with Solenoid 4-Contact (Spring Lock/Solenoid Lock) Door Monitor Monitor Door Monitor Door Door Monitor (Actuator inserted) Door (Actuator inserted) (Actuator inserted) Door Monitor Monitor (Actuator (Actuator inserted) inserted) (Actuator inserted) Door Monitor: Monitor: 1NC,1NO Door 1NC,1NO Door Monitor: 1NC,1NO Door Monitor: 1NC,1NO Door Monitor Monitor: 1NC,1NO11 Circuit: 11 Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: VB VC VD 11 11 11 23 11 23 23 23 23 Door Monitor: 1NC,1NO Door Monitor: 1NC,1NO Door Monitor: 1NC,1NO Door Monitor: 1NC,1NO Door Monitor Monitor: 1NC,1NO11 Circuit: 11 Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Door Monitor: 2NC 11 11 11 23 11 23 23 23 23 23 Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: 11 11 11 11 11 21 11 21 21 21 21 12 12 12 12 12 22 12 22 22 22 22 Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: 11 11 11 11 21 21 21 21 Door Monitor: 2NC Door Monitor: 2NC Door Monitor: 2NC Door Monitor Monitor: 2NC Circuit: Door Monitor: 2NC Door Monitor: 2NC Door Monitor: 2NC Door Monitor: 2NC Door Monitor Monitor: 2NC Circuit: 12 12 12 12 22 22 22 22 32 32 32 32 32 Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: 11 11 21 11 21 21 21 21 33 21 33 33 33 12 12 12 22 12 22 22 22 22 34 22 34 34 34 Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: 11 11 11 11 11 12 12 12 12 12 Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: 11 11 11 11 11 11 12 12 12 12 12 12 Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: 13 13 13 13 13 13 14 14 14 14 14 14 Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: 13 13 13 13 13 13 14 14 14 14 14 14 Door Monitor: Monitor: 1NC 1NC Door Door Monitor: 1NC Door Monitor: 1NC Door Monitor Monitor: 1NC Circuit: Monitor Circuit: VH Door Monitor: Monitor: 1NC 1NC Door Door Monitor: 1NC Door Monitor: 1NC Door Monitor Monitor: 1NC Circuit: Monitor Circuit: VJ Door Monitor: 1NO Door Monitor: 1NO Door Monitor: 1NO Door Monitor: 1NO Door Monitor Monitor: 1NO Circuit: VW Door Monitor: 1NO Door Monitor: 1NO 1NO Door Monitor: Door Monitor: 1NO Door Monitor Monitor: 1NO Circuit: VX 12 12 12 12 22 22 22 22 11 11 Monitor Circuit: 11 Monitor Circuit: 11 Monitor Circuit: 21 21 Monitor Circuit: Monitor Circuit: 21 Monitor Circuit: 21 Monitor Circuit: Circuit: 31 Monitor 31 Monitor Circuit: 31 Monitor Circuit: 31 Monitor Circuit: Monitor Circuit: Door Monitor: 2NC,1NO31 Door Monitor: 2NC,1NO Door Monitor: 2NC,1NO Door Monitor: 2NC,1NO Door Monitor Monitor: 11 Circuit: VG 12 12 12 12 12 24 12 24 24 24 24 12 12 12 12 12 24 12 24 24 24 24 24 Door Monitor: Monitor: 3NC 3NC Door Door Monitor: 3NC Door Monitor: 3NC Door Monitor Monitor: 3NC Circuit: Monitor Circuit: VF Gland Port Size Contact Configuration Circuit Code VA Package Quantity: 1 Spring lock Solenoid Part No. Lock Monitor Monitor Lock Monitor SpringLock lock→Solenoid OFF Spring lock→Solenoid OFF Lock Monitor Spring lock→Solenoid Lock Monitor OFF Spring lock→Solenoid Solenoid lock→Solenoid ON Solenoid lock→SolenoidOFF ON Spring lock→Solenoid OFF Solenoid lock→Solenoid ON Spring lock→Solenoid OFF Solenoid lock→Solenoid ON Solenoid lock→Solenoid lock→Solenoid ON (+) (–) Solenoid ON (+) (–) (+) (+) (+) A2 (+) A2 A2 A2 A2 (–) (–) A1 (–) A1 A1 A1 A1 Lock Lock Monitor Monitor Circuit: Circuit: 1NC,1NO 1NC,1NO Lock Monitor Circuit: 1NC,1NO Lock Monitor Circuit: Lock Circuit: 1NC,1NO 1NC,1NO 41 42 (Note) 41 Monitor 42 41 41 41 41 53 53 53 53 53 42 42 42 42 54 54 54 54 54 (Note) (Note) (Note) (Note) (Note) 41 41 41 41 51 51 51 51 51 51 42 42 42 42 52 52 52 52 52 52 (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) 41 41 41 41 53 53 53 53 53 53 42 42 42 42 54 54 54 54 54 54 (Note) (Note) (Note) (Note) 41 41 41 51 51 51 51 51 51 42 42 42 52 52 52 52 52 52 (Note) (Note) (Note) (Note) (Note) 41 41 41 41 42 42 42 42 (Note) (Note) (Note) (Note) Lock Monitor Circuit: 2NC Lock Monitor Circuit: 2NC Lock Monitor Circuit: 2NC Lock Monitor Circuit: 2NC Lock Monitor Circuit: 2NC 42 41 (Note) 41 42 Lock Monitor Circuit: 1NC,1NO Lock Monitor Circuit: 1NC,1NO Lock Monitor Circuit: Lock Circuit: 1NC,1NO 1NC,1NO (Note) 41 42 (Note) 41 Monitor 42 Lock Monitor Monitor Circuit: Circuit: 2NC 2NC Lock Lock Monitor Circuit: 2NC Lock Monitor Circuit: 2NC Lock Monitor Circuit: 2NC 41 42 (Note) 41 42 M20 M20 M20 (Note) (Note) (Note) (Note) (Note) (Note) M20 Lock Monitor Monitor Circuit: Circuit: 1NC 1NC Lock Lock Monitor Monitor Circuit: Circuit: 1NC 1NC Lock 41 42 42 (Note) 41 42 42 42 42 (Note) (Note) (Note) (Note) HS1T-VA7Y4ZM-G HS1T-VA44ZSM-G HS1T-VA7Y4ZSM-G (side-conduit model) (side-conduit model) HS1T-VB44ZM-G HS1T-VB7Y4ZM-G HS1T-VC44ZM-G HS1T-VC7Y4ZM-G HS1T-VC44ZSM-G HS1T-VC7Y4ZSM-G (side-conduit model) (side-conduit model) HS1T-VD44ZM-G HS1T-VD7Y4ZM-G HS1T-VD44ZSM-G HS1T-VD7Y4ZSM-G (side-conduit model) (side-conduit model) HS1T-VF44ZM-G HS1T-VF7Y4ZM-G HS1T-VF44ZSM-G HS1T-VF7Y4ZSM-G (side-conduit model) (side-conduit model) HS1T-VG44ZM-G HS1T-VG7Y4ZM-G HS1T-VG44ZSM-G HS1T-VG7Y4ZSM-G (side-conduit model) (side-conduit model) M20 Lock Monitor Monitor Circuit: Circuit: 1NC 1NC Lock Lock Monitor Circuit: 1NC Lock Monitor Circuit: Lock Circuit: 1NC 1NC (Note) 41 Monitor 42 41 42 (Note) 41 41 41 41 HS1T-VA44ZM-G M20 Lock Monitor Monitor Circuit: Circuit: 3NC 3NC Lock Lock Monitor Circuit: 3NC Lock Monitor Circuit: 3NC 3NC Lock Circuit: 41 Monitor 42 (Note) 41 42 (Note) 41 41 41 51 41 51 51 51 51 61 51 61 61 61 61 61 42 42 42 52 42 52 52 52 52 62 52 62 62 62 62 62 (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) M20 HS1T-VH44ZM-G HS1T-VH7Y4ZM-G 41 41 41 51 41 51 51 51 51 63 51 63 63 63 63 63 42 42 42 52 42 52 52 52 52 64 52 64 64 64 64 64 (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) M20 HS1T-VJ44ZM-G HS1T-VJ7Y4ZM-G M20 HS1T-VW44ZM-G HS1T-VW7Y4ZM-G M20 HS1T-VX44ZM-G HS1T-VX7Y4ZM-G Lock Monitor Monitor Circuit: Circuit: 2NC, 2NC, 1NO 1NO Lock Lock Monitor Monitor Circuit: Circuit: 2NC, 2NC, 1NO Lock Lock Circuit: 2NC, 1NO 1NO 41 Monitor 42 (Note) 41 42 (Note) Lock Monitor Circuit: 3NC Lock Monitor Monitor Circuit: Circuit: 3NC 3NC Lock Lock Monitor Circuit: Lock Circuit: 3NC 3NC 41 Monitor 42 (Note) 41 41 41 41 51 41 51 51 51 61 51 61 61 61 61 61 42 42 42 42 52 42 52 52 52 62 52 62 62 62 62 62 (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) 41 41 41 41 51 41 51 51 51 51 63 51 63 63 63 63 42 42 42 42 52 42 52 52 52 52 64 52 64 64 64 64 (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) (Note) Lock Monitor Circuit: 2NC, 1NO Lock Monitor Monitor Circuit: Circuit: 2NC, 2NC, 1NO 1NO Lock Lock Monitor Circuit: 2NC, 1NO Lock Circuit: 2NC, 1NO 41 Monitor 42 (Note) • The contact configuration shows the status when the actuator is inserted and the switch is locked. • Actuators are not supplied with the interlock switch and must be ordered separately. • For safety circuit input, connect to the monitor circuit with marking. • For side-conduit model, contact IDEC for details. (Part No: HS1T-SM-G) • See page 9 to 12 for circuit diagrams and operating characteristics. Note: Both spring lock and solenoid lock models have marking for lock monitoring. Note that solenoid lock models can be used in applications where lock for safety purpose is found unnecessary after a risk assessment, e.g. locking is needed for purposes such as in production processes. 5 HS1T Interlock Switches with Solenoid 2-Contact (Spring Lock/Solenoid Lock) Contact ConfigurationLock Monitor Circuit Code Door Monitor (Actuator inserted) Door Monitor Monitor Door Door Monitor (Actuator inserted) (Actuator inserted) (Actuator inserted) XD Door Monitor: 1NC Door Monitor: Monitor: 1NC 1NC Door Door Monitor Monitor: 1NC Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Door Monitor: 2NC Door Monitor: Monitor: 2NC Door 2NC Door Monitor Monitor: 2NC Circuit: XF Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Circuit: Monitor Monitor Monitor Circuit: Circuit: Monitor Circuit: Spring lock→Solenoid OFF Lock Monitor Solenoid lock→Solenoid Lock Monitor ON Monitor OFF Spring lock→Solenoid SpringLock lock→Solenoid OFF (+) (–) Spring lock→Solenoid Solenoid lock→SolenoidOFF ON Solenoid lock→Solenoid ON Solenoid lock→Solenoid ON A2 A1 (+) (+) (+) A2 A2 A2 Gland Port Size XH Solenoid Part No. (–) (–) (–) A1 A1 A1 Lock Monitor Circuit: 1NC Lock Monitor Monitor Circuit: Circuit: 1NC 1NC Lock Lock Monitor Circuit: 1NC M20 HS1T-XD44ZM-G HS1T-XD7Y4ZM-G 12 11 11 11 12 12 12 11 21 11 11 11 21 21 21 12 22 12 12 12 22 22 22 M20 HS1T-XF7Y4ZM-G 12 24 12 12 12 24 24 24 M20 HS1T-XG7Y4ZM-G 23 11 11 11 23 23 23 41 42 (Note) 41 41 41 42 42 42 (Note) (Note) (Note) HS1T-XH44ZM-G Lock Monitor Circuit: 2NC Lock Lock Monitor Monitor Circuit: Circuit: 2NC 2NC Lock Monitor Circuit: 2NC Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Spring lock 11 Door Monitor: 1NC, 1NO Door 1NC, 1NO 1NO Door Monitor: Monitor: 1NC, Door Monitor Monitor: 1NC, 1NO 11 Circuit: XG Package Quantity: 1 41 42 (Note) 41 41 51 41 51 51 51 42 42 52 42 52 52 52 (Note) (Note) (Note) (Note) (Note) (Note) HS1T-XH44ZSM-G HS1T-XH7Y4ZM-G (side-conduit model) M20 HS1T-XH44ZLM-G (rear unlock button model) HS1T-XH44ZLSM-G (rear unlock button model, side-conduit model) HS1T-XH7Y4ZSM-G (side-conduit model) • The contact configuration shows the status when the actuator is inserted and the switch is locked. • Actuators are not supplied with the interlock switch and must be ordered separately. • For safety circuit input, connect to the monitor circuit with marking. • For side-conduit model, contact IDEC for details. (Part No: HS1T-SM-G) • See page 13 to 14 for circuit diagrams and operating characteristics. Note: Both spring lock and solenoid lock models have marking for lock monitoring. Note that solenoid lock models can be used in applications where lock for safety purpose is found unnecessary after a risk assessment, e.g. locking is needed for purposes such as in production processes. 6 HS1T Interlock Switches with Solenoid 4-Contact/Rear Unlock Button (Spring Lock) Circuit Code Package Quantity: 1 Door Monitor Door Monitor Door Monitor (Actuator inserted) Door Monitor (Actuator inserted) (Actuator inserted) Door Monitor (Actuator inserted) (Actuator inserted) VA Door Monitor: Monitor: 1NC,1NO Door Door Monitor: 1NC,1NO 1NC,1NO Door Monitor Monitor: 1NC,1NO11 Circuit: Door Monitor Monitor: 1NC,1NO11 Monitor Circuit: 11 Circuit: Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: 23 11 23 23 11 23 23 VB Door Door Monitor: Monitor: 1NC,1NO 1NC,1NO Door Monitor: 1NC,1NO Door Monitor Monitor: 1NC,1NO Circuit: 11 Door Monitor Monitor: 1NC,1NO Monitor Circuit: Circuit: 11 VC Door Monitor: Monitor: 2NC Door Door Monitor: 2NC 2NC Door Monitor Monitor: 2NC Circuit: Door Monitor Monitor: 2NC Monitor Circuit: Circuit: VD Door 2NC Door Monitor: Monitor: 2NC 2NC Door Monitor: Door Monitor Monitor: 2NC Circuit: Door Monitor Monitor: 2NC Monitor Circuit: Circuit: VF Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Circuit: Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Circuit: Monitor Monitor Circuit: Circuit: Monitor Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Door Door Monitor: Monitor: 3NC 3NC Door Monitor: 3NC 3NC Door Monitor Monitor: Circuit: Door Monitor Monitor: 3NC Monitor Circuit: Circuit: Monitor Circuit: Circuit: Monitor Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Circuit: Circuit: Monitor Monitor Circuit: Monitor Circuit: Door Door Monitor: Monitor: 1NC 1NC Door Monitor: 1NC Door Monitor Monitor: 1NC Circuit: 1NC Door Monitor Monitor: Circuit: Monitor Circuit: VJ Gland Port Size Contact Configuration Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Monitor Circuit: Monitor Circuit: Monitor Monitor Circuit: Circuit: Monitor Circuit: Lock Monitor Lock Monitor Lock Monitor (Solenoid OFF) Lock Monitor (Solenoid OFF) (Solenoid OFF) Lock Monitor (Solenoid OFF) (+) (–) (+) (–) (Solenoid OFF) (+) (–) A2 (+) A2 (+) A2 A2 A2 11 23 11 23 23 11 23 23 11 11 11 21 11 21 21 11 21 21 12 12 12 22 12 22 22 12 22 22 11 11 11 21 11 21 21 11 21 21 12 12 12 22 12 22 22 12 22 22 11 11 11 21 11 21 21 31 11 21 31 31 21 31 31 12 12 12 22 12 22 22 32 12 22 32 32 22 32 32 11 11 11 11 11 12 12 12 12 12 A1 (–) A1 (–) A1 A1 A1 M20 HS1T-VA44ZLM-G Lock Lock Monitor Monitor Circuit: Circuit: 2NC 2NC Lock Monitor Circuit: 2NC Lock Monitor Circuit: 2NC 42 41 Monitor (Note) Lock Circuit: 2NC 41 42 (Note) M20 HS1T-VB44ZLM-G Lock Monitor Monitor Circuit: 1NC,1NO Lock 1NC,1NO Lock Monitor Circuit: Circuit: 1NC,1NO Lock Circuit: 1NC,1NO (Note) 41 Monitor 42 Lock Monitor Circuit: 1NC,1NO (Note) 41 42 42 (Note) 41 M20 HS1T-VC44ZLM-G Lock Monitor Circuit: 2NC Lock Monitor Monitor Circuit: Circuit: 2NC 2NC Lock Lock Circuit: 2NC 41 Monitor 42 (Note) Lock Monitor Circuit: 41 42 42 (Note) 2NC 41 (Note) Lock Monitor Monitor Circuit: 1NC,1NO 1NC,1NO Lock Lock Monitor Circuit: Circuit: 1NC,1NO Lock Circuit: 1NC,1NO 41 Monitor 42 (Note) Lock Monitor Circuit: 41 42 (Note) 1NC,1NO 41 42 (Note) 12 12 12 24 12 24 24 12 24 24 12 12 12 24 12 24 24 12 24 24 Spring lock Part No. 41 53 41 53 53 53 53 42 54 42 54 54 54 54 (Note) (Note) 41 41 51 41 51 51 51 51 42 42 52 42 52 52 52 52 (Note) (Note) (Note) (Note) (Note) (Note) (Note) 41 53 41 53 53 53 53 42 54 42 54 54 54 54 (Note) (Note) 41 51 41 51 51 51 51 42 52 42 52 52 52 52 (Note) (Note) (Note) (Note) (Note) (Note) M20 41 41 42 42 (Note) (Note) M20 Lock Lock Monitor Monitor Circuit: Circuit: 1NC 1NC Lock Monitor Circuit: 1NC Lock Monitor Circuit: 1NC (Note) 41 Monitor 42 Lock Circuit: 1NC (Note) 41 42 (Note) 41 42 HS1T-VD44ZLM-G (side-conduit model) HS1T-VF44ZLM-G 42 52 52 42 52 64 52 64 52 64 64 64 (Note) (Note) (Note) (Note) (Note) HS1T-VF44ZLSM-G (side-conduit model) Lock Lock Monitor Monitor Circuit: Circuit: 2NC,1NO 2NC,1NO Lock Monitor Circuit: 2NC,1NO Lock Monitor Circuit: 2NC,1NO 41 42 (Note) Lock Monitor Circuit: 41 42 (Note) 41 42 (Note) 2NC,1NO 41 51 51 41 51 63 51 63 51 63 63 63 HS1T-VD44ZLSM-G M20 HS1T-VJ44ZLM-G • See page 8 to 9 for circuit diagrams and operating characteristics. 4-Contact/Dual Safety Circuit (Spring Lock) Package Quantity: 1 Gland Port Size Contact Configuration Circuit Code Main Circuit: 1NC+1NC, 1NC+1NC Door Monitor (Actuator inserted) Lock Monitor (Solenoid OFF) (+) A2 DD Monitor Circuit: Monitor Circuit: 11 21 12 22 Spring lock Part No. 41 51 HS1T-DD44ZM-G (–) A1 42 52 M20 HS1T-DD44ZSM-G (Note) (Note) (side-conduit model) • See page 12 for circuit diagrams and operating characteristics. 4-Contact/Dual Safety Circuit/Rear Unlock Button (Spring Lock) Package Quantity: 1 Gland Port Size Contact Configuration Circuit Code Main Circuit: 1NC+1NC, 1NC+1NC Door Monitor (Actuator inserted) Lock Monitor (Solenoid OFF) (+) A2 DD Monitor Circuit: Monitor Circuit: 11 21 12 22 Spring lock Part No. 41 51 HS1T-DD44ZLM-G (–) A1 42 52 M20 (Note) (Note) HS1T-DD44ZLSM-G (side-conduit model) • See page 12 for circuit diagrams and operating characteristics. • The contact configuration shows the status when the actuator is inserted and the switch is locked. • Actuators are not supplied with the interlock switch and must be ordered separately. 7 HS1T Interlock Switches with Solenoid Circuit Diagrams and Operating Characteristics 4-Contact/Rear Unlock Button (Spring Lock) Status 1 Door closed Machine ready to operate Solenoid de-energized Interlock Switch Status When unlocking manually Status 2 Status 3 Status 4 Door closed Machine cannot be operated Solenoid energized Door open Machine cannot be operated Solenoid energized Door open Machine cannot be operated Solenoid de-energized Door closed Machine cannot be operated Solenoid de-energized Press Door Status •Turn the •Press the rear manual unlocking unlock key (*1) button (*2) (−) A1 (+) A2 Circuit Example: HS1T-VA4 Door HS1T-VA4 Door Monitor (Actuator inserted) Monitor Circuit: 11 12 Monitor Circuit: 23 24 Monitor Circuit: HS1T-VB4 Monitor Circuit: 11 12 Monitor Circuit: 23 24 Monitor Circuit: HS1T-VC4 Part No. and Circuit Diagram Monitor Circuit: 11 12 Monitor Circuit: 21 22 Monitor Circuit: HS1T-VD4 Monitor Circuit: 11 12 Monitor Circuit: 21 22 Monitor Circuit: HS1T-VF4 Monitor Circuit: 11 12 Monitor Circuit: 21 22 Monitor Circuit: 31 32 HS1T-VG4 Monitor Circuit: 11 12 Monitor Circuit: 21 22 Monitor Circuit: 33 34 HS1T-VH4 Monitor Circuit: 11 12 Monitor Circuit: Monitor Circuit: (+) A2 (−) A1 (+) A2 (−) A1 (+) A2 (+) A2 (−) A1 (−) A1 11 12 41 42 11 12 41 42 11 12 41 42 11 12 41 42 11 12 41 42 23 24 53 54 23 24 53 54 23 24 53 54 23 24 53 54 23 24 53 54 Closed (locked) Closed (unlocked) Open Open Closed (unlocked) OFF (de-energized) ON (energized) ON (energized) OFF (de-energized) OFF (de-energized) Monitor Circuit (door closed) 11−12 Lock Monitor Circuit (Solenoid OFF) Monitor (door open) (+) (–) 23−24 A2 A1 Monitor Circuit (locked) 41−42 41 42 Monitor Circuit (unlocked) 53 54 53−54 Monitor Circuit (door closed) 11−12 Monitor Circuit (door open) 23−24 41 42 Monitor Circuit (locked) 41−42 51 52 Monitor Circuit (locked) 51−52 Monitor Circuit (door closed) 11−12 Monitor Circuit (door closed) 21−22 41 42 Monitor Circuit (locked) 41−42 53 54 Monitor Circuit (unlocked) 53−54 Monitor Circuit (door closed) 11−12 Monitor Circuit (door closed) 21−22 41 42 Monitor Circuit (locked) 41−42 51 52 Monitor Circuit (locked) 51−52 Monitor Circuit (door closed) 11−12 Monitor Circuit (door closed) 21-22 41 42 Monitor Circuit (door closed) 31-32 Monitor Circuit (locked) 41-42 Monitor Circuit (door closed) 11−12 Monitor Circuit (door closed) 21-22 41 42 Monitor Circuit (door open) 33-34 Monitor Circuit (door locked) 41-42 Monitor Circuit (door closed) 11-12 Monitor Circuit (locked) 41-42 41 42 Monitor Circuit (locked) 51 52 51-52 61 62 Monitor Circuit (locked) 61-62 Solenoid Power A1-A2 (all models) • The contact configuration shows the status when the actuator is inserted and the switch is locked. • Monitor Circuit: Sends monitoring signals of protective door open/closed status (door monitor) or protective door lock/unlock status (lock monitor). *1) Actuator can be unlocked manually for confirming the door movement before wiring and energizing, and also for emergency situation such as power failure. *2) When an operator is confined within a dangerous zone, the actuator can be unlocked manually by pressing the rear unlock button (rear unlock button model). 8 HS1T Interlock Switches with Solenoid Circuit Diagrams and Operating Characteristics 4-Contact/Rear Unlock Button (Spring Lock) Status 1 Door Closed Machine ready to operate Solenoid de-energized Interlock Switch Status When unlocking manually Status 2 Status 3 Status 4 Door Closed Machine cannot be operated Solenoid energized Door open Machine cannot be operated Solenoid energized Door open Machine cannot be operated Solenoid de-energized Door Closed Machine cannot be operated Solenoid de-energized Press Door Status •Turn the •Press the rear manual unlocking unlock key (*1) button (*2) (−) A1 (+) A2 Circuit Example: HS1T-VA4 Door HS1T-VJ4 Door Monitor Part No. and Circuit Diagram (Actuator inserted) Monitor Circuit: 11 12 Monitor Circuit: Monitor Circuit: HS1T-VW4 Monitor Circuit: 13 14 Monitor Circuit: Monitor Circuit: HS1T-VX4 Monitor Circuit: 13 14 Monitor Circuit: Monitor Circuit: (−) A1 (+) A2 (+) A2 (+) A2 (−) A1 11 12 41 42 11 12 41 42 11 12 41 42 23 24 53 54 23 24 53 54 23 24 53 54 11 23 12 24 41 53 (+) A2 (−) A1 (−) A1 42 11 12 41 42 54 23 24 53 54 Closed (locked) Closed (unlocked) Open Open Closed (unlocked) OFF (de-energized) ON (energized) ON (energized) OFF (de-energized) OFF (de-energized) Monitor Circuit (door closed) 11−12 Lock Monitor (Solenoid OFF) Monitor Circuit (locked) (+) (–) 41−42 A2 A1 Monitor Circuit (locked) 41 42 51−52 51 52 Monitor Circuit (unlocked) 63 64 63−64 Monitor Circuit (door open) 13−14 Monitor Circuit (locked) 41−42 41 42 Monitor Circuit 51 52 (locked) 61 62 51−52 Monitor Circuit (locked) 61−62 Monitor Circuit (door open) 13−14 Monitor Circuit (locked) 41 42 41−42 51 52 Monitor Circuit (locked) 63 64 51−52 Monitor Circuit (unlocked) 63−64 Solenoid Power A1-A2 (all models) • The contact configuration shows the status when the actuator is inserted and the switch is locked. • Monitor Circuit: Sends monitoring signals of protective door open/closed status (door monitor) or protective door lock/unlock status (lock monitor). *1) Actuator can be unlocked manually for confirming the door movement before wiring and energizing, and also for emergency situation such as power failure. *2) When an operator is confined within a dangerous zone, the actuator can be unlocked manually by pressing the rear unlock button (rear unlock button model). Operating Characteristics (Reference) 0 (Actuator Mounting Reference Position) Approx. 4.2 (Locked position) Approx. 9.8 Approx. 28.5 (mm) Approx. 11.6 : Contacts ON Door Monitor Circuit (door open, NO) (closed) Door Monitor Circuit (door closed, NC) Lock Monitor Circuit (unlocked, NO) Lock Monitor Circuit (locked, NC) : Contacts OFF (open) • The characteristics shown in the chart above are of the straight actuator (HS9Z-A11T) and right-angle actuator (HS9Z-A12T). • The operation characteristics show the contact status when the actuator enters the entry slot of an interlock switch. 9 HS1T Interlock Switches with Solenoid Circuit Diagrams and Operating Characteristics 4-Contact (Solenoid Lock) Status 1 Door closed Machine ready to operate Solenoid energized Interlock Switch Status Status 2 Status 3 Status 4 Unlocking using Manual Unlock Key Door closed Machine cannot be operated Solenoid de-energized Door open Machine cannot be operated Solenoid de-energized Door open Machine cannot be operated Solenoid energized Door closed Machine cannot be operated Solenoid de-energized  energized Door Status When unlocking manually (+) A2 Circuit Example: HS1T-VA7Y Door HS1T-VA7Y Door Monitor (Actuator inserted) Lock Monitor (Solenoid ON) (+) A2 Monitor Circuit: Monitor Circuit: Monitor Circuit: 11 12 23 24 (–) A1 41 42 (*3) 53 54 Part No. and Circuit Diagram HS1T-VB7Y Monitor Circuit: Monitor Circuit: Monitor Circuit: 11 12 23 24 41 42 (*3) 51 52 (*3) 41 42 (*3) HS1T-VC7Y Monitor Circuit: Monitor Circuit: Monitor Circuit: 11 12 21 22 53 54 HS1T-VD7Y Monitor Circuit: Monitor Circuit: Monitor Circuit: 11 12 21 22 41 42 (*3) 51 52 (*3) (−) A1 (+) A2 (−) A1 (+) A2 (−) A1 (+) A2 (+) A2 (−) A1 (−) A1 11 12 41 42 11 12 41 42 11 12 41 42 11 12 41 42 11 12 41 42 23 24 53 54 23 24 53 54 23 24 53 54 23 24 53 54 23 24 53 54 Closed (locked) Closed (unlocked) Open Open Closed (unlocked) ON (energized) OFF (de-energized) OFF (de-energized) ON (energized) (*2) OFF (de-energized)  ON (energized) (*1) (*2) Monitor Circuit (door closed) 11−12 Monitor Circuit (door open) 23−24 Monitor Circuit (locked) 41−42 Monitor Circuit (unlocked) 53−54 Monitor Circuit (door closed) 11−12 Monitor Circuit (door open) 23−24 Monitor Circuit (locked) 41−42 Monitor Circuit (locked) 51−52 Monitor Circuit (door closed) 11−12 Monitor Circuit (door closed) 21−22 Monitor Circuit (locked) 41−42 Monitor Circuit (unlocked) 53−54 Monitor Circuit (door closed) 11−12 Monitor Circuit (door closed) 21−22 Monitor Circuit (locked) 41−42 Monitor Circuit (locked) 51−52 Solenoid Power A1-A2 (all models) • The contact configuration shows the status when the actuator is inserted and the switch is locked. • Monitor Circuit: Sends monitoring signals of protective door open/closed status (door monitor) or protective door lock/unlock status (lock monitor). *1) Do not attempt manual unlocking when the solenoid is energized. *2) Do not energize the solenoid for a long time while the door is open or when the door is unlocked manually. *3) Both spring lock and solenoid lock models have marking for lock monitoring. Note that solenoid lock models can be used in applications where lock for safety purpose is found unnecessary after a risk assessment, e.g. locking is needed for purposes such as in production processes. Operating Characteristics (Reference) 0 (Actuator Mounting Reference Position) Approx. 4.2 (Locked position) Approx. 9.8 Approx. 28.5 (mm) Approx. 11.6 : Contacts ON Door Monitor Circuit (door open, NO) (closed) Door Monitor Circuit (door closed, NC) Lock Monitor Circuit (unlocked, NO) Lock Monitor Circuit (locked, NC) : Contacts OFF (open) • The characteristics shown in the chart above are of the straight actuator (HS9Z-A11T) and right-angle actuator (HS9Z-A12T). • The operation characteristics show the contact status when the actuator enters the entry slot of an interlock switch. 10 HS1T Interlock Switches with Solenoid Circuit Diagrams and Operating Characteristics 4-Contact (Solenoid Lock) Status 1 Door closed Machine ready to operate Solenoid energized Interlock Switch Status Status 2 Status 3 Status 4 Unlocking using Manual Unlock Key Door closed Machine cannot be operated Solenoid de-energized Door open Machine cannot be operated Solenoid de-energized Door open Machine cannot be operated Solenoid energized Door closed Machine cannot be operated Solenoid de-energized  energized Door Status When unlocking manually (+) A2 Circuit Example: HS1T-VA7Y Door HS1T-VF7Y Door Monitor (Actuator inserted) Lock Monitor (Solenoid ON) (+) A2 Monitor Circuit: Monitor Circuit: Monitor Circuit: 11 12 21 22 31 32 (–) A1 41 42 (*3) 41 42 51 52 61 62 (*3) (*3) (*3) 41 42 (*3) 41 42 51 52 63 64 (*3) (*3) 41 42 51 52 61 62 (*3) (*3) (*3) 41 42 51 52 63 64 (*3) (*3) HS1T-VH7Y Monitor Circuit: Monitor Circuit: Monitor Circuit: 11 12 Part No. and Circuit Diagram HS1T-VG7Y Monitor Circuit: Monitor Circuit: Monitor Circuit: 11 12 21 22 33 34 HS1T-VJ7Y Monitor Circuit: Monitor Circuit: Monitor Circuit: 11 12 HS1T-VW7Y Monitor Circuit: Monitor Circuit: Monitor Circuit: 13 14 HS1T-VX7Y Monitor Circuit: Monitor Circuit: Monitor Circuit: 13 14 Solenoid Power A1-A2 (all models) (−) A1 (+) A2 (−) A1 11 12 41 42 11 12 41 42 23 24 53 54 23 24 53 54 (+) A2 11 23 12 24 41 53 (−) A1 (+) A2 (+) A2 (−) A1 (−) A1 42 11 12 41 42 11 12 41 42 54 23 24 53 54 23 24 53 54 Closed (locked) Closed (unlocked) Open Open Closed (unlocked) ON (energized) OFF (de-energized) OFF (de-energized) ON (energized) (*2) OFF (de-energized)  ON (energized) (*1) (*2) Monitor Circuit (door closed) 11−12 Monitor Circuit (door closed) 21−22 Monitor Circuit (door closed) 31−32 Monitor Circuit (locked) 41−42 Monitor Circuit (door closed) 11−12 Monitor Circuit (locked) 41−42 Monitor Circuit (locked) 51−52 Monitor Circuit (locked) 61−62 Monitor Circuit (door closed) 11−12 Monitor Circuit (door closed) 21−22 Monitor Circuit (door open) 33-34 Monitor Circuit (locked) 41−42 Monitor Circuit (door closed) 11−12 Monitor Circuit (locked) 41−42 Monitor Circuit (locked) 51−52 Monitor Circuit (unlocked) 63-64 Monitor Circuit (door open) 13-14 Monitor Circuit (locked) 41−42 Monitor Circuit (locked) 51−52 Monitor Circuit (locked) 61-62 Monitor Circuit (door open) 13-14 Monitor Circuit (locked) 41−42 Monitor Circuit (locked) 51−52 Monitor Circuit (unlocked) 63-64 • The contact configuration shows the status when the actuator is inserted and the switch is locked. • Monitor Circuit: Sends monitoring signals of protective door open/closed status (door monitor) or protective door lock/unlock status (lock monitor). *1) Do not attempt manual unlocking when the solenoid is energized. *2) Do not energize the solenoid for a long time while the door is open or when the door is unlocked manually. *3) Both spring lock and solenoid lock models have marking for lock monitoring. Note that solenoid lock models can be used in applications where lock for safety purpose is found unnecessary after a risk assessment, e.g. locking is needed for purposes such as in production processes. Operating Characteristics (Reference) 0 (Actuator Mounting Reference Position) Approx. 4.2 (Locked position) Approx. 9.8 Approx. 28.5 (mm) Approx. 11.6 : Contacts ON Door Monitor Circuit (door open, NO) (closed) Door Monitor Circuit (door closed, NC) Lock Monitor Circuit (unlocked, NO) Lock Monitor Circuit (locked, NC) : Contacts OFF (open) • The characteristics shown in the chart above are of the straight actuator (HS9Z-A11T) and right-angle actuator (HS9Z-A12T). • The operation characteristics show the contact status when the actuator enters the entry slot of an interlock switch. 11 HS1T Interlock Switches with Solenoid Circuit Diagrams and Operating Characteristics 4-Contact/Dual Safety Circuit, 4-Contact/Dual Safety Circuit/Rear Unlock Button (Spring Lock) Status 1 Door closed Machine ready to operate Solenoid de-energized Interlock Switch Status Status 2 Status 3 Status 4 Door closed Machine cannot be operated Solenoid energized Door open Machine cannot be operated Solenoid energized Door open Machine cannot be operated Solenoid de-energized Unlocking using Manual Unlock Key Door closed Machine cannot be operated Solenoid de-energized Press Door Status •Turn the •Press the rear manual unlocking unlock key (*1) button (*2) (+) A2 Circuit Example: HS1T-DD4 Door Part No. and Circuit Diagram HS1T-DD44 Door Monitor (Actuator inserted) Lock Monitor (Solenoid OFF) (+) A2 Monitor Circuit: 11 12 Monitor Circuit: 21 22 (+) A2 (+) A2 (−) A1 (+) A2 (−) A1 (−) A1 (+) A2 (−) A1 11 12 41 42 11 12 41 42 11 12 41 42 11 12 41 42 11 12 41 42 21 22 51 52 21 22 51 52 21 22 51 52 21 22 51 52 21 22 51 52 Closed (locked) Closed (unlocked) Open Open Closed (unlocked) OFF (de-energized) ON (energized) ON (energized) OFF (de-energized) OFF (de-energized) Main Circuit 11−42 (–) A1 41 42 51 52 HS1T-DD44L Monitor Circuit: 11 12 Monitor Circuit: 21 22 (−) A1 Main Circuit 21−52 Main Circuit 11−42 41 42 51 52 Main Circuit 21−52 Solenoid Power A1-A2 (all model) • The contact configuration shows the status when the actuator is inserted and the switch is locked. • Main Circuit: Connected to the control circuit of machine drive part, sending interlock signals of the protective door. • For safety circuit input, connect to the monitor circuit. *1) Actuator can be unlocked manually for confirming the door movement before wiring and energizing, and also for emergency situation such as power failure. *2) When an operator is confined within a dangerous zone, the actuator can be unlocked manually by pressing the rear unlock button. (rear unlock button model) Operating Characteristics (Reference) 0 (Actuator Mounting Reference Position) Approx. 4.2 (Locked position) Approx. 9.8 Approx. 28.5 (mm) Approx. 11.6 Main Circuit : Contacts ON (closed) : Contacts OFF (open) • The characteristics shown in the chart above are of the straight actuator (HS9Z-A11T) and right-angle actuator (HS9Z-A12T). • The operation characteristics show the contact status when the actuator enters the entry slot of an interlock switch. 12 HS1T Interlock Switches with Solenoid Circuit Diagrams and Operating Characteristics 2-Contact (Spring Lock) Status 1 Interlock Switch Status Door closed Machine ready to operate Solenoid de-energized When unlocking manually Status 2 Status 3 Status 4 Door closed Machine cannot be operated Solenoid energized Door open Machine cannot be operated Solenoid energized Door open Machine cannot be operated Solenoid de-energized Door closed Machine cannot be operated Solenoid de-energized Press Door Status •Turn the •Press the rear manual unlocking unlock key (*1) button (*2) (+) A2 Circuit Example: HS1T-XD4 11 Door Part No. and Circuit Diagram HS1T-XD4 Door Monitor (Actuator inserted) (+) 42 11 12 41 (−) A1 42 (+) A2 11 12 41 (+) A2 (−) A1 42 11 12 41 (−) A1 42 (+) A2 11 12 41 (−) A1 42 Closed (locked) Closed (unlocked) Open Open Closed (unlocked) OFF (de-energized) ON (energized) ON (energized) OFF (de-energized) OFF (de-energized) (–) A1 41 42 HS1T-XH4 Monitor Circuit: Monitor Circuit: 41 (+) A2 Monitor Circuit Lock Monitor (door closed) (Solenoid OFF) 11-12 A2 Monitor Circuit: 11 12 Monitor Circuit: 12 (−) A1 41 42 51 52 Monitor Circuit (locked) 41-42 Monitor Circuit (locked) 41-42 Monitor Circuit (locked) 51-52 Solenoid Power A1-A2 (all model) • The contact configuration shows the status when the actuator is inserted and the switch is locked. • Monitor Circuit: Sends monitoring signals of protective door open/closed status (door monitor) or protective door lock/unlock status (lock monitor). *1) Actuator can be unlocked manually for confirming the door movement before wiring and energizing, and also for emergency situation such as power failure. *2) When an operator is confined within a dangerous zone, the actuator can be unlocked manually by pressing the rear unlock button. (rear unlock button model) Operating Characteristics (Reference) 0 (Actuator Mounting Reference Position) Approx. 4.2 (Locked position) Approx. 9.8 Approx. 28.5 (mm) Approx. 11.6 : Contacts ON Door Monitor Circuit (door open, NO) (closed) Door Monitor Circuit (door closed, NC) Lock Monitor Circuit (unlocked, NO) Lock Monitor Circuit (locked, NC) : Contacts OFF (open) • The characteristics shown in the chart above are of the straight actuator (HS9Z-A11T) and right-angle actuator (HS9Z-A12T). • The operation characteristics show the contact status when the actuator enters the entry slot of an interlock switch. 13 HS1T Interlock Switches with Solenoid Circuit Diagrams and Operating Characteristics 2-Contact (Solenoid Lock) Interlock Switch Status Status 1 Status 2 Status 3 Status 4 Unlocking using Manual Unlock Key Door closed Machine ready to operate Solenoid energized Door closed Machine cannot be operated Solenoid de-energized Door open Machine cannot be operated Solenoid de-energized Door open Machine cannot be operated Solenoid energized Door closed Machine cannot be operated Solenoid de-energized  energized Door Status When unlocking manually (+) A2 Circuit Example: HS1T-XD7Y 11 Door HS1T-XD7Y Door Monitor (Actuator inserted) Lock Monitor (Solenoid ON) (+) A2 Monitor Circuit: Monitor Circuit: 11 12 (–) A1 41 42 (*4) Part No. and Circuit Diagram HS1T-XF7Y (*3) Monitor Circuit: Monitor Circuit: 11 12 21 22 42 11 12 41 (−) A1 42 (+) A2 11 12 41 (+) A2 (−) A1 42 11 12 41 (+) A2 (−) A1 42 11 12 41 (−) A1 42 Closed (locked) Closed (unlocked) Open Open Closed (unlocked) OFF (energized) OFF (de-energized) OFF (de-energized) ON (energized) (*2) OFF (de-energized)  ON (energized) (*1) (*2) Monitor Circuit (door closed) 11-12 Monitor Circuit (locked) 41-42 Monitor Circuit (door closed) 21-22 Monitor Circuit (door closed) 11-12 11 12 23 24 Monitor Circuit (door open) 23-24 HS1T-XH7Y Monitor Circuit: Monitor Circuit: 41 (+) A2 Monitor Circuit (door closed) 11-12 HS1T-XG7Y (*3) Monitor Circuit: Monitor Circuit: 12 (−) A1 41 42 51 52 (*4) (*4) Monitor Circuit (locked) 41-42 Monitor Circuit (locked) 51-52 Solenoid Power A1-A2 (all models) • The contact configuration shows the status when the actuator is inserted and the switch is locked. • Monitor Circuit: Sends monitoring signals of protective door open/closed status (door monitor) or protective door lock/unlock status (lock monitor). *1) Do not unlock manually while the solenoid is energized. *2) Do not energize the solenoid for a long period of time while the door is open or while the door is unlocked manually. *3) Circuit codes XF and XG do not have signals to notify whether the switch is locked or unlocked. A different method should be used to check the lock status. *4) Both spring lock and solenoid lock models have marking for lock monitoring. Note that solenoid lock models can be used in applications where lock for safety purpose is found unnecessary after a risk assessment, e.g. locking is needed for purposes such as in production processes. Operating Characteristics (Reference) 0 (Actuator Mounting Reference Position) Approx. 4.2 (Locked position) Approx. 9.8 Approx. 28.5 (mm) Approx. 11.6 : Contacts ON Door Monitor Circuit (door open, NO) (closed) Door Monitor Circuit (door closed, NC) Lock Monitor Circuit (unlocked, NO) Lock Monitor Circuit (locked, NC) : Contacts OFF (open) • The characteristics shown in the chart above are of the straight actuator (HS9Z-A11T) and right-angle actuator (HS9Z-A12T). • The operation characteristics show the contact status when the actuator enters the entry slot of an interlock switch. 14 HS1T Interlock Switches with Solenoid Interlock Switch Dimensions and Mounting Hole Layouts All dimensions in mm HS1T-4ZM-G 7.1 When using Horizontal Mounting/Straight Actuator (HS9Z-A11T) RP: Reference mounting position 2.5 3-M5 Screw HS9Z-A11T Actuator ø10 9 18 30 6.5 (24.5) 40.1 4 (Material: Plastic) 143 7 to 8 17.8 97.8 ø5 .2 56.2 20.8 59.4 RP 4.6 Slot Plug (*1) 35 (2.6±0.5)✽ .1 ø5 Manual Unlock Key (5.1±0.5)✽ 3 (8) Accessories (supplied) 30 97.8 30 22 Mounting Hole Layout (24) 15 9 4 61.6 56.8 RP 7 1 40 20 40 6.5 HS1T-4ZSM-G (side-conduit model) 7.1 When using Horizontal Mounting/Straight Actuator (HS9Z-A11T) RP: Reference mounting position 4 61.6 56.8 RP .1 9 ø5 (5.1±0.5)✽ 35 2.5 Mounting Hole Layout 30 HS9Z-A11T Actuator 3-M5 Screw 125.5 40.1 4 30 (8) 104.6 125.5 104.6 170 ø5 .2 56.2 20.8 59.4 RP 4.6 Slot Plug (*1) (2.6±0.5)✽ 30 22 45 7 to 8 22.5 7 1 17.5 40 20 40 7 • Dimensions above are at factory setting. *1) Be sure to plug unused actuator entry slots using square plugs so that dust does not enter into the entry slots. (Square plug is inserted at factory setting.) ✽ Actuator mounting reference position 15 HS1T Interlock Switches with Solenoid Interlock Switch Dimensions and Mounting Hole Layouts All dimensions in mm HS1T-4ZLM-G (with rear unlock button) When using Horizontal Mounting/Straight Actuator (HS9Z-A11T) 7.1 Mounting Hole Layout Manual Unlock Key RP: Reference mounting position (Material: Plastic) .1 ø10 3 (24) 15 9 2.5 HS9Z-A11T Actuator 18 6.5 (24.5) Rear Unlock Button 7 to 8 27 40.1 4 4.6 Slot Plug (*1) 7.7 143 97.8 ø5 .2 56.2 20.8 30 (5.1±0.5)✽ 35 (2.6±0.5)✽ 9 ø5 (8) ø2 0 30 22 20.8 3-M5 Screw 97.8 4 40 30 61.6 56.8 RP 59.4 RP Accessories (supplied) 17.8 Rear Unlocking Button 7 1 40 HS1T-4ZLSM-G (side-conduit model/rear unlock button) 7.1 When using Horizontal Mounting/Straight Actuator (HS9Z-A11T) 4 RP: Reference mounting position 61.6 56.8 RP (8) 30 Rear unlock button 20.8 3-M5 Screw 40.1 4 Mounting Hole Layout 125.5 Rear unlock mechanical indicator 104.6 170 104.6 ø5 .2 56.2 125.5 20.8 59.4 RP 4.6 Slot Plug (*1) 2.5 ø20 9 ø 30 (5.1±0.5)✽ 35 5.1 (2.6±0.5)✽ 30 22 45 7 to 8 22.5 7 17.5 1 40 20 40 7 • Dimensions above are at factory setting. *1) Be sure to plug unused actuator entry slots using square plugs so that dust does not enter into the entry slots. (Square plug is inserted at factory setting.) ✽ Actuator mounting reference position 16 HS1T Interlock Switches with Solenoid Actuator / Accessory Actuator Description Part No. (Ordering Part No.) Package Quantity Straight with rubber bushings HS9Z-A11T 1 Right-angle with rubber bushings HS9Z-A12T 1 Remarks Actuator retention force is Fzh=5,000N. • Above actuators can only be used for HS1T. Do not used on other models. Note) Use dedicated actuators only. When other actuators are used, the interlock switch may be damaged. Accessory Description Part No. (Ordering Part No.) Package Quantity HS9Z-T3 Manual Unlock Key (long) Remarks Material: Metal (Used if the HS1T is installed far inside the equipment to reach to the manual lock.) 1 Interlock Switch Dimensions and Mounting Hole Layouts All dimensions in mm Actuator (42.5) 40 47 19.3 0.8 .1 ø5.1 Mounting Hole Layout 0.8 5 -M rew Sc 2 3 When mounted (8) 3 ° 90 5.1 When mounted (8) ø5 Actuator Cover (supplied) 12.3 40 22 40 22 18.6 43 ø15 20.5 11.5 18.6 43 5 22 9 ø1 Right-angle with rubber bushings HS9Z-A12T 5.1 Straight with rubber bushings HS9Z-A11T Accessory 130 4 ø10 15 15 (24) 9 ø4 3 Manual Unlock Key (long) (metal) HS9Z-T3 18 6.5 (24.5) 17 HS1T Interlock Switches with Solenoid Safety Precautions • Turn power off before installation, removal, wiring, maintenance, or inspection of the interlock switch. Otherwise electric shock or fire may occur. • If relays are used in the circuit between the interlock switch and the load, use only safety relays, since welded or sticking contacts of standard relays may invalidate the functions of the interlock switch. Perform a risk assessment and make a safety circuit which satisfies the requirements of the safety category. • Do not place a PLC in the circuit between the interlock switch and the load. Safety security can be endangered in the event of a malfunction of the PLC. • Do not disassemble or modify the interlock switch, otherwise malfunction or accident may occur. • Do not install the actuator in a location where a human body may come into contact. Otherwise injury may occur. • Solenoid lock is locked when energized, and unlocked when deenergized. When energization is interrupted due to wire disconnection or other failures, the interlock switch may be unlocked causing possible danger to the operators. Solenoid lock must not be used in applications where locking is strictly required for safety. Perform a risk assessment and determine whether solenoid lock is required. • HS11T interlock switches are Type 2 low level coded interlocking devices (ISO14119). According to EN ISO/ ISO14119, the following is required to minimize defeat when installing and constructing systems: 1. Prevent dismantling or de-positioning of the elements of the interlocking device by use of non-detachable fixing (e.g. welding, gluing, one-way screws, riveting). However, use of non-detachable fixing can be an inappropriate solution in cases where a failure of the interlocking device during lifetime of the machinery can be expected and a fast change is necessary. In this case, measures mentioned below should be used to provide the required level of risk reduction. 2. Apply at least one out of the four measures below.  Mounting out of reach.  Physical obstruction or shielding.  Mounting in hidden position.  Integration of defeat monitoring by means of status monitoring/cyclic testing. Instructions Installation • Do not apply excessive shock to the interlock switch when opening or closing the door. A shock to the interlock switch exceeding 1,000 m/s2 may cause damage to the interlock switch. • Install a guide on the door and make sure that force is not applied in the direction other than the actuator entry direction. • Do not pull the actuator during lock status. Do not use the interlock switch as a locking device regardless of the door type. To install a locking device, use a bracket as mentioned in page 3 of the instruction manual. • Make sure that the installation surface of the interlock switch is flat and has sufficient strength to not deform when the interlock switch is installled. Also, do not place foreign objects between the interlock switch and the installation surface. The interlock switch may not operate properly if the surface is not flat of a foreign object is placed in between. • If the operating atmosphere is contaminated, use a protective cover to prevent entry of foreign objects into the interlock switch through the actuator entry slots. Entry of foreign objects into the interlock switch may affect the mechanism of the interlock switch and cause a breakdown. • Make sure that the actuator does not scape the entry of the metal head. Otherwise, damage may occur. • Install the interlock switch in a location where there is no risk of damage. Also, perform risk assessment before use and take measures such as attaching a protective cover if necessary. • While the solenoid is energized, the interlock switch temperature rises approximately 40°C above the ambient temperature (to approximately 95°C while the ambient temperature is 55°C). To prevent burns, do not touch. If cables come into contact with the interlock switch, use heat-resistant cables. • The solenoid has polarity. Make sure of the correct polarity when wiring. Do not apply overvoltage, otherwise the solenoid will be burnt. • When wiring, make sure that water or oil does not enter from the end of the cable. 18 • Use dedicated actuators only. If other actuators are used, the interlock switch may be damaged. • When wiring to the terminal block using a screwdriver while holding the interlock switch in the hands, be careful not to damage fingers with the tip of the screwdriver. • Do not push in the screwdriver with excessive force when wiring to the terminal block. Internal parts may crack and cause damage. • Regardless of door types, do not use the interlock switch as a door stop. Install a mechanical door stop at the end of the door to protect the interlock switch against excessive force. • Safety function of the door interlock switch will be lost if a spare key is inserted into the interlock switch. Make sure that a spare key is not used on the interlock switch. • Do not cut or modify the actuator. Otherwise, damage may occur. • If multiple safety components are wired in series, the Performance Level to EN ISO 13849-1 will be reduced due to degradation of the failure detection function. • Insulation of the cable should withstand environmental influences. • The entire concept of the control system, in which the safety component is integrated, must be validated to EN ISO 13849-2. HS1T Interlock Switches with Solenoid Instructions Rotating the Head Rear Unlock Button and Mechanical Indicator • The rotating head has an allowable movement range. Do not turn the head exceed the movement range. Otherwise, damage may occur. • Tightening the head stopper screw withoug aligning the  marks indicated on the head and body and may cause damage • After installing the rear unlocking button, apply thread-locking adhesive to the screw so that the screw does not loosen. • Make sure that foreign objects do not enter between the head and body when rotating the head. • Make sure to tighten the head stopper screw securely. Loose screws may cause malfunction. • Do not loosen the head stopper screw other than when rotating the head. HS1T-L Manual Unlocking Rear unlock button Normal Position • When locking or unlocking the interlock switch manually, turn the key fully using the manual unlock key supplied with the interlock switch as shown below. Using the interlock switch with the key not fully turned (less than 90°) may cause damage to the interlock switch or operation failures. • When manually unlocked, the interlock switch will keep the main circuit disconnected and the door unlocked. Main circuit and lock monitor circuit remain open. Front manual unlock key hole Manual unlock key (supplied) LOCK Unlocked UNLOCK Normal Position LOCK UNLOCK Manual Unlocking Position HS1T-4 The HS1T-4 allows manual unlocking of the actuator to pre-check proper door operation before wiring or turning power on, as well as for emergency use such as a power failure. Manual Unlocking Position • Use the rear unlock button when a worker is locked inside a safety fence (hazard area). (Compliant with escape release described in EN ISO/ ISO 14119 [2003] and GS-ET-19) • When the rear unlock button is pressed, the interlock switch is unlocked and the door can be opened. • To lock the interlock switch, pull back the button. When the button remains pressed, the interlock switch cannot be locked even if the door is closed, and the main circuit remains open. • When the rear unlock button is pressed, the mechanical indicator is displayed on the side of the interlock switch. The lock status can be identified from outside the safety fence. • Install the rear unlock mechanical indicator on either side of the interlock switch. Notes • Install the rear unlock button inside the safety fence (hazardous area) where only the operator is accessible. Do not install where the rear unlock button can be reached by an operator outside the safety fence (hazardous area). Otherwise, the interlock switch may be unlocked during machine operation, causing danger. • Operate the rear unlock button by hand only. Do not use a tool or with excessive force. Do not apply force to the button from the direction other than the proper direction, otherwise the button will be damaged. HS1T-7Y The solenoid interlock switch does not unlock even when the solenoid is de-energized. However, the interlock switch can be unlocked manually in emergency cases. Notes • Before manually unlocking the interlock switch, make sure that the machine has come to a complete stop. Manual unlocking during operation may unlock the interlock switch before the machine stops, and the function of interlock switch with solenoid is lost. • On solenoid lock models, do not manually unlock while the solenoid is energized. • Do not apply excessive force (0.45 N·m or more) to the manual unlock key hole, otherwise the hole will be damaged. • Do not leave the manual unlock key attached to the interlock switch during operation. This is dangerous because the interlock switch can be unlocked while the machine is in operation. 19 www.idec.com Head Office 6-64, Nishi-Miyahara-2-Chome, Yodogawa-ku, Osaka 532-0004, Japan USA Germany Singapore Thailand Australia Taiwan IDEC Corporation APEM GmbH IDEC Izumi Asia Pte. Ltd. IDEC Asia (Thailand) Co., Ltd IDEC Australia Pty. Ltd. IDEC Taiwan Corporation Tel: +1-408-747-0550 Tel: +49-40-25 30 54 - 0 Tel: +65-6746-1155 Tel: +66-2-392-9765 Tel: +61-3-8523-5900 Tel: +886-2-2698-3929 opencontact@idec.com service@eu.idec.com info@sg.idec.com sales@th.idec.com sales@au.idec.com service@tw.idec.com Specifications and other descriptions in this catalog are subject to change without notice. Information in this catalog is current as of May 2019. 2019 IDEC Corporation, All Rights Reserved. EP1702-1 Hong Kong China/Shanghai China/Shenzhen China/Beijing Japan IDEC Izumi (H.K.) Co., Ltd. IDEC (Shanghai) Corporation IDEC (Shenzhen) Corporation IDEC (Beijing) Corporation IDEC Corporation Tel: +852-2803-8989 Tel: +86-21-6135-1515 Tel: +86-755-8356-2977 Tel: +86-10-6581-6131 Tel: +81-6-6398-2527 info@hk.idec.com idec@cn.idec.com idec@cn.idec.com idec@cn.idec.com marketing@idec.co.jp
HS1T-VD44ZSM-G. 价格&库存
很抱歉,暂时无法提供与“HS1T-VD44ZSM-G.”相匹配的价格&库存,您可以联系我们找货
