1000 Eaton Boulevard
Cleveland, OH 44122
United States
SmartOnline 208/240 & 120V 6kVA 5.4kW DoubleConversion UPS, 6U Rack/Tower, Extended Run,
Network Card Options, USB, DB9 Serial, Bypass
Switch, Outlets
MODEL NUMBER: SU6000RT4UTF
Highlights
6000VA / 6kVA / 5400W on-line
double-conversion 4U
rack/tower UPS, Sine Wave
Includes 4U UPS power module
with maintenance bypass switch
and 2U transformer module
Extended runtime options,
Interactive LCD interface,
Economy-mode option, 0.9
power factor
USB, RS232 & EPO ports; Slot
for network management card
options
NEMA L6-30P 208/240V 60Hz
input; NEMA L6-30R, L6-20R
(208/240V), 5-15/20R and 515R (120V) outlets
Package Includes
Description
Featuring true on-line operation with pure sine wave output, zero transfer time to battery and complete
UPS replacement capability with no downtime, the SU6000RT4UTF provides the highest level of
protection available for mission-critical equipment from all power problems. It converts incoming AC power
to DC, and re-converts it back to filtered AC output with a pure sine wave, providing ultimate protection.
The SU6000RT4UTF has a 6kVA/5400W capacity and 16 AC outlets (4 5-15R; 8 5-15/20R; 2 L6-20R; 2
L6-30R). Using the 2U transformer, the SU6000RT4UTF can support both low- and high-voltage
equipment.
With its detachable PDU, the SU6000RT4UTF is easily hot-swappable by a user of any skill set—no need
for lengthy and expensive service calls, and no downtime if a repair or battery replacement is needed. In
bypass mode, the PDU passes power to equipment without the use of the power and battery modules,
allowing them to be removed while keeping your application in operation.
UPS battery backup keeps connected equipment operational through short power failures, and provides
time to save data and perform an orderly system shutdown in case of a prolonged blackout. The
SU6000RT4UTF’s runtime can be expanded with external battery packs.
The SU6000RT4UTF features a highly efficient (96%) economy mode setting that can significantly reduce
a facility's energy costs by minimizing heat output, reducing cooling requirements and consuming less
electricity.
An LCD display with LED indicators enables IT personnel to monitor operating modes and conditions. The
LCD/LED panel rotates for viewing in horizontal rack or vertical tower installations and includes an audible
alarm that signals various conditions.
The SU6000RT4UTF features a USB port and a DB9 port that, when used with Tripp Lite's downloadable
PowerAlert software, provides comprehensive network power monitoring and control. An optional network
management card enables the UPS to operate as an IP managed device.
The unit requires only 6U of rack space in a standard rack enclosure and can be installed in a 2-post rack
using the 2POSTRMKITHD accessory (2 required), or in a tower configuration with the 2-9USTAND
accessory.
Features
Tripp Lite SU6000RT4UTF 6000VA / 6kVA / 5400 watt on-line, double-conversion UPS system in a 6U
rack/tower compatible configuration (4U power module plus 2U low-voltage transformer; at 208V
nominal, output is limited to 4992 watts)
Full-time active power conditioning maintains clean, continuous dual-conversion AC output free of
1/7
SU6000RT4UHVPM hot
swappable UPS Power Module
SUPDMB6K Detachable PDU
with Maintenance Bypass
Switch
SU6000XFMR2U low voltage
transformer
1 x 6-ft. USB Cable
1 x 6-ft. DB9 Cable
4-Post Rackmount Hardware (2
sets)
Cleveland, OH 44122
United States
voltage fluctuations, power interruptions and line noise
Fault tolerant electronic bypass maintains utility output during a variety of UPS fault conditions
Detachable back panel PDU contains input line cord connection, output receptacles and manual bypass
switch to support hot-swappable whole UPS replacement with no interruption to connected equipment
L6-30P input plug
UPS supported outlets include two L6-30R, two L6-20R, 8 5-15/20R and 4 5-15R outlets
Included rail kit supports 4U 19 inch rackmount installation in 4 post racks
Optional 2POSTRMKITHD supports installation in 2 post 19 inch racks (2 required for SU6000RT4UTF)
Optional 2-9USTAND supports upright tower placement (1 required for SU6000RT4UTF)
Maximum installed rack depth of only 21.8 in. / 55.3 cm
Maintains full-time sine wave output within 2% of selected 208/240V and 120V nominal at 60Hz in
double conversion mode
Corrects brownouts to 156V at full load (100V at 50% load or less)
Corrects overvoltages to 290V at full load (300V at 90% load or less)
Double-conversion operation offers full-time AC to DC, then DC to AC conversion to maintain perfectly
regulated sine wave AC output with enhanced protection from harmonic distortion, fast electrical
impulses and other hard-to-solve power problems not addressed by other UPS types
High efficiency ECONOMY MODE operation significantly reduces BTU heat output and operating
energy costs
Network-grade AC surge and noise suppression
Supports detailed monitoring of equipment load levels, self-test data and utility power conditions via
built-in RS-232, USB and optional network management card options
Compatible with Tripp Lite UPS management card options TLNETCARD, WEBCARDLX,
SNMPWEBCARD, MODBUSCARD and RELAYIOCARD
Optional RELAYIOMINI interface module offers three configurable hard contact closure outputs for
custom event notification (requires removal of USB interface module)
HID-compliant USB interface enables integration with built-in power management and auto shutdown
features of Windows and Mac OS X
USB & Serial ports enable data-saving unattended shutdown when used with Tripp Lite's PowerAlert
software, available via FREE download from tripplite.eaton.com/products/power-alert
Front panel LEDs and LCD readout with scroll controls support front-panel visual monitoring of all major
UPS functions with support for a variety of control options to support advanced UPS settings and
configurations
LED/LCD display panel rotates for viewing in rackmount or tower configurations
Supports Emergency Power Off (EPO) via built-in interface
Battery independent restart ensures automatic UPS power-up without user interaction after lengthy
power outages, even when batteries are expired and require replacement
BP192V12-3U external battery packs are field replaceable and hot swappable
Intelligent battery management system with temperature-compensated charging extends battery life
Some external battery configurations require the use of Tripp Lite's External Battery Configuration
Software (see manual)
Specifications
OVERVIEW
UPC Code
037332157102
UPS Type
On-Line
2/7
Cleveland, OH 44122
United States
INPUT
Input Phase
Single-Phase
Rated input current (Maximum Load)
31.9A (200V), 30.6A (208V), 29A (220V), 27.7A (230V), 26.6A (240V)
Nominal Input Voltage(s) Supported
208V AC; 240V AC
Nominal Input Voltage Description
Factory configured to 208V
UPS Input Connection Type
L6-30P
UPS Input Cord Length (ft.)
10
UPS Input Cord Length (m)
3.1
Recommended Electrical Service
30A
OUTPUT
Output Capacity (VA)
6000
Output Capacity (kVA)
6
Output Capacity (Watts)
5400
Output Capacity (kW)
5.4
Output Capacity Details
Output capacity de-rates to 4992 watts when used at 208V nominal; Supports up to 105% load continuously in
double conversion mode, 106 to 125% for 1 minute, 126% to 150% for 30 seconds; Loads over 150% trigger
immediate bypass mode operation to support loads directly from mains power; Double conversion mode is
automatically restored as the overload is cleared
Power Factor
.9
Crest Factor
3:1
Nominal Voltage Details
This configuration requires the Power Module be set to 208 or 240V output voltage; included step-down transformer
supports 120V output (when the voltage-selection switch on the transformer module is set to match the 208 or 240V
power module setting)
Frequency Compatibility
60 Hz
Frequency Compatibility Details
Output frequency regulation +/-0.05Hz (free running)
Output Voltage Regulation (Line
Mode)
+/- 2%
(Economy Line Mode)
+/- 10%
Output Voltage Regulation (Battery
Mode)
+/- 2%
Output Receptacle Details
Output receptacles and input line cord are mounted on a detachable PDU backplate with bypass switch to enable
hot-swappable power module replacement
Output Circuit Breakers
High voltage 20A breaker protects L6-20R outlets, L6-30R outlets are unbreakered; Low voltage 20A breakers
protect 4 5-15/20R outlets each; Low voltage 15A breakers protect 2 5-15/20R outlets each
Output AC Waveform (AC Mode)
Pure Sine wave
Output AC Waveform (Battery
Mode)
Pure Sine wave
Nominal Output Voltage(s)
Supported
120V; 208V; 240V
3/7
Cleveland, OH 44122
United States
Output Receptacles
(4) 5-15R; (8) 5-15/20R; (2) L6-20R; (2) L6-30R
Individually Controllable Load Banks
No
BATTERY
Battery Type
Valve Regulated Lead Acid (VRLA)
Runtime Full Load (min.)
2 min. (5400W)
Runtime Half Load (min.)
8.5 min. (2700W)
Expandable Runtime
Yes
External Battery Pack Compatibility
BP192V1037C-1PH; BP192V12-3U ; BP192V1407C-1PH;
BP192V557C-1PH; BP192V787C1PH ; BP192V5RT2U (limit 1)
DC System Voltage (VDC)
192
Battery Recharge Rate (Included
Batteries)
6 hours from 10% to 90% (typical, full load discharge)
Battery Access
Front panel battery access door
Internal UPS Replacement Battery
Cartridge
RBC5-192
Battery Replacement Description
Hot-swappable, user replaceable batteries
VOLTAGE REGULATION
Voltage Regulation Description
Online, double-conversion power conditioning
Overvoltage Correction
Corrects overvoltages as high as 300V (