1000 Eaton Boulevard
Cleveland, OH 44122
United States
TAA-Compliant SmartPro 230V 3kVA 2.25kW
Line-Interactive Sine Wave UPS, Extended Run,
SNMP, Webcard, 2U Rack/Tower, USB, DB9
Serial
MODEL NUMBER: SMX3000RT2UTAA
Highlights
Federal Trade Agreements Act /
TAA Compliant for GSA
Schedule purchases
3kVA / 3000VA line interactive
2U rack/tower UPS; Sine wave
output
230V nominal output during
brownouts to 151V and
overvoltages to 282V
USB, RS232, EPO & optional
SNMP/Web card are available
for simultaneous use
Detailed status LEDs; 3
switched output load banks
C20 inlet; 8 C13 & 1 C19
outlets; Includes 3 C13 to C14
cables
Package Includes
Description
SMX3000RT2UTAA UPS
System
PowerAlert software with USB
and DB9 cables
Mounting hardware for 4 post
rackmount applications
Cable for Emergency Power Off
interface
Instruction manual with warranty
information
Tripp Lite's SMX3000RT2UTAA is compliant with the Federal Trade Agreements Act (TAA) for GSA
Schedule purchases. This intelligent, line interactive rack/tower uninterruptible power supply prevents data
loss, downtime and equipment damage due to power outages, voltage fluctuations and transient surges.
Requires only two rack spaces (2U) in a standard rack enclosure. Large internal batteries offer 11 minutes
half load runtime and 4 minutes at full load. Runtime is expandable with optional BP48V24-2U or
BP48V60RT-3U external battery packs. Maintains regulated 230V nominal output without using battery
power during brownouts and overvoltages from 151 to 282V. 3000VA/2250 watt power handling capability
and full time sine wave output offers guaranteed compatibility with networking, telecom and other sensitive
electronic applications. Includes a total of 9 outlets with 3 load banks that are individually switchable via
software interface to reboot select equipment on demand or shed less significant loads to extend battery
runtime for more critical equipment. Supports simultaneous remote monitoring of UPS and site power
conditions via built-in USB and DB9 monitoring ports. Includes PowerAlert UPS monitoring and
unattended shutdown software with complete cabling. Built-in accessory slot supports SNMP with optional
SNMPWEBCARD adapter. Emergency Power Off (EPO) interface offers option for instantaneous poweroff of UPS and connected equipment in the case of fire or emergency. Multi-function audible alarms and
set of 5 front panel LEDs offer at-a-glance notification of UPS and line power status. Network-grade AC
surge suppression protects equipment from damage and performance problems resulting from transient
surges and line noise. Attractive all-black color scheme.
Features
Compliant with the Federal Trade Agreements Act (TAA) for GSA Schedule purchases
SMX3000RT2UTAA line interactive UPS
3000VA/2250 watt power handling capability with sine wave output
1/6
Cleveland, OH 44122
United States
Supports 2U rackmount installation in 4 post equipment racks, 2 post rackmount installation requires
2POSTRMKITWM, upright tower installation requires 2-9USTAND accessory
Large internal batteries support a half load of 1500VA for 11 minutes and a full load of 3000VA for 4
minutes
Extended runtime is available with optional BP48V24-2U / BP48V242UTAA (limit 1) OR BP48V60RT3U
/ BP48V60RT3UTAA (no limit)
Some external battery configurations require the use of Tripp Lite's External Battery Configuration
Software (see manual)
Maintains regulated 230V nominal output during brownouts and overvoltages from 151 to 282V
Includes 9 UPS supported outlets arranged in 3 individually controllable load banks (2 outlets per bank)
that can be powered off and back on again via software interface
IEC320-C20 input connection accepts a variety of detachable cordsets to match country or site-specific
wall receptacles
PowerAlert UPS monitoring and unattended shutdown software enables configurable network broadcast
messaging, email notification, event logging and running user-defined script commands
Offers simultaneous monitoring through included USB and DB9 interface ports, or the monitoring by any
number of additional servers over IP
Emergency Power Off (EPO) interface with cable
Supports Tripp Lite's WatchDog software application (requires optional WATCHDOGSW)
Built-in accessory slot supports SNMP with optional SNMPWEBCARD adapter
Multi-function audible alarms and set of 5 front panel LEDs
Network-grade AC surge suppression
UPS battery set ships fully assembled, no time consuming connection of internal batteries by user is
necessary
Specifications
OVERVIEW
UPC Code
037332153364
UPS Type
Line-Interactive
INPUT
Nominal Input Voltage(s) Supported
230V AC
UPS Input Connection Type
C20 inlet
UPS Input Connection Description
IEC320-C20 input connection accepts a variety of detachable cordsets to match country or site-specific wall
receptacles
Input Circuit Breakers
20A
Input Phase
Single-Phase
OUTPUT
Output Capacity (VA)
3000
Output Capacity (kVA)
3
Output Capacity (Watts)
2250
2/6
Cleveland, OH 44122
United States
Output Capacity (kW)
2.2
Power Factor
0.8
Nominal Voltage Details
230v nominal inverter output voltage
Frequency Compatibility
50 / 60 Hz
Output Voltage Regulation (Line
Mode)
-15%, +8%
Output Voltage Regulation (Battery
Mode)
+/- 5%
Included Output Power Cables
Includes 3 C13 to C14 output power cables
Load Management Receptacles
Three switchable two-outlet C13 load banks
Output Circuit Breakers
10A (x2) - each breaker protects 4 C13 outlets, C19 outlet is unbreakered
Output AC Waveform (AC Mode)
Sine wave
Output AC Waveform (Battery
Mode)
Pure Sine wave
Nominal Output Voltage(s)
Supported
220V; 230V; 240V
Output Receptacles
(8) C13; (1) C19
Individually Controllable Load Banks
No
BATTERY
Runtime Full Load (min.)
4 min. (2250w)
Runtime Half Load (min.)
11 min. (1125w)
Expandable Runtime
Yes
External Battery Pack Compatibility
BP48V24-2U (limit 1); BP48V60RT-3U (multi-pack compatible)
DC System Voltage (VDC)
48
Battery Recharge Rate (Included
Batteries)
Less than 4.5 hours from 10% to 90%
Battery Access
Front panel battery access door
Internal UPS Replacement Battery
Cartridge
RBC94-2U
Battery Replacement Description
Hot-swappable, user replaceable batteries
VOLTAGE REGULATION
Voltage Regulation Description
Automatic voltage regulation (AVR) maintains line power operation with an input voltage range of 151 to 282
Overvoltage Correction
Input voltages between 245 and 282 are reduced by 12%
Undervoltage Correction
Input voltages between 181 and 199 are boosted by 12%
Severe Undervoltage Correction
Input voltages between 151 and 180 are boosted by 24%
3/6
Cleveland, OH 44122
United States
USER INTERFACE, ALERTS & CONTROLS
Switches
2 Switches control off/on power status and alarm-cancel/self-test operation
Alarm Cancel Operation
Power-fail alarm can be silenced using alarm-cancel switch; once silenced, alarm will re-sound to indicate lowbattery status
Audible Alarm
Audible alarm indicates power-failure, overload and low-battery conditions
LED Indicators
5 LEDs indicate line power, battery power, overload, voltage regulation and battery low/replace status
SURGE / NOISE SUPPRESSION
UPS AC Suppression Joule Rating
480
UPS AC Suppression Response
Time
Instantaneous
EMI / RFI AC Noise Suppression
Yes
PHYSICAL
Primary Form Factor
Rackmount
Rack Height
2U
Cooling Method
Fan
Installation Form Factors Supported
with Included Accessories
4 post 19 inch rackmount
with Optional Accessories
2 post rackmount ( 2POSTRMKITWM ); Wallmount
( 2POSTRMKITWM ); Tower ( 29USTAND )
Primary UPS Depth (mm)
483
Primary UPS Height (mm)
89
Primary UPS Width (mm)
445
Shipping Dimensions (hwd / in.)
9.00 x 23.50 x 20.00
Shipping Dimensions (hwd / cm)
22.86 x 59.69 x 50.80
Shipping Weight (lbs.)
72.60
Shipping Weight (kg)
32.93
UPS Housing Material
Steel
UPS Power Module Dimensions
(hwd, cm)
8.89 x 44.45 x 48.26
(hwd, in.)
3.5 x 17.5 x 19
UPS Power Module Weight (kg)
29.03
UPS Power Module Weight (lbs.)
64
ENVIRONMENTAL
4/6
Cleveland, OH 44122
United States
Operating Temperature Range
+32 to +104 degrees Fahrenheit / 0 to +40 degrees Celsius
Storage Temperature Range
+5 to +122 degrees Fahrenheit / -15 to +50 degrees Celsius
Relative Humidity
0 to 95%, non-condensing
AC Mode BTU / Hr. (Full Load)
236.6
Battery Mode BTU / Hr. (Full Load)
1245.3
AC Mode Efficiency Rating (100%
Load)
97%
COMMUNICATIONS
Network Monitoring Port Description
Supports detailed monitoring of UPS and site power conditions; 1 USB port, 1 DB9 serial and 1 SNMP accessory
slot.
PowerAlert Software
Included
Communications Cable
USB and DB9 and EPO cabling included
WatchDog Compatibility
Supports Watchdog application, OS and hard-reboot restart options for remote applications
Communications Interface
USB (HID enabled); DB9 Serial; EPO (emergency power off); Slot for SNMP/Web interface
LINE / BATTERY TRANSFER
Transfer Time
2-4 milliseconds
Low Voltage Transfer to Battery
Power (Setpoint)
151
High Voltage Transfer to Battery
Power (Setpoint)
282
FEATURES & SPECIFICATIONS
Cold Start (Startup in Battery Mode
During a Power Failure)
Cold-start operation supported
High Availability UPS Features
Hot swappable batteries
Green Energy-Saving Features
Greater than 95% efficiency - GREEN UPS; Individually controllable load banks
Grounding Lug
Back panel grounding lug
WARRANTY & SUPPORT
Product Warranty Period
(International)
2-year limited warranty
Product Warranty Period (Mexico)
Product Warranty Period (Puerto
Rico)
5/6
Cleveland, OH 44122
United States
© 2023 Eaton. All Rights Reserved.
Eaton is a registered trademark. All other trademarks
are the property of their respective owners.
6/6
很抱歉,暂时无法提供与“SMX3000RT2UTAA”相匹配的价格&库存,您可以联系我们找货