1000 Eaton Boulevard
Cleveland, OH 44122
United States
SmartOnline 120V 1500VA 1.35kW DoubleConversion UPS - 6 Outlets, Extended Run, Card
Slot, LCD, USB, DB9, 2U
Highlights
Offers network-grade protection
against power failures and
voltage fluctuations
Zero transfer time between online and battery modes for
uninterrupted operation
Optional external battery packs
provide additional runtime for
applications requiring it
Optional WEBCARDLX network
interface required to use Auto
Probe feature
ENERGY STAR-certified to
save electricity, lower costs, and
protect the environment
MODEL NUMBER: SU1500RTXLCD2U
Applications
On-line double-conversion UPS provides pure sine wave AC output to server and network equipment in
data centers and computer rooms.
Deliver perfectly regulated sine
wave output to mission-critical
equipment
Protect connected components
from dangerous surges, spikes
and line noise
Keep equipment operational
through power failures
Allow time to save data and
safely shut down components in
case of a prolonged blackout
Features
Double-Conversion UPS Protects Equipment against Damage, Downtime and Data Loss
This 100/110/120/127V 50/60 Hz UPS system with IGBT technology maintains perfect output by
converting AC input to DC, then reconverting UPS output to fully regulated sine wave AC with +/-2%
voltage regulation in online and battery modes. Featuring a 1350W capacity, high 0.9 power factor, 570
joules of surge suppression, true on-line operation with pure sine wave output and zero transfer to battery
mode in on-line double-conversion mode, the SmartOnline® SU1500RTXLCD2U double-conversion UPS
provides the highest level of AC power protection and battery backup for critical network closet, computer
room and data center equipment.
Individually Controllable Load Banks Let You Access and Control Outlets Remotely
Six NEMA 5-15R outlets are split evenly into two switchable three-outlet load banks, allowing you to
reboot select components or shed loads remotely.
Reliable, Expandable Battery Backup Keeps You Operational Through Power Outages
The field-replaceable, hot-swappable internal battery provides 14 minutes of support at half load (675W)
and 4.2 minutes at full load (1350W), keeping protected equipment operational through power failures. For
mission-critical applications demanding scalable extended runtime, the UPS supports external battery
packs, such as Tripp Lite's BP48V24-2U (sold separately). The intelligent battery management system
with temperature-compensated charging extends battery life.
ENERGY STAR-Certified Economy Mode Helps You Save Money and Protect the Environment
By meeting strict EPA efficiency guidelines, this ENERGY STAR-certified UPS system helps you save
money and energy. A power-saving Economy mode setting option offers enhanced efficiency and reduced
BTU output when utility power is already high quality.
Automatically Turns Back On After Power Is Restored
Battery-independent restart ensures automatic UPS power-up without user interaction after lengthy power
outages, even when batteries are expired and require replacement.
Intuitive Front-Panel Interface for Convenient UPS Operation and Monitoring
1/7
Package Includes
SU1500RTXLCD2U
SmartOnline Double-Conversion
UPS
USB cable
RS-232 cable
EPO cable
4-post rack-mounting hardware
Owner’s manual
Cleveland, OH 44122
United States
The front-panel LCD features nine selectable screens of UPS data (including load, voltage and battery
data) and 16 screens of configuration and setup options. LEDs indicate line power availability, AC to DC
conversion, battery mode operation, inverter mode, ECO mode operation, bypass mode operation and AC
output status.
Advanced Communications Ports Allow for Automatic Saves and Shutdowns
RS-232 and HID-compliant USB ports connect to a computer running Tripp Lite's free downloadable
PowerAlert® software to enable safe unattended file saves and system shutdown in case of a prolonged
power failure. An EPO port connects the UPS to a contact closure switch to enable emergency inverter
shutdown. Cables are included.
Optional WEBCARDLX Network Interface Offers 24/7 Access
The SU1500RTXLCD2U includes a slot for an optional Java-free HTML5-based WEBCARDLX (sold
separately) that enables full remote access for site power and UPS status monitoring, configuration,
control and email notifications via secure web browser, SNMP, telnet or SSH. It supports 10/100 Mbps
auto-sensing for optimum communication with an Ethernet network. Automated alerts help prevent
accidental overloads, power loss and downtime. WEBCARDLX 15.5.2 or later is required to use the Auto
Probe feature, which can prevent costly service calls by automatically rebooting non-responsive network
devices.
Versatile Installation Options
Hardware is included for mounting the UPS system in 2U of space in an EIA-standard 19-inch 4-post rack.
Use the optional 2POSTRMKITWM (sold separately) for 2-post rack mounting or the optional 2-9USTAND
(sold separately) for mounting in an upright tower position. The 10-ft. (3.05 m) power cord with NEMA 520P plug connects to any compatible AC outlet.
Specifications
OVERVIEW
UPC Code
037332168610
UPS Type
On-Line
INPUT
Input Phase
Single-Phase
Rated input current (Maximum Load)
12A
Nominal Input Voltage(s) Supported
100V AC; 110V AC; 115V AC; 120V AC; 127V AC
Nominal Input Voltage Description
120V factory default
UPS Input Connection Type
5-15P
Input Circuit Breakers
20A
UPS Input Cord Length (ft.)
10
UPS Input Cord Length (m)
3.1
Recommended Electrical Service
15A 120V
OUTPUT
Output Capacity (VA)
1500
Output Capacity (kVA)
1.5
2/7
Cleveland, OH 44122
United States
Output Capacity (Watts)
1350
Output Capacity (kW)
1.35
Output Capacity Details
ON LINE MODE: Maximum output capacity ratings is reduced to 1215 watts at 115V nominal and 1080 watts at
100V nominal; FREQUENCY REGULATION / CONVERSION MODE: Maximum output ratings are reduced in
frequency regulation / conversion mode (127/120V 945 watts / 115V 850 watts / 110V 804 watts / 100V 756 watts)
OVERLOAD CAPACITY: Supports inverter operation up to 105% load continuously, 125% load for 3 minutes; 150%
load for 30 seconds and >150% load for 0.5 seconds before switching to BYPASS (when bypass input voltage and
frequency are WITHIN bypass limits) or SHUTDOWN (when bypass input voltage or frequency are OUTSIDE
bypass limits)
Power Factor
0.9
Crest Factor
3:1
Nominal Voltage Details
120V factory-default nominal voltage; Less than 3% THD for linear loads and less than 5% for non-linear computer
loads
Frequency Compatibility
50 / 60 Hz; Supports 50 to 60 Hz and 60 to 50 Hz conversion
Frequency Compatibility Details
ON LINE MODE: Output frequency is automatically configured to match nominal input frequency on startup; Output
matches input frequency when +/-5Hz of nominal; Output is regulated to +/-0.05Hz when input frequency exceeds
+/-5Hz of nominal. UPS switches to battery mode when input frequency is below 40Hz or above 70Hz.
FREQUENCY REGULATION / CONVERSION MODE: Output is regulated to +/-0.05Hz of selected output frequency
input is 40 to 70Hz; UPS switches to battery mode when input frequency is below 40Hz or above 70Hz. BATTERY
MODE: Output is regulated to +/-0.05Hz.
Output Voltage Regulation (Line
Mode)
+/- 2%
(Economy Line Mode)
+/- 10%
Output Voltage Regulation (Battery
Mode)
+/- 3%
Load Management Receptacles
Two switchable three-outlet 5-15R load banks
Output AC Waveform (AC Mode)
Pure Sine wave
Output AC Waveform (Battery
Mode)
Pure Sine wave
Nominal Output Voltage(s)
Supported
100V; 110V; 115V; 120V; 127V
Output Receptacles
(6) 5-15R
Yes
BATTERY
Battery Type
Valve Regulated Lead Acid (VRLA)
Runtime Full Load (min.)
4.2 min. (1350W)
Runtime Half Load (min.)
14 min. (675W)
Expandable Runtime
Yes
Expandable Runtime Description
Some external battery configurations require the use of Tripp Lite's External Battery Configuration Software, see
manual for details
External Battery Pack Compatibility
BP48V24-2U (limit 1); BP48V60RT-3U (multi-pack compatible); BP48V272US (multi-pack compatible)
3/7
Cleveland, OH 44122
United States
DC System Voltage (VDC)
48
Battery Recharge Rate (Included
Batteries)
Less than 3 hours recharge to 90%; Add 6 hours per BP48V27-2US (typical, full load discharge)
Battery Access
Front panel battery access
Internal UPS Replacement Battery
Cartridge
RBC94-2U
Battery Replacement Description
Hot-swappable, user replaceable batteries
VOLTAGE REGULATION
Voltage Regulation Description
Online, double-conversion power conditioning maintains 2% output voltage regulation during brownouts and
overvoltages
Overvoltage Correction
Corrects overvoltages to 150V (0-100% load)
Undervoltage Correction
Corrects undervoltages to 100V at full load (90V at 100V nominal)
Severe Undervoltage Correction
Corrects brownouts to 70V (70% load) & 55V (33% load)
USER INTERFACE, ALERTS & CONTROLS
Front Panel LCD Display
Front panel LCD information and configuration screen offers detailed UPS and site power status and operating data,
plus configuration of voltage, frequency, operating mode, alarm function and a variety of additional options
Switches
2 switches control off/on power status and alarm-cancel operation; 2 additional scroll-down and scroll-up / select
options enable LCD status viewing and configuration options
Alarm Cancel Operation
Power-fail alarm can be temporarily silenced using alarm-cancel switch; silent mode alarm configuration option
available
Audible Alarm
Audible alarm indicates UPS startup, power-failure, low-battery, overload, UPS fault and remote shutdown
conditions
LED Indicators
7 front panel LEDs indicate line power availability, AC to DC conversion, battery mode operation, inverter mode, eco
mode operation, bypass mode operation and AC output status
SURGE / NOISE SUPPRESSION
UPS AC Suppression Joule Rating
570
UPS AC Suppression Response
Time
Instantaneous
UPS Dataline Suppression
1 line TEL/DSL (1 in / 1 out); 10/100Base T Ethernet
EMI / RFI AC Noise Suppression
Yes
PHYSICAL
Primary Form Factor
Rackmount
Rack Height
2U
Cooling Method
Fan
Included Mounting Accessory
Description
Included 4POSTRAILKIT mounting bracket enables installation in 4 post racks from 20.5 to 36 inches (521 to
914mm)
Installation Form Factors Supported
with Included Accessories
4 post 19 inch rackmount
4/7
Cleveland, OH 44122
United States
with Optional Accessories
2 post rackmount ( 2POSTRMKITWM ); Wallmount
( 2POSTRMKITWM ); Tower ( 29USTAND )
Minimum Required Rack Depth (cm)
55.88
(inches)
22
Minimum Required Rack Depth with
External Battery Pack (cm)
65
External Battery Pack (in.)
25.5
without External Battery Pack (cm)
55
without External Battery Pack (in.)
21.5
Optional Mounting Accessory Notes
Optional 2-9USTAND enables upright tower UPS placement; 2POSTRMKITWM enables wall-mount and 2-post rackmount installation;
4POSTRAILKITWM enables installation in 4-post short-depth
racks from 14.5 to 23.5 inches (368 to 597mm); UPSHDEARKIT enables installation in 2 or 4-post
racks using front vertical rails only, without rear support
Primary UPS Depth (mm)
470
Primary UPS Height (mm)
89
Primary UPS Width (mm)
445
Shipping Dimensions (hwd / in.)
9.20 x 23.30 x 19.20
Shipping Dimensions (hwd / cm)
23.37 x 59.18 x 48.77
Shipping Weight (lbs.)
63.75
Shipping Weight (kg)
28.92
UPS Housing Material
Steel
UPS Power Module Dimensions
(hwd, cm)
8.89 x 44.45 x 46.99
(hwd, in.)
3.5 x 17.5 x 18.5
UPS Power Module Weight (kg)
20.50
UPS Power Module Weight (lbs.)
45.2
Unit Dimensions (hwd / in.)
3.500 x 17.500 x 18.500
Unit Weight (lbs.)
45.200
Unit Weight (kg)
20.50
ENVIRONMENTAL
Operating Temperature Range
32° to 104°F (0° to 40°C)
5/7
Cleveland, OH 44122
United States
Storage Temperature Range
5° to 122°F (-20° to 40°C) with batteries; -13° to 131°F (-25° to 55°C) without batteries
Relative Humidity
0 to 95%, non-condensing
AC Mode BTU / Hr. (Full Load)
455
AC Economy Mode BTU / Hr. (Full
Load)
294
Battery Mode BTU / Hr. (Full Load)
559
AC Economy Mode Efficiency Rating
(100% Load)
94%
Audible Noise
45 dBA at 1m front side
Operating Elevation (m)
Up to 3000m
COMMUNICATIONS
Network Management Cards
SNMPWEBCARD; TLNETCARD ; WEBCARDLX ; MODBUSCARD ; RELAYIOCARD
Network Monitoring Port Description
Supports detailed monitoring of UPS and site power conditions; DB9 port supports RS232 and contact closure
communications
PowerAlert Software
For local monitoring via the UPS’s built-in communication ports, download PowerAlert software at
https://tripplite.eaton.com/products/power-alert
Communications Cable
USB and DB9 cabling included
WatchDog Compatibility
Supports Watchdog application, OS and hard-reboot restart options for remote applications
Description
Network management card optional
Communications Interface
Contact closure; DB9 Serial; EPO (emergency power off); Slot for SNMP/Web interface; USB (HID enabled)
LINE / BATTERY TRANSFER
Transfer Time
Zero (0 milliseconds) in double-conversion mode; 4 milliseconds economy mode
Low Voltage Transfer to Battery
Power (Setpoint)
100V at full load (90V full load at 100V nominal setting); 70V at 70% load; 55V at 33% load
High Voltage Transfer to Battery
Power (Setpoint)
150
FEATURES & SPECIFICATIONS
Cold Start (Startup in Battery Mode
During a Power Failure)
Cold-start operation supported
High Availability UPS Features
Auto Probe Monitoring and Reboot (requires WEBCARDLX); Automatic inverter bypass; Hot swappable batteries;
Remote management; Surge/noise protection; Zero transfer time
Green Energy-Saving Features
High efficiency economy mode operation; Individually controllable load banks; Schedulable daily hours of economy
mode operation
STANDARDS & COMPLIANCE
Product Certifications
CSA (Canada); UL 1778
6/7
Cleveland, OH 44122
United States
Product Compliance
RoHS; ENERGY STAR Qualified; FCC Part 15 Class A (USA)
WARRANTY & SUPPORT
Product Warranty Period
(Worldwide)
2-year limited warranty
Connected Equipment Insurance
(U.S., Canada & Puerto Rico)
$250,000 Ultimate Lifetime
Insurance
© 2023 Eaton. All Rights Reserved.
Eaton is a registered trademark. All other trademarks
are the property of their respective owners.
7/7
