1000 Eaton Boulevard
Cleveland, OH 44122
United States
Eaton Tripp Lite series SmartOnline 120V
2200VA 1.8kW Double-Conversion UPS - 7
Outlets, Extended Run, Card Slot, LCD, USB,
DB9, 2U
MODEL NUMBER: SU2200RTXLCD2U
Highlights
Offers network-grade protection
against power failures and
voltage fluctuations
Zero transfer time between online and battery modes for
uninterrupted operation
Optional external battery packs
provide additional runtime for
applications requiring it
Optional WEBCARDLX network
interface required to use Auto
Probe feature
ENERGY STAR-certified to
save electricity, lower costs, and
protect the environment
Applications
On-line double-conversion UPS provides pure sine wave AC output to server and network equipment in
data centers and computer rooms.
Deliver perfectly regulated sine
wave output to mission-critical
equipment
Protect connected components
from dangerous surges, spikes
and line noise
Keep equipment operational
through power failures
Allow time to save data and
safely shut down components in
case of a prolonged blackout
Features
Double-Conversion UPS Protects Equipment against Damage, Downtime and Data Loss
This 100/110/120/127V 50/60 Hz UPS system with IGBT technology maintains perfect output by
converting AC input to DC, then reconverting UPS output to fully regulated sine wave AC with +/-2%
voltage regulation in online and battery modes. Featuring a 1800W capacity, high 0.8 power factor, 570
joules of surge suppression, true on-line operation with pure sine wave output and zero transfer time to
battery mode in on-line double-conversion mode, the SmartOnline® SU2200RTXLCD2U doubleconversion UPS provides the highest level of AC power protection and battery backup for critical network
closet, computer room and data center equipment.
Individually Controllable Load Banks Let You Access and Control Outlets Remotely
Six NEMA 5-15/20R outlets are split evenly into two switchable three-outlet load banks, allowing you to
reboot select components or shed loads remotely. In addition to those six outlets, this UPS provides one
unswitched NEMA L5-20R outlet for powering a critical component or in-rack PDU.
Reliable, Expandable Battery Backup Keeps You Operational Through Power Outages
The field-replaceable, hot-swappable internal battery provides 12 minutes of support at half load (900W)
and four minutes at full load (1800W), keeping protected equipment operational through power failures.
For mission-critical applications demanding scalable extended runtime, the UPS supports external battery
packs, such as Tripp Lite's BP48V24-2U (sold separately). The intelligent battery management system
with temperature-compensated charging extends battery life.
ENERGY STAR-Certified Economy Mode Helps You Save Money and Protect the Environment
By meeting strict EPA efficiency guidelines, this ENERGY STAR-certified UPS system helps you save
money and energy. A power-saving Economy mode setting option offers enhanced efficiency and reduced
BTU output when utility power is already high quality.
Set Output Frequency to Match That of Your Connected Equipment
Using the UPS in Frequency Conversion mode will correct or convert the incoming frequency of 50 Hz to
output 60 Hz (and vice versa).
1/7
Package Includes
SU2200RTXLCD2U
SmartOnline Double-Conversion
UPS
USB cable
RS-232 cable
EPO cable
4-post rack-mounting hardware
Owner’s manual
Cleveland, OH 44122
United States
Intuitive Front-Panel Interface for Convenient UPS Operation and Monitoring
The front-panel LCD features nine selectable screens of UPS data (including load, voltage and battery
data) and 16 screens of configuration and setup options. LEDs indicate line power availability, AC to DC
conversion, battery mode operation, inverter mode, ECO mode operation, bypass mode operation and AC
output status.
Advanced Communications Ports Allow for Automatic Saves and Shutdowns
RS-232 and HID-compliant USB ports connect to a computer running Tripp Lite's free downloadable
PowerAlert® software to enable safe unattended file saves and system shutdown in case of a prolonged
power failure. An EPO port connects the UPS to a contact closure switch to enable emergency inverter
shutdown. Cables are included.
Optional WEBCARDLX Network Interface Offers 24/7 Access
The SU2200RTXLCD2U includes a slot for an optional Java-free HTML5-based WEBCARDLX (sold
separately) that enables full remote access for site power and UPS status monitoring, configuration,
control and email notifications via secure web browser, SNMP, telnet or SSH. It supports 10/100 Mbps
auto-sensing for optimum communication with an Ethernet network. Automated alerts help prevent
accidental overloads, power loss and downtime. WEBCARDLX 15.5.2 or later is required to use the Auto
Probe feature, which can prevent costly service calls by automatically rebooting non-responsive network
devices.
Versatile Installation Options
Hardware is included for mounting the UPS system in 2U of space in an EIA-standard 19-inch 4-post rack.
Use the optional 2POSTRMKITWM (sold separately) for 2-post rack mounting or the optional 2-9USTAND
(sold separately) for mounting in an upright tower position. The 10-ft. (3.05 m) power cord with NEMA 520P plug connects to any compatible AC outlet.
Specifications
OVERVIEW
UPC Code
037332168955
UPS Type
On-Line
INPUT
Input Phase
Single-Phase
Rated input current (Maximum Load)
16A
Nominal Input Voltage(s) Supported
100V AC; 110V AC; 115V AC; 120V AC; 127V AC
Nominal Input Voltage Description
120V factory default
UPS Input Connection Type
5-20P
Input Circuit Breakers
30A
UPS Input Cord Length (ft.)
10
UPS Input Cord Length (m)
3.1
Recommended Electrical Service
20A 120V
OUTPUT
Output Capacity (VA)
2200
2/7
Cleveland, OH 44122
United States
Output Capacity (kVA)
2.2
Output Capacity (Watts)
1800
Output Capacity (kW)
1.8
Output Capacity Details
ON LINE MODE: Maximum output capacity is reduced to 1620 watts at 115V nominal and 1440 watts at 100V
nominal; FREQUENCY REGULATION / CONVERSION MODE: Maximum output ratings are reduced in frequency
regulation / conversion mode (127/120V 1260 watts / 115V 1134 watts / 110V 1071 watts / 100V 1008 watts)
OVERLOAD CAPACITY: Supports inverter operation up to 105% load continuously, 125% load for 3 minutes; 150%
load for 30 seconds and >150% load for 0.5 seconds before switching to BYPASS (when bypass input voltage and
frequency are WITHIN bypass limits) or SHUTDOWN (when bypass input voltage or frequency are OUTSIDE
bypass limits)
Power Factor
0.82
Crest Factor
3:1
Nominal Voltage Details
120V factory-default nominal voltage
Frequency Compatibility
50 / 60 Hz; Supports 50 to 60 Hz and 60 to 50 Hz conversion
Frequency Compatibility Details
ON LINE MODE: Output frequency is automatically configured to match nominal input frequency on startup; Output
matches input frequency when +/-5Hz of nominal; Output is regulated to +/-0.05Hz when input frequency exceeds
+/-5Hz of nominal. UPS switches to battery mode when input frequency is below 40Hz or above 70Hz.
FREQUENCY REGULATION / CONVERSION MODE: Output is regulated to +/-0.05Hz of selected output frequency
input is 40 to 70Hz; UPS switches to battery mode when input frequency is below 40Hz or above 70Hz. BATTERY
MODE: Output is regulated to +/-0.05Hz.
Output Voltage Regulation (Line
Mode)
+/- 2%
(Economy Line Mode)
+/- 10%
Output Voltage Regulation (Battery
Mode)
+/- 3%
Load Management Receptacles
Two switchable three-outlet 5-15/20R load banks
Output AC Waveform (AC Mode)
Pure Sine wave
Output AC Waveform (Battery
Mode)
Pure Sine wave
Nominal Output Voltage(s)
Supported
100V; 110V; 115V; 120V; 127V
Output Receptacles
(6) 5-15/20R; (1) L5-20R
Yes
BATTERY
Battery Type
Valve Regulated Lead Acid (VRLA)
Runtime Full Load (min.)
4 min. (1800W)
Runtime Half Load (min.)
12 min. (900W)
Expandable Runtime
Yes
Expandable Runtime Description
Some external battery configurations require the use of Tripp Lite's External Battery Configuration Software, see
manual for details
3/7
Cleveland, OH 44122
United States
External Battery Pack Compatibility
BP48V24-2U (limit 1); BP48V60RT-3U (multi-pack compatible); BP48V272US (multi-pack compatible)
DC System Voltage (VDC)
48
Battery Recharge Rate (Included
Batteries)
Less than 3 hours recharge to 90% (typical, full load discharge)
Battery Access
Front panel battery access
Internal UPS Replacement Battery
Cartridge
RBC94-2U
Battery Replacement Description
Hot-swappable, user replaceable batteries
VOLTAGE REGULATION
Voltage Regulation Description
Online, double-conversion power conditioning maintains 2% output voltage regulation during brownouts and
overvoltages
Overvoltage Correction
Corrects overvoltages to 150V (0-100% load)
Undervoltage Correction
Corrects undervoltages to 100V at full load (90V at 100V nominal)
Severe Undervoltage Correction
Corrects brownouts to 70V (70% load) & 55V (33% load)
USER INTERFACE, ALERTS & CONTROLS
Front Panel LCD Display
Front panel LCD information and configuration screen offers detailed UPS and site power status and operating data,
plus configuration of voltage, frequency, operating mode, alarm function and a variety of additional options
Switches
2 switches control off/on power status and alarm-cancel operation; 2 additional scroll-down and scroll-up / select
options enable LCD status viewing and configuration options
Alarm Cancel Operation
Power-fail alarm can be temporarily silenced using alarm-cancel switch; silent mode alarm configuration option
available
Audible Alarm
Audible alarm indicates UPS startup, power-failure, low-battery, overload, UPS fault and remote shutdown
conditions
LED Indicators
7 front panel LEDs indicate line power availability, AC to DC conversion, battery mode operation, inverter mode, eco
mode operation, bypass mode operation and AC output status
SURGE / NOISE SUPPRESSION
UPS AC Suppression Joule Rating
570
UPS AC Suppression Response
Time
Instantaneous
UPS Dataline Suppression
1 line TEL/DSL (1 in / 1 out); 10/100Base T Ethernet
EMI / RFI AC Noise Suppression
Yes
PHYSICAL
Primary Form Factor
Rackmount
Rack Height
2U
Cooling Method
Fan
4/7
Cleveland, OH 44122
United States
Included Mounting Accessory
Description
Included 4POSTRAILKIT mounting bracket enables installation in 4 post racks from 20.5 to 36 inches (521 to
914mm)
Installation Form Factors Supported
with Included Accessories
4 post 19 inch rackmount
with Optional Accessories
2 post rackmount ( 2POSTRMKITWM ); 2-4 post front rail
rackmount ( UPSHDEARKIT ); 4 post rackmount short-depth ( 4POSTRAILKITWM ); Tower ( 29USTAND ); Wallmount ( 2POSTRMKITWM )
Minimum Required Rack Depth (cm)
55.88
(inches)
22
Minimum Required Rack Depth with
External Battery Pack (cm)
66
External Battery Pack (in.)
26
without External Battery Pack (cm)
61
without External Battery Pack (in.)
24
Optional Mounting Accessory Notes
Optional 2-9USTAND enables upright tower UPS placement; 2POSTRMKITWM enables wall-mount and 2-post rackmount installation;
4POSTRAILKITWM enables installation in 4-post short-depth
racks from 14.5 to 23.5 inches (368 to 597mm); UPSHDEARKIT enables installation in 2 or 4-post
racks using front vertical rails only, without rear support
Primary UPS Depth (mm)
483
Primary UPS Height (mm)
89
Primary UPS Width (mm)
445
Shipping Dimensions (hwd / in.)
9.10 x 23.20 x 19.30
Shipping Dimensions (hwd / cm)
23.11 x 58.93 x 49.02
Shipping Weight (lbs.)
64.25
Shipping Weight (kg)
29.14
UPS Housing Material
Steel
UPS Power Module Dimensions
(hwd, cm)
8.89 x 44.45 x 48.26
(hwd, in.)
3.5 x 17.5 x 19
UPS Power Module Weight (kg)
22.00
UPS Power Module Weight (lbs.)
48.5
Unit Weight (lbs.)
48.500
Unit Weight (kg)
22.00
5/7
Cleveland, OH 44122
United States
ENVIRONMENTAL
Operating Temperature Range
32° to 104°F (0° to 40°C)
Storage Temperature Range
5° to 122°F (-15° to 50°C)
Relative Humidity
0 to 95%, non-condensing
AC Mode BTU / Hr. (Full Load)
684
AC Economy Mode BTU / Hr. (Full
Load)
392
Battery Mode BTU / Hr. (Full Load)
1085
AC Economy Mode Efficiency Rating
(100% Load)
94%
Audible Noise
57 dBA at 1m front side
Operating Elevation (m)
Up to 3000m
COMMUNICATIONS
Network Management Cards
SNMPWEBCARD; TLNETCARD ; WEBCARDLX ; MODBUSCARD ; RELAYIOCARD
Network Monitoring Port Description
Supports detailed monitoring of UPS and site power conditions; DB9 port supports RS232 and contact closure
communications
PowerAlert Software
For local monitoring via the UPS’s built-in communication ports, download PowerAlert software at
https://tripplite.eaton.com/products/power-alert
Communications Cable
USB and DB9 cabling included
WatchDog Compatibility
Supports Watchdog application, OS and hard-reboot restart options for remote applications
Description
Network management card optional
Communications Interface
Contact closure; DB9 Serial; EPO (emergency power off); Slot for SNMP/Web interface; USB (HID enabled)
LINE / BATTERY TRANSFER
Transfer Time
Zero (0 milliseconds) in double-conversion mode; 4 milliseconds economy mode
Low Voltage Transfer to Battery
Power (Setpoint)
100V at full load (90V full load at 100V nominal setting); 70V at 70% load; 55V at 33% load
High Voltage Transfer to Battery
Power (Setpoint)
150
FEATURES & SPECIFICATIONS
Cold Start (Startup in Battery Mode
During a Power Failure)
Cold-start operation supported
High Availability UPS Features
Auto Probe Monitoring and Reboot (requires WEBCARDLX); Automatic inverter bypass; Hot swappable batteries;
Remote management; Surge/noise protection; Zero transfer time
Green Energy-Saving Features
High efficiency economy mode operation; Individually controllable load banks; Schedulable daily hours of economy
mode operation
6/7
Cleveland, OH 44122
United States
STANDARDS & COMPLIANCE
Product Certifications
CSA (Canada); UL 1778
Product Compliance
RoHS; ENERGY STAR Qualified; FCC Part 15 Class A (USA)
WARRANTY & SUPPORT
Product Warranty Period
(Worldwide)
2-year limited warranty
Connected Equipment Insurance
(U.S., Canada & Puerto Rico)
$250,000 Ultimate Lifetime
Insurance
© 2023 Eaton. All Rights Reserved.
Eaton is a registered trademark. All other trademarks
are the property of their respective owners.
7/7
